Start with the opening paragraph 8.15.1.1 where it states - EXPOSED combustible 
construction shall be protected


Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Mar 16, 2017, at 1:42 PM, Mick Dugal <[email protected]> wrote:
> 
> Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL listed 
> assembly) and a dropped acoustical grid ceiling still require sprinklers? 
> Would NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers from such a 
> space?
> 
> 
> 8.15.1.2.10     Concealed spaces where rigid materials are used and the 
> exposed surfaces have a flame spread index of 25 or less, and the materials 
> have been demonstrated not to propagate fire more than 10.5 ft (3.2 m) when 
> tested in accordance with ASTM E 84, Standard Test Method of Surface Burning 
> Characteristics of Building Materials, or ANSI/UL 723, Standard for Test for 
> Surface Burning Characteristics of Building Materials, extended for an 
> additional 20 minutes in the form in which they are installed, shall not 
> require sprinkler protection.
> 
> 