RE: UG pipe - min burry depth

2012-06-07 Thread Dewayne Martinez
Any comments on this for me?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Wednesday, June 06, 2012 8:49 AM
To: SprinklerFORUM
Subject: UG pipe - min burry depth

Must a minimum burry depth below the frost line be used for UG pipe to a
test header and FDC that are normally not filled with water?

I have always tried to maintain this depth in fear of the frost heave
damaging the pipe but I am being questioned in the office and wanted to
get others opinions.

Thanks, 

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120606/552cf0a7/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE:RTI

2012-06-07 Thread bcasterline
correction, meter, not feet. i should have looked in 13 instead of  
trying to recall and thinking i needed to convert. but i now have  
another (perhaps stupid) question re the definition of fast response  
and standard response: if fast is RTI=50 or less and standard is 80 or  
more, what is in between called? I am really more interested in the  
reasoning for the DEFINITION in NFPA #13, not some box of heads in RTI  
limbo. Any TC members out there not totally fed-up with me yet?


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: UG pipe - min burry depth

2012-06-07 Thread Morey, Mike
10.4 Depth of Cover is seperate from 10.5 Protection Against Freezing, yet 
still requires burying the pipe at least 1 foot below the frost line.  I would 
say that requirement applies regardless of whether or not the pipe has water in 
it to freeze?  Typically we treat FDC piping the same way as we'd treat regular 
UG especially since there's the risk of the ball drip plugging up etc.



From: sprinklerforum-boun...@firesprinkler.org on behalf of Dewayne Martinez
Sent: Thu 6/7/2012 6:19 AM
To: SprinklerFORUM
Subject: RE: UG pipe - min burry depth



Any comments on this for me?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Wednesday, June 06, 2012 8:49 AM
To: SprinklerFORUM
Subject: UG pipe - min burry depth

Must a minimum burry depth below the frost line be used for UG pipe to a
test header and FDC that are normally not filled with water?

I have always tried to maintain this depth in fear of the frost heave
damaging the pipe but I am being questioned in the office and wanted to
get others opinions.

Thanks,



Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)



-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120606/552cf0a7/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


-- next part --
A non-text attachment was scrubbed...
Name: winmail.dat
Type: application/ms-tnef
Size: 4522 bytes
Desc: not available
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/9fc54fc3/attachment.bin
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: UG pipe - min burry depth

2012-06-07 Thread Jeff Garrison
I don't think it's a code issue.
It does seem prudent to keep it below the frost line,
but that may be higher that the bury requirements for a lead-in.

On Thu, Jun 7, 2012 at 6:19 AM, Dewayne Martinez deway...@dbfp.net wrote:

 Any comments on this for me?

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
 Martinez
 Sent: Wednesday, June 06, 2012 8:49 AM
 To: SprinklerFORUM
 Subject: UG pipe - min burry depth

 Must a minimum burry depth below the frost line be used for UG pipe to a
 test header and FDC that are normally not filled with water?

 I have always tried to maintain this depth in fear of the frost heave
 damaging the pipe but I am being questioned in the office and wanted to
 get others opinions.

 Thanks,



 Dewayne Martinez

 Design Build Fire Protection

 262-784-7900 (w)

 262-784-8401 (f)

 414-349-0468 (cell)



 -- next part --
 An HTML attachment was scrubbed...
 URL:
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
 ments/20120606/552cf0a7/attachment.htmlhttp://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120606/552cf0a7/attachment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/aabdbc05/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RTI

2012-06-07 Thread Brad Casterline
never mind (coffee worked), it's called 'nobody makes them because they
would not be UL Listed', and it points out the amazing (to me) tolerances
sprinklers are manufactured to.

-Original Message-
From: bcasterl...@fsc-inc.com [mailto:bcasterl...@fsc-inc.com] 
Sent: Thursday, June 07, 2012 5:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE:RTI

correction, meter, not feet. i should have looked in 13 instead of  
trying to recall and thinking i needed to convert. but i now have  
another (perhaps stupid) question re the definition of fast response  
and standard response: if fast is RTI=50 or less and standard is 80 or  
more, what is in between called? I am really more interested in the  
reasoning for the DEFINITION in NFPA #13, not some box of heads in RTI  
limbo. Any TC members out there not totally fed-up with me yet?

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RTI

2012-06-07 Thread George Church
The amount of significant digits we work to in various aspects is quite varied.
Some folks believe calc programs down to the .001 level when it all comes down 
to a gauge bouncing around in a variable water supply with uncontrolled changes.
Yet we worry about inches in other areas.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline
Sent: Thursday, June 07, 2012 7:37 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RTI

never mind (coffee worked), it's called 'nobody makes them because they would 
not be UL Listed', and it points out the amazing (to me) tolerances sprinklers 
are manufactured to.

-Original Message-
From: bcasterl...@fsc-inc.com [mailto:bcasterl...@fsc-inc.com]
Sent: Thursday, June 07, 2012 5:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE:RTI

correction, meter, not feet. i should have looked in 13 instead of trying to 
recall and thinking i needed to convert. but i now have another (perhaps 
stupid) question re the definition of fast response and standard response: if 
fast is RTI=50 or less and standard is 80 or more, what is in between called? I 
am really more interested in the reasoning for the DEFINITION in NFPA #13, not 
some box of heads in RTI limbo. Any TC members out there not totally fed-up 
with me yet?

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RTI Cloud Deluge

2012-06-07 Thread Bill Brooks
Yes we have a rulebook instead of an engineering approach (thank goodness),
and yes we have been fumbling around for many years about this cloud thing,
but in the name of common sense (which I hope we still have a little of)
this design approach must be stopped at all costs.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike
Hairfield
Sent: Wednesday, June 06, 2012 3:36 PM
To: AFSA SprinklerFORUM
Subject: RE: RTI


You won't believe this!
 
Armstrong ceiling clouds that are arched, architect doesn't want to
penetrate the clouds like the Armstrong data sheet shows so we have QR
sprinklers above the clouds and a deluge system of sidewall sprinklers feed
from the soffits throwing water under the clouds. Some big DA came up with
this idea.
 
It's a tiered classroom with a sloping floor, I suggested they install some
life preservers for the students so they won't drown when the system trips.
 
