Re: [Emc-users] Homing and f-error

2007-06-16 Thread Jon Elson
Ray Henry wrote:
 It could also be me reading it wrong.  I had an issue trying to home
 using a shared limit pin.  The one axis I was homing was fine but all
 the others would fault.  No way around it after the ignore limit code
 was made single axis.
If the limit switches are shared, then the first axis must be 
moved off the limit switch before the 2nd axis can search for 
home, then again for the 3rd axis.  Just setting the home 
position to a large enough non-zero value should accomplish that.

 Long ago we found that motion stuttered during homing.  Some sort of
 pause in the motion while EMC looked at the home pin.  If this is still
 the case, it might cause the increased following error that was
 observed.
No pause anymore.  There is a bit of a glitch, at least on some 
encoder counter schemes, when the encoder count is suddenly set 
to zero by the index pulse.  It is pretty small, as the driver 
masks most of the discontinuity.

Missed you at the CNC Workshop!

Jon

-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-14 Thread rehenry


Hi Chris

I guess I missed it also.  Saw the later post where there was a suggested work 
around since this is a Mesa card setup.  It would be possible to add a normally 
closed real relay contact between the limit prox and the drive's directional 
inhibit input that, when pulled by the homing pin in HAL would disconnect that 
input.  I'll put my flame suit on after that suggestion.

Ray

On Wed, 13 Jun 2007 10:40:48 -0500, Enhanced Machine Controller (EMC) 
emc-users@lists.sourceforge.net said:
On Wed, Jun 13, 2007 at 08:48:43AM -0500, Ray Henry wrote:
 
 It could also be me reading it wrong.  I had an issue trying to home
 using a shared limit pin.  The one axis I was homing was fine but all
 the others would fault.  No way around it after the ignore limit code
 was made single axis.
 
 Long ago we found that motion stuttered during homing.  Some sort of
 pause in the motion while EMC looked at the home pin.  If this is still
 the case, it might cause the increased following error that was
 observed.
 
 Ray


Ray I missed the last paragraph of Richard's message at the first
reading, but down there he says that his switches disable the servo
amp during the homing process, which causes a larger following error.

The motion (decelerating to a stop after touching the switch) is
commanded smoothly, but his machine can't track it well, because the
amp is off, and the axis is coasting.

Chris


-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users



-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-13 Thread Chris Radek
On Tue, Jun 12, 2007 at 05:51:37PM +0100, Richard Arthur wrote:
 I have a problem with f-error being larger than normal when homing.

...

 Am I correct in thinking the larger than nomal f-error is caused  by the 
 servo amp being disabled by the the limit switch during the homing sequence?

Yes I'm sure you're right

 What can you suggest to overcome this so that I can run it with minimum 
 FERROR and MIN_FERROR settings?

You have to arrange not to do that.  A separate home switch seems like
the best answer, but it's probably not the easiest.  (I'm not sure
what the easiest would be).  I say the separate switch is best,
because any other solution would involve sometimes disabling your
safety measures on the limit switches.

Chris

-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-13 Thread Alex Joni
Ray,

I don't think it's a matter of development thinking.
If he hits teh limit switch and that physically disables his drives then 
it's not soemtihng you can overcome by software,
or maybe am I reading it all wrong?

Regards,
Alex


 Wah.  We really need to get some sort of order in our development
 thinking here.  Sure professional machines use three switches at one end
 of travel and two at the other but that does not obviate the need for
 lesser systems for us little light machine guys.

 Note: Indepentantly of EMC2, the limit switches disable the servo amps
 in the current direction of travel only.


-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-13 Thread Ray Henry

It could also be me reading it wrong.  I had an issue trying to home
using a shared limit pin.  The one axis I was homing was fine but all
the others would fault.  No way around it after the ignore limit code
was made single axis.

Long ago we found that motion stuttered during homing.  Some sort of
pause in the motion while EMC looked at the home pin.  If this is still
the case, it might cause the increased following error that was
observed.

Ray




On Wed, 2007-06-13 at 16:30 +0300, Alex Joni wrote:
 Ray,
 
 I don't think it's a matter of development thinking.
 If he hits teh limit switch and that physically disables his drives then 
 it's not soemtihng you can overcome by software,
 or maybe am I reading it all wrong?
 
 Regards,
 Alex
 
 
  Wah.  We really need to get some sort of order in our development
  thinking here.  Sure professional machines use three switches at one end
  of travel and two at the other but that does not obviate the need for
  lesser systems for us little light machine guys.
 
  Note: Indepentantly of EMC2, the limit switches disable the servo amps
  in the current direction of travel only.
 
 
 -
 This SF.net email is sponsored by DB2 Express
 Download DB2 Express C - the FREE version of DB2 express and take
 control of your XML. No limits. Just data. Click to get it now.
 http://sourceforge.net/powerbar/db2/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users
 


-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-13 Thread Ray Henry

Wah.  We really need to get some sort of order in our development
thinking here.  Sure professional machines use three switches at one end
of travel and two at the other but that does not obviate the need for
lesser systems for us little light machine guys.

The fact that some folk would like to stack all of the limits on a
single pin and then try to home from any one of them is not an error, it
is an integrator decision that should/must be allowed in the software.
Some of the recent changes to HAL and Motion have made it very difficult
to use EMC2 in these circumstances.  IMO we are getting close to a
critical lack of proper flexible task planning.

