I was talking to signature solar today.
Signature solar and EG4 are sister companies. I don’t have info if one owns the
other or if they are equal partners?
They did admit they bought OB. But didn’t know if signature or EG4 bought them.
Jay
has 3 vaults and a Radian. JohnOn Mon, May 20, 2024 at 7:22 PM jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:HI All
I got a call from a fellow installer who needs a UL listed lithium battery.
Say 30-50 kwh. open loop as its working with existing OB radians.
Could be o
old.To say I am curious about what is going on is an understatement. Aloha,Lou Russo Ownerl...@spreesolarsystems.com808 345 6762Spree Solar Systems LLC CT-34322On Sun, May 19, 2024 at 2:21 AM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:I agree with you WilliamWhile there
results allow that.Dan FinkOwner, Buckville Energy Consulting LLCIREC Certified Instructor for PV and Small Wind InstallationNABCEP Certified PV System InspectorNABCEP PV Associatedanbo...@gmail.com970-672-4342 On Mon, May 20, 2024 at 5:22 PM jay via RE-wrenches <re-wrenches@lists.re-wrenches.
HI All
I got a call from a fellow installer who needs a UL listed lithium battery.
Say 30-50 kwh. open loop as its working with existing OB radians.
Could be outside or inside
It so confusing to find the right battery I’d thought I would ask what folks
are using/recommending.
thanks
jay
I agree with you WilliamWhile there could be all sorts of valid reasons for the downtime. What’s not acceptable is the lack of communication and notification that it was going to happen or had happened. If they do have new owners they are not starting well. JayOn May 18, 2024, at 9:42 PM, William
It’s an interesting design. I went to a seminar on it. Wiring the main power distribution center, is a bit tricky with how they designed or not wire room. Probably want to use cobra wire. The battery voltage design is unusual in that more batteries increases the voltage, not bad just different.
HI William,
Yes the FM-100 has no problem with keeping the volts pretty tight and i’ve not
heard of any lithium related issues, and someone is bound to chime in if there
are.
jay
> On May 8, 2024, at 9:39 AM, William Miller wrote:
>
> Jay:
>
> I am considering ditching
.
jay
> On May 8, 2024, at 9:00 AM, William Miller wrote:
>
> Jay:
>
> Thank you for taking the time.
>
> We are doing just what you suggest as an interim solution.
>
> The shortcoming of this work-around is that the highest setting for this
> relay function is
A possible fix.
You could run a DC relay on the SB PV input that would be voltage triggered to
prevent the battery volts from getting higher than you want.
The SI has 2 aux relays I think? Or could do a tristar with RD-1 relay that
has 4 channels.
Just a thought
jay
> On May 7, 2024, at
Hi WilliamHave you talked to fortress about the SOC getting so out of calibration in such a short period of time?JayOn May 7, 2024, at 11:16 PM, William Miller via RE-wrenches wrote:Friends: I am still wrestling with problems integrating a Sunny Island / Sunny Boy AC coupled system to a set of 5
I wanted to follow up on this thread. According to the sol Ark website. The US 8 kw is rated at 120/240. Which I’ve always thought mean 3 wire. L1,L2,N. The US 5kw is 120v only. L1, N Do I have this correct?JayOn May 4, 2024, at 9:15 AM, Tom McCalmont via RE-wrenches wrote:It does not do
Maybe the new 5kw 120v unit is the 8kw at 120v?JayOn May 3, 2024, at 4:22 PM, Tom McCalmont via RE-wrenches wrote:David is correct. We have some experience with Sol-Ark’s inverter, and it’s a good product. However, be aware that you can configure it either as a 120V inverter with a max. output
According to the nameplate 6% @ 170°cOn Apr 26, 2024, at 4:33 PM, Darryl Thayer via RE-wrenches wrote:Do you know the transformer impedance?On Fri, Apr 26, 2024, 5:54 PM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:Hi all.
Anyone know what the tare loss and effi
with propane heat, cooking, water heater, dryer and no
AC.
I don’t know.
