Bob,

My thought is that it's asking for a way to evaluate the one variable which can't be changed - elevation gain or loss.

Just my opinion,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/> ***
On 01/09/2020 1:41 PM, Bob Knight via Sprinklerforum wrote:

From NFPA 13 (2013 ED), 23.1.3 (37) Relative  elevations  of  sprinklers,  junction  points,  and supply or reference points.

This is probably an obvious question, but not to me.  What is this asking for?

Thank you,

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

FBK-LOGO-EMAIL