The problem is there are no low impedance ground available. The mains power cable ground is not low impedance at high frequency and the common mode voltage of inverters will couple a high frequency current into the ground cable. The trick usually used is to isolate logical ground and increase

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-20 Thread Peter Blodow
Przemek, the shield picks up stray energy from the suroundings. The inside of it is a faraday cage and free of electric fields, which is what we aim at. Now, as the shield has picked up the noise energy, (re)converting electromagnetic field energy to real voltage and current, it must get rid

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-18 Thread Steve Stallings
. Steve Stallings -Original Message- From: Przemek Klosowski [mailto:przemek.klosow...@gmail.com] Sent: Wednesday, March 18, 2015 11:12 AM To: Enhanced Machine Controller (EMC) Subject: Re: [Emc-users] VFD causing limits to trip. Huh? On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-18 Thread Karlsson Wang
To: Enhanced Machine Controller (EMC) Subject: Re: [Emc-users] VFD causing limits to trip. Huh? On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow p.blo...@dreki.de wrote: Steve, this is a good description of noise reduction by shielding. To make it more exact, the shield should

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-18 Thread Przemek Klosowski
On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow p.blo...@dreki.de wrote: Steve, this is a good description of noise reduction by shielding. To make it more exact, the shield should be grounded at the end where the lower impedance is, mostly the signal source. This is opposite to what Steve

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Mark Wendt
On Mon, Mar 16, 2015 at 4:40 PM, Karlsson Wang nicklas.karls...@karlssonwang.se wrote: I think you are right and will just try to dig a little bit deeper. A shield is primarily intended to prevent electrostatic coupling from the outside world. So by grounding in the consuming end the shield

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Mark Wendt
On Tue, Mar 17, 2015 at 5:49 AM, Nicklas Karlsson nicklas.karls...@karlssonwang.se wrote: Yes a shield has two primary jobs but ground impedance is far from zero at high frequency. The shield will not stay at fixed potential at high frequency for a noise source. If there are three-phase

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Nicklas Karlsson
Yes a shield has two primary jobs but ground impedance is far from zero at high frequency. The shield will not stay at fixed potential at high frequency for a noise source. If there are three-phase input and a ground Cable summed current thru all four may be zero but there may be a current flow

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Bertho Stultiens
On 03/17/2015 12:33 AM, Karlsson Wang wrote: The frequency converters I have seen for electric motors generate a square wave voltage. To generate a sinus the duty cycle is varied to get sinus voltage in average and usually the current is close to sinus. Most modern converters are class D

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Bertho Stultiens
On 03/16/2015 09:40 PM, Karlsson Wang wrote: A shield is primarily intended to prevent electrostatic coupling from the outside world. So by grounding in the consuming end the shield will get the ground potential of the consumer and the signal cables will be shielded from different external

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Steve Stallings
...@gmail.com] Sent: Monday, March 16, 2015 7:54 AM To: Enhanced Machine Controller (EMC) Subject: Re: [Emc-users] VFD causing limits to trip. Huh? Are the shielded wires only grounded at one end and at the controller end? On Sun, Mar 15, 2015 at 1:22 PM, Karlsson Wang nicklas.karls

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Matt Tucci
Are the shielded wires only grounded at one end and at the controller end? On Sun, Mar 15, 2015 at 1:22 PM, Karlsson Wang nicklas.karls...@karlssonwang.se wrote: I think grounding is the most important. There are normally a common mode voltage at the inverter output to motor so the inverter

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Peter Blodow
-Original Message- From: Matt Tucci [mailto:matt2c1...@gmail.com] Sent: Monday, March 16, 2015 7:54 AM To: Enhanced Machine Controller (EMC) Subject: Re: [Emc-users] VFD causing limits to trip. Huh? Are the shielded wires only grounded at one end and at the controller end? On Sun, Mar 15

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Karlsson Wang
The frequency converters I have seen for electric motors generate a square wave voltage. To generate a sinus the duty cycle is varied to get sinus voltage in average and usually the current is close to sinus. Then it come to quality I guess the large difference is in filters and coupling to