Thanks
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver
AC future breaker panel. All lighting was Edison base lamps, and all wiring was NMB Romex. I wired like a normal house except for a 120-v panel and 12-v panel I relay and momentary switch by appliance for easy turning on of AC inverter. On Wed, Apr 24, 2024 at 8:49 AM Jay via RE-wrenches <
Yeah definitely no second battery. On Apr 24, 2024, at 6:41 AM, Howie Michaelson via RE-wrenches wrote:Jason,My vote would be for using a 120 to 12vDC power supply large enough to handle the remaining 12 vDC loads and skip the second battery bank. In my mind, this is simpler, cleaner, and if the
I agree with John. Most 12v fridges have small compressors. But I don’t know what they have. Personally a major reason to go 120/ac is to get a normal refrigerator. But you can measure the surge/load and then size the charger accordingly. One feature of going charger is the lights are a lot
I’ve done this many times
I use an Iota or power max charger to run the DC.
Jay
> On Apr 23, 2024, at 2:42 PM, Jason Szumlanski via RE-wrenches
> wrote:
>
>
> I have an off-grid client who is working on replacing old equipment at a
> cabin. He has a lot of 12
HI All
Speaking of batteries I wonder what you all make of this.
I was reading the Fortress battery manual and it says they don’t recommend
adding new lithium batteries to older lithium batteries if the age is over 1
year difference.
Thoughts?
thanks
jay
ler Troubleshoot Help
>
> It may be the fan. I had an FM 80 where the fan went bad that caused very
> limited solar production throughout the day.
>
> Michael D Nelson
> MD Electric & Solar, Inc.
> 707-684-0064 mobile
> 707-884-1862 office
> www.mdelectricsolar.co
.
the 80 takes 3 minutes, the 60 takes 2 hours.
jay
> On Apr 23, 2024, at 6:00 AM, Jim Gowdy via RE-wrenches
> wrote:
>
> I'm troubleshooting the solar aspect of a small offgrid 120v outback system
> and need some opinions. The customer was complaining that the generator was
>
vs 8kw inverter.
And if customer decides to go more solar, then the AIO is already set up to add
more with $0 expense on the CC side.
A whole new world
Jay
> On Apr 10, 2024, at 11:06 AM, Maverick Brown via RE-wrenches
> wrote:
>
> Logan
>
> Is MidNite making the AI
you go the smaller the wire.
My 2 cents
jay
> On Apr 10, 2024, at 10:40 AM, Chris Daum via RE-wrenches
> wrote:
>
>
> The crazy things folks do. Dear people: We have a fellow who has an initial
> off-grid array with a Radian 8048A (and related e-panel, etc.) and si
Hi David,
I’m going to disagree.
The fortress and EG4 are made by LUX.
It says so right on the cover.
And I’ve talked to Fortress about this.
Sol Ark is made by Deye
Jay
> On Apr 10, 2024, at 10:12 AM, david quattro wrote:
>
> I have not installed an Fortress yet, but I know they
Can you explain what changes the eg4 18 inverter has vs the Envy as to LA
programming?
To me the Envy has a big advantage due to it having AGS warm up/cool down that
the EG4 does not.
Jay
> On Apr 10, 2024, at 7:49 AM, Howie Michaelson via RE-wrenches
> wrote:
>
> Jo
Hi scott
Yes I think for new larger systems the AIO are the present/future
Jay
> On Apr 9, 2024, at 9:42 PM, scot.a...@solarcentex.com wrote:
>
>
> Wow, are we in the golden age of inverter/chargers? If it had 200-a.p pass
> thru it would be near perfect.
>
> Begs th
Hi All,
Does anyone know the pricing and when it’ll be available?
The New Midnite MN15-12KW-AIO All in One (AIO) inverter
Looks good.
thanks
jay___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List
If your looking to fasten into the steel pipe you look at Dynamicfasteners.comGreat productsJayOn Apr 3, 2024, at 5:34 PM, david quattro via RE-wrenches wrote:because it is an awning seems like you may be able to disturb the roof layer above the purlins, even if temporarily?If so then i think an
2 things. Maybe you can sell them a service contract and clear/check the events 1x week via optics. I don’t know if there is a way to prioritize events. To me Ive always had good success with the fndc in regards to be pretty accurate for reading %. Getting rid of it seems the wrong way to go. And
As to the envy not being good for LA batteries. Yes rhe 60v max is just too low. Does it have 3 stage charging?I’m curious to see what the new midnite solar inverter has to offer. It shows up to 64v battery. JayOn Mar 28, 2024, at 6:44 AM, John Blittersdorf via RE-wrenches wrote:Howie, I
Here is an interesting design. PowerField Energy PowerRack PV solar ballasted ground mount systemsolar-electric.comOn Mar 21, 2024, at 11:08 AM, Bradley Bassett via RE-wrenches wrote:Is Aerocompact still around ? They had a nice simple ballasted ground mountBrad BassettOn Thu, Mar 21, 2024,
on who you get on the phone if they will help you or not
which isn’t good.