Mike
 

 

 From: craig.pr...@ch2m.com
 To: sprinklerforum@firesprinkler.org
 Subject: RE: RTI
 Date: Wed, 6 Jun 2012 19:29:07 +
 
 Are the detectors at the same temperature as the QR heads? That just sound
weird, what would be in the same room that would be protected by deluge
system and also allow QR sprinklers?
 
 Craig L. Prahl, CET
 Fire Protection
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension 74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike 
 Hairfield
 Sent: Wednesday, June 06, 2012 2:08 PM
 To: AFSA SprinklerFORUM
 Subject: RE: RTI
 
 
 There are QR Sprinklers in the same room that has a deluge system with 
 open heads in it, they want to make sure that the detectors do not trip
the deluge system first.
 
 
 
 
  From: ccah...@burnsmcd.com
  To: sprinklerforum@firesprinkler.org
  Date: Wed, 6 Jun 2012 12:31:18 -0500
  Subject: RE: RTI
  
  Curious if you know why the AHJ wanted to know? Listings take care of
either FR/QR or SR. 
  
  Chris Cahill, PE*
  Senior Fire Protection Engineer, Aviation  Facilities Group Burns  
  McDonnell
  8201 Norman Center Drive
  Bloomington, MN 55437
  Phone: 952.656.3652
  Fax: 952.229.2923
  ccah...@burnsmcd.com
  www.burnsmcd.com
  
  Proud to be one of FORTUNE's 100 Best Companies to Work For 
  *Registered in: MN
  
  
  
  
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org 
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike 
  Hairfield
  Sent: Wednesday, June 06, 2012 12:26 PM
  To: AFSA SprinklerFORUM
  Subject: RE: RTI
  
  
  Thanks,
  
  They told me it was 36.
  
  Mike
  
  
   From: craig.pr...@ch2m.com
   To: sprinklerforum@firesprinkler.org
   Subject: RE: RTI
   Date: Wed, 6 Jun 2012 17:21:17 +
   
   Call Tyco.
   
   
   Craig L. Prahl, CET
   Fire Protection
   CH2MHILL
   Lockwood Greene
   1500 International Drive
   Spartanburg, SC 29304-0491
   Direct - 864.599.4102
   Fax - 864.599.8439
   CH2MHILL Extension 74102
   craig.pr...@ch2m.com
   
   
   
   -Original Message-
   From: sprinklerforum-boun...@firesprinkler.org
   [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
   Mike Hairfield
   Sent: Wednesday, June 06, 2012 1:19 PM
   To: AFSA SprinklerFORUM
   Subject: RTI
   
   
   I have a AHJ wanting to know what is the RTI for a TYCO FR-B TY3231
155 degree pendent sprinkler.
   
   How do I determine the RTI?
   
   Mike
   -- next part -- An HTML attachment was 
   scrubbed...
   URL: 
   http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
   atta chments/20120606/0ddfb8a7/attachment.html
   ___
   Sprinklerforum mailing list
   Sprinklerforum@firesprinkler.org
   http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
   ___
   Sprinklerforum mailing list
   Sprinklerforum@firesprinkler.org
   http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  
  -- next part -- An HTML attachment was 
  scrubbed...
  URL: 
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/at
  tachments/20120606/47d8575c/attachment.html
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 -- next part -- An HTML attachment was 
 scrubbed...
 URL: 
 

RE: UG pipe - min burry depth

2012-06-07 Thread Craig.Prahl
There is no direction provided for this particular situation.  I would treat it 
the same as the rest of the system since if it was used it could have water 
laying in it and if that water froze because the pipe was above the frost line, 
the FDC could be rendered inoperative.  Also by burying it at the same depth 
you would not have to be concerned with potential traffic loading issues.

There's my 2 cents for the day.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
craig.pr...@ch2m.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne Martinez
Sent: Thursday, June 07, 2012 6:20 AM
To: SprinklerFORUM
Subject: RE: UG pipe - min burry depth

Any comments on this for me?

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Wednesday, June 06, 2012 8:49 AM
To: SprinklerFORUM
Subject: UG pipe - min burry depth

Must a minimum burry depth below the frost line be used for UG pipe to a
test header and FDC that are normally not filled with water?

I have always tried to maintain this depth in fear of the frost heave
damaging the pipe but I am being questioned in the office and wanted to
get others opinions.

Thanks, 

 

Dewayne Martinez

Design Build Fire Protection

262-784-7900 (w)

262-784-8401 (f)

414-349-0468 (cell)

 

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120606/552cf0a7/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: UG pipe - min burry depth

2012-06-07 Thread Dewayne Martinez
Thanks guys, this is what I thought.  The question arose with I had my
pipe for a free standing FDC and test header exiting the building at
6'6 below grade and the sanitary exited at 3'0 below grade.   

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff
Garrison
Sent: Thursday, June 07, 2012 6:24 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: UG pipe - min burry depth

I don't think it's a code issue.
It does seem prudent to keep it below the frost line, but that may be
higher that the bury requirements for a lead-in.

On Thu, Jun 7, 2012 at 6:19 AM, Dewayne Martinez deway...@dbfp.net
wrote:

 Any comments on this for me?

 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne

 Martinez
 Sent: Wednesday, June 06, 2012 8:49 AM
 To: SprinklerFORUM
 Subject: UG pipe - min burry depth

 Must a minimum burry depth below the frost line be used for UG pipe to

 a test header and FDC that are normally not filled with water?

 I have always tried to maintain this depth in fear of the frost
heave
 damaging the pipe but I am being questioned in the office and wanted 
 to get others opinions.

 Thanks,



 Dewayne Martinez

 Design Build Fire Protection

 262-784-7900 (w)

 262-784-8401 (f)

 414-349-0468 (cell)



 -- next part -- An HTML attachment was 
 scrubbed...
 URL:
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
 ch 
 ments/20120606/552cf0a7/attachment.htmlhttp://fireball.firesprinkler.
 org/mailman/private/sprinklerforum/attachments/20120606/552cf0a7/attac
 hment.html
 
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

-- next part --
An HTML attachment was scrubbed...
URL:
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ments/20120607/aabdbc05/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: UG pipe - min burry depth

2012-06-07 Thread Sprinkler Academy - C Bilbo

We all interchangeably use the words underground, water supply, and supply 
piping.  And the rules originated in NFPA 24, Standard for the Installation of 
Private Fire Service Mains and their Appurtenances (I love that someone came 
up with the word appurtenances.)
 
