Good point Duane, zoned evacuation is often the case for I-2 occupancies. 
Should be spelled out somewhere in the contract docs. 

Justin Reid

Sent from my iPhone

> On Apr 13, 2016, at 6:01 PM, Duane Johnson <[email protected]> 
> wrote:
> 
> Don't forget the other half of the comment...evacuation. If the egress plan 
> includes zoned evacuation, in lieu of general building evacuation, then the 
> flow switch used to move folks from one smoke compartment to the other will 
> need to align with the compartments and the voice evacuation messages. If 
> egress plans tell you to move across a fire/smoke barrier but the fire alarm 
> message is playing or partially playing in that zone, then you have a 
> problem. Sections 9.6.3 and 9.6.7 in NFPA 101 provide some direction. However 
> all of this is a design choice and process that must be coordinated during 
> the design development phase, not during shop drawing development.
> 
> Forward the comment to the AE for resolution. 
> 
> Duane Johnson 
> Strickland Fire Protection
> Sent from my iPhone
> 
>> On Apr 13, 2016, at 8:52 PM, Sprinkler <[email protected]> wrote:
>> 
>> Some people have already hit the nail on the head. If the smoke control 
>> system sequence of operations matrix requires the fire sprinklers to 
>> initiate automatic control, then they have to be zoned per the smoke zones 
>> (CBC 909.12.3, 2013 edition, check yours to make sure it is not a California 
>> thing). Automatic control for smoke control is for pressurization system 
>> (supply or exhaust). Is it possible the plan checkers "evacuation" comment 
>> is maybe smoke evacuation? 
>> 
>> The reason they must be zoned is because certain dampers and fans have to 
>> activate based on where the fire is. If there is not 100% smoke detector 
>> coverage, then the only thing to locate the fire based on a zone is the flow 
>> switch on the riser. 
>> 
>> IF there is 100% smoke detector coverage you could ask that the smoke 
>> control initiation be based on that. 
>> 
>> If the smoke control method for your building is passive, 909.12.2.2, 
>> (passive basically being only dampers) then those dampers can be activated 
>> by local smokes to each damper which may already be provided. 
>> 
>> Check your contract docs to see if there is a Smoke Control Rational 
>> Analysis Report. If there is there is likely a sequence of operations matrix 
>> and smoke zones shown in the document. It might say smokes initiate or it 
>> might say sprinklers initiate. Check it out. 
>> 
>> If there is nothing in your contract docs that states the smoke zones or any 
>> other indication of "automatic" versus "passive" system...then initiate your 
>> change order accordingly. 
>> 
>> Hope this helps. 
>> 
>> Justin Reid
>> 
>> 
>> 
>> 
>> Sent from my iPhone
>> 
>>> On Apr 13, 2016, at 4:57 PM, Travis Mack, SET <[email protected]> wrote:
>>> 
>>> It doesn't.  I was just hoping there wasn't some strange reference in the 
>>> I-codes or NFPA 101 that requires the smoke, alarm and sprinkler zones to 
>>> follow the same footprint in an I-2 occupancy. This project currently has 3 
>>> risers.  It would go to 8 if we have to follow smoke zones as there are 8 
>>> smoke compartments.  Also, this was originally a loop system.  That would 
>>> break so all of the pipe sizing would go up.  It would just be a real 
>>> nightmare to adjust for something that I am hoping is not an obscure 
>>> reference.
>>> 
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> 2508 E Lodgepole Drive
>>> Gilbert, AZ 85298
>>> 480-505-9271
>>> fax: 866-430-6107
>>> email:[email protected]
>>> 
>>> http://www.mfpdesign.com
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>> LinkedIn: https://www.linkedin.com/in/travismack
>>> 
>>>> On 4/13/2016 4:46 PM, Matthew J Willis wrote:
>>>> Ok, first thing in the am, I am re reading 13 on where any of this applies 
>>>> to a sprinkler drawing....
>>>> 
>>>> 
>>>> 
>>>> Sent from my Verizon Wireless 4G LTE smartphone
>>>> 
>>>> 
>>>> -------- Original message --------
>>>> From: Brad Casterline <[email protected]>
>>>> Date: 04/13/2016 5:44 PM (GMT-07:00)
>>>> To: [email protected]
>>>> Subject: Re: Fire Sprinkler Plan to Match Evacuation Plan??
>>>> 
>>>> Just a heads-up Travis,
>>>> It might go deeper than matching footprints- that is rarely a problem.
>>>> A problem would be if the exhaust rate sizer used QR, 165F, at max 225
>>>> S.F., but you, being a 13 aficionado, installed QR, 200F, at 324 S.F.
>>>> 
>>>> In a ~16 ft ceiling the exhaust rate would fall about 20,000 CFM short...
>>>> 
>>>> ballpark figures, of course.
>>>> 
>>>> Brad
>>>> On Apr 13, 2016 5:42 PM, "Roland Huggins" <[email protected]>
>>>> wrote:
>>>> 
>>>>> There is a section in the IBC that tries to address the fact that fire
>>>>> alarm zones and sprinklers zones are different sizes and that the larger
>>>>> sprinkler zone is NOT limited to the size of the fire alarm zone. See
>>>>> section 907.6.4
>>>>> 
>>>>> Roland
>>>>> 
>>>>> 
>>>>> Roland Huggins, PE - VP Engineering
>>>>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>>>>> Dallas, TX
>>>>> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>>>>> 
>>>>> 
>>>>> 
>>>>>>> On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]>
>>>>>> wrote:
>>>>>> I have a reviewer stating that the fire sprinkler plan has to match the
>>>>> evacuation plan and the smoke zones of the fire alarm plan. This is an I-2
>>>>> Occupancy.  Has anyone ever come across this?  After 3 weeks in plan
>>>>> review, he kicked it back saying he can't review until we provide this
>>>>> information. It is the first time I have ever heard of this.
>>>>>> Travis Mack, SET
>>>>>> MFP Design, LLC
>>>>>> 2508 E Lodgepole Drive
>>>>>> Gilbert, AZ 85298
>>>>>> 480-505-9271
>>>>>> fax: 866-430-6107
>>>>>> email:[email protected]
>>>>>> 
>>>>>> http://www.mfpdesign.com
>>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>>> LinkedIn: https://www.linkedin.com/in/travismack
>>>>>> 
>>>>>> 
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> 
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org