Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-20 Thread Karlsson Wang
The problem is there are no low impedance ground available. The mains power 
cable ground is not low impedance at high frequency and the common mode voltage 
of inverters will couple a high frequency current into the ground cable. The 
trick usually used is to isolate logical ground and increase common mode 
resistance to reduce the ground current which also will lower the high 
frequency ground voltage.

From the outside you machine have two or more power cables and one ground 
cable. There will be a capacitance between each output phase from the 
inverters and ground. This capacitance connected to ground is switched between 
the lowest and highest input voltage which of course will make a high 
frequency current flow into the high frequency non zero impedance ground.

If you connect to a star ground inside your machine they will all bounce around 
with the same voltage.

Nicklas Karlsson




On Fri, 20 Mar 2015 17:54:23 +0100
Peter Blodow p.blo...@dreki.de wrote:

 Przemek, the shield picks up stray energy from the suroundings. The 
 inside of it is a faraday cage and free of electric fields, which is 
 what we aim at. Now, as the shield has picked up the noise energy, 
 (re)converting electromagnetic field energy to real voltage and current, 
 it must get rid of it somewhere. This is most quickly done by a low 
 resistance, i.e. low impedance, shorting the noise current to ground on 
 the sending side without reaching the signal consumer.
 Sorry for answering late, I was on a short trip for the last days.
 Peter
 
 
 Am 18.03.2015 17:11, schrieb Przemek Klosowski:
  On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow p.blo...@dreki.de wrote:
  Steve,
  this is a good description of noise reduction by shielding. To make it
  more exact, the shield should be grounded at the end where the lower
  impedance is, mostly the signal source.
  This is opposite to what Steve said, which was to ground near the
  signals are consumed, which makes more sense to me because shield
  potentials, if any, have smaller chance of leaking through to the
  signal wires.
  From the impedance point of view, I would also worry more about
  interference near high-impedance nodes rather than low-impedance
  nodes, just because smal currents result in larger voltages there.
 
  Can you summarize the rationale for your recommendation in the
  language of electromagnetics?
 
 
 
 ---
 Diese E-Mail wurde von Avast Antivirus-Software auf Viren geprüft.
 http://www.avast.com
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-20 Thread Peter Blodow
Przemek, the shield picks up stray energy from the suroundings. The 
inside of it is a faraday cage and free of electric fields, which is 
what we aim at. Now, as the shield has picked up the noise energy, 
(re)converting electromagnetic field energy to real voltage and current, 
it must get rid of it somewhere. This is most quickly done by a low 
resistance, i.e. low impedance, shorting the noise current to ground on 
the sending side without reaching the signal consumer.
Sorry for answering late, I was on a short trip for the last days.
Peter


Am 18.03.2015 17:11, schrieb Przemek Klosowski:
 On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow p.blo...@dreki.de wrote:
 Steve,
 this is a good description of noise reduction by shielding. To make it
 more exact, the shield should be grounded at the end where the lower
 impedance is, mostly the signal source.
 This is opposite to what Steve said, which was to ground near the
 signals are consumed, which makes more sense to me because shield
 potentials, if any, have smaller chance of leaking through to the
 signal wires.
 From the impedance point of view, I would also worry more about
 interference near high-impedance nodes rather than low-impedance
 nodes, just because smal currents result in larger voltages there.

 Can you summarize the rationale for your recommendation in the
 language of electromagnetics?



---
Diese E-Mail wurde von Avast Antivirus-Software auf Viren geprüft.
http://www.avast.com


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-18 Thread Steve Stallings
If one is trying to minimize radiated interference from
a signal source, then grounding the shield at the source 
end makes sense. 

My suggestion of grounding the shield at the consumer
of the signals was based on reducing the likelihood of
a hostile external noise source confusing the consumer.

Steve Stallings

 -Original Message-
 From: Przemek Klosowski [mailto:przemek.klosow...@gmail.com] 
 Sent: Wednesday, March 18, 2015 11:12 AM
 To: Enhanced Machine Controller (EMC)
 Subject: Re: [Emc-users] VFD causing limits to trip. Huh?
 
 On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow 
 p.blo...@dreki.de wrote:
  Steve,
  this is a good description of noise reduction by shielding. 
 To make it
  more exact, the shield should be grounded at the end where the lower
  impedance is, mostly the signal source.
 
 This is opposite to what Steve said, which was to ground near the
 signals are consumed, which makes more sense to me because shield
 potentials, if any, have smaller chance of leaking through to the
 signal wires.
 From the impedance point of view, I would also worry more about
 interference near high-impedance nodes rather than low-impedance
 nodes, just because smal currents result in larger voltages there.
 
 Can you summarize the rationale for your recommendation in the
 language of electromagnetics?
 
 --
 
 Dive into the World of Parallel Programming The Go Parallel 
 Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is 
 your hub for all
 things parallel software development, from weekly thought 
 leadership blogs to
 news, videos, case studies, tutorials and more. Take a look 
 and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users
 


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-18 Thread Karlsson Wang
I also agree about this.


Nicklas Karlsson



On Wed, 18 Mar 2015 12:43:16 -0500
Steve Stallings steve...@newsguy.com wrote:

 If one is trying to minimize radiated interference from
 a signal source, then grounding the shield at the source 
 end makes sense. 
 
 My suggestion of grounding the shield at the consumer
 of the signals was based on reducing the likelihood of
 a hostile external noise source confusing the consumer.
 
 Steve Stallings
 
  -Original Message-
  From: Przemek Klosowski [mailto:przemek.klosow...@gmail.com] 
  Sent: Wednesday, March 18, 2015 11:12 AM
  To: Enhanced Machine Controller (EMC)
  Subject: Re: [Emc-users] VFD causing limits to trip. Huh?
  
  On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow 
  p.blo...@dreki.de wrote:
   Steve,
   this is a good description of noise reduction by shielding. 
  To make it
   more exact, the shield should be grounded at the end where the lower
   impedance is, mostly the signal source.
  
  This is opposite to what Steve said, which was to ground near the
  signals are consumed, which makes more sense to me because shield
  potentials, if any, have smaller chance of leaking through to the
  signal wires.
  From the impedance point of view, I would also worry more about
  interference near high-impedance nodes rather than low-impedance
  nodes, just because smal currents result in larger voltages there.
  
  Can you summarize the rationale for your recommendation in the
  language of electromagnetics?
  
  --
  
  Dive into the World of Parallel Programming The Go Parallel 
  Website, sponsored
  by Intel and developed in partnership with Slashdot Media, is 
  your hub for all
  things parallel software development, from weekly thought 
  leadership blogs to
  news, videos, case studies, tutorials and more. Take a look 
  and join the 
  conversation now. http://goparallel.sourceforge.net/
  ___
  Emc-users mailing list
  Emc-users@lists.sourceforge.net
  https://lists.sourceforge.net/lists/listinfo/emc-users
  
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-18 Thread Przemek Klosowski
On Mon, Mar 16, 2015 at 11:34 AM, Peter Blodow p.blo...@dreki.de wrote:
 Steve,
 this is a good description of noise reduction by shielding. To make it
 more exact, the shield should be grounded at the end where the lower
 impedance is, mostly the signal source.

This is opposite to what Steve said, which was to ground near the
signals are consumed, which makes more sense to me because shield
potentials, if any, have smaller chance of leaking through to the
signal wires.
From the impedance point of view, I would also worry more about
interference near high-impedance nodes rather than low-impedance
nodes, just because smal currents result in larger voltages there.

Can you summarize the rationale for your recommendation in the
language of electromagnetics?

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Mark Wendt
On Mon, Mar 16, 2015 at 4:40 PM, Karlsson  Wang 
nicklas.karls...@karlssonwang.se wrote:

 I think you are right and will just try to dig a little bit deeper.

 A shield is primarily intended to prevent electrostatic coupling from the
 outside world. So by grounding in the consuming end the shield will get the
 ground potential of the consumer and the signal cables will be shielded
 from different external electric fields. This should motivate why as you
 say the shield should be connected in this end only. If there are current
 there is also a potential difference.

 I consider the VFD to be a noise source since it have common mode voltage
 which will emit an electrical field. There is also a capacitance between
 the VFD cables and shield. Since Shield impedance on high frequency is far
 from zero the shield around the VFD cables will not be at GND potential.
 The most common method is to increase common mode inductance by a filter
 but I have also seen active filters which reduce the common mode voltage
 and multiple step voltage inverters.


 Nicklas Karlsson



A shield has two primary jobs - keep interference from the outside getting
in, and keeping the signal inside the shield from getting out.

Mark
--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Mark Wendt
On Tue, Mar 17, 2015 at 5:49 AM, Nicklas Karlsson 
nicklas.karls...@karlssonwang.se wrote:

 Yes a shield has two primary jobs but ground impedance is far from zero at
 high frequency. The shield will not stay at fixed potential at high
 frequency for a noise source.

 If there are three-phase input and a ground Cable summed current thru all
 four may be zero but there may be a current flow from the three-phase
 Cable to to ground cable. At high frequency impedance in ground cable is
 far from zero and there will noise on the ground cable.

 Nicklas Karlsson



True, but as Bertho pointed out, there are a few different ways to skin a
cat when it comes to shielding stray noise.  Filters can be added to the
cable to suppress or allow certain frequency bands, and where and how you
ground the shield can also have a lot to do with what you are actually
shielding from or for.

Mark
--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Nicklas Karlsson
Yes a shield has two primary jobs but ground impedance is far from zero at
high frequency. The shield will not stay at fixed potential at high
frequency for a noise source.

If there are three-phase input and a ground Cable summed current thru all
four may be zero but there may be a current flow from the three-phase
Cable to to ground cable. At high frequency impedance in ground cable is
far from zero and there will noise on the ground cable.

