Interesting since NFPA 25 does not require the inspector to identify recalled 
products.  It's the responsibility of the owner.  As such, either the 
requirement to look for them was in the contract or Walgreens was a big 
customer for this guy so they "voluntarily" bit the bullet.

Roland




On Sep 6, 2013, at 2:34 PM, [email protected] wrote:

> 
> Chris, et al:
> 
> 
> Thank you for that Code update, Chris...Here's one for you: Some years back 
> (when we held the Walgreen's sprinkler inspection account for NM), I attended 
> a Walgreen's annual Corporate LP/FP meeting at their headquarters in 
> Deerfield. "Recalls" were on the docket. I was told at that meeting that one 
> of the contractors (present) for other States did NOT report recalls in one 
> (or more) Walgreen's Stores in that State (Eastern U.S.). The "free" 
> replacement period had passed. That sprinkler contractor ended up paying - 
> out of pocket - for the replacements (at Walgreen's "urging" I am sure).
> 
> 
> 
> Just food for thought?
> 
> 
> Regards-
> 
> 
> Jerry
> [email protected]
> Santa Fe, New Mexico USA
> (800) 503.1961  nationwide
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> 
> -----Original Message-----
> From: Cahill, Christopher <[email protected]>
> To: sprinklerforum <[email protected]>
> Sent: Fri, Sep 6, 2013 3:14 pm
> Subject: RE: Central Recall Comments
> 
> 
> It was voluntary in regards to the Consumer Product Safety Commission.  CPSC 
> has 
> never issued a mandatory recall, they are all voluntary technically.  That 
> aside 
> it wasn't voluntary any more once the IFC kicked in 2006.  If you are under 
> that 
> or newer they are required to be replaced.  If you find one today it must be 
> replaced under IFC 901.9 ('06, '09, '12 (.10))
> 
> I'm trying to figure out if Tyco finished their work they were responsible 
> for. 
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer 
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]
> www.burnsmcd.com
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For
> *Registered in: MN
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] 
> On Behalf Of [email protected]
> Sent: Friday, September 06, 2013 4:00 PM
> To: [email protected]
> Subject: Re: Central Recall Comments
> 
> Chris, et al:
> 
> 
> Regarding the "recall" - I seem to 'recall' (?) (and still hear) the term 
> "voluntary" used before the (TYCO/CENTRAL GB) recall...And, yes, I suspect 
> there 
> are probably (still) at least a few million of those sprinklers "in service".
> 
> 
> 
> Regards to all-
> 
> 
> 
> Jerry
> 
> 
> [email protected]
> 
> 
> Jerry D. Watts, SFPE
> President & Co-Founder
> ACCENT FIRE ENGINEERING INT'L. Ltd.*
> Santa Fe, New Mexico USA
> (800) 503.1961  nationwide
> 
> 
> *Licensed Fire Engineers-Architects/Inspectors/Investigators: AZ  CA  CO  NM  
> NV  
> NY  TX  UT  KS MD  MS
> 
> 
> 
> 
> -----Original Message-----
> From: Cahill, Christopher <[email protected]>
> To: sprinklerforum <[email protected]>
> Sent: Fri, Sep 6, 2013 2:45 pm
> Subject: Central Recall
> 
> 
> Yes, I know this expired back in '07.  Or at least Tyco paying for 
> replacements 
> expired, the heads are still recalled.  The question is have all submitted 
> claims been replaced?  I know there are a lot of them still out there that 
> were 
> never claimed under the recall.
> 
> Chris Cahill, PE*
> Senior Fire Protection Engineer
> Burns & McDonnell
> 8201 Norman Center Drive
> Bloomington, MN 55437
> Phone:  952.656.3652
> Fax:  952.229.2923
> [email protected]<mailto:[email protected]>
> www.burnsmcd.com<http://www.burnsmcd.com/>
> 
> Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN
> 
> 
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org