But any pipe that is BURIED is covered by the rules of Chapter 10 in NFPA 13. 
 And since ANY pipe on a sprinkler system can be considered water pipe, 
section 10.4.1 would apply to your situation: The depth of cover over water 
pipes shall be determined by the maximum depth of frost penetration in the 
locality where the pipe is laid.
 
And since Mr. Wagoner is the Chairman of that Committee, I'll defer to any 
additional comments he may have.
 

It should be recognized that the above is my opinion as a member of the NFPA, 
and has not been processed as a formal interpretation in accordance with the 
NFPA Regulations Governing Committee Projects and should therefore not be 
considered, nor relied upon, as the official position of the the NFPA, nor any 
of their technical committees. 

Sincerely,


Cecil Bilbo 
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com
ce...@sprinkleracademy.com
 
OUR STUDENTS SAVE LIVES!!


 

 Subject: RE: UG pipe - min burry depth
 Date: Thu, 7 Jun 2012 08:03:29 -0500
 From: deway...@dbfp.net
 To: sprinklerforum@firesprinkler.org
 
 Thanks guys, this is what I thought. The question arose with I had my
 pipe for a free standing FDC and test header exiting the building at
 6'6 below grade and the sanitary exited at 3'0 below grade. 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Jeff
 Garrison
 Sent: Thursday, June 07, 2012 6:24 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: UG pipe - min burry depth
 
 I don't think it's a code issue.
 It does seem prudent to keep it below the frost line, but that may be
 higher that the bury requirements for a lead-in.
 
 On Thu, Jun 7, 2012 at 6:19 AM, Dewayne Martinez deway...@dbfp.net
 wrote:
 
  Any comments on this for me?
 
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
 
  Martinez
  Sent: Wednesday, June 06, 2012 8:49 AM
  To: SprinklerFORUM
  Subject: UG pipe - min burry depth
 
  Must a minimum burry depth below the frost line be used for UG pipe to
 
  a test header and FDC that are normally not filled with water?
 
  I have always tried to maintain this depth in fear of the frost
 heave
  damaging the pipe but I am being questioned in the office and wanted 
  to get others opinions.
 
  Thanks,
 
 
 
  Dewayne Martinez
 
  Design Build Fire Protection
 
  262-784-7900 (w)
 
  262-784-8401 (f)
 
  414-349-0468 (cell)
 
 
 
  -- next part -- An HTML attachment was 
  scrubbed...
  URL:
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/atta
  ch 
  ments/20120606/552cf0a7/attachment.htmlhttp://fireball.firesprinkler.
  org/mailman/private/sprinklerforum/attachments/20120606/552cf0a7/attac
  hment.html
  
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 -- next part --
 An HTML attachment was scrubbed...
 URL:
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
 ments/20120607/aabdbc05/attachment.html
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/3c4fcc81/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RTI Cloud Deluge

2012-06-07 Thread Fairchild, Jack
Prior to my arrival, my company designed a group B building with a 300 foot 
long corridor which had a slot atrium.  The floor opening consisted of a 3 
foot wide slot that ran the entire length along the outside wall.  The code 
consultant recommended a deluge system the entire length of the slot.  The 
architects loved this idea.  As a result they will occasionally suggest this as 
an alternative solution to some scheme they have in their brains at which point 
I voice loudly how this is the dumbest hair brained idea I had ever seen and 
the company is very lucky it has not released.  Fortunately it was multi-zoned 
and provided with multiple interlocks.

Jack Fairchild


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bill Brooks
Sent: Thursday, June 07, 2012 8:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RTI Cloud Deluge

Yes we have a rulebook instead of an engineering approach (thank goodness), and 
yes we have been fumbling around for many years about this cloud thing, but in 
the name of common sense (which I hope we still have a little of) this design 
approach must be stopped at all costs.

Bill Brooks

William N. Brooks, P.E.
Brooks Fire Protection Engineering Inc.


-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike Hairfield
Sent: Wednesday, June 06, 2012 3:36 PM
To: AFSA SprinklerFORUM
Subject: RE: RTI


You won't believe this!
 
Armstrong ceiling clouds that are arched, architect doesn't want to penetrate 
the clouds like the Armstrong data sheet shows so we have QR sprinklers above 
the clouds and a deluge system of sidewall sprinklers feed from the soffits 
throwing water under the clouds. Some big DA came up with this idea.
 
It's a tiered classroom with a sloping floor, I suggested they install some 
life preservers for the students so they won't drown when the system trips.
 
Mike
 

 

 From: craig.pr...@ch2m.com
 To: sprinklerforum@firesprinkler.org
 Subject: RE: RTI
 Date: Wed, 6 Jun 2012 19:29:07 +
 
 Are the detectors at the same temperature as the QR heads? That just 
 sound
weird, what would be in the same room that would be protected by deluge system 
and also allow QR sprinklers?
 
 Craig L. Prahl, CET
 Fire Protection
 CH2MHILL
 Lockwood Greene
 1500 International Drive
 Spartanburg, SC  29304-0491
 Direct - 864.599.4102
 Fax - 864.599.8439
 CH2MHILL Extension 74102
 craig.pr...@ch2m.com
 
 
 
 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike 
 Hairfield
 Sent: Wednesday, June 06, 2012 2:08 PM
 To: AFSA SprinklerFORUM
 Subject: RE: RTI
 
 
 There are QR Sprinklers in the same room that has a deluge system with 
 open heads in it, they want to make sure that the detectors do not 
 trip
the deluge system first.
 
 
 
 
  From: ccah...@burnsmcd.com
  To: sprinklerforum@firesprinkler.org
  Date: Wed, 6 Jun 2012 12:31:18 -0500
  Subject: RE: RTI
  
  Curious if you know why the AHJ wanted to know? Listings take care 
  of
either FR/QR or SR. 
  
