Just to clarify, in case anyone wasn't aware, the referenced EC storage 
sprinklers, Tyco TY9128 and the Viking V595, are not ESFR sprinklers.
They are CMDA / CMSA standard response.

Larry Keeping

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Nicky Marshall
Sent: February-12-18 2:13 PM
To: [email protected]
Subject: RE: Help Finding ESFR upright greater than K17

Most of the responses do not seem to have answered your question if you are 
specifically looking for an upright ESFR sprinkler.

To my knowledge, the K17 Tyco TY7126 is the biggest upright ESFR unless you go 
Extended Coverage K25: TY9128 and Viking VK595.
If you can go standard response (CMSA) then there are more choices. K17: 
TY7153, TY7151, VK580 and Reliable RA1124.  Then K25 VK598 and Victaulic V4603.


Nicky Marshall
Southern Regional Manager
PROTECH DESIGN LIMITED
Specialist Fire Protection Consultants
Phone: +64 (0)3 579 5577 extn 2  Mobile: +64 (0)21 433 488  Email: 
[email protected]<mailto:[email protected]>  Skype: 
nicky-marshall Web :www.protechdesign.co.nz
Address:105A Alabama Rd, Redwoodtown, Blenheim 7201, NZ Postal: PO Box 4022, 
Redwood Village, Blenheim 7242, NZ

"I always wondered why somebody doesn't do something about that. Then I 
realised I was somebody" Lily Tomlin

From: Jeff Polke [mailto:[email protected]]
Sent: Tuesday, 13 February 2018 5:30 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Help Finding ESFR upright greater than K17

Good morning all.  I am looking for an expert in ESFR sprinkler heads to help 
me find a ESFR upright head with at least a K factor 17(not 16.8).  There does 
not seem to be other companies that make these ESFR other Tyco. Please let me 
know.  Thanks.

Jeffrey Polke
Co-President
[email protected]<mailto:[email protected]>


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to