I've quoted a few systems with an IOTA charger and small inverter. I have
not had any feedback yet. I figure the separate battery charger and
inverter won't make the loads flicker so much when the sun comes and goes.
I'm not sure if the SPS comes back automatically when it's been overloaded
That document refers to 2008 NEC 690.9 code which has the exemption that is
used for grounded inverters. Section 690.35 for ungrounded systems just
refers back to 690.9 for over-current protection. So I do not see any
indication that two strings on an ungrounded inverter could not have the
same
I've been promoting the use of the remote on/off terminals that are
available in most inverters, which can be connected to the AUX in the
Birdhouse. For a very minimum effort and cost, the inverter AC output would
be shutdown when the rapid shutdown is activated. I think using the remote
on/off
I have one in a test system charging an Aquion battery. It has 11 REC
modules in one string feeding it. I programmed it using MSView from my
place remotely and once I got all the comm programming right it worked
great. I now monitor it over the company VPN using a browser and it seems
to be
My SMA micro-inverters have been rock solid for a couple of years. They do
not taper off and do not communicate with the Sunny Island. The only issue
I've had is that it seems that an internet connection is needed for the
monitoring to work, even for the local monitoring. If there is no
monitoring
rester between the module(s) and the
> inverter, making micros more vulnerable in that regard.
>
>
>
> Bill Dorsett
>
>
>
> *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On
> Behalf Of *Bradley Bassett
> *Sent:* Thursday, September 15, 2016
Try Solar Cowboyz in Grass Valley. They may be able to repair it, they
say.
http://www.solarcowboyz.com/
Brad
On Fri, Jan 13, 2017 at 10:26 AM, William Miller
wrote:
> Dear Wrenches:
>
>
>
> I have a customer with a SMA SB2500U exhibiting the vac-bfr error code. I
>
It would be difficult to know what the inverters are doing without a
Multigate in the circuit. There is no monitoring, LED indicators, or other
means to see the status of the inverters. It would require a third party
meter to see if there was current flow or not. My hunch is that the
inverters
SnapNrack makes a snap on channel for the REC module as part of their
rail-less system. I expect it would be a little pricey to buy full lengths
of it, assuming they'd sell it that way. One can ask.
Brad
AEE Solar
On Thu, Jan 12, 2017 at 7:10 PM, William Miller
wrote:
I just checked with SMA and they do not have an RS485 card for the -40
inverters. What this means is that you can set them up to be permanently in
off grid mode where the SB will follow the frequency shift of the SI, ok
for an off grid system. But for grid tie with backup, the SB will not
Dana,
For off grid you may not want to use the constant pressure pumps. They will
run a little bit, a lot of the time to keep the pressure constant. I think
it might be more efficient to use a pressure switch and regular pressure
tank. Anyone with experience in this?
Brad
On Wed, Apr 26, 2017
To clarify what Darryl is saying, that is to separate them electrically
only. To loosen the main nut holding the stack together is to destroy them
permanently. I inherited five stacks that had been in service with good
results. I had actually been working the system hard remotely using
OpticsRE,
I was lucky that my local county Hazo-house took a look at the MSDS and
said drop them off. The person there saw my big MSDS printout and said uh
oh, but then she knew just where to look and said fine no problem drop them
off. Too bad not everyone is that knowledgeable about what they are looking
Mine had been mishandled when taken out of service, the uninstaller
loosened the main nuts on the top of the stacks. They were then trucked up
the west coast that way. Loosening the main nut is known to damage them,
and I expect the vibration from being trucked probably finished the job.
Brad
On
The OutBack GFP breaker is generally on the battery side of the charge
control, the RTB breaker for the ICS+ is installed on the array side of the
charge control. I have not seen, nor been told by OutBack engineers, that
there is a GFP in the ICS+ combiner, but that is where the AFCI is.
Brad
AEE
I set it up so the 12VDC transmitter was powered by the AUX on one of the
charge controls. Except the receivers did not go on with the charge control
I have.
