A corridor is not a concealed space.  Is the rest of the area around the 
corridor sprinklered?  What does this corridor serve?  Is it for egress?


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mick Dugal
Sent: Thursday, March 16, 2017 4:42 PM
To: [email protected]
Subject: Concealed Combustible Spaces with Gyp Bd? [EXTERNAL]

Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL listed 
assembly) and a dropped acoustical grid ceiling still require sprinklers? Would 
NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers from such a space?


8.15.1.2.10     Concealed spaces where rigid materials are used and the exposed 
surfaces have a flame spread index of 25 or less, and the materials have been 
demonstrated not to propagate fire more than 10.5 ft (3.2 m) when tested in 
accordance with ASTM E 84, Standard Test Method of Surface Burning 
Characteristics of Building Materials, or ANSI/UL 723, Standard for Test for 
Surface Burning Characteristics of Building Materials, extended for an 
additional 20 minutes in the form in which they are installed, shall not 
require sprinkler protection.