Nicklas Karlsson



 On Mon, Mar 16, 2015 at 4:40 PM, Karlsson  Wang 
 nicklas.karls...@karlssonwang.se wrote:

 I think you are right and will just try to dig a little bit deeper.

 A shield is primarily intended to prevent electrostatic coupling from
 the
 outside world. So by grounding in the consuming end the shield will get
 the
 ground potential of the consumer and the signal cables will be shielded
 from different external electric fields. This should motivate why as you
 say the shield should be connected in this end only. If there are
 current
 there is also a potential difference.

 I consider the VFD to be a noise source since it have common mode
 voltage
 which will emit an electrical field. There is also a capacitance between
 the VFD cables and shield. Since Shield impedance on high frequency is
 far
 from zero the shield around the VFD cables will not be at GND potential.
 The most common method is to increase common mode inductance by a filter
 but I have also seen active filters which reduce the common mode voltage
 and multiple step voltage inverters.


 Nicklas Karlsson



 A shield has two primary jobs - keep interference from the outside getting
 in, and keeping the signal inside the shield from getting out.

 Mark
 --
 Dive into the World of Parallel Programming The Go Parallel Website,
 sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for
 all
 things parallel software development, from weekly thought leadership blogs
 to
 news, videos, case studies, tutorials and more. Take a look and join the
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users




--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-17 Thread Bertho Stultiens
On 03/17/2015 12:33 AM, Karlsson  Wang wrote:
 The frequency converters I have seen for electric motors generate a
 square wave voltage. To generate a sinus the duty cycle is varied to
 get sinus voltage in average and usually the current is close to
 sinus.

Most modern converters are class D amplifiers. One main difference is in
the headroom they provide in the switch-frequency. The cheaper ones have
about one order of magnitude headroom whereas the really good ones have
up to two orders of magnitude headroom, frequency wise (switch frequency
vs. output frequency).

There is a trade-off between output accuracy and cost of switching and
filtering. It all comes down to money ;-)

Second, as you note, the current may be sinusoidal, but that does not
mean that the voltage is sinusoidal. A motor is an inductive load, where
the voltage and current are not in phase. This results in a problem for
control loops where you have to choose between current based or voltage
based regulation. Both have merits, but ultimately, the result of the
output is in the quality of the filters in the VFD and the impedance
matching between VFD, cabling and motor, which have to span a
considerable frequency range.


 Then it come to quality I guess the large difference is in filters
 and coupling to control signal ground. There exist true sinus output
 but I think all of them are sold as true sinus for a higher price.

Yes. The filters are very important. But you have to look at the system
as a whole to build a good one. Components must be matched properly for
best results.
Non-sinusoidal drivers may be adequate for many systems, but when the
power goes up, the EMI pollution generally increases too. It is a
question of keeping EMI under control. Eliminating it completely is utopia.

-- 
Greetings Bertho

(disclaimers are disclaimed)

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Bertho Stultiens
On 03/16/2015 09:40 PM, Karlsson  Wang wrote:
 A shield is primarily intended to prevent electrostatic coupling from
 the outside world. So by grounding in the consuming end the shield
 will get the ground potential of the consumer and the signal cables
 will be shielded from different external electric fields. This should
 motivate why as you say the shield should be connected in this end
 only. If there are current there is also a potential difference.

There are generally three cases to consider:
1) a shield as a Faraday cage; this means that only one side of the
shield may be connected to go into the earth/ground star-point where you
maintain an absolute reference of zero (0V). The shield is used to dump
all (most) cable-internal EM radiation into a low-impedance star-point
via the shield.

2) a shield as in a coaxial conductor; here the signal is contained in
the cable and the shield is part of the conducting circuit. This works
on basis of very tightly controlled cable properties and is generally
limited to a specific frequency range per cable specs.

3) all other cases; the shield is connected at both sides and is
intentionally or unintentionally part of the conducting circuit. This
case will generally give you worse results in terms of EMI emissions and
protection. The shield will radiate and may act as an antenna to worsen
the situation.


 I consider the VFD to be a noise source since it have common mode
 voltage which will emit an electrical field. There is also a
 capacitance between the VFD cables and shield. Since Shield impedance
 on high frequency is far from zero the shield around the VFD cables
 will not be at GND potential. The most common method is to increase
 common mode inductance by a filter but I have also seen active
 filters which reduce the common mode voltage and multiple step
 voltage inverters.

With respect to VFD systems; the amount of junk they produce depends on
the quality of the converter.

The best version generates a relatively pure sinusoidal output and the
EMI it generates is very minimal. Such VFD can normally be connected
without problem with unshielded cabling.

The lesser quality emulates a sinusoidal output, but has substantial
higher harmonics. These VFDs are not too shabby, but they can cause
interference. The best solution is to filter the output before putting
it on (long) cables. No shielding is required when the harmonics are
under control, but it generally does not hurt to use a Faraday cage type
shield.

The cheap VFDs are poor substitutes and generate nearing square-wave
output. The amount of EMI from higher harmonics is high and is often
difficult to filter at the source. These VFDs should be used with both
output filters and shielded cabling.

The remaining problem that may arise is EMI from the motor. The
remaining harmonics may radiate from the motor just as easily. That
cannot be solved with shielding of the cables. You must ensure proper
earthing of the motor as well and it should be enclosed in a proper
metal casing.

It should also be noted that VFD frequency changes cause harmonics in
the output. If you turn on/off the hard way, then you can introduce some
transients that are very hard to control. The best way is to control the
up-/down-going frequency such that no abrupt changes can occur and
therefore no transients are allowed to be created due to too fast changes.

-- 
Greetings Bertho

(disclaimers are disclaimed)

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Steve Stallings
I would recommend that shielded signal cables have the
shield grounded only at the end where the signals are 
consumed. 

If a ground is needed by the device at the end of the
cable, you should use a conductor inside rather than 
the shield itself.

If there are signals going both ways, provide the shield
ground connection at the end where the most sensitive
signals are consumed.

The purpose of grounding only one end of the shield is
to prevent current from flowing in the shield itself and
distorting the signals due to electromagnetic coupling.

A shield is primarily intended to prevent electrostatic
coupling from the outside world.

If the cable does not contain sensitive signals, such as
the power cable from a VFD to the spindle, then it is
acceptable to ground both ends of the shield.

Steve Stallings
www.PMDX.com


 -Original Message-
 From: Matt Tucci [mailto:matt2c1...@gmail.com] 
 Sent: Monday, March 16, 2015 7:54 AM
 To: Enhanced Machine Controller (EMC)
 Subject: Re: [Emc-users] VFD causing limits to trip. Huh?
 
 Are the shielded wires only grounded at one end and at the 
 controller end?
 
 On Sun, Mar 15, 2015 at 1:22 PM, Karlsson  Wang 
 nicklas.karls...@karlssonwang.se wrote:
 
  I think grounding is the most important. There are normally 
 a common mode
  voltage at the inverter output to motor so the inverter 
 power ground will
  bounce around each time inverter is switched. If this 
 bouncing is coupled
  to the logic ground there may be a lot of problems.
 
  Nicklas Karlsson
 
 
 
 
  On Sun, 15 Mar 2015 14:39:24 + (GMT)
  russ...@lls.lls.com (Russell Brown) wrote:
 
  
   I promised to report back so...
  
   I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 
 400Hz) on the
   VFD mains input and that did make a difference.  My 
 failing case job ran
   70% of the way through where without it the job failed 
 10% in.  Not the
   complete solution though.
  
   I then tried a ferrite core (mains clipon stylee) on the 
 input of the
   field power supply.  No difference.  A ferrite core (ring 
 with both
   wires looped through it a couple of times) on the output 
 of the 12V
   field power made no difference either.
  
   A ferrite core (ring as above) on the limit switch wires 
 fitted at the
   Mesa end made no difference either.
  
   So...  finally I replaced the limit switch wires with 
 shielded cable
   (grounded only at the Mesa end).  That seemed to do the 
 final trick and
   the job ran all the way through.
  
   Of course I don't know if this is a 100% fix or just enough to get
   through my failing case (other jobs without all the above have run
   fine).  I guess time will tell.
  
   Hope that's useful for someone.
  
   --
Regards,
Russell

 
   | Russell Brown  | MAIL: russ...@lls.com PHONE: 
 01780 471800 |
   | Lady Lodge Systems | WWW Work: http://www.lls.com   
|
   | Peterborough, England  | WWW Play: 
 http://www.ruffle.me.uk |

 
  
  
  
 --
 
   Dive into the World of Parallel Programming The Go 
 Parallel Website,
  sponsored
   by Intel and developed in partnership with Slashdot 
 Media, is your hub
  for all
   things parallel software development, from weekly thought 
 leadership
  blogs to
   news, videos, case studies, tutorials and more. Take a 
 look and join the
   conversation now. http://goparallel.sourceforge.net/
   ___
   Emc-users mailing list
   Emc-users@lists.sourceforge.net
   https://lists.sourceforge.net/lists/listinfo/emc-users
 
 
  
 --
 
  Dive into the World of Parallel Programming The Go Parallel Website,
  sponsored
  by Intel and developed in partnership with Slashdot Media, 
 is your hub for
  all
  things parallel software development, from weekly thought 
 leadership blogs
  to
  news, videos, case studies, tutorials and more. Take a look 
 and join the
  conversation now. http://goparallel.sourceforge.net/
  ___
  Emc-users mailing list
  Emc-users@lists.sourceforge.net
  https://lists.sourceforge.net/lists/listinfo/emc-users
 
 --
 
 Dive into the World of Parallel Programming The Go Parallel 
 Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is 
 your hub for all
 things parallel software development, from weekly thought 
 leadership blogs to
 news, videos, case studies, tutorials and more. Take a look 
 and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Matt Tucci
Are the shielded wires only grounded at one end and at the controller end?

