Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL
listed assembly) and a dropped acoustical grid ceiling still require
sprinklers? Would NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers
from such a space?


8.15.1.2.10     Concealed spaces where rigid materials are used and the
exposed surfaces have a flame spread index of 25 or less, and the materials
have been demonstrated not to propagate fire more than 10.5 ft (3.2 m) when
tested in accordance with ASTM E 84, Standard Test Method of Surface
Burning Characteristics of Building Materials, or ANSI/UL 723, Standard for
Test for Surface Burning Characteristics of Building Materials, extended
for an additional 20 minutes in the form in which they are installed, shall
not require sprinkler protection.