On January 14, 2020 at 3:08 PM Steve Leyton via Sprinklerforum <[email protected]> wrote:

My FAVORITE things to put on shop drawings (because it drove our spoiled union fitters CRAZY) was to write GOE or TOE on an over-cut piece of pipe.   If we were in a big hurry and had no real idea of where or how to start resolving an issue, I’d use VIF (verify in field).   That was always good for a phone call …

Steve L.

 

From: Sprinklerforum [mailto:[email protected]] On Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, January 14, 2020 12:03 PM
To: [email protected]
Cc: Kyle.Montgomery; Bruce Verhei
Subject: RE: [EXTERNAL] Re: NFPA 13, 23.1.3 (37)

 

Are you familiar with the term ‘C.O.J.’?

 

Heheheh…

 

Just in case you aren’t, it’s not dirty or anything. It means “cut on job”.

 

-Kyle M

 

From: Sprinklerforum [mailto:[email protected]] On Behalf Of Bruce Verhei via Sprinklerforum
Sent: Monday, January 13, 2020 7:42 PM
To: [email protected]
Cc: Bruce Verhei <[email protected]>
Subject: [EXTERNAL] Re: NFPA 13, 23.1.3 (37)

 

I’ve never drawn up a fab order. I always assumed you’d need this information. Do I get it wrong. 

 

Best.

 

Bruce Verhei 


On Jan 13, 2020, at 06:15, Prahl, Craig/GVL via Sprinklerforum <[email protected]> wrote:

I’m curious why there is any confusion over this?  

 

Example: If you have sprinklers on sprigs and don’t provide any elevation information, the shop drawing reviewer or permit reviewer will have to calculate the fitting takeouts and sprig lengths to be sure your sprinkler is within the allowable dimensions from the deck.  Without piping elevations how will the crew know where the pipe is supposed to be routed so that it doesn’t run into every other system that’s in the same space?

 

When reviewing calculations, having elevations shown on the drawing that correlate to the calcs helps verify that the design depicted on drawings and in the calcs actually match.

 

Dimensions are great too as well as building column lines for reference.  

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | [email protected] | www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum <[email protected]> On Behalf Of Sprinkler Academy - C Bilbo via Sprinklerforum
Sent: Thursday, January 9, 2020 6:10 PM
To: [email protected]; [email protected]
Cc: Sprinkler Academy - C Bilbo <[email protected]>
Subject: [EXTERNAL] Re: NFPA 13, 23.1.3 (37)

 


Bob,
The committee wants to see relative elevation changes.  This helps with lengths of pipe and calcs too.
We use the word relative because it doesn't need to be Above Sea Level.
(But I think you already know this!!)

Cecil




It should be recognized that the above is my opinion as a member of the NFPA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the the NFPA, nor any of their technical committees.

Sincerely,


Cecil Bilbo
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com
[email protected]
??
OUR STUDENTS SAVE LIVES!!


From: Sprinklerforum <[email protected]> on behalf of Bob Knight via Sprinklerforum <[email protected]>
Sent: Thursday, January 9, 2020 3:41:36 PM
To: [email protected] <[email protected]>
Cc: Bob Knight <[email protected]>
Subject: NFPA 13, 23.1.3 (37)

 

From NFPA 13 (2013 ED), 23.1.3 (37)  Relative  elevations  of  sprinklers,  junction  points,  and supply or reference points.

This is probably an obvious question, but not to me.  What is this asking for?

 

 

Thank you,

 

Bob Knight, CET III

Fire by Knight, LLC

208-318-3057

<image001.jpg>

 

 



NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to