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Karlsson Wang
: [Emc-users] VFD causing limits to trip. Huh? Are the shielded wires only grounded at one end and at the controller end? On Sun, Mar 15, 2015 at 1:22 PM, Karlsson Wang nicklas.karls...@karlssonwang.se wrote: I think grounding is the most important. There are normally

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Greg Bentzinger
Pardon my ignorance... But is there a significant difference between use of shielded cable between VFD and motor vrs lines in hard or flex metal conduit which makes a complete ground at each end? Thanks Greg -- Dive

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Bertho Stultiens
On 03/16/2015 07:33 PM, Greg Bentzinger wrote: Pardon my ignorance... But is there a significant difference between use of shielded cable between VFD and motor vrs lines in hard or flex metal conduit which makes a complete ground at each end? Both cable-shield and a conducting cable-pipe

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Peter C. Wallace
On Sun, 15 Mar 2015, Kirk Wallace wrote: Date: Sun, 15 Mar 2015 07:54:46 -0700 From: Kirk Wallace kwall...@wallacecompany.com Reply-To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net To: emc-users@lists.sourceforge.net Subject: Re: [Emc-users] VFD causing limits

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Russell Brown
I promised to report back so... I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the VFD mains input and that did make a difference. My failing case job ran 70% of the way through where without it the job failed 10% in. Not the complete solution though. I then tried a

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Kirk Wallace
On 03/15/2015 07:39 AM, Russell Brown wrote: I promised to report back so... I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the VFD mains input and that did make a difference. My failing case job ran 70% of the way through where without it the job failed 10% in. Not

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Karlsson Wang
I think grounding is the most important. There are normally a common mode voltage at the inverter output to motor so the inverter power ground will bounce around each time inverter is switched. If this bouncing is coupled to the logic ground there may be a lot of problems. Nicklas Karlsson

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-09 Thread Karlsson Wang
Here http://www.beama.org.uk/en/publications/technical-guides.cfm/motor-shaft-voltages is a another pain in the regions not to far behind called bearing currents. Regards Nicklas Karlsson On Fri, 06 Mar 2015 12:34:07 -0500 Dave Cole linuxcncro...@gmail.com wrote: VFDs and AC servo drives

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-09 Thread Karlsson Wang
Grounding is really important. Noise on logical ground usually cause communication errors and could of course trigger a limit swith, have you tried lower input impedance? A common mode filter on the output may be a good idea. I have the theoretical knowledge but limited experience. Nicklas

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-09 Thread Karlsson Wang
) emc-users@lists.sourceforge.net Sent: Friday, March 6, 2015 1:58:09 PM Subject: Re: [Emc-users] VFD causing limits to trip. Huh? My 2'X4' CNC router has a 2.2 KW water cooled spindle and VFD - the typical Chinese kit off eBay. http://www.ebay.com/itm/221354796303 I'm getting noise

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-07 Thread Kirk Wallace
On 03/07/2015 12:44 AM, Russell Brown wrote: Many thanks for all the input chaps. The consensus seems to be a) Add a mains input filter. b) Shield the limit switch wires. c) Stick ferrites in. d) Mask the problem with a debounce :-) Another method to consider. Common inputs have high

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-07 Thread Russell Brown
Many thanks for all the input chaps. The consensus seems to be a) Add a mains input filter. b) Shield the limit switch wires. c) Stick ferrites in. d) Mask the problem with a debounce :-) As I have a pretty solid failing case, I figure it's worth while seeing if A-C can fix it before masking

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Gregg Eshelman
On 3/6/2015 6:54 AM, Todd Zuercher wrote: You might be able to get away with just adding a debounce to the limit inputs. That worked for me on a machine that was giving me false trips on the X limit. I suspected mine was a dodgy cable at the time, but it might have been cross talk since it

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Gregg Eshelman
On 3/6/2015 1:52 PM, Bruce Layne wrote: The LCD is on an articulated arm, a little above eye level, mounted to the side of the large nonmetallic enclosure. The VFD is mounted in the steel electrical enclosure about five feet lower. The cables all exit through cable clamps in holes on the