Ray



On Wed, 2007-06-13 at 08:07 -0500, Chris Radek wrote:
 On Tue, Jun 12, 2007 at 05:51:37PM +0100, Richard Arthur wrote:
  I have a problem with f-error being larger than normal when homing.
 
 ...
 
  Am I correct in thinking the larger than nomal f-error is caused  by the 
  servo amp being disabled by the the limit switch during the homing sequence?
 
 Yes I'm sure you're right
 
  What can you suggest to overcome this so that I can run it with minimum 
  FERROR and MIN_FERROR settings?
 
 You have to arrange not to do that.  A separate home switch seems like
 the best answer, but it's probably not the easiest.  (I'm not sure
 what the easiest would be).  I say the separate switch is best,
 because any other solution would involve sometimes disabling your
 safety measures on the limit switches.
 
 Chris
 
 -
 This SF.net email is sponsored by DB2 Express
 Download DB2 Express C - the FREE version of DB2 express and take
 control of your XML. No limits. Just data. Click to get it now.
 http://sourceforge.net/powerbar/db2/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users
 


-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-13 Thread Chris Radek
On Wed, Jun 13, 2007 at 08:48:43AM -0500, Ray Henry wrote:
 
 It could also be me reading it wrong.  I had an issue trying to home
 using a shared limit pin.  The one axis I was homing was fine but all
 the others would fault.  No way around it after the ignore limit code
 was made single axis.
 
 Long ago we found that motion stuttered during homing.  Some sort of
 pause in the motion while EMC looked at the home pin.  If this is still
 the case, it might cause the increased following error that was
 observed.
 
 Ray


Ray I missed the last paragraph of Richard's message at the first
reading, but down there he says that his switches disable the servo
amp during the homing process, which causes a larger following error.

The motion (decelerating to a stop after touching the switch) is
commanded smoothly, but his machine can't track it well, because the
amp is off, and the axis is coasting.

Chris


-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] Homing and f-error

2007-06-13 Thread RogerN

- Original Message - 
From: Chris Radek [EMAIL PROTECTED]
To: Enhanced Machine Controller (EMC) 
emc-users@lists.sourceforge.net
Sent: Wednesday, June 13, 2007 8:07 AM
Subject: Re: [Emc-users] Homing and f-error


 You have to arrange not to do that.  A separate home switch seems like
 the best answer, but it's probably not the easiest.  (I'm not sure
 what the easiest would be).  I say the separate switch is best,
 because any other solution would involve sometimes disabling your
 safety measures on the limit switches.

 Chris

I had an idea I plan to try on my machine when I get to that point. 
Have a push button that jumps limit switches only while held in.  My 
machine had motor and belt guards which means I have to dis-assemble the 
machine or hotwire to enable the amps to jog it off the limit switch. 
My purpose was to be able to jog off limit switches but it could also be 
held while homing from limit switches.

Roger


-
This SF.net email is sponsored by DB2 Express
Download DB2 Express C - the FREE version of DB2 express and take
control of your XML. No limits. Just data. Click to get it now.
http://sourceforge.net/powerbar/db2/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


[Emc-users] Homing and f-error

2007-06-12 Thread Richard Arthur
I have a problem with f-error being larger than normal when homing.

I ran this program :
%
G00 G40 G49 G80
G90 G54 G20 G61
G00 X0.2
G01 X0.1 F6.
X0.2
X0.1
X0.2
X0.1
X0.2
M02
%
and took a screenshot of HAL Oscilloscope to demonstrate normal f-error:
http://imagebin.org/8953

This next screenshot shows the f-error when homing:
http://imagebin.org/8954

My mill set-up:
EMC 2.1.6
3 axis
Servos
2 Hall effect limit switches/axis (no home switch)
Note: Indepentantly of EMC2, the limit switches disable the servo amps 
in the current direction of travel only.
 
 From m5i20 .ini:

# First axis
[AXIS_0]

TYPE =  LINEAR
HOME =  0.0
MAX_VELOCITY =  4.0
MAX_ACCELERATION =  20.0
BACKLASH = 0.000
INPUT_SCALE =   2
OUTPUT_SCALE = 1
OUTPUT_OFFSET = 0
MIN_LIMIT = -32.0
MAX_LIMIT = 20.0
FERROR =0.02
MIN_FERROR = 0.02
HOME_OFFSET =   -0.1
HOME_SEARCH_VEL =   0.1
HOME_LATCH_VEL =0.01
HOME_USE_INDEX =FALSE
HOME_IGNORE_LIMITS =YES
MAX_OUTPUT =10
# PID tuning params
DEADBAND =  0.15
P = 200
I = 0
D = 0
FF0 =   0
FF1 =   1
BIAS =  0

The problem exists on all axis. f-error reduces as HOME_SEARCH_VEL and 
HOME_LATCH_VEL decrease.

Am I correct in thinking the larger than nomal f-error is caused  by the 
servo amp being disabled by the the limit switch during the homing sequence?

What can you suggest to overcome this so that I can run it with minimum 
FERROR and MIN_FERROR settings?

Thank you.

Richard.




-