  Chris Cahill, PE*
  Senior Fire Protection Engineer, Aviation  Facilities Group Burns  
  McDonnell
  8201 Norman Center Drive
  Bloomington, MN 55437
  Phone: 952.656.3652
  Fax: 952.229.2923
  ccah...@burnsmcd.com
  www.burnsmcd.com
  
  Proud to be one of FORTUNE's 100 Best Companies to Work For 
  *Registered in: MN
  
  
  
  
  -Original Message-
  From: sprinklerforum-boun...@firesprinkler.org
  [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike 
  Hairfield
  Sent: Wednesday, June 06, 2012 12:26 PM
  To: AFSA SprinklerFORUM
  Subject: RE: RTI
  
  
  Thanks,
  
  They told me it was 36.
  
  Mike
  
  
   From: craig.pr...@ch2m.com
   To: sprinklerforum@firesprinkler.org
   Subject: RE: RTI
   Date: Wed, 6 Jun 2012 17:21:17 +
   
   Call Tyco.
   
   
   Craig L. Prahl, CET
   Fire Protection
   CH2MHILL
   Lockwood Greene
   1500 International Drive
   Spartanburg, SC 29304-0491
   Direct - 864.599.4102
   Fax - 864.599.8439
   CH2MHILL Extension 74102
   craig.pr...@ch2m.com
   
   
   
   -Original Message-
   From: sprinklerforum-boun...@firesprinkler.org
   [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of 
   Mike Hairfield
   Sent: Wednesday, June 06, 2012 1:19 PM
   To: AFSA SprinklerFORUM
   Subject: RTI
   
   
   I have a AHJ wanting to know what is the RTI for a TYCO FR-B 
   TY3231
155 degree pendent sprinkler.
   
   How do I determine the RTI?
   
   Mike
   -- next part -- An HTML attachment was 
   scrubbed...
   URL: 
   http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
   atta chments/20120606/0ddfb8a7/attachment.html
   ___
   Sprinklerforum mailing list
   Sprinklerforum@firesprinkler.org
   

RE: RTI

2012-06-07 Thread RFletcher
Calc with computer to 6 decimals, measure with micrometer, mark with piece of 
chalk and chop off with an axe.


Ron Fletcher
Aero Automatic
Phoenix, AZ




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Thursday, June 07, 2012 5:27 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RTI

The amount of significant digits we work to in various aspects is quite varied.
Some folks believe calc programs down to the .001 level when it all comes down 
to a gauge bouncing around in a variable water supply with uncontrolled changes.
Yet we worry about inches in other areas.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline
Sent: Thursday, June 07, 2012 7:37 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RTI

never mind (coffee worked), it's called 'nobody makes them because they would 
not be UL Listed', and it points out the amazing (to me) tolerances sprinklers 
are manufactured to.

-Original Message-
From: bcasterl...@fsc-inc.com [mailto:bcasterl...@fsc-inc.com]
Sent: Thursday, June 07, 2012 5:34 AM
To: sprinklerforum@firesprinkler.org
Subject: RE:RTI

correction, meter, not feet. i should have looked in 13 instead of trying to 
recall and thinking i needed to convert. but i now have another (perhaps 
stupid) question re the definition of fast response and standard response: if 
fast is RTI=50 or less and standard is 80 or more, what is in between called? I 
am really more interested in the reasoning for the DEFINITION in NFPA #13, not 
some box of heads in RTI limbo. Any TC members out there not totally fed-up 
with me yet?

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Art Tiroly
Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having fire
hydrants

I heard more about this today from an Illinois plumbing inspector. For those
interested, they (or maybe just he) consider a fire hydrant as a device to
which applies Part 890 Plumbing Code Section 890.1140 Special Applications
and Installations. The catching sections are 890.1140 e) 1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this section,
i.e. that which are special, are hose outlets, yard hydrants with weeps,
flush valves, laundry machines, dishwashers, medical water aspirators,
mobile homes and carbonated beverage machines.

One would think that section title Special Applications and Installations
intends to single out specifically named applications and installations. For
example there is a trade distinction between Yard Hydrants and Fire Hydrants
that any reasonable tradesman would know. If this code truly intends to
apply to both Yard Hydrants and Fire Hydrants then it would not be special
and the wording would be Hydrants. Incidentally there is no mention of any
fire protection related devices at all in the section. All mention of fire
protection devices, which surely must have special distinction to most,
occurs in a different 890 subsection. Claiming this section applies also to
fire protection is to expand its special scope to included another very
special application, thereby denying the section's purpose.

The question stills stands for those in the Illinois area. Is this actually
the state's stance? For the case where I heard about this, the state will
be making another arm of the state put an RPZ device in a hot box on the
piping between an ordinary, existing fire hydrant and the private main it
connects to, because that one hydrant is being moved due to a new drive and
that section of existing underground is being replace, not as its own small
project but as part of a much larger project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, rfletc...@aerofire.com wrote:

 The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines 
 to FP systems. RPZ's are required for systems with chemicals like 
 antifreeze or AFFF and double checks for others. It says they are not 
 required for private hydrant only lines that comply with city water 
 main and AWWA standards.

 To the best of my knowledge there is no requirement in the 
 International Plumbing Code.


 Ron Fletcher
 Aero Automatic
 Phoenix, AZ




 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org 
 [mailto:sprinklerforum-boun...@firesprinkler.org
 ] On Behalf Of Timothy W Goins
 Sent: Wednesday, June 06, 2012 5:40 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: RPZ for a dedicated private underground fire mains having 
 fire hydrants

 Most THINK that the AWWA recommends BFP's on ALL firelines, especially 
 deadened lines over 100 feet, but the AWWA does NOT recommend backflow 
 protection on hydrant only lines.

 For I am not ashamed of the gospel , , because it is God's power for 
 salvation to everyone who believes... HCS Romans 1:16

 On Jun 6, 2012, at 12:56 AM, bcasterl...@fsc-inc.com wrote:

 accounting departments see plus signs when they see marketing 
 department, lunch n learn, and regulatory agencies on the same spread 
 sheet line lol (and some consulting engineering firms).
 Steve- can you explain the USC friction loss graphs? there is some 
 diff in turning on and turning off?
 Quoting Ron Greenman rongreen...@gmail.com:

 I think the backflow prevention device manufacturers have a lot of 
 influence with a fair share of regulatory agencies.

