If all of the exposed surfaces of the concealed space are covered with 
sheetrock, then they are typically excluded from what I have seen.

Matt

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mick Dugal
Sent: Monday, March 20, 2017 11:31 AM
To: [email protected]
Subject: Re: Concealed Combustible Spaces with Gyp Bd?

Anyone have any input?


On Thu, Mar 16, 2017 at 4:54 PM, rongreenman . 
<[email protected]<mailto:[email protected]>> wrote:
Is it that obvious?


On Thu, Mar 16, 2017 at 2:25 PM, Mick Dugal 
<[email protected]<mailto:[email protected]>> wrote:
Obviously I'm talking about the concealed space above the dropped ceiling.


On Thu, Mar 16, 2017 at 1:57 PM, 
<[email protected]<mailto:[email protected]>> wrote:
A corridor is not a concealed space.  Is the rest of the area around the 
corridor sprinklered?  What does this corridor serve?  Is it for egress?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:(864)%20920-7540>
Fax - 864.920.7129<tel:(864)%20920-7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Mick Dugal
Sent: Thursday, March 16, 2017 4:42 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Concealed Combustible Spaces with Gyp Bd? [EXTERNAL]

Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL listed 
assembly) and a dropped acoustical grid ceiling still require sprinklers? Would 
NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers from such a space?


8.15.1.2.10     Concealed spaces where rigid materials are used and the exposed 
surfaces have a flame spread index of 25 or less, and the materials have been 
demonstrated not to propagate fire more than 10.5 ft (3.2 m) when tested in 
accordance with ASTM E 84, Standard Test Method of Surface Burning 
Characteristics of Building Materials, or ANSI/UL 723, Standard for Test for 
Surface Burning Characteristics of Building Materials, extended for an 
additional 20 minutes in the form in which they are installed, shall not 
require sprinkler protection.



_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org



--
Ron Greenman

[email protected]<mailto:[email protected]>

253.576.9700<tel:(253)%20576-9700>

The Universe is monstrously indifferent to the presence of man. -Werner Herzog, 
screenwriter, film director, author, actor and opera director (1942-)

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to