Brad
On Tue, Aug 14, 2018 at 8:42 PM, Jeremy Rodriguez
wrote:
> We’ve installed many Midnite BHs with the disconnecting combiners (and
>
Kris,
LG batteries are not approved for off grid use at this time, and the only
inverter they work with so far is the StorEdge which is not an off grid
inverter. This pertains to the high voltage units anyway. And, I'm not
aware of anyone bringing the 48v units into the country yet. Either of
I have multiple ElSid pumps in my heating system which have been running
for just about 15 years without the slightest hitch. At 10W each they are
hard to beat, but they do need DC so a power supply is needed. I ran them
off 24VDC direct from the battery for the first 10 years and from a small
I have a long triplex wire run with a smaller neutral to my place from the
utility entrance, and I do end up with a large load on one leg often. When
another large load is on the other leg to balance the legs, it reduces the
voltage drop dramatically. The voltage on the one leg rises when I
A more recent spec sheet shows the MPPT window starting at 200v instead of
250v, which is a significant improvement.
Brad
On Tue, Sep 25, 2018 at 2:41 PM Dave Angelini Offgrid Solar <
offgridso...@sti.net> wrote:
> AEE had a training course webinar. The screenshot is from them and they
> say
Better yet, use Amphenol connectors.
Brad
On Mon, Dec 24, 2018 at 1:43 PM Tom Duffy wrote:
> If you’re showing a lower voltage tray in the stack… You can’t overcharge
> the whole set to get the 6 volt tray to come up but you can separate
> (electrically) not physically (leave the center bolt
I think you can leave it DC coupled and enable grid tie in the Sunny Island
inverters. It might not be quite as efficient but a lot more cost
effective. If you don't already have it Midnite makes a comm box that makes
the Classic look like an SMA device. That might be helpful to coordinate
MPPT
Jay,
The inverter will do 5kW to backup with 7.6kW surge. My understanding is
that it will draw from the PV as a priority and then battery. The battery
can do this power level also, though LG recommends keeping to 3.3kW most of
the time for longer battery life. I'm not sure how much effect the
Try Franklin solar pumps
http://solar.franklin-electric.com/products/subdrive/subdrive-solarpak/
Brad
On Wed, Feb 6, 2019 at 1:26 PM William Miller
wrote:
> Friends:
>
>
>
> I have been asked to consult on an agricultural water pumping project.
> The project is funded in part by NRCS. There
And make sure that both ends of the Xanbus network are properly terminated.
Brad
On Fri, Feb 1, 2019 at 8:44 AM Sandra Herrera <
sandra.herr...@schneider-electric.com> wrote:
> Hello Drake.
>
> In the Xanbus network, you have devices with power such as inverters, and
> other devices without
The IMO FireRaptor units are as far as I know immune to any interference
from charge controls or inverters. It does not rely on wireless or power
line communications. It is simply a hard wired module level disconnect that
runs on 24VDC. It has two-wire daisy chain cables between them, with a nice
I still recommend using a relay triggered from the Aux for AC coupling, it
works reliably and quickly.
Brad
AEE Solar
On Wed, Jun 5, 2019 at 10:11 AM Kienan Maxfield
wrote:
> Jay,
>
> It waits 50 seconds to even start to try to shift the frequency. I don’t
> know how long it takes to get up to
As Aquion said, loosening the main nut will destroy the battery. I can
vouch for that as well, not my doing, but I could not recover the batteries
where that had been done. I tightened the nuts and got just about one cycle
before they were gone.
I suspect that the temperature cycling of the
You could also look for an SMA SB700. Not very efficient and the metering
is pretty far off, but likely much better than an old AES.
Brad
On Sun, Apr 28, 2019 at 8:49 PM Peter Parrish
wrote:
> I replaced a number of AES (?) 120 Vac 1 kW grid tied inverter back when I
> was just starting out
Gary, MidNite Solar sells their MNEPV16-600-RT breaker. It is 16A and is 2"
wide and DIN rail mount.
Brad
AEE Solar
On Tue, Apr 23, 2019 at 5:16 AM gary easton wrote:
> I’m looking for a load break rated 15amp 600v DC breaker din rail mount.
> Any suggestions?
> --
> Sent from Gmail Mobile
>
I think you do need either a battery or AC source to start up the inverter
in the morning. It's also possible that if it is overloaded and shuts down
it might not restart. It will not start from PV alone.
Brad
On Wed, Aug 28, 2019 at 6:28 PM Chris Sparadeo
wrote:
> Jay,
>
> My understanding is
I've noticed this is worse with multiple bulbs in one fixture, and it is
even slightly noticeable on grid power, but worse on inverter power. I
first saw this with CFL's also, but not as bad as with the LED's. And this
is without any motor loads going. It's not consistent either, sometimes it
does
Someone previously at AEE tried to get NEMA involved in setting a standard,
but it turned out that they were not getting cooperation from the mfg, so
could not proceed.