 On Tue, Jun 5, 2012 at 9:05 PM, Steve Leyton 
 st...@protectiondesign.com
 wrote:

 Private fire service mains in CA have required backflows for years.
 The type of device varies by water authority standards, but pretty 
 much throughout Southern California the use of an RPDA is standard 
 practice.
 Whether the downstream connections are sprinklers only, plus one 
 hydrant or with multiple hydrants, a backflow appliance is required 
 on a private
 fire service main.   The thinking isn't that hydrants represent a  
 cross
 connection or contamination threat per se, but that a private 
 property owner can make whatever connections they want in the dark 
 of night after
 final acceptance testing.   So better safe than sorry,  
 bureaucratically
 speaking ...

 SML
 In SoCal, where nothing surprises anymore

 

 From: sprinklerforum-boun...@firesprinkler.org 

RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Steve Leyton
Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest
and most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire
water.  And of course, the California Dept. of Health has a few opinions
on what you have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

I heard more about this today from an Illinois plumbing inspector. For
those interested, they (or maybe just he) consider a fire hydrant as a
device to which applies Part 890 Plumbing Code Section 890.1140 Special
Applications and Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this
section, i.e. that which are special, are hose outlets, yard hydrants
with weeps, flush valves, laundry machines, dishwashers, medical water
aspirators, mobile homes and carbonated beverage machines.

One would think that section title Special Applications and
Installations
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire
Hydrants that any reasonable tradesman would know. If this code truly
intends to apply to both Yard Hydrants and Fire Hydrants then it would
not be special
and the wording would be Hydrants. Incidentally there is no mention of
any fire protection related devices at all in the section. All mention
of fire protection devices, which surely must have special distinction
to most, occurs in a different 890 subsection. Claiming this section
applies also to fire protection is to expand its special scope to
included another very special application, thereby denying the section's
purpose.

The question stills stands for those in the Illinois area. Is this
actually the state's stance? For the case where I heard about this, the
state will be making another arm of the state put an RPZ device in a
hot box on the piping between an ordinary, existing fire hydrant and the
private main it connects to, because that one hydrant is being moved due
to a new drive and that section of existing underground is being
replace, not as its own small project but as part of a much larger
project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, rfletc...@aerofire.com wrote:

 The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines 
 to FP systems. RPZ's are required for systems with chemicals like 
 antifreeze or AFFF and double checks for others. It says they are not 
 required for private hydrant only lines that comply with city water 
 main and AWWA standards.

 To the best of my knowledge there is no requirement in the 
 International Plumbing Code.


 Ron Fletcher
 Aero Automatic
 Phoenix, AZ




 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org
 ] On Behalf Of Timothy W Goins
 Sent: Wednesday, June 06, 2012 5:40 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: RPZ for a dedicated private underground fire mains having

 fire hydrants

 Most THINK that the AWWA recommends BFP's on ALL firelines, especially

 deadened lines over 100 feet, but the AWWA does NOT recommend backflow

 protection on hydrant only lines.

 For I am not ashamed of the gospel , , because it is God's power for 
 salvation to everyone who believes... HCS Romans 1:16

 On Jun 6, 2012, at 12:56 AM, bcasterl...@fsc-inc.com wrote:

 accounting departments see plus signs when they see marketing 
 department, lunch n learn, and regulatory agencies on the same spread

 sheet line lol (and some consulting engineering firms).
 Steve- can you explain the USC friction loss graphs? there is some 
 diff in turning on and turning off?
 Quoting Ron 

Re: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Letterman, Todd
Hey Steve have you been on the design end of a Fire Protection System using 
reclaimed water? If you have wanted to know what issues you ran across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest
and most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire
water.  And of course, the California Dept. of Health has a few opinions
on what you have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

I heard more about this today from an Illinois plumbing inspector. For
those interested, they (or maybe just he) consider a fire hydrant as a
device to which applies Part 890 Plumbing Code Section 890.1140 Special
Applications and Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this
section, i.e. that which are special, are hose outlets, yard hydrants
with weeps, flush valves, laundry machines, dishwashers, medical water
aspirators, mobile homes and carbonated beverage machines.

One would think that section title Special Applications and
Installations
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire
Hydrants that any reasonable tradesman would know. If this code truly
intends to apply to both Yard Hydrants and Fire Hydrants then it would
not be special
and the wording would be Hydrants. Incidentally there is no mention of
any fire protection related devices at all in the section. All mention
of fire protection devices, which surely must have special distinction
to most, occurs in a different 890 subsection. Claiming this section
applies also to fire protection is to expand its special scope to
included another very special application, thereby denying the section's
purpose.

The question stills stands for those in the Illinois area. Is this
actually the state's stance? For the case where I heard about this, the
state will be making another arm of the state put an RPZ device in a
hot box on the piping between an ordinary, existing fire hydrant and the
private main it connects to, because that one hydrant is being moved due
to a new drive and that section of existing underground is being
replace, not as its own small project but as part of a much larger
project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, rfletc...@aerofire.com wrote:

 The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines 
 to FP systems. RPZ's are required for systems with chemicals like 
 antifreeze or AFFF and double checks for others. It says they are not 
 required for private hydrant only lines that comply with city water 
 main and AWWA standards.

 To the best of my knowledge there is no requirement in the 
 International Plumbing Code.


 Ron Fletcher
 Aero Automatic
 Phoenix, AZ




 -Original Message-
 From: sprinklerforum-boun...@firesprinkler.org
 [mailto:sprinklerforum-boun...@firesprinkler.org
 ] On Behalf Of Timothy W Goins
 Sent: Wednesday, June 06, 2012 5:40 AM
 To: sprinklerforum@firesprinkler.org
 Subject: Re: RPZ for a dedicated private underground fire mains having

 fire hydrants

 Most THINK that the AWWA recommends BFP's on ALL firelines, especially

 deadened lines over 100 feet, but the AWWA does NOT recommend backflow

 protection on hydrant only lines.

 For I am not ashamed of the gospel , , because it is God's power 

Re: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Ron Greenman
 Greenman rongreen...@gmail.com:
 
  I think the backflow prevention device manufacturers have a lot of
  influence with a fair share of regulatory agencies.
 
  On Tue, Jun 5, 2012 at 9:05 PM, Steve Leyton
  st...@protectiondesign.com
  wrote:
 
  Private fire service mains in CA have required backflows for years.
  The type of device varies by water authority standards, but pretty
  much throughout Southern California the use of an RPDA is standard
  practice.
  Whether the downstream connections are sprinklers only, plus one
  hydrant or with multiple hydrants, a backflow appliance is required
  on a private
  fire service main.   The thinking isn't that hydrants represent a
  cross
  connection or contamination threat per se, but that a private
  property owner can make whatever connections they want in the dark
  of night after
  final acceptance testing.   So better safe than sorry,
  bureaucratically
  speaking ...
 
