I'm going to chime in with a point.   Probably plenty all ready know it, but 
maybe some don't.
Virtually all home solar is actually kind of technically violating some 
electrical rules.   The reason is thatbreakers were not intended to be used to 
back feed power, but that is the easiest way, so the code peopleactually look 
the other way.

The problem is as follows.
Imagine a 200 amp panel for you house.    It has a big 200 amp breaker at the 
top and the bus bars are designed to handle 200 amps.Further imagine that you 
have a 40 amp solar.
So imagine you have no solar (it's dark) and you turn on every appliance and 
you are drawing 200 amps.  (or a tiny bit less).    No problem as the main 
breaker (the 200amp one) doesn't flip yet.      Now turn on the 40 amps of 
solar and now the main breaker is only seeing 160 amps (160 from the power 
company and 40 from the solar is going into your appliances.    But the 
important thing is the bus bars are still seeing (or potentially seeing 200 
amps).        Now start charging your EV (say it's 40 amps)  so now the bus 
bars are seeing 240 amps and the main breaker STILL doesn't flip (because it's 
now it only sees 200 amps.
So you are technically over powering the panel bus bars more than they are 
rated for.
The proper solution is actually to put in a NEW main breaker of 160 amps but 
almost nobody does that.

But the reality is the code people fudge it and allow 20% but it's not really 
correct.
Anyway I'm guessing this has something to do with your adding outlets to a 
solar panel not being entirely kosher.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://lists.evdl.org/private.cgi/ev-evdl.org/attachments/20240311/6489e531/attachment.htm>
_______________________________________________
Address messages to ev@lists.evdl.org
No other addresses in TO and CC fields
HELP: http://www.evdl.org/help/

Reply via email to