Thats why I”m looking for any help to find the right phone number or person who
will/can help.
I’m guessing its either the envoy needs to be rebooted or its broken.
thanks
jay
> On Mar 15, 2024, at 11:49 AM, da
have a person/number etc of who will help them?
Thanks
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
HI All
Any recommendations for quality DC fountain pumps?
Brands, suppliers etc
thanks
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change
Hi williamFor checking level the best trick I’ve ever seen is a solid glass rod. I can’t remember if you have to grind one end flat or not. When you put the end into the water the top end your looking at changes color. The side you look at would be the one you grind. Mark the rod with tape or use
of the ITC?
I figure it adds something but not 30%. However I have no data to go on.
Anyone know anything I might tell him or a link to a study etc?
Thanks in advance
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http
Hi williamIs California now doing demand charges? And is it instantaneous or 15 minute average? JayOn Feb 25, 2024, at 11:23 AM, William Miller via RE-wrenches wrote:Friends:I am pondering a plan to prevent usage spikes. It would involve installing a battery inverter that has true generator
Hi williamFronius 7.6 kw are in stock. I’ve installed a number of fronius with no issues. JayOn Feb 22, 2024, at 4:56 PM, William Miller via RE-wrenches wrote:Friends: Now that RSS is required on almost every installation, I am having trouble finding a plain old, non-battery, non-MLPE string
Hi JohnThe work around is to make sure you e got a new enough serial number to at least talk to them about what ever the issue is. But this is a huge new development in a bad way.JayOn Feb 22, 2024, at 6:55 AM, John Blittersdorf via RE-wrenches wrote:I just tried to get Outback tech support and
Does anyone have a working phone number for AP systems?
I have a system that works but all the LED lights don’t work on the inverters
thanks
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List
A number of people have mentioned strict code compliance.
How are lead batteries dealing with this?
thanks
jay
> On Feb 17, 2024, at 12:27 PM, Ray Walters via RE-wrenches
> wrote:
>
> Chris;
>
> I was definitely moving to the LFP camp for off grid for all the same reason
fortress is making improvements to their firmware for sure. The fortress envy 12 has generator warmup/cool down which is a really important feature IMO. The eg4 not. Nor does the Deye sol ark. JayOn Feb 16, 2024, at 8:48 PM, Chris Sparadeo via RE-wrenches wrote:Howie,The EG4 18K and the
Hi williamCould you share the equipment used and what issues you had?ThxJayOn Feb 14, 2024, at 3:13 PM, William Miller via RE-wrenches wrote:Peter: I have only purchased one set of Fortress batteries. There have been issues, I am sure many of them self-induced. Fortress has been overall very
Hi Kevin
Thanks, I heard that exact thing from someone else.
Do you know if the CC are connected via Xanbus, does that also prevent EQ in
the CC?
Jay
> On Feb 12, 2024, at 4:36 PM, Kevin Pegg via RE-wrenches
> wrote:
>
> I have seen the same behaviour on a few older XW60
thoughts?
thanks
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cg
I would use a sealed relay. The SS one should work. Or a 12v cube relay like in cars. Super cheap and reliable JayBOSCH 0332209150 Changeover Mini Relay - 5 Pins, 12 V, 20/30 A - Singleamazon.comOn Feb 9, 2024, at 12:55 PM, William Miller via RE-wrenches wrote:Dan: I think a solid state relay
st? I knew it was
time.
Sincerely,
Ray Walters
Remote Solar
On 2/7/2024 9:19 AM, jay via
RE-wrenches wrote:
One of the things that I’m just now learning is about BMS
failure/warranty/fix/replacement.
Some can be field
Hi All,
Can anyone tell me off the top of their head if older Rolls
6CS 25PS
Do they have welded or bolted internal connections?
I have a site I’m going to, very remote that might have a bad cell or two and
I’m just figuring out how I’m going to bypass the bad cells.
thanks
jay
One of the things that I’m just now learning is about BMS
failure/warranty/fix/replacement.
Some can be field installed some need to go back to the OEM.
I guess its something else we need to check on.
Jay
> On Feb 7, 2024, at 9:06 AM, Bradley Bassett via RE-wrenches
>
I guess the SCP is back in production.