Brad
On Thu, Sep 19, 2019 at 1:28 PM Bryan Norkunas wrote:
> Yes, I have seen and have copies of many of these 3rd party
>
Mark,
The difference is that when AC coupled the power is coming backwards into
the AC out. When it's charging from the grid or generator it is charging
from the AC inputs. The inverter can control the charge from the inputs but
not what is coming in reverse into the output.
Brad
On Sun, Nov 3,
If you're not using the SB -40 inverter's rapid shutdown system, it has the
SPS Secure Power Supply which does just what your customer wants.
My understanding from talking to inverter mfg, is that trying to do AC
coupling with a smaller battery inverters does not work because the
anti-islanding
The 200PLC was not an Enersys battery, and is no longer available, the
upcoming 200HLC will be the Enersys replacement for the 200PLC.
The manual for the 200-PLC is posted here: PLC_User_Manual.pdf
My hunch is that the anti-islanding in the grid tie inverter is going to
push the little battery inverter out of spec, even with a diversion load,
and they will never connect. But I'd be very interested to see if that is
so if someone tries it.
Brad
AEE Solar
On Wed, Mar 4, 2020 at 4:08 PM
The best price I've found for the handbook is at Barnes & Noble. If you go
into the store you have to ask for the internet price. Also at least at my
store they had it behind the counter in case you go looking for it.
Brad
On Wed, Jan 8, 2020 at 3:26 PM Jason Szumlanski <
Jay,
I don't have one to measure, but according to OB the NSB190FT BLUE+ battery
fits at 12.6" tall and the NSB210FT BLUE+ battery at 12.9" tall does not.
Brad
On Mon, May 11, 2020 at 3:42 PM jay wrote:
> HI All,
>
> I’m wondering if anyone has a outback battery box that they can measure
>
I can confirm that the SnapNrack series 200 ground mount is alive and well.
The series 100 roof mount has been replaced by the UltraRail product.
Brad Bassett
AEE Solar (which is part of the same company as SnapNrack)
On Mon, May 4, 2020 at 7:12 PM Glenn Burt wrote:
> We use it on almost all
Discover Battery has been around since just after WWII. I think that since
each Li battery is native to the system voltage, the way to get some
redundancy is to simply have more than one battery, most systems will
anyway. Then if one fails you can use the other ones until the failed one
is
I think there is a jumper in the FM100 that will allow the Mate3s to
communicate with it. I don't remember off hand where it is and am not at a
computer with that info, but maybe this will prompt a look at the manual to
see if they mention it.
Brad
On Fri, Oct 16, 2020 at 11:11 PM William Miller
>
> Dan Fink
> Owner, Buckville Energy Consulting
> NABCEP Certified PV System Inspector
> IREC Certified Instructor™ for:
> ~ PV Installation Professional
> ~ Small Wind Installer
> NABCEP Registered Continuing Education Providers
> d anbo...@gmail.com
> 970-6
At least when we sold these they were not listed. We got caught on this a
couple of times in WA state and were not allowed to install them. Also Grundfos
said not to use a Gfi with them. Maybe a dc gfi might be ok on the PV side of
the CU200.
Brad
Sent from my iPhone
> On Oct 27, 2020, at
Wow! Someone else with SMA SB240's, I have 12 of them that I've AC coupled
to an XW+5548. They are very solid performers.
Brad
AEE Solar
On Fri, Jun 12, 2020 at 3:39 PM Mark Frye wrote:
> Hello,
>
> I have a small array of 8 - SMA SB240 microinverters on the roof. Peak
> power out of the array
B240 does not have frequency shift /wattage control. How are you
> implementing charge control in stand alone mode?
> On 6/12/2020 4:28 PM, Bradley Bassett wrote:
>
> Wow! Someone else with SMA SB240's, I have 12 of them that I've AC coupled
> to an XW+5548. They are very solid performe
e
> controller has a high limit switch which I could use to cut the AC feed to
> the GT inverters. But then both functions are in the same device. On the
> other hand, it is a very reliable device soperhaps sufficient.
> On 6/12/2020 6:37 PM, Bradley Bassett wrote:
>
> I have a rel
The only 120VAC grid tie inverters that I know of are the OutBack FXR
series.
