I'm curious why there is any confusion over this? Example: If you have sprinklers on sprigs and don't provide any elevation information, the shop drawing reviewer or permit reviewer will have to calculate the fitting takeouts and sprig lengths to be sure your sprinkler is within the allowable dimensions from the deck. Without piping elevations how will the crew know where the pipe is supposed to be routed so that it doesn't run into every other system that's in the same space?
When reviewing calculations, having elevations shown on the drawing that correlate to the calcs helps verify that the design depicted on drawings and in the calcs actually match. Dimensions are great too as well as building column lines for reference. Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | [email protected]<mailto:[email protected]> | www.jacobs.com<http://www.jacobs.com/> 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected]> On Behalf Of Sprinkler Academy - C Bilbo via Sprinklerforum Sent: Thursday, January 9, 2020 6:10 PM To: [email protected]; [email protected] Cc: Sprinkler Academy - C Bilbo <[email protected]> Subject: [EXTERNAL] Re: NFPA 13, 23.1.3 (37) Bob, The committee wants to see relative elevation changes. This helps with lengths of pipe and calcs too. We use the word relative because it doesn't need to be Above Sea Level. (But I think you already know this!!) Cecil It should be recognized that the above is my opinion as a member of the NFPA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the the NFPA, nor any of their technical committees. Sincerely, Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 217.607.0325 www.sprinkleracademy.com<https://urldefense.com/v3/__http:/www.sprinkleracademy.com__;!!B5cixuoO7ltTeg!XkRGRr99xdaYdXH-7ZtUy7WBSB6JojsVotvM0MEf4HstA0lFb_iFkQjqkCfIZhe8rg$> [email protected]<mailto:[email protected]> ?? OUR STUDENTS SAVE LIVES!! ________________________________ From: Sprinklerforum <[email protected]<mailto:[email protected]>> on behalf of Bob Knight via Sprinklerforum <[email protected]<mailto:[email protected]>> Sent: Thursday, January 9, 2020 3:41:36 PM To: [email protected]<mailto:[email protected]> <[email protected]<mailto:[email protected]>> Cc: Bob Knight <[email protected]<mailto:[email protected]>> Subject: NFPA 13, 23.1.3 (37) >From NFPA 13 (2013 ED), 23.1.3 (37) Relative elevations of sprinklers, >junction points, and supply or reference points. This is probably an obvious question, but not to me. What is this asking for? Thank you, Bob Knight, CET III Fire by Knight, LLC 208-318-3057 [FBK-LOGO-EMAIL] ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org