On Sun, Mar 15, 2015 at 1:22 PM, Karlsson  Wang 
nicklas.karls...@karlssonwang.se wrote:

 I think grounding is the most important. There are normally a common mode
 voltage at the inverter output to motor so the inverter power ground will
 bounce around each time inverter is switched. If this bouncing is coupled
 to the logic ground there may be a lot of problems.

 Nicklas Karlsson




 On Sun, 15 Mar 2015 14:39:24 + (GMT)
 russ...@lls.lls.com (Russell Brown) wrote:

 
  I promised to report back so...
 
  I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the
  VFD mains input and that did make a difference.  My failing case job ran
  70% of the way through where without it the job failed 10% in.  Not the
  complete solution though.
 
  I then tried a ferrite core (mains clipon stylee) on the input of the
  field power supply.  No difference.  A ferrite core (ring with both
  wires looped through it a couple of times) on the output of the 12V
  field power made no difference either.
 
  A ferrite core (ring as above) on the limit switch wires fitted at the
  Mesa end made no difference either.
 
  So...  finally I replaced the limit switch wires with shielded cable
  (grounded only at the Mesa end).  That seemed to do the final trick and
  the job ran all the way through.
 
  Of course I don't know if this is a 100% fix or just enough to get
  through my failing case (other jobs without all the above have run
  fine).  I guess time will tell.
 
  Hope that's useful for someone.
 
  --
   Regards,
   Russell
   
  | Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
  | Lady Lodge Systems | WWW Work: http://www.lls.com  |
  | Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
   
 
 
 --
  Dive into the World of Parallel Programming The Go Parallel Website,
 sponsored
  by Intel and developed in partnership with Slashdot Media, is your hub
 for all
  things parallel software development, from weekly thought leadership
 blogs to
  news, videos, case studies, tutorials and more. Take a look and join the
  conversation now. http://goparallel.sourceforge.net/
  ___
  Emc-users mailing list
  Emc-users@lists.sourceforge.net
  https://lists.sourceforge.net/lists/listinfo/emc-users


 --
 Dive into the World of Parallel Programming The Go Parallel Website,
 sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for
 all
 things parallel software development, from weekly thought leadership blogs
 to
 news, videos, case studies, tutorials and more. Take a look and join the
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Peter Blodow
Steve,
this is a good description of noise reduction by shielding. To make it 
more exact, the shield should be grounded at the end where the lower 
impedance is, mostly the signal source. And not using the shield as a 
conductor is useful because any current flow in the shield would cause 
magnetic noise to be induced in the conductors along inside the cable. 
Even in power cables, grounding both ends of the shield may cause ground 
loops,resulting in mains frequency currents (formerly: hum) that are 
hard to locate. Generally, magnetic noise is harder to fight than 
electrostatic.

Peter

Am 16.03.2015 15:41, schrieb Steve Stallings:
 I would recommend that shielded signal cables have the
 shield grounded only at the end where the signals are
 consumed.

 If a ground is needed by the device at the end of the
 cable, you should use a conductor inside rather than
 the shield itself.

 If there are signals going both ways, provide the shield
 ground connection at the end where the most sensitive
 signals are consumed.

 The purpose of grounding only one end of the shield is
 to prevent current from flowing in the shield itself and
 distorting the signals due to electromagnetic coupling.

 A shield is primarily intended to prevent electrostatic
 coupling from the outside world.

 If the cable does not contain sensitive signals, such as
 the power cable from a VFD to the spindle, then it is
 acceptable to ground both ends of the shield.

 Steve Stallings
 www.PMDX.com


 -Original Message-
 From: Matt Tucci [mailto:matt2c1...@gmail.com]
 Sent: Monday, March 16, 2015 7:54 AM
 To: Enhanced Machine Controller (EMC)
 Subject: Re: [Emc-users] VFD causing limits to trip. Huh?

 Are the shielded wires only grounded at one end and at the
 controller end?

 On Sun, Mar 15, 2015 at 1:22 PM, Karlsson  Wang 
 nicklas.karls...@karlssonwang.se wrote:

 I think grounding is the most important. There are normally



---
Diese E-Mail wurde von Avast Antivirus-Software auf Viren geprüft.
http://www.avast.com


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Karlsson Wang
The frequency converters I have seen for electric motors generate a square wave 
voltage. To generate a sinus the duty cycle is varied to get sinus voltage in 
average and usually the current is close to sinus.

Then it come to quality I guess the large difference is in filters and coupling 
to control signal ground. There exist true sinus output but I think all of them 
are sold as true sinus for a higher price.


Nicklas Karlsson




On Mon, 16 Mar 2015 22:19:42 +0100
Bertho Stultiens ber...@vagrearg.org wrote:

 On 03/16/2015 09:40 PM, Karlsson  Wang wrote:
  A shield is primarily intended to prevent electrostatic coupling from
  the outside world. So by grounding in the consuming end the shield
  will get the ground potential of the consumer and the signal cables
  will be shielded from different external electric fields. This should
  motivate why as you say the shield should be connected in this end
  only. If there are current there is also a potential difference.
 
 There are generally three cases to consider:
 1) a shield as a Faraday cage; this means that only one side of the
 shield may be connected to go into the earth/ground star-point where you
 maintain an absolute reference of zero (0V). The shield is used to dump
 all (most) cable-internal EM radiation into a low-impedance star-point
 via the shield.
 
 2) a shield as in a coaxial conductor; here the signal is contained in
 the cable and the shield is part of the conducting circuit. This works
 on basis of very tightly controlled cable properties and is generally
 limited to a specific frequency range per cable specs.
 
 3) all other cases; the shield is connected at both sides and is
 intentionally or unintentionally part of the conducting circuit. This
 case will generally give you worse results in terms of EMI emissions and
 protection. The shield will radiate and may act as an antenna to worsen
 the situation.
 
 
  I consider the VFD to be a noise source since it have common mode
  voltage which will emit an electrical field. There is also a
  capacitance between the VFD cables and shield. Since Shield impedance
  on high frequency is far from zero the shield around the VFD cables
  will not be at GND potential. The most common method is to increase
  common mode inductance by a filter but I have also seen active
  filters which reduce the common mode voltage and multiple step
  voltage inverters.
 
 With respect to VFD systems; the amount of junk they produce depends on
 the quality of the converter.
 
 The best version generates a relatively pure sinusoidal output and the
 EMI it generates is very minimal. Such VFD can normally be connected
 without problem with unshielded cabling.
 
 The lesser quality emulates a sinusoidal output, but has substantial
 higher harmonics. These VFDs are not too shabby, but they can cause
 interference. The best solution is to filter the output before putting
 it on (long) cables. No shielding is required when the harmonics are
 under control, but it generally does not hurt to use a Faraday cage type
 shield.
 
 The cheap VFDs are poor substitutes and generate nearing square-wave
 output. The amount of EMI from higher harmonics is high and is often
 difficult to filter at the source. These VFDs should be used with both
 output filters and shielded cabling.
 
 The remaining problem that may arise is EMI from the motor. The
 remaining harmonics may radiate from the motor just as easily. That
 cannot be solved with shielding of the cables. You must ensure proper
 earthing of the motor as well and it should be enclosed in a proper
 metal casing.
 
 It should also be noted that VFD frequency changes cause harmonics in
 the output. If you turn on/off the hard way, then you can introduce some
 transients that are very hard to control. The best way is to control the
 up-/down-going frequency such that no abrupt changes can occur and
 therefore no transients are allowed to be created due to too fast changes.
 
 -- 
 Greetings Bertho
 
 (disclaimers are disclaimed)
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users


-- 
Karlsson  Wang nicklas.karls...@karlssonwang.se

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought 

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Karlsson Wang
I think you are right and will just try to dig a little bit deeper.

A shield is primarily intended to prevent electrostatic coupling from the 
outside world. So by grounding in the consuming end the shield will get the 
ground potential of the consumer and the signal cables will be shielded from 
different external electric fields. This should motivate why as you say the 
shield should be connected in this end only. If there are current there is also 
a potential difference.

I consider the VFD to be a noise source since it have common mode voltage which 
will emit an electrical field. There is also a capacitance between the VFD 
cables and shield. Since Shield impedance on high frequency is far from zero 
the shield around the VFD cables will not be at GND potential. The most common 
method is to increase common mode inductance by a filter but I have also seen 
active filters which reduce the common mode voltage and multiple step voltage 
inverters.


Nicklas Karlsson



On Mon, 16 Mar 2015 09:41:15 -0500
Steve Stallings steve...@newsguy.com wrote:

 I would recommend that shielded signal cables have the
 shield grounded only at the end where the signals are 
 consumed. 
 
 If a ground is needed by the device at the end of the
 cable, you should use a conductor inside rather than 
 the shield itself.
 
 If there are signals going both ways, provide the shield
 ground connection at the end where the most sensitive
 signals are consumed.
 
 The purpose of grounding only one end of the shield is
 to prevent current from flowing in the shield itself and
 distorting the signals due to electromagnetic coupling.
 
 A shield is primarily intended to prevent electrostatic
 coupling from the outside world.
 
 If the cable does not contain sensitive signals, such as
 the power cable from a VFD to the spindle, then it is
 acceptable to ground both ends of the shield.
 
 Steve Stallings
 www.PMDX.com
 
 
  -Original Message-
  From: Matt Tucci [mailto:matt2c1...@gmail.com] 
  Sent: Monday, March 16, 2015 7:54 AM
  To: Enhanced Machine Controller (EMC)
  Subject: Re: [Emc-users] VFD causing limits to trip. Huh?
  
