Bobby, Just saw your post on the sprinkler forum, basically you are right, do NOT delete sprinkler protection from a pool area. There is frequently a large amount of plastics and combustibles stored around pool areas with little or no adult supervision of the working crew.
Plastic pipe is perfect for this type of installation, see page 11 of this website: http://www.harvelsprinklerpipe.com/design_installation/pdf/installation-instructions.pdf You also need to specify a Teflon coated sprinkler heads, the chlorine used in pools causes corrosion to unprotected brass, which will require replacement in a few years. Use stainless steel ATR and hangers as well. Sounds like the local AHJ hasn't seen a fire extend from the pool area in to a hotel or school, look around on the web there are photos and reports available. Hope this might help. Yours truly, Captain Frank J. Herrick City Of Leawood Fire Department 14801 Mission Road Leawood, Ks. 66224-9560 Office: 913.681.6788 x 26 Fax: 913.681.2399 Fire Sprinklers Save Lives, Property, the Environment, and Water - Protect what you value most! -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110909/ccd5d4ed/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum