Did a job once where is was claimed that a flow switch activation dictated 
which smoke zones would operate. Always figured it was crap but we got a change 
order to re-zone every time the smoke zones changed so we didn't argue.
Fletch


Sent from my iPhone

> On Apr 13, 2016, at 7:57 PM, Travis Mack, SET <[email protected]> wrote:
> 
> It doesn't.  I was just hoping there wasn't some strange reference in the 
> I-codes or NFPA 101 that requires the smoke, alarm and sprinkler zones to 
> follow the same footprint in an I-2 occupancy. This project currently has 3 
> risers.  It would go to 8 if we have to follow smoke zones as there are 8 
> smoke compartments.  Also, this was originally a loop system.  That would 
> break so all of the pipe sizing would go up.  It would just be a real 
> nightmare to adjust for something that I am hoping is not an obscure 
> reference.
> 
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> 480-505-9271
> fax: 866-430-6107
> email:[email protected]
> 
> http://www.mfpdesign.com
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to us via: https://www.hightail.com/u/MFPDesign
> LinkedIn: https://www.linkedin.com/in/travismack
> 
>> On 4/13/2016 4:46 PM, Matthew J Willis wrote:
>> Ok, first thing in the am, I am re reading 13 on where any of this applies 
>> to a sprinkler drawing....
>> 
>> 
>> 
>> Sent from my Verizon Wireless 4G LTE smartphone
>> 
>> 
>> -------- Original message --------
>> From: Brad Casterline <[email protected]>
>> Date: 04/13/2016 5:44 PM (GMT-07:00)
>> To: [email protected]
>> Subject: Re: Fire Sprinkler Plan to Match Evacuation Plan??
>> 
>> Just a heads-up Travis,
>> It might go deeper than matching footprints- that is rarely a problem.
>> A problem would be if the exhaust rate sizer used QR, 165F, at max 225
>> S.F., but you, being a 13 aficionado, installed QR, 200F, at 324 S.F.
>> 
>> In a ~16 ft ceiling the exhaust rate would fall about 20,000 CFM short...
>> 
>> ballpark figures, of course.
>> 
>> Brad
>> On Apr 13, 2016 5:42 PM, "Roland Huggins" <[email protected]>
>> wrote:
>> 
>>> There is a section in the IBC that tries to address the fact that fire
>>> alarm zones and sprinklers zones are different sizes and that the larger
>>> sprinkler zone is NOT limited to the size of the fire alarm zone. See
>>> section 907.6.4
>>> 
>>> Roland
>>> 
>>> 
>>> Roland Huggins, PE - VP Engineering
>>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>>> Dallas, TX
>>> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>>> 
>>> 
>>> 
>>>>> On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]>
>>>> wrote:
>>>> I have a reviewer stating that the fire sprinkler plan has to match the
>>> evacuation plan and the smoke zones of the fire alarm plan. This is an I-2
>>> Occupancy.  Has anyone ever come across this?  After 3 weeks in plan
>>> review, he kicked it back saying he can't review until we provide this
>>> information. It is the first time I have ever heard of this.
>>>> Travis Mack, SET
>>>> MFP Design, LLC
>>>> 2508 E Lodgepole Drive
>>>> Gilbert, AZ 85298
>>>> 480-505-9271
>>>> fax: 866-430-6107
>>>> email:[email protected]
>>>> 
>>>> http://www.mfpdesign.com
>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>> LinkedIn: https://www.linkedin.com/in/travismack
>>>> 
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> 
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to