  SML
  In SoCal, where nothing surprises anymore
 
  
 
  From: sprinklerforum-boun...@firesprinkler.org on behalf of
  AKS-Gmail-IMAP
  Sent: Tue 6/5/2012 7:24 PM
  To: sprinklerforum@firesprinkler.org
  Subject: RPZ for a dedicated private underground fire mains having
  fire hydrants
 
 
 
  I am hearing that in Illinois the state plumbing inspectors insist
  on RPZ back flow prevention for fire hydrants on dedicated
  underground private service mains. What is up with that?
 
  Allan Seidel
  St. Louis. MO
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
  -- next part -- A non-text attachment was
  scrubbed...
  Name: winmail.dat
  Type: application/ms-tnef
  Size: 4685 bytes
  Desc: not available
  URL: 
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
  att
  achments/20120605/c0c6b675/attachment.bin
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
  --
  Ron Greenman
  Instructor
  Fire Protection Engineering Technology Bates Technical College
  1101 So. Yakima Ave.
  Tacoma, WA 98405
 
  rgreen...@bates.ctc.edu
 
  http://www.bates.ctc.edu/fireprotection/
 
  253.680.7346
  253.576.9700 (cell)
 
  Member:
  ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
 
  They are happy men whose natures sort with their vocations. -Francis
  Bacon, essayist, philosopher, and statesman (1561-1626)
  -- next part -- An HTML attachment was
  scrubbed...
  URL:
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
  att
  achments/20120605/19d8453d/attachment.html
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 -- next part --
 An HTML attachment was scrubbed...
 URL:
 
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
 s/20120606/015d1967/attachment.html
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/5e773027/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Steve Leyton
We are doing our first building system off RW at this time.  From our
due diligence for the current project, we learned that in NorCal, there
have been a few building systems connected to reclaimed.  There are some
in the Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks
utterly conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

Hey Steve have you been on the design end of a Fire Protection System
using reclaimed water? If you have wanted to know what issues you ran
across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest
and most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire
water.  And of course, the California Dept. of Health has a few opinions
on what you have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

I heard more about this today from an Illinois plumbing inspector. For
those interested, they (or maybe just he) consider a fire hydrant as a
device to which applies Part 890 Plumbing Code Section 890.1140 Special
Applications and Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this
section, i.e. that which are special, are hose outlets, yard hydrants
with weeps, flush valves, laundry machines, dishwashers, medical water
aspirators, mobile homes and carbonated beverage machines.

One would think that section title Special Applications and
Installations
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire
Hydrants that any reasonable tradesman would know. If this code truly
intends to apply to both Yard Hydrants and Fire Hydrants then it would
not be special
and the wording would be Hydrants. Incidentally there is no mention of
any fire protection related devices at all in the section. All mention
of fire protection devices, which surely must have special distinction
to most, occurs in a different 890 subsection. Claiming this section
applies also to fire protection is to expand its special scope to
included another very special application, thereby denying the section's
purpose.

The question stills stands for those in the Illinois area. Is this
actually the state's stance? For the case where I heard about this, the
state will be making another arm of the state put an RPZ device in a
hot box on the piping between an ordinary, existing fire hydrant and the
private main it connects to, because that one hydrant is being moved due
to a new drive and that section of existing underground is being
replace, not as its own small project but as part of a much larger
project.

Allan Seidel
St. Louis, MO

On Jun 6, 2012, at 8:13 AM, rfletc...@aerofire.com wrote:

 The 2006 Uniform Plumbing Code 603.4.16.1requires backflows in lines 
 to FP systems. RPZ's are required for 

RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Steve Leyton
That's for full doc in AutoCad and CA?   Presuming yes, design team
meetings are to be in San Diego?   Only one trip to the project site for
CA inspection?   That's pretty tight, but I'm inclined to do it for a
chance to show HMC what we can do.   


Steve L 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, June 07, 2012 9:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

We are doing our first building system off RW at this time.  From our
due diligence for the current project, we learned that in NorCal, there
have been a few building systems connected to reclaimed.  There are some
in the Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks
utterly conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

Hey Steve have you been on the design end of a Fire Protection System
using reclaimed water? If you have wanted to know what issues you ran
across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest
and most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire
water.  And of course, the California Dept. of Health has a few opinions
on what you have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

I heard more about this today from an Illinois plumbing inspector. For
those interested, they (or maybe just he) consider a fire hydrant as a
device to which applies Part 890 Plumbing Code Section 890.1140 Special
Applications and Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this
section, i.e. that which are special, are hose outlets, yard hydrants
with weeps, flush valves, laundry machines, dishwashers, medical water
aspirators, mobile homes and carbonated beverage machines.

One would think that section title Special Applications and
Installations
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire
Hydrants that any reasonable tradesman would know. If this code truly
intends to apply to both Yard Hydrants and Fire Hydrants then it would
not be special
and the wording would be Hydrants. Incidentally there is no mention of
any fire protection related devices at all in the section. All mention
of fire protection devices, which surely must have special distinction
to most, occurs in a different 890 subsection. Claiming this section
applies also to fire protection is to expand its special scope to
included another very special application, thereby denying the section's
purpose.

The question stills stands for those in the Illinois area. Is this
actually the state's stance? For the case where I 

RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Steve Leyton
Sorry all:  Trying to close a project and replied to the wrong email.

Steve 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, June 07, 2012 10:04 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

That's for full doc in AutoCad and CA?   Presuming yes, design team
meetings are to be in San Diego?   Only one trip to the project site for
CA inspection?   That's pretty tight, but I'm inclined to do it for a
chance to show HMC what we can do.   