But if I understand correctly you still need the insight to program the XWPRO
versions?
thx
jay
> On Feb 7, 2024, at 8:50 AM, Drake Chamberlin via RE-wrenches
> wrote:
>
> My experience with using Insight and Xanbus is that the projec
Does anyone know if Lorentz pumps still exist in the US.
Someone is looking for a PS200 control box.
It seems to be intermittent
Thx
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address
I’d use an IMO disconnect as you don’t have any current limitations.
I think sometimes things get lost in translation.
Jay
> On Jan 18, 2024, at 8:43 AM, Jason Szumlanski via RE-wrenches
> wrote:
>
>
> I am installing an EG4 off-grid 3k inverter for the first time, an
or not?
thanks in advance
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cg
There is or was a setting in the mate 3/s that the rebulk volts has a trigger. If the voltage doesn’t get below it it won’t charge (absorb) properly. Fix is to set the rebulk up higher than the charge voltsI don’t know if that’s your issue or not but I have fixed this on systems. JayOn Jan 12,
.
Jay
> On Jan 3, 2024, at 3:04 PM, Ron Young via RE-wrenches
> wrote:
>
> Hi Wrenches & Happy New Year!
>
> I have a client who wants to switch between two 24v 800 a/h battery banks. I
> know this isn’t a recommended strategy and have advised him accordingl
I think that using a megger etc to test the panels and wires is what I’d do before I yanked out all the Wires. They are not that expensive anymore and maybe possible to rent one?JayOn Dec 13, 2023, at 8:53 AM, Dave Tedeyan via RE-wrenches wrote:Hi All,I am curious to hear if anyone else has run
Hi Drake
Try this one. I get a lot of equipment from supply house.
Since you need on with temp rise it’s an AC type.
This one will do 8 amps at 120v so a small amp dc fan won’t hurt the relay.
Jay
https://www.supplyhouse.com/White-Rodgers-1609-101-Refrigeration-Temperature-Control-30
Agreed to all said. Numerous systems with mate 3/3s and every inverter and stacking is all fine. New hub 10:3 required. MX CC don’t appear on the mate 3/s. Few of my systems are on optics so can’t comment on that. JayOn Dec 12, 2023, at 1:15 PM, Roland Shackelford via RE-wrenches wrote:We have
there that should work for a
holes. Just thought I’d check to see if anyone has any suggestions.
Thx
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change
my assumption. However an open relay exhibits some fairly high impedance. The symptoms indicate the SI shuts down but the batteries remain connected. Something allows 69 volts on the battery terminals…William MillerMiller Solar.com805-438-5600www.millersolar.comOn Sun, Nov 12, 2023 at 2:22 PM Jay
Maybe someone else knows differently but it was explained to me that the fortress batteries have a relay that disconnects the battery if the voltage gets to high or low. There isn’t any electronic device to change battery impedance besides what the actual cells are doing. JayOn Nov 12, 2023, at
I’ve wondered what other variables are at work given that mostly these connectors work as they should. I’d like to see them come with plugs covering the openings. This would keep dirt, salt air, moisture, etc out until they are connected. As to if there were lots of failures with SW modules then
It depends a lot on the what you want.
open chassis
sound enclosed
super quite
tier 4
prime/standby
built in 2 wire start
etc.
MQ power make great units.
https://www.mqpower.com/whisperwatt.html
<https://www.mqpower.com/whisperwatt.html>
jay
> On Nov 4, 2023, at 7:45 AM, Mac Lew
.
---
Drake Chamberlin
Athens Electric LLC
Ohio Electrical Contractor’s License 44810
NABCEP Certified PV Installation Professional
On 2023-10-31 12:14, Jay via RE-wrenches wrote:
Is the radian connected to grid sell?
If so then I'd say yes the higher grid voltage is preventing
You could ask the wrenches bout how to make the window wider?
I don’t know
jay
> On Oct 31, 2023, at 10:14 AM, Jay wrote:
>
> Is the radian connected to grid sell?
>
> If so then I’d say yes the higher grid voltage is preventing connection.
>
> Jay
>
>&g
Is the radian connected to grid sell? If so then I’d say yes the higher grid voltage is preventing connection. JayOn Oct 31, 2023, at 9:35 AM, Drake Chamberlin via RE-wrenches wrote:
Jay,
It was a problem that surfaced before. Outback tech support was unable to figure it out. Then, the problem
to 264VAC.On Mon, Oct 30, 2023 at 6:57 AM Drake Chamberlin via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:
Hi Jay,
The inverter won't even connect to the grid. It stays in the state where it is sampling the grid, AC in light blinking.
