You say that, but we've had a fire marshal in the past try and require a 
control valve and drain on every branch line in a retail building, so you could 
isolate only the area requiring work.   
  

  
  

  
  
>   
> On Feb 2, 2018 at 3:12 PM,  <Steve Leyton 
> (mailto:[email protected])>  wrote:
>   
>   
>           
>   
>
>  Why not proposed valves every 50’ or so to be sure that you can isolate down 
> to the smallest section(s) of pipe for potential interruptions?      (SMH)
>
>   
>
>     
>
>   
>
>  If the intent is to work on the feed pipe then how far down the line would 
> you have to put the FDC to arrange it so it wouldn’t be interrupted?      
> Seems to me the AHJ is wishfully trying to design for a scenario that has an 
> infinitesimal chance of occurring in the first place and that can’t be 
> “pumped around” in any case.      Because such as scenario isn’t reasonably 
> foreseeable, the standard (14) is mute in that regard.
>
>   
>
>     
>
>   
>
>  SL
>
>   
>
>     
>
>   
>
>     
>
>   
>
>     
>
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> Dewayne Martinez
>   Sent:  Friday, February 02, 2018 11:42 AM
>   To:  [email protected]
>   Subject:  RE: FDC  &  Pump
>
>   
>   
>   
>
>   
>
>   
>
>  No,
>
>   
>
>  I have had to put an extra control valve for the standpipe feed at point of 
> connection to the riser manifold in addition to the standpipe isolation 
> valves.    The AHJ’s reasoning was that if work was required on the feed pipe 
> it could be isolated and wouldn’t affect the other systems on the manifold.
>
>   
>
>     
>
>   
>   
>
>  Thank you,
>
>   
>
>  Dewayne Martinez
>
>   
>
>  Fire Protection Design Manager
>
>   
>
>     
>
>   
>
>  TOTALMechanical
>
>   
>
>  BuildingIntegrity
>
>   
>
>   
> W234 N2830 Paul Rd.
>  Pewaukee, WI    53072
>
>   
>
>   [email protected] (mailto:[email protected])
>
>   
>
>  Ph:    262-522-7110
>
>   
>
>  Cell: 414-406-5208
>
>   
>
>   http://www.total-mechanical.com/   
>
>   
>
>                       
>
>   
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  Steve 
> Leyton
>   Sent:  Friday, February 02, 2018 9:39 AM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  RE: FDC  &  Pump
>
>   
>   
>   
>
>   
>
>   
>
>  What valve are you referring to as “standpipe feed” control?    Are you 
> talking about the isolation valves required in 6.3.2?      If that’s the 
> valve you’re referring to, then no you do not have to pump downstream of that 
> (those) valve(s).
>
>   
>
>     
>
>   
>
>  The foregoing is my opinion only and is not intended to represent the NFPA 
> 14 Technical Committee, nor serve as an interpretation of the standard.
>
>   
>
>     
>
>   
>
>  SL   
>
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  
> Dewayne Martinez
>   Sent:  Friday, February 02, 2018 4:29 AM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  RE: FDC  &  Pump
>
>   
>   
>   
>
>   
>
>   
>
>  Tom,
>
>   
>
>  Are you saying that if I put a control valve for the standpipe feed at the 
> riser manifold and the FDC is connected to the riser manifold that I must 
> also connect the FDC downstream of the standpipe feed control valve?    Is 
> that in 14?    I have had a couple of AHJ’s make me put a control valve in 
> over the years and I didn’t know it was wrong.    I thought it was just like 
> the individual system control valves on the manifold.
>
>   
>   
>
>  Thank you,
>
>   
>
>  Dewayne Martinez
>
>   
>
>  Fire Protection Design Manager
>
>   
>
>     
>
>   
>
>  TOTALMechanical
>
>   
>
>  BuildingIntegrity
>
>   
>
>   
> W234 N2830 Paul Rd.
>  Pewaukee, WI    53072
>
>   
>
>   [email protected] (mailto:[email protected])
>
>   
>
>  Ph:    262-522-7110
>
>   
>
>  Cell: 414-406-5208
>
>   
>
>   http://www.total-mechanical.com/   
>
>   
>
>                       
>
>   
>   
>
>     
>
>   
>   
>   
>
>  From:    Sprinklerforum 
> [mailto:[email protected]]  On Behalf Of  Tom 
> Duross
>   Sent:  Wednesday, January 31, 2018 4:36 PM
>   To:   [email protected] 
> (mailto:[email protected])
>   Subject:  RE: FDC  &  Pump
>
>   
>   
>   
>
>   
>
>   
>
>  What Larry said..
>
>   
>
>  And there can’t be any valves between the FDC and the FDV’s on the standpipe 
> unless you have more than one standpipe and have isolation valves at the base 
> of each standpipe so you can’t take them off the riser manifold, for example.
>
>   
>
>  TD
>
>   
>
>     
>
>   
>
>   
>
>   
>
> The requirement is from NFPA 13, not from NFPA 20. Here is the text from NFPA 
> 13-2013:
>
>   
>
>   
>
>   
>
> 8.17.2.4.8    Fire department connections shall not be connected on the 
> suction side of fire pumps.
>
>   
>
>   
>
>   
>
> Larry Keeping
>
>   
>
>   
>
>   
>
>   
>
>   
>   
>   
>   
>   
>
> I have always installed FDC's on the discharge side of fire pumps.    Looking 
> through 2013 NFPA 20, I don't see anything precluding the instillation   on 
> the supply side.    Is the FDC allowed to be installed on the supply?
>
>   
>   
>   
>
> I have a contractor that has installed the FDC on the supply run-in, instead 
> of stubing up a secondary line from the remote FDC.
>
>   
>   
>   
>
> Thanks,
>
>   
>   
>   
>
> Jamie
>
>   
>   
>   
>   
>   
>  _______________________________________________ Sprinklerforum mailing list 