I don't know. If someone drove the little submarine into the joust bay
there'd be exposed wood and some could die.


On Mon, Mar 20, 2017 at 11:03 AM Parsley Consulting <
[email protected]> wrote:

> According to one source
> <http://sfm.dps.louisiana.gov/doc_flamespread.html> I looked over, Gypsum
> wallboard has a flame spread rating of 10-15, and gypsum sheathing has a
> flame spread rating of 15-20, both of which are below the magic NFPA 13
> number of 25.  According to a tech data sheet from Dunn Edwards paints
> <https://de-production-media.s3.amazonaws.com/uploads/techinal_bulletins/54ac433b6137650002090000/TechSheet_flameSpreadRatings.pdf>,
> gypsum board is rated as a Class A rated material which would have a flame
> spread of from 0 - 25, so it apparently doesn't exceed the maximum allowed
> by -13.
>
> *Ken Wagoner, SET Parsley Consulting*
>
>
>
> * 350 West 9th Avenue, Suite 206 Escondido, California 92025 Phone
> 760-745-6181 Visit our website <http://www.parsleyconsulting.com/> *
> On 03/20/2017 10:37 AM, Mick Dugal wrote:
>
> Right, but then it directs you to the exceptions:
> 8.15.1.2.1*    Concealed spaces of noncombustible and limited-combustible
> construction with minimal combustible loading having no access shall not
> require sprinkler protection
>
> I would think the above code applies but does adding 2 layers of 5/8"
> drywall make wood framing noncombustible *construction*?
>
> If not, then I wonder about:
>
> 8.15.1.2.10     Concealed spaces where rigid materials are used and the
> exposed surfaces have a flame spread index of 25 or less, and the materials
> have been demonstrated not
> to propagate fire more than 10.5 ft (3.2 m) when tested in accordance with
> ASTM E 84, Standard Test Method of Surface Burning Characteristics of
> Building Materials, or ANSI/UL
> 723, Standard for Test for Surface Burning Characteristics of Building
> Materials, extended for an additional 20 minutes in the form in which they
> are installed, shall not require
> sprinkler protection.
>
>
> On Mon, Mar 20, 2017 at 10:32 AM, Roland Huggins <
> [email protected]> wrote:
>
> Start with the opening paragraph 8.15.1.1 where it states - EXPOSED
> combustible construction shall be protected
>
>
> Roland Huggins, PE - Senior VP Engineering
>
> American Fire Sprinkler Assn.
>
> Dallas, TX
>
> http://www.firesprinkler.org
>
>
> Fire Sprinklers Saves Lives
>
>
>
>
> On Mar 16, 2017, at 1:42 PM, Mick Dugal <[email protected]>
> wrote:
>
> Would a wood framed corridor rocked with 2 layers of 5/8" gyp bd (a UL
> listed assembly) and a dropped acoustical grid ceiling still require
> sprinklers? Would NFPA 13 :8.15.1.2.10 permit the exclusion of sprinklers
> from such a space?
>
>
> 8.15.1.2.10     Concealed spaces where rigid materials are used and the
> exposed surfaces have a flame spread index of 25 or less, and the materials
> have been demonstrated not to propagate fire more than 10.5 ft (3.2 m) when
> tested in accordance with ASTM E 84, Standard Test Method of Surface
> Burning Characteristics of Building Materials, or ANSI/UL 723, Standard for
> Test for Surface Burning Characteristics of Building Materials, extended
> for an additional 20 minutes in the form in which they are installed, shall
> not require sprinkler protection.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
> _______________________________________________
> Sprinklerforum mailing 
> [email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
-- 
Sent from Gmail Mobile