  Are the shielded wires only grounded at one end and at the 
  controller end?
  
  On Sun, Mar 15, 2015 at 1:22 PM, Karlsson  Wang 
  nicklas.karls...@karlssonwang.se wrote:
  
   I think grounding is the most important. There are normally 
  a common mode
   voltage at the inverter output to motor so the inverter 
  power ground will
   bounce around each time inverter is switched. If this 
  bouncing is coupled
   to the logic ground there may be a lot of problems.
  
   Nicklas Karlsson
  
  
  
  
   On Sun, 15 Mar 2015 14:39:24 + (GMT)
   russ...@lls.lls.com (Russell Brown) wrote:
  
   
I promised to report back so...
   
I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 
  400Hz) on the
VFD mains input and that did make a difference.  My 
  failing case job ran
70% of the way through where without it the job failed 
  10% in.  Not the
complete solution though.
   
I then tried a ferrite core (mains clipon stylee) on the 
  input of the
field power supply.  No difference.  A ferrite core (ring 
  with both
wires looped through it a couple of times) on the output 
  of the 12V
field power made no difference either.
   
A ferrite core (ring as above) on the limit switch wires 
  fitted at the
Mesa end made no difference either.
   
So...  finally I replaced the limit switch wires with 
  shielded cable
(grounded only at the Mesa end).  That seemed to do the 
  final trick and
the job ran all the way through.
   
Of course I don't know if this is a 100% fix or just enough to get
through my failing case (other jobs without all the above have run
fine).  I guess time will tell.
   
Hope that's useful for someone.
   
--
 Regards,
 Russell
 
  
| Russell Brown  | MAIL: russ...@lls.com PHONE: 
  01780 471800 |
| Lady Lodge Systems | WWW Work: http://www.lls.com   
 |
| Peterborough, England  | WWW Play: 
  http://www.ruffle.me.uk |
 
  
   
   
   
  --
  
Dive into the World of Parallel Programming The Go 
  Parallel Website,
   sponsored
by Intel and developed in partnership with Slashdot 
  Media, is your hub
   for all
things parallel software development, from weekly thought 
  leadership
   blogs to
news, videos, case studies, tutorials and more. Take a 
  look and join the
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Greg Bentzinger
Pardon my ignorance...

But is there a significant difference between use of shielded cable between VFD 
and motor vrs lines in hard or flex metal conduit which makes a complete ground 
at each end?

Thanks

Greg

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-16 Thread Bertho Stultiens
On 03/16/2015 07:33 PM, Greg Bentzinger wrote:
 Pardon my ignorance...
 
 But is there a significant difference between use of shielded cable 
 between VFD and motor vrs lines in hard or flex metal conduit which 
 makes a complete ground at each end?

Both cable-shield and a conducting cable-pipe will work the same for
most practical purpuses. The trick for effective shields is that it
should not carry the ground (current) from one side to the other. If the
shield is grounded on both sides, then you most probably leak the signal
at the shield (the signal is no longer contained).

The *real* difference is that a (properly) shielded cable has tightly
controlled impedance and coaxial properties, which is an important
attribute and a requirement for most application. Using a pipe will have
an impedance at some level and is not guaranteed to be the same over
the entire length. The result is that you may introduce signal
reflection when using a pipe(*).

Usually, the shield is connected at one (!) star-point connection to
earth where all earth and shield connections come together. It may then
be connected from there to ground using a parallel RC
100..1000k//1..100n@1..2kV (may need to experiment with values for best
suppresion). The resistor is to level any potential (static) buildup and
the capacitor shorts the AC components.

It is a lot cheaper to use a pipe and run some wires in there. But, as
said before, you need to measure the exact impact of doing so. You may
end up worse if you do it wrongly.


(*) With high power signals, such as motor driving lines, reflections
can overload the drivers or the feeding PSU. High-power lines should
always be as short as possible and tightly impedance controlled.

-- 
Greetings Bertho

(disclaimers are disclaimed)

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Peter C. Wallace
On Sun, 15 Mar 2015, Kirk Wallace wrote:

 Date: Sun, 15 Mar 2015 07:54:46 -0700
 From: Kirk Wallace kwall...@wallacecompany.com
 Reply-To: Enhanced Machine Controller (EMC)
 emc-users@lists.sourceforge.net
 To: emc-users@lists.sourceforge.net
 Subject: Re: [Emc-users] VFD causing limits to trip. Huh?
 
 On 03/15/2015 07:39 AM, Russell Brown wrote:

 I promised to report back so...

 I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the
 VFD mains input and that did make a difference.  My failing case job ran
 70% of the way through where without it the job failed 10% in.  Not the
 complete solution though.

 ... snip

 So...  finally I replaced the limit switch wires with shielded cable
 (grounded only at the Mesa end).  That seemed to do the final trick and
 the job ran all the way through.

 ... snip

 Thank you for posting your results. I'll have to put shielding a little
 higher on my list. Don't forget about differential signaling, higher
 signal voltage and formal cable termination.

 -- 
 Kirk Wallace
 http://www.wallacecompany.com/machine_shop/
 http://www.wallacecompany.com/E45/


As a general rule ferrite beads help with current noise
(ground bumping for example) and are not useful on high impedance
inputs while shielding helps with capacitively coupled noise (say from 350V 
square waves from VFD into limit switch wires)




 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users


Peter Wallace
Mesa Electronics

(\__/)
(='.'=) This is Bunny. Copy and paste bunny into your
()_() signature to help him gain world domination.


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Russell Brown

I promised to report back so...

I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the
VFD mains input and that did make a difference.  My failing case job ran
70% of the way through where without it the job failed 10% in.  Not the
complete solution though.

I then tried a ferrite core (mains clipon stylee) on the input of the
field power supply.  No difference.  A ferrite core (ring with both
wires looped through it a couple of times) on the output of the 12V
field power made no difference either.

A ferrite core (ring as above) on the limit switch wires fitted at the
Mesa end made no difference either.

So...  finally I replaced the limit switch wires with shielded cable
(grounded only at the Mesa end).  That seemed to do the final trick and
the job ran all the way through.

Of course I don't know if this is a 100% fix or just enough to get
through my failing case (other jobs without all the above have run
fine).  I guess time will tell.

Hope that's useful for someone.

-- 
 Regards,
 Russell
 
| Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
| Lady Lodge Systems | WWW Work: http://www.lls.com  |
| Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
 

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Kirk Wallace
On 03/15/2015 07:39 AM, Russell Brown wrote:

 I promised to report back so...

 I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the
 VFD mains input and that did make a difference.  My failing case job ran
 70% of the way through where without it the job failed 10% in.  Not the
 complete solution though.

... snip

 So...  finally I replaced the limit switch wires with shielded cable
 (grounded only at the Mesa end).  That seemed to do the final trick and
 the job ran all the way through.

... snip

Thank you for posting your results. I'll have to put shielding a little 
higher on my list. Don't forget about differential signaling, higher 
signal voltage and formal cable termination.

-- 
Kirk Wallace
http://www.wallacecompany.com/machine_shop/
http://www.wallacecompany.com/E45/

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-15 Thread Karlsson Wang
I think grounding is the most important. There are normally a common mode 
voltage at the inverter output to motor so the inverter power ground will 
bounce around each time inverter is switched. If this bouncing is coupled to 
the logic ground there may be a lot of problems.

Nicklas Karlsson




On Sun, 15 Mar 2015 14:39:24 + (GMT)
russ...@lls.lls.com (Russell Brown) wrote:

 
 I promised to report back so...
 
 I fitted the filter (Schaffner FN2030 Series 16A 250 V ac 400Hz) on the
 VFD mains input and that did make a difference.  My failing case job ran
 70% of the way through where without it the job failed 10% in.  Not the
 complete solution though.
 
 I then tried a ferrite core (mains clipon stylee) on the input of the
 field power supply.  No difference.  A ferrite core (ring with both
 wires looped through it a couple of times) on the output of the 12V
 field power made no difference either.
 
 A ferrite core (ring as above) on the limit switch wires fitted at the
 Mesa end made no difference either.
 
 So...  finally I replaced the limit switch wires with shielded cable
 (grounded only at the Mesa end).  That seemed to do the final trick and
 the job ran all the way through.
 
 Of course I don't know if this is a 100% fix or just enough to get
 through my failing case (other jobs without all the above have run
 fine).  I guess time will tell.
 
 Hope that's useful for someone.
 
 -- 
  Regards,
  Russell
  
 | Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
 | Lady Lodge Systems | WWW Work: http://www.lls.com  |
 | Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
  
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-09 Thread Karlsson Wang
Here 
http://www.beama.org.uk/en/publications/technical-guides.cfm/motor-shaft-voltages
 is a another pain in the regions not to far behind called bearing currents.

Regards Nicklas Karlsson


On Fri, 06 Mar 2015 12:34:07 -0500
Dave Cole linuxcncro...@gmail.com wrote:

 VFDs and AC servo drives oftentimes create noise on the incoming AC 
 power lines to the drives.That noise can cause interference issues 
 with system electronics.
 
 I recommend you purchase an incoming line filter to keep the noise from 
 backing up into your AC power line.
 
 This is a filter I used on a recent installation.  Put this as close to 
 the drive/s power input connection as practical.
 
 http://www.automationdirect.com/adc/Shopping/Catalog/Drives/AC_Drive_%28VFD%29_Spare_Parts_-a-_Accessories/GS_EMI_-z-_RF_Filters/EMI_-z-_RF_Filters_%28All_GS_Drives%29/20DRT1W3S
 
 There are cheaper filters available but I know that this one works.
 
