I believe the way to do it codewise would be to add a subpanel at the base
of the solar array, with a breaker in it feeding the dedicated solar
circuit (the inverter or inverters -- often I end up with multiple
inverters to get to 50A anyway unless using a single 11.4kW, so am adding
an inverter combiner panel for that reason) and a breaker feeding the EV
charging outlet.  It's legal to connect the PV to a subpanel, or a series
of subpanels, as long as you follow the 120% rule all the way back through
every panel along the way.

On Sun, Mar 10, 2024 at 3:08 PM (-Phil-) via EV <ev@lists.evdl.org> wrote:

> Yes, you'd need a subpanel, as any outlets you add could get 50A from the
> breaker PLUS whatever your solar is generating.  The 120v outlet without a
> proper breaker to limit current is super dangerous, as you'll definitely
> get 50A even at night, and even more during the day!
>
> On Sun, Mar 10, 2024 at 2:56 PM Mark Hanson via EV <ev@lists.evdl.org>
> wrote:
>
> >
> > >
> > > Hi Folks
> > > I was reading in Solar Power World where a California solar installer
> > adds a 14/50 240Vac 50A outlet on the same solar array 50a circuit (for
> EV
> > charging). We have added 120vac courtesy outlets on our solar array and
> > pass inspection even though NEC says solar must be on a dedicated circuit
> > (also tap off garage circuits that are not dedicated). I couldn’t find
> > anything direct on Google if it’s a code violation to add a 240V outlet
> > like we do a 120V outlet on the same 50A branch circuit?  Does anyone
> know
> > if this is ok/code compliant?
> > I assume a local 50A breaker to the 14/50 outlet might be needed since
> > there’s two sources, 40A solar plus 50A from panel branch circuit.
> > > Best regards Mark
> > > Sent from my iPhone
> > _______________________________________________
> > Address messages to ev@lists.evdl.org
> > No other addresses in TO and CC fields
> > HELP: http://www.evdl.org/help/
> >
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20240310/c3d769cc/attachment.htm
> >
> _______________________________________________
> Address messages to ev@lists.evdl.org
> No other addresses in TO and CC fields
> HELP: http://www.evdl.org/help/
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20240310/1caae5ff/attachment.htm>
_______________________________________________
Address messages to ev@lists.evdl.org
No other addresses in TO and CC fields
HELP: http://www.evdl.org/help/

Reply via email to