Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL listed assembly) and a dropped acoustical grid ceiling still require sprinklers? Would NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers from such a space?
8.15.1.2.10 Concealed spaces where rigid materials are used and the exposed surfaces have a flame spread index of 25 or less, and the materials have been demonstrated not to propagate fire more than 10.5 ft (3.2 m) when tested in accordance with ASTM E 84, Standard Test Method of Surface Burning Characteristics of Building Materials, or ANSI/UL 723, Standard for Test for Surface Burning Characteristics of Building Materials, extended for an additional 20 minutes in the form in which they are installed, shall not require sprinkler protection.