Yeah, NEC requires a GFCI for all outdoor outlets.  If you hardwire an EVSE
in, you don't need it, as the EVSE contains its own.

A common use for 15-50's outdoor is powering RV shore power.


On Sun, Mar 10, 2024 at 7:04 PM Bill Dube via EV <ev@lists.evdl.org> wrote:

> The NEC has changed through the years regarding GFCI protection.
>
> 120vac outdoor outlets were required to be GFCI protected since ~1972.
>
> In the '80s when I worked as an electrician, outdoor 240 volt NEMA 14-50
> outlets were not required to be GFCI protected, but when used to power a
> hot tub, or near a pool, they were required to be GFCI protected.
> However, the newest NEC regulations require, as I understand it, all
> outdoor outlets up to 50 amps be GFCI protected. (I suppose you could
> put in a 60 amp breaker to get around the regulation...)
>
> You should not even mention that an EV might use this outlet. It is
> simply an outdoor NEMA 14-50 outlet. Perhaps for a welder, or ???
>
> The NEC has become more strict in the past 40 years. :-)
>
> Depending on the brand of panel, 50amp 240V two-pole GFCI breakers are
> not insanely expensive. Typically $100 to $150. (For a Scheneider brand,
> they can cost over $400, however.) Choose your brand of sub-panel panel
> based on your breaker cost. :-) I would put the GFCI breaker so that is
> is handy to the outlet so you can easily reset it. At 5 mA trip
> threshold, you are likely to have to reset it with regularity. :-)
>
>  >>>> GFCI rant <<<
>
> In the USA, the GFCI is set at an insanely low trip threshold of 5 mA.
> This is a bit of overreach by the NEC folks. It was initially set far to
> conservatively and they can't go up now that they have set the standard
> at 5 mA.
>
> In NZ, and other parts of the civilized world, the ground fault (or
> residual current) trip threshold is 30 mA.  For context, it takes about
> 100 mA, directly across the chest of a healthy adult to cause a fatal
> shock. Small children and adults with unhealthy hearts, have a lower
> threshold than 100 mA. Thus, in hospitals, daycare facilities, etc. they
> set the requirement at 10 mA for devices with in their reach.
>
> The base voltage in NZ, and most of the world, is 230V. This actually
> doubles the chance of getting the critical 100 mA jolt across the chest,
> but 30 mA is is still a safer option. First, the threshold is 1/3 of
> what is considered the lowest fatal shock current. Next, a shock
> directly across the chest is quite rare. You have to touch something of
> opposite electrical potential with each hand or arm. This is a _very_
> rare occurrence.
>
> The consequence of 5 mA threshold is nuisance tripping. Indeed, less
> trip current is "more safe" than more, I suppose, but it is impractical
> to apply GFCI to more that select parts of the house (and to the
> business.) In contrast the ENTIRE house is protected by GFCI in NZ under
> the modern NZ electrical code. Your electric range is GFCI protected, as
> are all your appliances, and every light fixture. Every outlet in the
> entire house is GFCI protected. You have one GFCI 30 mA breaker to cover
> the entire house, and it rarely trips. If the trip was 5 mA, this would
> be completely impractical as the nuisance tripping would make normal
> activities impossible. A hair dryer could easily darken your entire house.
>
> I should note that commercial settings also have (with some exceptions)
> this facility-wide 30 mA GFCI protection on everything, under the modern
> electrical code.
>
> Bill D.
>
> On 3/11/2024 10:55 AM, Mark Hanson via EV wrote:
> >> Hi Folks
> >> I was reading in Solar Power World where a California solar installer
> adds a 14/50 240Vac 50A outlet on the same solar array 50a circuit (for EV
> charging). We have added 120vac courtesy outlets on our solar array and
> pass inspection even though NEC says solar must be on a dedicated circuit
> (also tap off garage circuits that are not dedicated). I couldn’t find
> anything direct on Google if it’s a code violation to add a 240V outlet
> like we do a 120V outlet on the same 50A branch circuit?  Does anyone know
> if this is ok/code compliant?
> > I assume a local 50A breaker to the 14/50 outlet might be needed since
> there’s two sources, 40A solar plus 50A from panel branch circuit.
> >> Best regards Mark
> >> Sent from my iPhone
> > _______________________________________________
> > Address messages t...@lists.evdl.org
> > No other addresses in TO and CC fields
> > HELP:http://www.evdl.org/help/
> >
> -------------- next part --------------
> An HTML attachment was scrubbed...
> URL: <
> http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20240311/90d5a3cf/attachment.htm
> >
> _______________________________________________
> Address messages to ev@lists.evdl.org
> No other addresses in TO and CC fields
> HELP: http://www.evdl.org/help/
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20240310/64842406/attachment.htm>
_______________________________________________
Address messages to ev@lists.evdl.org
No other addresses in TO and CC fields
HELP: http://www.evdl.org/help/

Reply via email to