Obviously I'm talking about the concealed space above the dropped ceiling.

On Thu, Mar 16, 2017 at 1:57 PM, <[email protected]> wrote:

> A corridor is not a concealed space.  Is the rest of the area around the
> corridor sprinklered?  What does this corridor serve?  Is it for egress?
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540 <(864)%20920-7540>
>
> Fax - 864.920.7129 <(864)%20920-7129>
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:[email protected].
> org] *On Behalf Of *Mick Dugal
> *Sent:* Thursday, March 16, 2017 4:42 PM
> *To:* [email protected]
> *Subject:* Concealed Combustible Spaces with Gyp Bd? [EXTERNAL]
>
>
>
> Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL
> listed assembly) and a dropped acoustical grid ceiling still require
> sprinklers? Would NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers
> from such a space?
>
>
>
>
>
> 8.15.1.2.10     Concealed spaces where rigid materials are used and the
> exposed surfaces have a flame spread index of 25 or less, and the materials
> have been demonstrated not to propagate fire more than 10.5 ft (3.2 m) when
> tested in accordance with ASTM E 84, Standard Test Method of Surface
> Burning Characteristics of Building Materials, or ANSI/UL 723, Standard for
> Test for Surface Burning Characteristics of Building Materials, extended
> for an additional 20 minutes in the form in which they are installed, shall
> not require sprinkler protection.
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.
> org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to