Penny,

This is only partially correct.  See the 5th bullet item in R9-11 of section
9.7.1 of Telcordia GR-1089-CORE issue 3.

"Multiple bonding or grounding conductors shall not be secured by the same
bolt and shall not need to be removed to perform other service or installation
procedures.  It is permissible to connect other bonding or grounding
conductors to a grounding connector provided a reliable bond between the
connector and the equipment is not disturbed during the installation, service
or maintenance."

This means if a product has a grounding post, the main protective earth
connector can be installed with nuts and lock washers for instance, and then
another ground connection can be made to the same stud provided it does not
loosen the original protective earth connection.

In essence what it is saying is that two ground connectors cannot be connected
unless separate fastening devices are used between each.  In addition the
primary protective earth connection cannot be disturbed by the secondary earth
connection.

This also allows a bolt on the inner side of an equipment chassis to be
connected to say the PCB ground, while the same bolt on the outside of the
chassis is connected to a wire that eventually attaches to the frame.


Jim 

Jim Wiese 
NEBS Project Manager/Senior Compliance Engineer 
ADTRAN, INC. 
901 Explorer Blvd. 
P.O. Box 140000 
Huntsville, AL 35814-4000 
256-963-8431 
256-963-8250 fax 
[email protected] 




From: Robbins, Penny D. [mailto:[email protected]]
Sent: Wednesday, July 30, 2003 11:56 AM
To: [email protected]
Subject: RE: Number of Terminations on a Ground Stud?



Telcordia's GR-1089 limits the number to ONE per stud.



From: Momcilovic, Nick [mailto:[email protected]] 
Sent: Wednesday, July 30, 2003 12:03 PM
To: [email protected]
Subject: Number of Terminations on a Ground Stud?



Is anyone familiar with any requirement that limits the number of ground
terminations on a single stud?  I heard that the limit is two per stud but I
was not able to confirm this with any of the standards we have.

Thanks in advance for your help.

Sincerely,

Nick Momcilovic
Product Safety

Quad/Tech, Inc.
A Subsidiary of Quad/Graphics

Sussex, Wisconsin
414-566-7915 phone
414-566-9576 fax 
[email protected]
www.qtiworld.com


This message is from the IEEE EMC Society Product Safety Technical Committee
emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line. All
emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     [email protected]
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              [email protected]
     Dave Heald:               [email protected]

For policy questions, send mail to:
     Richard Nute:           [email protected]
     Jim Bacher:             [email protected]

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to