Brad
On Thu, Jan 14, 2021 at 6:19 AM Glenn Burt wrote:
> I dont think micros do only 120 volts though...
>
> Maybe a Schneider SW inverter? I recently was called to work on a DIY
> special that used a 4024 that was
The system currently has a 600 foot run of 2-2-4 aluminum from the service
to the house loads. The load is often only 120VAC which gives a large
voltage drop using only the #2 and #4 conductors. My thought was to install
an autotransformer at the load end so that the current runs through the #2
I'd recommend the best battery that is close to those is the Deka UnigyII.
Top notch quality, similar rack. Made in USA. I've been curious about the
FireFly batteries, but not much in the way of reviews for solar use. RV use
gets mixed reviews, but are mostly for the smaller units.
Brad
On Thu,
As I remember Ananda got a UL listing with a rating up to 60VDC on their
APT power centers using the QOU breakers. I think the SqD rating on those
is the same as for the QO breakers at 48VDC. I would not go any higher than
that though. Also be aware that the QO does not work well when used at
If you open terminals 4 and 12 it will turn off the Skybox, both PV input
and AC as far as I know. Terminals 5 and 13 then will open on RSD to send a
signal to whatever other devices need RSD.
Brad
On Sun, Nov 7, 2021 at 9:34 AM Kirk Herander wrote:
> I just installed one of these in a
Jay,
As I remember, that is the classic failure mode. We used to see it now and
then, more often than we liked. It's why I used to recommend always getting
the extended warranty. And, it can be either the CU200 or the pump itself.
It might also be a corroded connection between the two.
Brad
On
I have about 1200 ft from float switches, two in parallel, to the CU200 and
another 200 ft to the pump without any issues. If there is bad connection it
could be a problem though.
Brad
Sent from my iPhone
> On Feb 25, 2022, at 12:17 PM, Nick Soleil wrote:
>
> Hi Jay,
>
> Is it a long wire
I have not had any feedback about different shunts not working. I can’t see how
the FNDC would even be able to tell the difference if they are the same ratio.
Brad B
Sent from my iPhone
> On Mar 1, 2022, at 8:00 AM, Kirk Herander wrote:
>
> Thanks all. I just found it is included as
I think the blank GSLC comes with the main breaker bracket and the bus bars
for connecting them. What I have not had a chance to try is connecting the
breaker bus that usually connects the bottom of the two main breakers
directly to the upper bus bars, and not installing the two breakers at all.
"A switch, outside of the building, opening the PV circuit to the power
electronics, and functioning as the pv system disco and the rapid shutdown
initiation device, should be all that is required."
That is what I have found most inspectors will accept, but not all. A
strict reading of the code
I’ve had LED lights, with multiples in one fixture, flicker on grid power.
Brad
Sent from my iPhone
> On Feb 4, 2022, at 7:18 AM, Dana Orzel wrote:
>
> Ditto on misc flickering w LEDs on my Off grid Radian system
> I have some LEDs that are absolutely stable all the time and some of the
>
Years ago, and maybe still there, a siphon was used to go over the existing
dam on the Pocono reservoir to run a hydro generator. There was a vacuum
pump pulling a vacuum at the top of the arch to keep it full of water in
case air bubbles got in. They did have to prime it to get it going. I think
Over the years I have *never *seen loads, no matter how small, taken off of
a mid point of a battery not cause serious issues with cell balancing. Even
with the use of the Vanner equalizer there were always still problems with
the battery bank. So I would never do it. When I converted to a 48
I used to have both an array at a 60° tilt and one at 14° tilt. In the
winter the high tilt array did better on sunny days, and on cloudy days the
shallow array did better. They were different modules and different sized
arrays, so without more analysis than I did, it would be hard to tell which
I had a talk with tech support at APS about using the APSmart RSD devices
in my DC coupled system. I found it hard to understand him so I'm not
completely clear on what he said. One thing was clear and that is they do
not test these for use with charge controllers, so can't support that use.
Other
curiosity, what is the actual difference between the two on those
> cloudy days.
>
> Thx
> Jay
>
>
>
> On Oct 25, 2023, at 5:04 PM, Bradley Bassett via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>
> I used to have both an array at a 60° tilt and
AFAIK Or any of the variants of that like the dual input unit
Brad
Sent from my iPhone
> On Apr 19, 2022, at 9:18 AM, jay via RE-wrenches
> wrote:
>
> HI All
>
> I’ve got a project coming up that has specified a Schneider XW 80/600
> controller.
>
> Its going to need RS.
>
> Is the only
The Schneider RSD switch has a Tigo transmitter, which is no longer SunSpec
compliant. SunSpec devices do NOT work. I know for certain that the APsmart
devices do not work.
Fire Raptors are very robust and might be a good choice for off grid where
reliability is paramount. But they come with 6ft
Hi George, It's good to see you're still with REC.
I'd assume this would fall under the purview of UL rather than NEC.
Anything that meets UL will pass NEC. With temperature derates I think
you'd have had to go to larger wire long ago to meet NEC standards.
It might be good to go to a larger
The Samlex EVO4248SP is a potential substitute. The only system panel is the
MidNite E-panel. This is a 4.2 kW split phase inverter.
Brad
AEE Solar
Sent from my iPhone
> On Jul 20, 2022, at 1:25 PM, Ron Young via RE-wrenches
> wrote:
>
> I have been waiting literally months for delivery of
Check out YouTube videos by Will Prowse. He’s used them and taken them apart.
It would be better if any wrenches have used them though
Brad
Sent from my iPhone
> On Jul 28, 2022, at 12:49 PM, Dave Tedeyan via RE-wrenches
> wrote:
>
> Hi all,
>
> Does anyone have any experience with EG4
The EVO has an AUX contact closure, either NO or NC that can be programmed
for a two wire generator. If you need 3 or 4 wire start logic you can use
the Atkinson GSCM.
Brad
On Fri, Sep 2, 2022 at 9:30 PM frenergy via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Doesn't the EVO have
I'm curious what you consider mediocre about the HomeGrid?
Brad
On Mon, Oct 10, 2022 at 7:07 PM Lou Russo via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Aloha All,
>
> I am considering doing a job with one of these (14kWH) with a Sol-Ark 12kW
> for a client who is demanding them.
The ACLD was long ago discontinued. The Morningstar relay driver would work
fine. I think Magnum limited the size of the grid tie inverter to 90% of
the Magnum inverter max power. So 3960W for a MS4448PAE.
Brad
On Sat, Oct 8, 2022 at 8:47 AM Jay via RE-wrenches <
Matt Ferrell gives a good summary of the issues:
https://www.youtube.com/watch?v=3JqzSsStwF4
Brad
On Wed, Aug 17, 2022 at 5:55 AM jay via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi All,
>
> Some asked me a question about recycling of panels and I can’t exactly
> find out the
It’s not required but it has the only reliable means of generator start stop.
There are three relays that can be programmed. You can’t get accurate battery
state of charge by using voltage except near empty or full. The LynkII also has
a little bar graph showing state of charge to the nearest
Samlex EVO4024 is supposed to be a very robust simple inverter. 120VAC
output, AC charging, good value.
Brad
On Tue, Jan 3, 2023 at 6:44 AM Chris Sparadeo via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hey there,
>
> I have a client with a dead 24V Xantrex SW…It had a good 20+
The Radian grid AC in is connected to the utility side of the transfer
switch. You may need a service rated fused disconnect on that line,
probably 60A. Then you can feed the AC out to the generator input on the
transfer switch to power the main house panel. It's best and usually
required by code
If they are the AES 48-6650 batteries I think they do *not* have low
temperature mode, and will be damaged if they are charged while they are
below freezing. The AES 48-3000 I think *do* have a low temperature mode
and would prevent charging if they are below freezing.
Wind will tend to make any
The issue as I see it is that the Tigo RSS Transmitter and the APsmart
transmitter are both rated to draw up to 800ma. The 12VDC output of the
Sol-Ark inverters is limited to 100ma. Since some have used this
successfully I suppose that means that either these transmitters don't
really use more
On some LFP batteries the cell balancing only happens at full charge, so
you do need to get to full every so often. Discover AES is one that needs
this.
Brad
On Sat, Nov 19, 2022 at 10:10 AM Dana Orzel via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Another issue is what charge
My design for one customer was to have one initiator for the PV and
inverter, and a separate one for the battery initiator. And, to put up a
plaque giving instructions to turn off the PV and inverter first, then the
battery.