Is the default high voltage for the nominal 240 V 28
below the
rebulk volts. If you’re deep cycling it usually will with default settings
The default high voltage window for ac input is default at 140v.
Hope this helps
Jay
> On Oct 29, 2023, at 11:14 AM, Drake Chamberlin via RE-wrenches
> wrote:
>
>
> My Radian GS 8048
I’m going to both agree and disagree Agree The older inverters ( Schneider, Outback, etc) your drawing is correct. Disagree For many new inverters ( sol ark, ev4, fortress) they bring ac coupling into the inverter directly. Usually on the generator input and not in the backup loads panel. And I
the
chemistry.
3. lower the LBCO all the way down and if using AGS then lower the volts on
that to and also reduce the run time/abosrb time.
Good luck,
Jay
> On Oct 27, 2023, at 9:49 AM, Howie Michaelson via RE-wrenches
> wrote:
>
> Hey Will,
>
> At the ri
is doing fine.
Its 3% per 1000, and the variables of density altitude are: temperature,
humidity, air pressure, elevation.
I don’t understand why the generator support would allow for higher amps as
well?
jay
> On Oct 27, 2023, at 11:40 AM, Darryl Thayer via RE-wrenches
>
Hi BradOut of curiosity, what is the actual difference between the two on those cloudy days. ThxJayOn Oct 25, 2023, at 5:04 PM, Bradley Bassett via RE-wrenches wrote:I used to have both an array at a 60° tilt and one at 14° tilt. In the winter the high tilt array did better on sunny days, and on
it. By my math we should be able to see about 6KW+/- of charging power. We are using Generator input mode I believe. We will try switching to Support mode and see if that helps. By the way batteries are 8- Simpliphi 3.8. Sent from my Galaxy Original message From: Jay via RE
Hi all.
Any quick answers about how the ITC tax credit deals with loans on a solar
system?
Thanks
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
What is the charger ac limit set to?JayOn Oct 25, 2023, at 2:38 PM, Mac Lewis via RE-wrenches wrote:Hi Amos,What input mode are you using?Try switching to "support" mode and see if the charging current increases. On Wed, Oct 25, 2023, 1:24 PM Amos Post via RE-wrenches
Hi williamCan you tell us which SI/SB you have?JayOn Oct 21, 2023, at 5:49 PM, William Miller via RE-wrenches wrote:Friends:I’m kinda stuck on a project setting up a SI/SB AC coupled system off grid. When the SB inverters ramp up the battery voltage jumps to 69 pretty quickly and the system
I tell my clients to wash your panels like you’d wash your car. Similar soaps if needed to remove pollen or harder to remove things and softer bristle brushes help. Doing it during the heat of the day means a larger chance of mineral deposits vs cooler times depending on your water. Myself I don’t
In my buddies case, most definitely XW Pro
jay
> On Oct 13, 2023, at 9:39 AM, Dave Angelini Offgrid Solar via RE-wrenches
> wrote:
>
> It must be an XW+ that died. The XW pro field circuit validation testing beta
> was complete in early 2019.
>
> That XWP is stil
I have a buddy that has had two different stacked pairs with issues. It took months of back and forth on the one which they did replace them however one of the inverters sent from Schneider was a euro 230/50hz. Taking another trip and more delay. And same guy, another project with monitoring etc
Does anyone have a link or picture of the ground anchor in question? I couldn’t find one. ThxJayOn Oct 12, 2023, at 7:07 AM, Dave Tedeyan via RE-wrenches wrote:Jeff, Thanks for the notes and things to look for from the field. I was not aware that there are two versions of their PowerJack out
Buy another SOK battery so that doesn’t happen. Or maybe happens lessJayOn Oct 11, 2023, at 5:55 PM, Kristopher Schmid via RE-wrenches wrote:Hello brain trust,Anyone have experience with SOK lithiums? Here's my issue. Client has a tiny home and bought their system online (I know, run away...).
I’d look at a 3 phase pump with vfd/soft start control and eliminate the start
surge.
Jay
> On Oct 11, 2023, at 8:12 AM, frenergy via RE-wrenches
> wrote:
>
>
> I'm looking for opinions and/or real world experience on recommendation for
> the largest 240V submersible
Hi guys
It’s for a 240vac relay between the generator and inverter so I can do warm up
/cool down.