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Jon Elson
On 03/06/2015 07:19 PM, Gregg Eshelman wrote: On 3/6/2015 6:54 AM, Todd Zuercher wrote: You might be able to get away with just adding a debounce to the limit inputs. That worked for me on a machine that was giving me false trips on the X limit. I suspected mine was a dodgy cable at the

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread N. Christopher Perry
Zuercher, If Gene is right, then there is a really big loop area. Ether the leads to the motor / drive are taking different paths or the is a big ground loop some place. You could try moving the leads around to confirm what Gene is suggesting. If this is the case, check for ground loops. If

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Watier Yves
Hi Russel, I got exactly the same troubles describes with the VFDs creating a lot of perturbation. Aspiration was also making perturbation for me. Thankfully at my work place we have experts on EMI and Stephen advices are what you need to follow. In my case, to solve it I had to shield the cable

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Matt Tucci
Wiring to the switch is damaged somewhere? On Fri, Mar 6, 2015 at 6:56 AM, Russell Brown russ...@lls.lls.com wrote: I've just fitted one of them there 'Chinese' 2.2kW watercooled motors with a Huanyang VFD as a second spindle on my mill. Last night doing some pocketing, when the cutter got

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Stephen Dubovsky
EMI. VFDs generate lots of it. You're likely getting lots of noise coupled into your limit switch cabling. Shield the vfd wires if possible. Running in a shielded single cable is probably best. Separate the motor and switch cables as much as possible too. On March 6, 2015 6:56:08 AM EST,

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread N. Christopher Perry
You could also put a reactor between the motor and drive. Might be a good idea to put a line filter on the power leads to the drive too. I'm not a fan of shielding, but it's certainly an option as well. N. Christopher Perry On Mar 6, 2015, at 7:36 AM, Stephen Dubovsky smdubov...@gmail.com

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Todd Zuercher
the debounce. - Original Message - From: N. Christopher Perry vwpe...@comcast.net To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net Sent: Friday, March 6, 2015 8:10:55 AM Subject: Re: [Emc-users] VFD causing limits to trip. Huh? You could also put a reactor between the motor

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Dave Cole
VFDs and AC servo drives oftentimes create noise on the incoming AC power lines to the drives.That noise can cause interference issues with system electronics. I recommend you purchase an incoming line filter to keep the noise from backing up into your AC power line. This is a filter I

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Andy Pugh
On 6 Mar 2015, at 12:56, Russell Brown russ...@lls.lls.com wrote: Any ideas what might cause this? Almost certainly EMI. An input filter for the VFD can help. Check eBay for Rasmi they are not expensive. If your mill is not downstream of an RCD then I have one spare you can have.

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Bruce Layne
My 2'X4' CNC router has a 2.2 KW water cooled spindle and VFD - the typical Chinese kit off eBay. http://www.ebay.com/itm/221354796303 I'm getting noise on the video signal that usually causes annoying screen jitter but sometimes blanks out the screen entirely, which can be a bit

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Todd Zuercher
...@thinkingdevices.com To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net Sent: Friday, March 6, 2015 1:58:09 PM Subject: Re: [Emc-users] VFD causing limits to trip. Huh? My 2'X4' CNC router has a 2.2 KW water cooled spindle and VFD - the typical Chinese kit off eBay. http

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread N. Christopher Perry
That's the big brother of the one I picked. N. Christopher Perry On Mar 6, 2015, at 12:34 PM, Dave Cole linuxcncro...@gmail.com wrote: VFDs and AC servo drives oftentimes create noise on the incoming AC power lines to the drives.That noise can cause interference issues with system

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Charles Steinkuehler
On 3/6/2015 1:43 PM, Todd Zuercher wrote: What sort of screen? and where is it in relation to the VFD? We have a router with 2 VFDs mounted on the outside of a wooden cabinet, and they wreak havoc on the CRT display inside the cabinet when they accelerate/decelerate (about 6 inches away). It

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Bruce Layne