Steve L 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve
Leyton
Sent: Thursday, June 07, 2012 9:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

We are doing our first building system off RW at this time.  From our
due diligence for the current project, we learned that in NorCal, there
have been a few building systems connected to reclaimed.  There are some
in the Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks
utterly conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

Hey Steve have you been on the design end of a Fire Protection System
using reclaimed water? If you have wanted to know what issues you ran
across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest
and most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire
water.  And of course, the California Dept. of Health has a few opinions
on what you have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art
Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having
fire hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having
fire hydrants

I heard more about this today from an Illinois plumbing inspector. For
those interested, they (or maybe just he) consider a fire hydrant as a
device to which applies Part 890 Plumbing Code Section 890.1140 Special
Applications and Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this
section, i.e. that which are special, are hose outlets, yard hydrants
with weeps, flush valves, laundry machines, dishwashers, medical water
aspirators, mobile homes and carbonated beverage machines.

One would think that section title Special Applications and
Installations
intends to single out specifically named applications and installations.
For example there is a trade distinction between Yard Hydrants and Fire
Hydrants that any reasonable tradesman would know. If this code truly
intends to apply to both Yard Hydrants and Fire Hydrants then it would
not be special
and the wording would be Hydrants. Incidentally there is no mention of
any fire protection related devices at all in the section. All mention
of fire 

RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Steve Leyton
Dude:

It's a GOVERNMENT REGULATION.  I have no idea what's to wash or flush; chances 
are there's no value to this additional layer of cost and hassle. Next 
question: where does this filthy run-off go?  Not to the storm drain system I 
hope; the otters will be slowly poisoned.

Steve 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Thursday, June 07, 2012 10:10 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Really RW?  We have a few problems with corrosion and MIC in potable water.  
What else might be in these RW system that is going to eat up our systems or I 
suppose might be better as a slim chance.  Can the chemical makeup of RW change 
over time and seasons further complicating what is does to our systems? 

What's the FD going to wash and flush?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation  Facilities Group Burns  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, June 07, 2012 11:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

We are doing our first building system off RW at this time.  From our due 
diligence for the current project, we learned that in NorCal, there have been a 
few building systems connected to reclaimed.  There are some in the 
Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks utterly 
conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

Hey Steve have you been on the design end of a Fire Protection System using 
reclaimed water? If you have wanted to know what issues you ran across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest and most 
obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire water.  
And of course, the California Dept. of Health has a few opinions on what you 
have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

I heard more about this today from an Illinois plumbing inspector. For those 
interested, they (or maybe just he) consider a fire hydrant as a device to 
which applies Part 890 Plumbing Code Section 890.1140 Special Applications and 
Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this section, 
i.e. that which are special, are hose outlets, yard hydrants with weeps, flush 
valves, 

Re: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Ron Greenman
/mailman/listinfo/sprinklerforum
 
 
  -- next part -- A non-text attachment was
  scrubbed...
  Name: winmail.dat
  Type: application/ms-tnef
  Size: 4685 bytes
  Desc: not available
  URL: 
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
  att
  achments/20120605/c0c6b675/attachment.bin
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
  --
  Ron Greenman
  Instructor
  Fire Protection Engineering Technology Bates Technical College
  1101 So. Yakima Ave.
  Tacoma, WA 98405
 
  rgreen...@bates.ctc.edu
 
  http://www.bates.ctc.edu/fireprotection/
 
  253.680.7346
  253.576.9700 (cell)
 
  Member:
  ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
 
  They are happy men whose natures sort with their vocations. -Francis

  Bacon, essayist, philosopher, and statesman (1561-1626)
  -- next part -- An HTML attachment was
  scrubbed...
  URL:
  http://fireball.firesprinkler.org/mailman/private/sprinklerforum/
  att
  achments/20120605/19d8453d/attachment.html
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 
 
 
 
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
  ___
  Sprinklerforum mailing list
  Sprinklerforum@firesprinkler.org
  http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 -- next part --
 An HTML attachment was scrubbed...
 URL:
 http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
 ment
 s/20120606/015d1967/attachment.html
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
 ___
 Sprinklerforum mailing list
 Sprinklerforum@firesprinkler.org
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum




-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

rgreen...@bates.ctc.edu

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/9c8d00e1/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread George Church
In a planter it'll pick up all the fertilizer, dog poop, and whatever else is 
soluble. 
Assume the FD will dump and flush their tank- likely as much water as the 
system took to put it out before they got there.

George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Thursday, June 07, 2012 1:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Really RW?  We have a few problems with corrosion and MIC in potable water.  
What else might be in these RW system that is going to eat up our systems or I 
suppose might be better as a slim chance.  Can the chemical makeup of RW change 
over time and seasons further complicating what is does to our systems? 

What's the FD going to wash and flush?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation  Facilities Group Burns  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, June 07, 2012 11:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

We are doing our first building system off RW at this time.  From our due 
diligence for the current project, we learned that in NorCal, there have been a 
few building systems connected to reclaimed.  There are some in the 
Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks utterly 
conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

Hey Steve have you been on the design end of a Fire Protection System using 
reclaimed water? If you have wanted to know what issues you ran across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest and most 
obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire water.  
And of course, the California Dept. of Health has a few opinions on what you 
have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

I heard more about this today from an Illinois plumbing inspector. For those 
interested, they (or maybe just he) consider a fire hydrant as a device to 
which applies Part 890 Plumbing Code Section 890.1140 Special Applications and 
Installations. The catching sections are 890.1140 e)
1) and 890.1140 e)
2) A) i). All the applications and installations mentioned by this section, 
i.e. that 

RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread George Church
Makes you wonder what we did before all the DCDA, RPZ, etc.

Oh, that's right- a single check, sometimes with a cheater meter, and/or an ALV 
or DPV.
Gosh, remember how many people used to get sick and/or die from our sprinkler 
systems before we added $1200 to $10,000 per system for REAL BFPs?
Hmmno, now that I think about it, I don't recall a single one. And I 
believe we had a tread about it in the Forum's infancy, and no one else did, 
either.


George L.  Church, Jr., CET  
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill, 
Christopher
Sent: Thursday, June 07, 2012 1:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Really RW?  We have a few problems with corrosion and MIC in potable water.  
What else might be in these RW system that is going to eat up our systems or I 
suppose might be better as a slim chance.  Can the chemical makeup of RW change 
over time and seasons further complicating what is does to our systems? 

What's the FD going to wash and flush?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation  Facilities Group Burns  McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: MN





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, June 07, 2012 11:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

We are doing our first building system off RW at this time.  From our due 
diligence for the current project, we learned that in NorCal, there have been a 
few building systems connected to reclaimed.  There are some in the 
Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks utterly 
conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Letterman, Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

Hey Steve have you been on the design end of a Fire Protection System using 
reclaimed water? If you have wanted to know what issues you ran across if any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest and most 
obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire water.  
And of course, the California Dept. of Health has a few opinions on what you 
have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire 
hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of AKS-Gmail-IMAP
Sent: Wednesday, June 06, 2012 10:49 PM
To: sprinklerforum@firesprinkler.org
Subject: Re: RPZ for a dedicated private underground fire mains having fire 
hydrants

I heard more about this today from an Illinois plumbing inspector. For those 
interested, they (or maybe just he) consider a fire hydrant as a device 

RE: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread John Drucker
It's not just the plumbing officials, in one case a local water purveyor
required it hot box and all.oh yea 10 mains feed the site.

John Drucker

-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church
Sent: Thursday, June 07, 2012 5:29 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire
hydrants

Makes you wonder what we did before all the DCDA, RPZ, etc.

Oh, that's right- a single check, sometimes with a cheater meter, and/or an
ALV or DPV.
Gosh, remember how many people used to get sick and/or die from our
sprinkler systems before we added $1200 to $10,000 per system for REAL BFPs?
Hmmno, now that I think about it, I don't recall a single one. And I
believe we had a tread about it in the Forum's infancy, and no one else did,
either.


George L.  Church, Jr., CET
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE   570-837-6335 fax
g...@rowesprinkler.com



-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Cahill,
Christopher
Sent: Thursday, June 07, 2012 1:10 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire
hydrants

Really RW?  We have a few problems with corrosion and MIC in potable water.
What else might be in these RW system that is going to eat up our systems or
I suppose might be better as a slim chance.  Can the chemical makeup of RW
change over time and seasons further complicating what is does to our
systems? 

What's the FD going to wash and flush?

Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation  Facilities Group Burns 
McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
ccah...@burnsmcd.com
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN





-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Steve Leyton
Sent: Thursday, June 07, 2012 11:53 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire
hydrants

We are doing our first building system off RW at this time.  From our due
diligence for the current project, we learned that in NorCal, there have
been a few building systems connected to reclaimed.  There are some in the
Dublin/Pleasanton/Livermore area, if I recall correctly (Tom
McKinnon are you out there?).   We've been told by the water purveyor
that no special treatment is required, but the fire dept. wants a wash 
flush station on the property.   We're configuring the site main with
BFP's as if the source main was potable, and on paper everything looks
utterly conventional.

SML




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Letterman,
Todd
Sent: Thursday, June 07, 2012 9:38 AM
To: 'sprinklerforum@firesprinkler.org'
Subject: Re: RPZ for a dedicated private underground fire mains having fire
hydrants

Hey Steve have you been on the design end of a Fire Protection System using
reclaimed water? If you have wanted to know what issues you ran across if
any?

- Original Message -
From: Steve Leyton [mailto:st...@protectiondesign.com]
Sent: Thursday, June 07, 2012 09:33 AM
To: sprinklerforum@firesprinkler.org sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire
hydrants

Well ... as ridiculous as all this may sound ...

In SoCal, we have water districts that are moving hard into reclaimed
water.   Golf courses and public green areas such as parks and right of
way planters and medians, are being irrigated with reclaimed.  Easiest and
most obvious application for RW as it can work quite well at low
residual pressures.   But water wise thinking being as it is, and
bureaucracy being as IT is, we are now seeing reclaimed used for fire water.
And of course, the California Dept. of Health has a few opinions on what you
have to do with fire apparatus that has pumped RW, such as
completely clean and flush.   So a BFP on a public hydrant, or on FD
suction hose is the next logical legislative solution.

SML 




-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Art Tiroly
Sent: Thursday, June 07, 2012 9:29 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: RPZ for a dedicated private underground fire mains having fire
hydrants

Then should public street hydrants need BFP installed? 


Arthur Tiroly
ATCO Fire Protection Design
Tiroly and Associates
24400 Highland Rd rm 25, CLE 44143
216-621-8899
216-570-7030 Cell
WWW.ATCOfirepro.com

-Original Message-

Re: RPZ for a dedicated private underground fire mains having fire hydrants

2012-06-07 Thread Ron Greenman
, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-- next part --
An HTML attachment was scrubbed...
URL: 
http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120607/315b96da/attachment.html
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


RE: RTI

2012-06-07 Thread Russell Carol Gregory
In our NZ Standard NZS541 a sprinkler with RTI between 50 and 80 is
designated a Special Response Sprinkler. These usually have a 4mm bulb. 
Std Response has a 5mm or larger bulb and the Fast Response has a 3mm
bulb.

Russell Gregory
Ph  03 338 4853
e-mail rcgreg...@snap.net.nz
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
bcasterl...@fsc-inc.com
Sent: Thursday, 7 June 2012 10:34 PM
To: sprinklerforum@firesprinkler.org
Subject: RE:RTI

correction, meter, not feet. i should have looked in 13 instead of trying to
recall and thinking i needed to convert. but i now have another (perhaps
stupid) question re the definition of fast response and standard response:
if fast is RTI=50 or less and standard is 80 or more, what is in between
called? I am really more interested in the reasoning for the DEFINITION in
NFPA #13, not some box of heads in RTI limbo. Any TC members out there not
totally fed-up with me yet?

___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


Re: RTI

2012-06-07 Thread Charles Thurston
Hello

Well the alarm guys that put the heat detector in the elevator shaft need to 
consider the RTI of the sprinkler head in comparison to the RTI of the Heat 
Detector they put within 24 of the sprinkler head also.  Going to be a Pain 
when the the requirement that anything within 48 of the bottom of the pit 
meets NEMA 4 to coordinate locations of the sprinkler head with the alarm 
device..

Thursday, June 7, 2012, 10:34:32 PM, you wrote:

 In our NZ Standard NZS541 a sprinkler with RTI between 50 and 80 is
 designated a Special Response Sprinkler. These usually have a 4mm bulb.
 Std Response has a 5mm or larger bulb and the Fast Response has a 3mm
 bulb.

 Russell Gregory
 Ph  03 338 4853
 e-mail rcgreg...@snap.net.nz


-- 
Best regards,
 Charlesmailto:charl...@mbfsg.com