It’s a 15kw generator derates to about 10-12 so 60-75 amps is all I am looking
for.
I’ll put it into a box of some sort.
Thx
Jay
> On Oct 3, 2023, at 3:47 PM, Starlight via RE-wrenc
.
Thanks
jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenche
I like the idea but haven’t used it yet. I don’t see any code issues with the longer wiring?JayOn Sep 28, 2023, at 10:52 AM, Kirk Herander via RE-wrenches wrote:All,Has anyone ever mounted MLEs (optimizers, microinverters, RSDs) on the perimeter of the array or elsewhere instead of underneath
I found this brand at Home Depot. No Ac required. Uses battery ignition. I didn’t look into reviews and Ive not used it. JaySummit Appliance 30 in. 3.7 cu. ft. Gas Range in White WNM210Phomedepot.comOn Sep 26, 2023, at 4:16 PM, Dave Angelini Offgrid Solar via RE-wrenches wrote:
Hey David,
I
bars
and plexi dead front vs 4/0 cable.
Jay
> On Sep 21, 2023, at 9:25 PM, frenergy via RE-wrenches
> wrote:
>
> Jay,
>
> I sent a diagram of my proposed arrangement and bus sizes to
> SimpliPhi prior to installation, which they approved. The buses (cop
a picture of an exceptionally large one. 24' long. I'm looking at the rack mounted set up because the bussing and cabling is done. 3 racks of 6 5kwhr batteries. All I will need is cabling from the racks to a small (in size) bussbarOn Mon, Sep 18, 2023 at 3:50 PM Jay <jay.pe...@gmail.com> wrote:
rack mount set up rather than AES's and custom bussing.Jason,That's exactly what I was thinking, if I go the Sol-Ark route. Last time I ordered custom panelboards like that, they were six months out.On Mon, Sep 18, 2023 at 1:18 PM Jay via RE-wrenches <re-wrenches@lists.re-wrenches.org> wrote:I
If 40kw is the peak and then there are new added loads, what 50-60kw? If it was me I’d be designing the inverters to handle the 50/60 kw with future expansion capabilities beyond that. Then how much kWh of storage are you going to need or maybe are planning for?At some point maybe looking at a
As I’ve been researching this, the Atkinson GSCM can do this when coupled to an
external relay.
If I understand correctly.
Jay
The warm up ( on delay ) is 0- 60 seconds,
the cool down ( off delay) is 0-120 seconds
https://thesolarstore.com/manuals/GSCM.pdf
> On Sep 16, 2023, at 9:20
I recently saw this. I haven’t used either, but its looks well done.
https://signaturesolar.com/eg4-powerpro-ess-14-3-28-6kwh-capacity-eg4-18kpv-eg4-powerpro-wallmount-battery-9540-pending/
with on delay relay.
Maybe there is a off the shelf generator transfer switch that has this built in?
Thanks in advance
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches@lists.re
Can you send pictures? JayOn Aug 29, 2023, at 5:54 PM, Jeremy Rodriguez via RE-wrenches wrote:
Leaking from somewhere mid way in the battery case I’m guessing.
The liquid followed a cable down to the BMS board and corroded it badly.
Jeremy Rodriguez
Solar Installation / Design
All
uck! Solar is cheap but boring!Dan FinkOwner, Buckville Energy Consulting LLCIREC Certified Instructor for PV and Small Wind InstallationNABCEP Certified PV System InspectorNABCEP PV Associatedanbo...@gmail.com970-672-4342 On Thu, Aug 17, 2023 at 9:11 AM Jay via RE-wrenches <re-wrenches@lists.re
Yeah just kinda of sad they are gone. Like others, a friend called looking to replace a very old whisper power. Ok more solar it is. ThxJayOn Aug 17, 2023, at 9:51 AM, Roy Butler via RE-wrenches wrote:
Good luck with that search Jay.
Most of the companies
Hi all
Is anyone making a good quality 1-2kw wind machine?
All of my searches come up with nothing.
Thanks in advance
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches
Hi KirkThanks. Their system is from around 2017. Battery/inverter have worked fine. Is there a way to go from offgrid like it is now to grid tie battery backup? And what parts are needed?ThxJayOn Aug 2, 2023, at 6:27 AM, Kirk Herander wrote:Hi Jay,The energy hub is incompatible with older
and battery
backup ( for a sub panel).
Is it just the SE energy hub backup interface? Or?
And does the 7600A work with that?
Thanks in advance
Jay
___
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE