That at least makes a ton of sense. 

Travis Mack, SET
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Apr 13, 2016, at 5:51 PM, Sprinkler <[email protected]> wrote:
> 
> Some people have already hit the nail on the head. If the smoke control 
> system sequence of operations matrix requires the fire sprinklers to initiate 
> automatic control, then they have to be zoned per the smoke zones (CBC 
> 909.12.3, 2013 edition, check yours to make sure it is not a California 
> thing). Automatic control for smoke control is for pressurization system 
> (supply or exhaust). Is it possible the plan checkers "evacuation" comment is 
> maybe smoke evacuation? 
> 
> The reason they must be zoned is because certain dampers and fans have to 
> activate based on where the fire is. If there is not 100% smoke detector 
> coverage, then the only thing to locate the fire based on a zone is the flow 
> switch on the riser. 
> 
> IF there is 100% smoke detector coverage you could ask that the smoke control 
> initiation be based on that. 
> 
> If the smoke control method for your building is passive, 909.12.2.2, 
> (passive basically being only dampers) then those dampers can be activated by 
> local smokes to each damper which may already be provided. 
> 
> Check your contract docs to see if there is a Smoke Control Rational Analysis 
> Report. If there is there is likely a sequence of operations matrix and smoke 
> zones shown in the document. It might say smokes initiate or it might say 
> sprinklers initiate. Check it out. 
> 
> If there is nothing in your contract docs that states the smoke zones or any 
> other indication of "automatic" versus "passive" system...then initiate your 
> change order accordingly. 
> 
> Hope this helps. 
> 
> Justin Reid
> 
> 
> 
> 
> Sent from my iPhone
> 
>> On Apr 13, 2016, at 4:57 PM, Travis Mack, SET <[email protected]> wrote:
>> 
>> It doesn't.  I was just hoping there wasn't some strange reference in the 
>> I-codes or NFPA 101 that requires the smoke, alarm and sprinkler zones to 
>> follow the same footprint in an I-2 occupancy. This project currently has 3 
>> risers.  It would go to 8 if we have to follow smoke zones as there are 8 
>> smoke compartments.  Also, this was originally a loop system.  That would 
>> break so all of the pipe sizing would go up.  It would just be a real 
>> nightmare to adjust for something that I am hoping is not an obscure 
>> reference.
>> 
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> email:[email protected]
>> 
>> http://www.mfpdesign.com
>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> LinkedIn: https://www.linkedin.com/in/travismack
>> 
>>> On 4/13/2016 4:46 PM, Matthew J Willis wrote:
>>> Ok, first thing in the am, I am re reading 13 on where any of this applies 
>>> to a sprinkler drawing....
>>> 
>>> 
>>> 
>>> Sent from my Verizon Wireless 4G LTE smartphone
>>> 
>>> 
>>> -------- Original message --------
>>> From: Brad Casterline <[email protected]>
>>> Date: 04/13/2016 5:44 PM (GMT-07:00)
>>> To: [email protected]
>>> Subject: Re: Fire Sprinkler Plan to Match Evacuation Plan??
>>> 
>>> Just a heads-up Travis,
>>> It might go deeper than matching footprints- that is rarely a problem.
>>> A problem would be if the exhaust rate sizer used QR, 165F, at max 225
>>> S.F., but you, being a 13 aficionado, installed QR, 200F, at 324 S.F.
>>> 
>>> In a ~16 ft ceiling the exhaust rate would fall about 20,000 CFM short...
>>> 
>>> ballpark figures, of course.
>>> 
>>> Brad
>>> On Apr 13, 2016 5:42 PM, "Roland Huggins" <[email protected]>
>>> wrote:
>>> 
>>>> There is a section in the IBC that tries to address the fact that fire
>>>> alarm zones and sprinklers zones are different sizes and that the larger
>>>> sprinkler zone is NOT limited to the size of the fire alarm zone. See
>>>> section 907.6.4
>>>> 
>>>> Roland
>>>> 
>>>> 
>>>> Roland Huggins, PE - VP Engineering
>>>> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
>>>> Dallas, TX
>>>> http://www.firesprinkler.org <http://www.firesprinkler.org/>
>>>> 
>>>> 
>>>> 
>>>>>> On Apr 13, 2016, at 11:20 AM, Travis Mack, SET <[email protected]>
>>>>> wrote:
>>>>> I have a reviewer stating that the fire sprinkler plan has to match the
>>>> evacuation plan and the smoke zones of the fire alarm plan. This is an I-2
>>>> Occupancy.  Has anyone ever come across this?  After 3 weeks in plan
>>>> review, he kicked it back saying he can't review until we provide this
>>>> information. It is the first time I have ever heard of this.
>>>>> Travis Mack, SET
>>>>> MFP Design, LLC
>>>>> 2508 E Lodgepole Drive
>>>>> Gilbert, AZ 85298
>>>>> 480-505-9271
>>>>> fax: 866-430-6107
>>>>> email:[email protected]
>>>>> 
>>>>> http://www.mfpdesign.com
>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>>>>> LinkedIn: https://www.linkedin.com/in/travismack
>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> 
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to