Brad
On Sat, Jan 28, 2023 at 4:22 PM William Miller via RE-wrenches <
I tried this back in the 1970's with an exercise bike and a high efficiency
generator (still have this if anyone wants it). If I pushed hard I could
get it up to 200W, but only sustain about 100W. The only time I used it is
when my battery was depleted and I wanted to watch TV. I had a 12VDC 5" B
;
> Solar Energy International
> http://www.solarenergy.org
>
>
>
> On Mon, Feb 20, 2023 at 3:13 PM Bradley Bassett via RE-wrenches <
> re-wrenches@lists.re-wrenches.org> wrote:
>
>> Flat is the preferred orientation and they say that if installed with the
>> cel
Flat is the preferred orientation and they say that if installed with the cells
vertical it would lose some small percentage of capacity. They never said
anything about reduced life that I remember. It is very easy to have short life
on these if not fully charged very often. The will sulphate
I have an XW5548+ with Gateway and Discover AES battery and can vouch that it
works slick.
Brad
AEE Solar
Sent from my iPhone
> On Mar 29, 2023, at 9:26 AM, Dave Angelini Offgrid Solar via RE-wrenches
> wrote:
>
> It will be some work to make this work right for you! The XWP is based on
That is with Discover batteries.
Sent from my iPhone
> On Feb 10, 2023, at 8:34 AM, Dave Angelini Offgrid Solar via RE-wrenches
> wrote:
>
> Agree Will and adding that for generator users closed loop will save 25% or
> more on fuel.
>
> I know alot of you folks do not use Schneider but it
Just so you know, AEE Solar still has a bunch of Magnum panels and
controls, no inverters, no support though. At least until they find someone
to take it all. Keep an eye out for other close out stuff too. But, yes
they are still going and working on getting better.
Brad Bassett
Retired---
1985
I have no experience with the Hawaii connection, but another choice for a
tap connector is the Ilso GTA type with cover. You don't have to cut the
tapped line and don't rely on piercing it.
Brad Bassett
Application Engineer (ret.) 1985 Solar Eng Svcs -> Applied Power -> Applied
Power (Idaho
Note that MidNite now also makes 2000A and 500A versions of their BCB. With
two Sol-Ark 15k you do need to use the 1000A version with 275A each
inverter. I can also confirm that you do need to use both of the battery
terminals in the Sol-Ark 15k for full power, or the Homegrid bus bars that
Jason
AEE might still have some of those if I remember
Brad.
Retired
On Thu, Jun 15, 2023, 7:41 AM Chris Daum via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Hi folks:
>
>
>
> Any chance one of you has this auto gen start module they can part with? I
> do NOT need the one with the
Regarding AEE and off grid support, I'm not really in touch with them much
any more so I can't say. You could ask Glenn Hall, he'd be able to say if
he's heard anything about hiring a new tech. Of course finding someone
with much off grid experience would be hard. Glenn and Alex do have some
I powered a MidNite LSOB transmitter from a Classic AUX, though the
receivers didn't work with the Classic. The Classic is limited to 200ma
output and the Tigo and APS transmitters are rated at up to 800ma input, so
it might overload the Classic AUX output if they really do draw that much.
I
Read the warranty. Very limited uses to maintain coverage. Mfg by an
Italian Co that is somewhat condescending toward customers. But of course
East Penn is good to work with. My understanding is that they do work with
the three phase Sol-Ark inverters.
Brad
On Wed, Feb 7, 2024 at 4:52 AM William
Note that the MPPT disco RS works only with Schneider charge controllers.
With any other charge controllers you'll need to use Fire Raptors.
Specifically the power line type rsd do not work with classic cc. I see no
reason why the Schneider units would not meet 2020 or 2023 codes.
On Mon, Jan 1,
Growatt MIN. They're capable of battery connection but work fine as a
string inverter at a decent price.
Brad
On Fri, Feb 23, 2024 at 4:09 AM Glenn Burt via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Fronius.
> Solis
>
> -Glenn
> Sent from my 'smart'phone, so please excuse typos
Is Aerocompact still around ? They had a nice simple ballasted ground mount
Brad Bassett
On Thu, Mar 21, 2024, 10:45 AM Kristopher Schmid via RE-wrenches <
re-wrenches@lists.re-wrenches.org> wrote:
> Thanks for the info, Sam.
>
> I guess that I should have mentioned that I am looking at an 8kw
I had a lot of trouble keeping QO breakers functional on a 12VDC
distribution system. I'd have to move them around every week or so to keep
a good contact on the plug in contacts. They seem to work fine on a 24VDC
system. I went to using MNPV or MNDC breakers instead in PV combiner or
other
95 matches