 Dave
 
 
 On 3/6/2015 6:56 AM, Russell Brown wrote:
  I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
  with a Huanyang VFD as a second spindle on my mill.
 
  Last night doing some pocketing, when the cutter got into the 'meat' of
  the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
  Axis 2 limit switch.
 
  This was unexpected as I was nowhere near the Z-axis limit switches so I
  checked the connections and started the job again  and it did
  exactly the same thing again in the same place!
 
  Just for fun, I reduced the DOC, tried again and the same thing happened
  in the same place (about 20 seconds into the job).  H
 
  The VFD is 1 foot away from the limit switch wiring, and the connection
  from the VFD to the motor is shielded and grounded at the VFD end.  I'm
  controlling the VFD with hy_vfd over RS485.
 
  The limit switches (normal microswitches bolted to the column) are wired
  to a Mesa 7i76 with 12V field power and have not played up before.
 
  I did an 'air-cut' and that ran well past the place it was consistently
  failing.
 
  I commented out:
 
  #net both-home-z =  axis.2.home-sw-in
  #net both-home-z =  axis.2.neg-lim-sw-in
  #net both-home-z =  axis.2.pos-lim-sw-in
 
  in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
  were left unchanged.
 
  I ran out of time to experiment much further but I'm struggling to see
  how the VFD could trip a simple limit switch when it's getting a bit
  loaded up (the spindle was only pulling ~1amp according to hy_vfd and
  it's rated for 8).
 
  I don't think it was simple vibration as I'd been fly cutting with my
  normal spindle shortly before and that didn't trip anything.
 
  Any ideas what might cause this?
 
 
 ---
 This email has been checked for viruses by Avast antivirus software.
 http://www.avast.com
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-09 Thread Karlsson Wang
Grounding is really important. Noise on logical ground usually cause 
communication errors and could of course trigger a limit swith, have you tried 
lower input impedance?

A common mode filter on the output may be a good idea.

I have the theoretical knowledge but limited experience.


Nicklas Karlsson




On Sat, 7 Mar 2015 08:44:11 + (GMT)
russ...@lls.lls.com (Russell Brown) wrote:

 
 Many thanks for all the input chaps.
 
 The consensus seems to be 
 
 a) Add a mains input filter.
 b) Shield the limit switch wires.
 c) Stick ferrites in.
 d) Mask the problem with a debounce :-)
 
 As I have a pretty solid failing case, I figure it's worth while seeing
 if A-C can fix it before masking the problem with a debounce.
 
 So I've ordered a filter; Schaffner FN2030 Series 16A 250 V ac 400Hz on
 the basis that Arceurotrade suggest them for their spindles and RS stock
 them :)
 
 I'll also replace the limit switch wires with twisted pair shielded and
 sprinkle some ferrites on the 7i76 inputs.
 
 I'll report back on the results.
 
 -- 
  Regards,
  Russell
  
 | Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
 | Lady Lodge Systems | WWW Work: http://www.lls.com  |
 | Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
  
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-09 Thread Karlsson Wang
The inverter output voltage have very fast flanks to get low switching losses 
and the circuit is closed by the capacitance in motor to protective earth. 
There are usually also a capacitance between internal transistors and cooling 
fin connected to protective earth. The capacitances charge/discharge with the 
switching frequency and usually cause severe problem with digital communication 
unless not mitigated. I have also read there may be current thru the bearings 
and EDM is known method for material removal.

A common mode filter rise the impedance in the loop from the power cables to 
the protective earth. I have also seen articles with active filters but not 
tried them myself yet.


Nicklas Karlsson



On Fri, 6 Mar 2015 14:43:00 -0500 (EST)
Todd  Zuercher zuerc...@embarqmail.com wrote:

 What sort of screen? and where is it in relation to the VFD?  We have a 
 router with 2 VFDs mounted on the outside of a wooden cabinet, and they wreak 
 havoc on the CRT display inside the cabinet when they accelerate/decelerate 
 (about 6 inches away).  It is fine while its running, just when stopping and 
 starting.  I was thinking I should make some sort of metal shield to mount 
 between them, but its been that way for more than 15 years without any thing 
 more than this aesthetic problem so it hasn't been real high on my to do 
 list. 
 
 - Original Message -
 From: Bruce Layne linux...@thinkingdevices.com
 To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net
 Sent: Friday, March 6, 2015 1:58:09 PM
 Subject: Re: [Emc-users] VFD causing limits to trip. Huh?
 
 
 My 2'X4' CNC router has a 2.2 KW water cooled spindle and VFD - the 
 typical Chinese kit off eBay.
 
 http://www.ebay.com/itm/221354796303
 
 I'm getting noise on the video signal that usually causes annoying 
 screen jitter but sometimes blanks out the screen entirely, which can be 
 a bit disconcerting when running a CNC machine.  That sounds like RFI, 
 but I used good shielded cable between the VFD and spindle motor.  The 
 shield is grounded at the VFD, and I think I upgraded to a better 
 quality shielded video cable, so I then assumed the noise was leaking 
 out as conducted (as opposed to radiated) interference on the VFD's 
 power leads, although I haven't verified that with the digital storage 
 oscilloscope.  I installed some toroids as RF chokes on the incoming VFD 
 power leads and it seemed to help a tiny bit.  I almost never use that 
 machine, so this problem wasn't high on my To Do list, but I'm building 
 a 2'X2' CNC router for me (the larger machine was mostly for my 
 brother), and I'd like to avoid replicating the problem on the second 
 CNC router build.
 
 I just ordered a 14A Rasmi power line input filter on eBay for the VFD.  
 It cost US$16 delivered.
 
 http://www.ebay.com/itm/290958532530
 
 Hat tip to Andy for the recommendation.
 
 
 
 
 On 03/06/2015 12:43 PM, Andy Pugh wrote:
  Almost certainly EMI. An input filter for the VFD can help. Check eBay 
  for Rasmi they are not expensive.
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-07 Thread Kirk Wallace
On 03/07/2015 12:44 AM, Russell Brown wrote:

 Many thanks for all the input chaps.

 The consensus seems to be

 a) Add a mains input filter.
 b) Shield the limit switch wires.
 c) Stick ferrites in.
 d) Mask the problem with a debounce :-)

Another method to consider. Common inputs have high impedance so the 
full induced voltage from noise gets applied to the input. I have often 
found that the signal (the good stuff we want) can drive the input to 
close to 5 Volts, but the input will trip at around 2.5 Volts depending 
on the input type. So the noise can be weaker than the signal and still 
be a problem. Placing a resistor from the input to the input's ground 
can load the noise enough to keep it below 2.5 Volts, but still have the 
signal above the tripping level. Using signal drivers to utilize 12 or 
24 Volt signals I believe is common for commercial machines, and they 
wouldn't add the cost if it were not needed.

Using twisted pair is effective. The twist cancels the induced noise 
which also can reduce the noise below the trip level, but leave the 
signal alone. In my experience, shielding and differential drivers 
haven't been all that effective, but may be worth a try.

Beyond a simple load resistor on the input, there are various methods to 
terminate a cable, such as terminating resistors, matched to the cable 
impedance, at both ends, to RC filters that can load the noise harder 
and leave more of the desired signal.

I would leave software filtering as a last resort.

Adding AC mains filters to VFD's, in my experience, has had the single 
biggest effect.

Also, my HNC lathe had AC filters on the motor leads. When I added a 
VFD, they turned to smoke and puddles of plastic. The filters were 
trying to do their job which is to filter high frequency, but the VFD 
output signal is pure high frequency. I replaced the filters with 
ferrite beads, but this didn't seem to help much.

My HNC lathe has most of the cabling running in common flexible or rigid 
metal conduit which may help. My mill has no cable shielding, just plain 
CAT5 twisted pair, input resistors, AC main filters on the VFD, and so 
far so good.

-- 
Kirk Wallace
http://www.wallacecompany.com/machine_shop/
http://www.wallacecompany.com/E45/

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-07 Thread Russell Brown

Many thanks for all the input chaps.

The consensus seems to be 

a) Add a mains input filter.
b) Shield the limit switch wires.
c) Stick ferrites in.
d) Mask the problem with a debounce :-)

As I have a pretty solid failing case, I figure it's worth while seeing
if A-C can fix it before masking the problem with a debounce.

So I've ordered a filter; Schaffner FN2030 Series 16A 250 V ac 400Hz on
the basis that Arceurotrade suggest them for their spindles and RS stock
them :)

I'll also replace the limit switch wires with twisted pair shielded and
sprinkle some ferrites on the 7i76 inputs.

I'll report back on the results.

-- 
 Regards,
 Russell
 
| Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
| Lady Lodge Systems | WWW Work: http://www.lls.com  |
| Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
 

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Gregg Eshelman
On 3/6/2015 6:54 AM, Todd Zuercher wrote:
 You might be able to get away with just adding a debounce to the limit 
 inputs.  That worked for me on a machine that was giving me false trips on 
 the X limit. I suspected mine was a dodgy cable at the time, but it might 
 have been cross talk since it hasn't given any problems since adding the 
 debounce.

VFDs are supposed to be directly connected to the 3 phase motors, but I 
wonder if it's possible to add capacitors or something to smooth out the 
output.

So far no issues running the early 1940's GE 3HP in my Monarch 12CK with 
a VFD. I never vary the speed from 60Hz. If it fries it *then* I'll 
figure out how to remove the massive thing from the base.


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Gregg Eshelman
On 3/6/2015 1:52 PM, Bruce Layne wrote:

 The LCD is on an articulated arm, a little above eye level, mounted to
 the side of the large nonmetallic enclosure.  The VFD is mounted in the
 steel electrical enclosure about five feet lower.  The cables all exit
 through cable clamps in holes on the bottom of the electrical enclosure.

 I really need to take the digital storage oscilloscope over there to
 quantify the noise problem.  I mostly designed it with EMI in mind to
 prevent problems, then did a couple of quick and dirty obvious fixes
 (better cable routing, ferrite magic beans) that seemed likely to help
 but didn't.  It's time to get serious, figure out the real issue and
 then fix it.  My ears perked up when I saw this thread.  I was hoping
 someone would fix my problem for me.  :-)

Magnetic interference shouldn't directly bother the LCD panel like it 
can a cathode ray tube. Inducing currents into the display cable via 
radio or magnetic interference is where you'll get the problems.

The internal electronics of LCD monitors are usually quite well 
shielded, though more likely to contain interference rather than block 
it out.

Could try a tinfoil hat approach. ;-) Wrap the display cable with 
aluminum tape then ground the ends to the not sticky side.

---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Jon Elson
On 03/06/2015 07:19 PM, Gregg Eshelman wrote:
 On 3/6/2015 6:54 AM, Todd Zuercher wrote:
 You might be able to get away with just adding a debounce to the limit 
 inputs.  That worked for me on a machine that was giving me false trips on 
 the X limit. I suspected mine was a dodgy cable at the time, but it might 
 have been cross talk since it hasn't given any problems since adding the 
 debounce.
 VFDs are supposed to be directly connected to the 3 phase motors, but I
 wonder if it's possible to add capacitors or something to smooth out the
 output.


No, you don't want capacitors directly on the output of the VFD.
The sharp, 400V edges will cause high currents, and either pop
the capacitors or the output transistors.  What you want is
a line filter module at the power input, and if that isn't good
enough, then a set of 3 inductors on the output to the motor.
I found a line filter on the line input cleared up some 
intermittent
problems on my mill.  I used a commercial line filter module.

Jon

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread N. Christopher Perry
Zuercher,

If Gene is right, then there is a really big loop area.  Ether the leads to the 
motor / drive are taking different paths or the is a big ground loop some place.

You could try moving the leads around to confirm what Gene is suggesting.  If 
this is the case, check for ground loops.  If there aren't any, then you should 
consider rearranging you wiring.

N. Christopher Perry

 On Mar 6, 2015, at 3:14 PM, Charles Steinkuehler char...@steinkuehler.net 
 wrote:
 
 On 3/6/2015 1:43 PM, Todd Zuercher wrote:
 What sort of screen? and where is it in relation to the VFD?  We have
 a router with 2 VFDs mounted on the outside of a wooden cabinet, and
 they wreak havoc on the CRT display inside the cabinet when they
 accelerate/decelerate (about 6 inches away).  It is fine while its
 running, just when stopping and starting.  I was thinking I should
 make some sort of metal shield to mount between them, but its been
 that way for more than 15 years without any thing more than this
 aesthetic problem so it hasn't been real high on my to do list.
 
 I know this one:
 
 You need a Mu-Metal shield.  The VFD is throwing enough current around a
 big enough loop it's generating magnetic fields (*NOT* EMI!) and
 distorting the video display.  It happens on speed changes because
 you're drawing lots of current.  It should also happen if you load the
 motor with a deep cut and push it close to it's rated power level.
 
 Really nice broadcast studio monitors are magnetically shielded to avoid
 this, but just about any other CRT monitor won't be.
 
 http://en.wikipedia.org/wiki/Mu-metal
 
 And yes, a magnetic field _is_ a form of EMI (Electro Magnetic
 Interference), but it's at a _really_ low frequency and thus is
 generally not affected by the typical EMI shielding practices that are
 mostly concerned with very high frequency effects.  You might have good
 luck simply turning the VFD to a different orientation (try rotating it
 on it's side or back and see if the problem gets any better or worse).
 
 -- 
 Charles Steinkuehler
 char...@steinkuehler.net
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Watier Yves
Hi Russel,

I got exactly the same troubles describes with the VFDs creating a lot
of perturbation. Aspiration was also making perturbation for me.
Thankfully at my work place we have experts on EMI and Stephen advices
are what you need to follow.

In my case, to solve it I had to shield the cable between the VFD and
the spindle and physically separate them (away from the cable chain in
my case).

Limits and touch probes are now with shielded cables and ferrites.
Also Shields are touching the metallic part of the connectors so as to
be linked to the electronic rack.

Between electronic rack, VFD generator and the machine I have metallic
braids (flat and large). Linking the axis together with this braids
might have helped also (and not relaying on the balls from the guiding
rails).

I also have a metallic plate which shield the control computer from the VFD.

Good luck solving this, sometimes it work for 20 minutes without
tripping a limit, but there is hope even with Chinese parts, now, for
me the setup is reliable.

Cheers,

--
Yves Watier



2015-03-06 13:36 GMT+01:00 Stephen Dubovsky smdubov...@gmail.com:
 EMI.  VFDs generate lots of it. You're likely getting lots of noise coupled 
 into your limit switch cabling.  Shield the vfd wires if possible. Running in 
 a shielded single cable is probably best. Separate the motor and switch 
 cables as much as possible too.

 On March 6, 2015 6:56:08 AM EST, russ...@lls.lls.com wrote:

I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
with a Huanyang VFD as a second spindle on my mill.

Last night doing some pocketing, when the cutter got into the 'meat' of
the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
Axis 2 limit switch.

This was unexpected as I was nowhere near the Z-axis limit switches so
I
checked the connections and started the job again  and it did
exactly the same thing again in the same place!

Just for fun, I reduced the DOC, tried again and the same thing
happened
in the same place (about 20 seconds into the job).  H

The VFD is 1 foot away from the limit switch wiring, and the connection
from the VFD to the motor is shielded and grounded at the VFD end.  I'm
controlling the VFD with hy_vfd over RS485.

The limit switches (normal microswitches bolted to the column) are
wired
to a Mesa 7i76 with 12V field power and have not played up before.

I did an 'air-cut' and that ran well past the place it was consistently
failing.

I commented out:

#net both-home-z =  axis.2.home-sw-in
#net both-home-z =  axis.2.neg-lim-sw-in
#net both-home-z =  axis.2.pos-lim-sw-in

in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
were left unchanged.

I ran out of time to experiment much further but I'm struggling to see
how the VFD could trip a simple limit switch when it's getting a bit
loaded up (the spindle was only pulling ~1amp according to hy_vfd and
it's rated for 8).

I don't think it was simple vibration as I'd been fly cutting with my
normal spindle shortly before and that didn't trip anything.

Any ideas what might cause this?

--
 Regards,
 Russell
 
| Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
| Lady Lodge Systems | WWW Work: http://www.lls.com  |
| Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
 

--
Dive into the World of Parallel Programming The Go Parallel Website,
sponsored
by Intel and developed in partnership with Slashdot Media, is your hub
for all
things parallel software development, from weekly thought leadership
blogs to
news, videos, case studies, tutorials and more. Take a look and join
the
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly 

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Matt Tucci
Wiring to the switch is damaged somewhere?

On Fri, Mar 6, 2015 at 6:56 AM, Russell Brown russ...@lls.lls.com wrote:


 I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
 with a Huanyang VFD as a second spindle on my mill.

 Last night doing some pocketing, when the cutter got into the 'meat' of
 the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
 Axis 2 limit switch.

 This was unexpected as I was nowhere near the Z-axis limit switches so I
 checked the connections and started the job again  and it did
 exactly the same thing again in the same place!

 Just for fun, I reduced the DOC, tried again and the same thing happened
 in the same place (about 20 seconds into the job).  H

 The VFD is 1 foot away from the limit switch wiring, and the connection
 from the VFD to the motor is shielded and grounded at the VFD end.  I'm
 controlling the VFD with hy_vfd over RS485.

 The limit switches (normal microswitches bolted to the column) are wired
 to a Mesa 7i76 with 12V field power and have not played up before.

 I did an 'air-cut' and that ran well past the place it was consistently
 failing.

 I commented out:

 #net both-home-z =  axis.2.home-sw-in
 #net both-home-z =  axis.2.neg-lim-sw-in
 #net both-home-z =  axis.2.pos-lim-sw-in

 in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
 were left unchanged.

 I ran out of time to experiment much further but I'm struggling to see
 how the VFD could trip a simple limit switch when it's getting a bit
 loaded up (the spindle was only pulling ~1amp according to hy_vfd and
 it's rated for 8).

 I don't think it was simple vibration as I'd been fly cutting with my
 normal spindle shortly before and that didn't trip anything.

 Any ideas what might cause this?

 --
  Regards,
  Russell
  
 | Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
 | Lady Lodge Systems | WWW Work: http://www.lls.com  |
 | Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
  


 --
 Dive into the World of Parallel Programming The Go Parallel Website,
 sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for
 all
 things parallel software development, from weekly thought leadership blogs
 to
 news, videos, case studies, tutorials and more. Take a look and join the
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Stephen Dubovsky
EMI.  VFDs generate lots of it. You're likely getting lots of noise coupled 
into your limit switch cabling.  Shield the vfd wires if possible. Running in a 
shielded single cable is probably best. Separate the motor and switch cables as 
much as possible too. 

On March 6, 2015 6:56:08 AM EST, russ...@lls.lls.com wrote:

I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
with a Huanyang VFD as a second spindle on my mill.

Last night doing some pocketing, when the cutter got into the 'meat' of
the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
Axis 2 limit switch.

This was unexpected as I was nowhere near the Z-axis limit switches so
I
checked the connections and started the job again  and it did
exactly the same thing again in the same place!

Just for fun, I reduced the DOC, tried again and the same thing
happened
in the same place (about 20 seconds into the job).  H

The VFD is 1 foot away from the limit switch wiring, and the connection
from the VFD to the motor is shielded and grounded at the VFD end.  I'm
controlling the VFD with hy_vfd over RS485.

The limit switches (normal microswitches bolted to the column) are
wired
to a Mesa 7i76 with 12V field power and have not played up before.

I did an 'air-cut' and that ran well past the place it was consistently
failing.

I commented out:

#net both-home-z =  axis.2.home-sw-in
#net both-home-z =  axis.2.neg-lim-sw-in
#net both-home-z =  axis.2.pos-lim-sw-in

in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
were left unchanged.

I ran out of time to experiment much further but I'm struggling to see
how the VFD could trip a simple limit switch when it's getting a bit
loaded up (the spindle was only pulling ~1amp according to hy_vfd and
it's rated for 8).

I don't think it was simple vibration as I'd been fly cutting with my
normal spindle shortly before and that didn't trip anything.

Any ideas what might cause this?

-- 
 Regards,
 Russell
 
| Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
| Lady Lodge Systems | WWW Work: http://www.lls.com  |
| Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
 

--
Dive into the World of Parallel Programming The Go Parallel Website,
sponsored
by Intel and developed in partnership with Slashdot Media, is your hub
for all
things parallel software development, from weekly thought leadership
blogs to
news, videos, case studies, tutorials and more. Take a look and join
the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users
--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread N. Christopher Perry
You could also put a reactor between the motor and drive.  Might be a good idea 
to put a line filter on the power leads to the drive too.

I'm not a fan of shielding, but it's certainly an option as well.

N. Christopher Perry

 On Mar 6, 2015, at 7:36 AM, Stephen Dubovsky smdubov...@gmail.com wrote:
 
 EMI.  VFDs generate lots of it. You're likely getting lots of noise coupled 
 into your limit switch cabling.  Shield the vfd wires if possible. Running in 
 a shielded single cable is probably best. Separate the motor and switch 
 cables as much as possible too. 
 
 On March 6, 2015 6:56:08 AM EST, russ...@lls.lls.com wrote:
 
 I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
 with a Huanyang VFD as a second spindle on my mill.
 
 Last night doing some pocketing, when the cutter got into the 'meat' of
 the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
 Axis 2 limit switch.
 
 This was unexpected as I was nowhere near the Z-axis limit switches so
 I
 checked the connections and started the job again  and it did
 exactly the same thing again in the same place!
 
 Just for fun, I reduced the DOC, tried again and the same thing
 happened
 in the same place (about 20 seconds into the job).  H
 
 The VFD is 1 foot away from the limit switch wiring, and the connection
 from the VFD to the motor is shielded and grounded at the VFD end.  I'm
 controlling the VFD with hy_vfd over RS485.
 
 The limit switches (normal microswitches bolted to the column) are
 wired
 to a Mesa 7i76 with 12V field power and have not played up before.
 
 I did an 'air-cut' and that ran well past the place it was consistently
 failing.
 
 I commented out:
 
 #net both-home-z =  axis.2.home-sw-in
 #net both-home-z =  axis.2.neg-lim-sw-in
 #net both-home-z =  axis.2.pos-lim-sw-in
 
 in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
 were left unchanged.
 
 I ran out of time to experiment much further but I'm struggling to see
 how the VFD could trip a simple limit switch when it's getting a bit
 loaded up (the spindle was only pulling ~1amp according to hy_vfd and
 it's rated for 8).
 
 I don't think it was simple vibration as I'd been fly cutting with my
 normal spindle shortly before and that didn't trip anything.
 
 Any ideas what might cause this?
 
 -- 
 Regards,
   Russell
 
 | Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
 | Lady Lodge Systems | WWW Work: http://www.lls.com  |
 | Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website,
 sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub
 for all
 things parallel software development, from weekly thought leadership
 blogs to
 news, videos, case studies, tutorials and more. Take a look and join
 the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Todd Zuercher
You might be able to get away with just adding a debounce to the limit inputs.  
That worked for me on a machine that was giving me false trips on the X limit. 
I suspected mine was a dodgy cable at the time, but it might have been cross 
talk since it hasn't given any problems since adding the debounce.

- Original Message -
From: N. Christopher Perry vwpe...@comcast.net
To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net
Sent: Friday, March 6, 2015 8:10:55 AM
Subject: Re: [Emc-users] VFD causing limits to trip. Huh?

You could also put a reactor between the motor and drive.  Might be a good idea 
to put a line filter on the power leads to the drive too.

I'm not a fan of shielding, but it's certainly an option as well.

N. Christopher Perry

 On Mar 6, 2015, at 7:36 AM, Stephen Dubovsky smdubov...@gmail.com wrote:
 
 EMI.  VFDs generate lots of it. You're likely getting lots of noise coupled 
 into your limit switch cabling.  Shield the vfd wires if possible. Running in 
 a shielded single cable is probably best. Separate the motor and switch 
 cables as much as possible too. 
 
 On March 6, 2015 6:56:08 AM EST, russ...@lls.lls.com wrote:
 
 I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
 with a Huanyang VFD as a second spindle on my mill.
 
 Last night doing some pocketing, when the cutter got into the 'meat' of
 the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
 Axis 2 limit switch.
 
 This was unexpected as I was nowhere near the Z-axis limit switches so
 I
 checked the connections and started the job again  and it did
 exactly the same thing again in the same place!
 
 Just for fun, I reduced the DOC, tried again and the same thing
 happened
 in the same place (about 20 seconds into the job).  H
 
 The VFD is 1 foot away from the limit switch wiring, and the connection
 from the VFD to the motor is shielded and grounded at the VFD end.  I'm
 controlling the VFD with hy_vfd over RS485.
 
 The limit switches (normal microswitches bolted to the column) are
 wired
 to a Mesa 7i76 with 12V field power and have not played up before.
 
 I did an 'air-cut' and that ran well past the place it was consistently
 failing.
 
 I commented out:
 
 #net both-home-z =  axis.2.home-sw-in
 #net both-home-z =  axis.2.neg-lim-sw-in
 #net both-home-z =  axis.2.pos-lim-sw-in
 
 in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
 were left unchanged.
 
 I ran out of time to experiment much further but I'm struggling to see
 how the VFD could trip a simple limit switch when it's getting a bit
 loaded up (the spindle was only pulling ~1amp according to hy_vfd and
 it's rated for 8).
 
 I don't think it was simple vibration as I'd been fly cutting with my
 normal spindle shortly before and that didn't trip anything.
 
 Any ideas what might cause this?
 
 -- 
 Regards,
   Russell
 
 | Russell Brown  | MAIL: russ...@lls.com PHONE: 01780 471800 |
 | Lady Lodge Systems | WWW Work: http://www.lls.com  |
 | Peterborough, England  | WWW Play: http://www.ruffle.me.uk |
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website,
 sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub
 for all
 things parallel software development, from weekly thought leadership
 blogs to
 news, videos, case studies, tutorials and more. Take a look and join
 the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc

Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Dave Cole
VFDs and AC servo drives oftentimes create noise on the incoming AC 
power lines to the drives.That noise can cause interference issues 
with system electronics.

I recommend you purchase an incoming line filter to keep the noise from 
backing up into your AC power line.

This is a filter I used on a recent installation.  Put this as close to 
the drive/s power input connection as practical.

http://www.automationdirect.com/adc/Shopping/Catalog/Drives/AC_Drive_%28VFD%29_Spare_Parts_-a-_Accessories/GS_EMI_-z-_RF_Filters/EMI_-z-_RF_Filters_%28All_GS_Drives%29/20DRT1W3S

There are cheaper filters available but I know that this one works.

Dave


On 3/6/2015 6:56 AM, Russell Brown wrote:
 I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
 with a Huanyang VFD as a second spindle on my mill.

 Last night doing some pocketing, when the cutter got into the 'meat' of
 the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
 Axis 2 limit switch.

 This was unexpected as I was nowhere near the Z-axis limit switches so I
 checked the connections and started the job again  and it did
 exactly the same thing again in the same place!

 Just for fun, I reduced the DOC, tried again and the same thing happened
 in the same place (about 20 seconds into the job).  H

 The VFD is 1 foot away from the limit switch wiring, and the connection
 from the VFD to the motor is shielded and grounded at the VFD end.  I'm
 controlling the VFD with hy_vfd over RS485.

 The limit switches (normal microswitches bolted to the column) are wired
 to a Mesa 7i76 with 12V field power and have not played up before.

 I did an 'air-cut' and that ran well past the place it was consistently
 failing.

 I commented out:

 #net both-home-z =  axis.2.home-sw-in
 #net both-home-z =  axis.2.neg-lim-sw-in
 #net both-home-z =  axis.2.pos-lim-sw-in

 in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
 were left unchanged.

 I ran out of time to experiment much further but I'm struggling to see
 how the VFD could trip a simple limit switch when it's getting a bit
 loaded up (the spindle was only pulling ~1amp according to hy_vfd and
 it's rated for 8).

 I don't think it was simple vibration as I'd been fly cutting with my
 normal spindle shortly before and that didn't trip anything.

 Any ideas what might cause this?


---
This email has been checked for viruses by Avast antivirus software.
http://www.avast.com


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Andy Pugh



 On 6 Mar 2015, at 12:56, Russell Brown russ...@lls.lls.com wrote:
 
 Any ideas what might cause this?

Almost certainly EMI. An input filter for the VFD can help. Check eBay for 
Rasmi they are not expensive.  
If your mill is not downstream of an RCD then I have one spare you can have. 
Otherwise make sure you get one with 3mA leakage current.  (This point is why 
I have a spare) 
Note that these go on the input to the VFD to keep noise out of the mains 
wiring. 

But the really simple solution is likely to be the HAL debounce component. 
20mS delay in a limit switch isn't critical. 
--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Bruce Layne

My 2'X4' CNC router has a 2.2 KW water cooled spindle and VFD - the 
typical Chinese kit off eBay.

http://www.ebay.com/itm/221354796303

I'm getting noise on the video signal that usually causes annoying 
screen jitter but sometimes blanks out the screen entirely, which can be 
a bit disconcerting when running a CNC machine.  That sounds like RFI, 
but I used good shielded cable between the VFD and spindle motor.  The 
shield is grounded at the VFD, and I think I upgraded to a better 
quality shielded video cable, so I then assumed the noise was leaking 
out as conducted (as opposed to radiated) interference on the VFD's 
power leads, although I haven't verified that with the digital storage 
oscilloscope.  I installed some toroids as RF chokes on the incoming VFD 
power leads and it seemed to help a tiny bit.  I almost never use that 
machine, so this problem wasn't high on my To Do list, but I'm building 
a 2'X2' CNC router for me (the larger machine was mostly for my 
brother), and I'd like to avoid replicating the problem on the second 
CNC router build.

I just ordered a 14A Rasmi power line input filter on eBay for the VFD.  
It cost US$16 delivered.

http://www.ebay.com/itm/290958532530

Hat tip to Andy for the recommendation.




On 03/06/2015 12:43 PM, Andy Pugh wrote:
 Almost certainly EMI. An input filter for the VFD can help. Check eBay 
 for Rasmi they are not expensive.


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Todd Zuercher
What sort of screen? and where is it in relation to the VFD?  We have a router 
with 2 VFDs mounted on the outside of a wooden cabinet, and they wreak havoc on 
the CRT display inside the cabinet when they accelerate/decelerate (about 6 
inches away).  It is fine while its running, just when stopping and starting.  
I was thinking I should make some sort of metal shield to mount between them, 
but its been that way for more than 15 years without any thing more than this 
aesthetic problem so it hasn't been real high on my to do list. 

- Original Message -
From: Bruce Layne linux...@thinkingdevices.com
To: Enhanced Machine Controller (EMC) emc-users@lists.sourceforge.net
Sent: Friday, March 6, 2015 1:58:09 PM
Subject: Re: [Emc-users] VFD causing limits to trip. Huh?


My 2'X4' CNC router has a 2.2 KW water cooled spindle and VFD - the 
typical Chinese kit off eBay.

http://www.ebay.com/itm/221354796303

I'm getting noise on the video signal that usually causes annoying 
screen jitter but sometimes blanks out the screen entirely, which can be 
a bit disconcerting when running a CNC machine.  That sounds like RFI, 
but I used good shielded cable between the VFD and spindle motor.  The 
shield is grounded at the VFD, and I think I upgraded to a better 
quality shielded video cable, so I then assumed the noise was leaking 
out as conducted (as opposed to radiated) interference on the VFD's 
power leads, although I haven't verified that with the digital storage 
oscilloscope.  I installed some toroids as RF chokes on the incoming VFD 
power leads and it seemed to help a tiny bit.  I almost never use that 
machine, so this problem wasn't high on my To Do list, but I'm building 
a 2'X2' CNC router for me (the larger machine was mostly for my 
brother), and I'd like to avoid replicating the problem on the second 
CNC router build.

I just ordered a 14A Rasmi power line input filter on eBay for the VFD.  
It cost US$16 delivered.

http://www.ebay.com/itm/290958532530

Hat tip to Andy for the recommendation.




On 03/06/2015 12:43 PM, Andy Pugh wrote:
 Almost certainly EMI. An input filter for the VFD can help. Check eBay 
 for Rasmi they are not expensive.


--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread N. Christopher Perry
That's the big brother of the one I picked.

N. Christopher Perry

 On Mar 6, 2015, at 12:34 PM, Dave Cole linuxcncro...@gmail.com wrote:
 
 VFDs and AC servo drives oftentimes create noise on the incoming AC 
 power lines to the drives.That noise can cause interference issues 
 with system electronics.
 
 I recommend you purchase an incoming line filter to keep the noise from 
 backing up into your AC power line.
 
 This is a filter I used on a recent installation.  Put this as close to 
 the drive/s power input connection as practical.
 
 http://www.automationdirect.com/adc/Shopping/Catalog/Drives/AC_Drive_%28VFD%29_Spare_Parts_-a-_Accessories/GS_EMI_-z-_RF_Filters/EMI_-z-_RF_Filters_%28All_GS_Drives%29/20DRT1W3S
 
 There are cheaper filters available but I know that this one works.
 
 Dave
 
 
 On 3/6/2015 6:56 AM, Russell Brown wrote:
 I've just fitted one of them there 'Chinese' 2.2kW watercooled motors
 with a Huanyang VFD as a second spindle on my mill.
 
 Last night doing some pocketing, when the cutter got into the 'meat' of
 the cut (6mm carbide 2 flute, 3mm DOC), Linuxcnc (v2.6.7) tripped with
 Axis 2 limit switch.
 
 This was unexpected as I was nowhere near the Z-axis limit switches so I
 checked the connections and started the job again  and it did
 exactly the same thing again in the same place!
 
 Just for fun, I reduced the DOC, tried again and the same thing happened
 in the same place (about 20 seconds into the job).  H
 
 The VFD is 1 foot away from the limit switch wiring, and the connection
 from the VFD to the motor is shielded and grounded at the VFD end.  I'm
 controlling the VFD with hy_vfd over RS485.
 
 The limit switches (normal microswitches bolted to the column) are wired
 to a Mesa 7i76 with 12V field power and have not played up before.
 
 I did an 'air-cut' and that ran well past the place it was consistently
 failing.
 
 I commented out:
 
 #net both-home-z =  axis.2.home-sw-in
 #net both-home-z =  axis.2.neg-lim-sw-in
 #net both-home-z =  axis.2.pos-lim-sw-in
 
 in my Mill.hal file and the job ran to the end.  Axis 0 and 1 limits
 were left unchanged.
 
 I ran out of time to experiment much further but I'm struggling to see
 how the VFD could trip a simple limit switch when it's getting a bit
 loaded up (the spindle was only pulling ~1amp according to hy_vfd and
 it's rated for 8).
 
 I don't think it was simple vibration as I'd been fly cutting with my
 normal spindle shortly before and that didn't trip anything.
 
 Any ideas what might cause this?
 
 ---
 This email has been checked for viruses by Avast antivirus software.
 http://www.avast.com
 
 
 --
 Dive into the World of Parallel Programming The Go Parallel Website, sponsored
 by Intel and developed in partnership with Slashdot Media, is your hub for all
 things parallel software development, from weekly thought leadership blogs to
 news, videos, case studies, tutorials and more. Take a look and join the 
 conversation now. http://goparallel.sourceforge.net/
 ___
 Emc-users mailing list
 Emc-users@lists.sourceforge.net
 https://lists.sourceforge.net/lists/listinfo/emc-users

--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Charles Steinkuehler
On 3/6/2015 1:43 PM, Todd Zuercher wrote:
 What sort of screen? and where is it in relation to the VFD?  We have
 a router with 2 VFDs mounted on the outside of a wooden cabinet, and
 they wreak havoc on the CRT display inside the cabinet when they
 accelerate/decelerate (about 6 inches away).  It is fine while its
 running, just when stopping and starting.  I was thinking I should
 make some sort of metal shield to mount between them, but its been
 that way for more than 15 years without any thing more than this
 aesthetic problem so it hasn't been real high on my to do list.

I know this one:

You need a Mu-Metal shield.  The VFD is throwing enough current around a
big enough loop it's generating magnetic fields (*NOT* EMI!) and
distorting the video display.  It happens on speed changes because
you're drawing lots of current.  It should also happen if you load the
motor with a deep cut and push it close to it's rated power level.

Really nice broadcast studio monitors are magnetically shielded to avoid
this, but just about any other CRT monitor won't be.

http://en.wikipedia.org/wiki/Mu-metal

And yes, a magnetic field _is_ a form of EMI (Electro Magnetic
Interference), but it's at a _really_ low frequency and thus is
generally not affected by the typical EMI shielding practices that are
mostly concerned with very high frequency effects.  You might have good
luck simply turning the VFD to a different orientation (try rotating it
on it's side or back and see if the problem gets any better or worse).

-- 
Charles Steinkuehler
char...@steinkuehler.net



signature.asc
Description: OpenPGP digital signature
--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users


Re: [Emc-users] VFD causing limits to trip. Huh?

2015-03-06 Thread Bruce Layne


On 03/06/2015 02:43 PM, Todd Zuercher wrote:
 What sort of screen?

20 LCD.  Dell, I think.



 Where is it in relation to the VFD?

The LCD is on an articulated arm, a little above eye level, mounted to 
the side of the large nonmetallic enclosure.  The VFD is mounted in the 
steel electrical enclosure about five feet lower.  The cables all exit 
through cable clamps in holes on the bottom of the electrical enclosure.

I really need to take the digital storage oscilloscope over there to 
quantify the noise problem.  I mostly designed it with EMI in mind to 
prevent problems, then did a couple of quick and dirty obvious fixes 
(better cable routing, ferrite magic beans) that seemed likely to help 
but didn't.  It's time to get serious, figure out the real issue and 
then fix it.  My ears perked up when I saw this thread.  I was hoping 
someone would fix my problem for me.  :-)




--
Dive into the World of Parallel Programming The Go Parallel Website, sponsored
by Intel and developed in partnership with Slashdot Media, is your hub for all
things parallel software development, from weekly thought leadership blogs to
news, videos, case studies, tutorials and more. Take a look and join the 
conversation now. http://goparallel.sourceforge.net/
___
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users