-----Original Message----- From: BF Blake
Sent: Friday, September 06, 2013 2:13 PM
To: [email protected]
Subject: RE: Central Recall

Chris,

No, all of the heads have NOT been replaced. My last call with the VRP office (now closed) was 10M heads out of the 35M were not replaced - that was several years ago.

But, having worked as a sprinkler service manager for SimplexGrinnell and several other fire sprinkler companies that have done inspections work I know for a fact that o-ring and Omega heads are still frequently found in the field and owners have been interviewed to determine if claim forms were executed or not.

The reasons for this are:

1. Non-Tyco ITM firms generally did NOT get paid to do the site surveys. Owners didn't have time, knowledge, skill or energy to fill out the claim forms. 2. A small number of ITM companies charged clients to conduct the field surveys and fill out the paperwork for the owners, but most ITM firms did not do this. The forms didn't get filled out and didn't get turned in. 3. The recalls were addressed under an Annex (A4.1.4) in NFPA 25 and not in the required section of 25. As a result, except with limited exception and a few AHJs (notably Alexandria VA) no AHJs required their replacement. 4. The Omegas, in particular, were in residential apartments where individual fire sprinkler head inspections were not and are not generally enforced, lots and lots of locked doors. Some AHJs, most notably, Florida, have and DO require individual head inspections per NFPA 25, most jurisdictions do not. With limited access or a "Barrier" to access these heads didn't get documented.

There are thousands and thousands of recalls in the field. Reagan International Airport DC is one high profile location where they exist. I see them all of the time in my travels.

Byron

(I now work for Tyco Fire Protection Products as a Territory Manager - Fixed Systems - Americas) - but previously I served as an inspection/service manager with SimplexGrinnell in CT and Montana/Wyoming. I also worked for several smaller firms in Colorado and Maryland and worked for Wayne Automatic in Florida.)

From: [email protected]
To: [email protected]
Date: Fri, 6 Sep 2013 15:45:44 -0500
Subject: Central Recall

Yes, I know this expired back in '07. Or at least Tyco paying for replacements expired, the heads are still recalled. The question is have all submitted claims been replaced? I know there are a lot of them still out there that were never claimed under the recall.

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]<mailto:[email protected]>
www.burnsmcd.com<http://www.burnsmcd.com/>

Proud to be one of FORTUNE's 100 Best Companies to Work For
*Registered in: MN




_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to