Re: [RE-wrenches] Sunnyboy TL with Batteries

2015-11-11 Thread Bradley Bassett
I've quoted a few systems with an IOTA charger and small inverter. I have not had any feedback yet. I figure the separate battery charger and inverter won't make the loads flicker so much when the sun comes and goes. I'm not sure if the SPS comes back automatically when it's been overloaded

Re: [RE-wrenches] fusing requirement for 4 strings run to a Inverter with 2 MPPT's

2016-01-30 Thread Bradley Bassett
That document refers to 2008 NEC 690.9 code which has the exemption that is used for grounded inverters. Section 690.35 for ungrounded systems just refers back to 690.9 for over-current protection. So I do not see any indication that two strings on an ungrounded inverter could not have the same

Re: [RE-wrenches] Rapid Shutdown

2016-03-15 Thread Bradley Bassett
I've been promoting the use of the remote on/off terminals that are available in most inverters, which can be connected to the AUX in the Birdhouse. For a very minimum effort and cost, the inverter AC output would be shutdown when the rapid shutdown is activated. I think using the remote on/off

Re: [RE-wrenches] Morningstar 600 V MPPT

2016-04-07 Thread Bradley Bassett
I have one in a test system charging an Aquion battery. It has 11 REC modules in one string feeding it. I programmed it using MSView from my place remotely and once I got all the comm programming right it worked great. I now monitor it over the company VPN using a browser and it seems to be

Re: [RE-wrenches] micro-inverters

2016-09-15 Thread Bradley Bassett
My SMA micro-inverters have been rock solid for a couple of years. They do not taper off and do not communicate with the Sunny Island. The only issue I've had is that it seems that an internet connection is needed for the monitoring to work, even for the local monitoring. If there is no monitoring

Re: [RE-wrenches] micro-inverters

2016-09-15 Thread Bradley Bassett
rester between the module(s) and the > inverter, making micros more vulnerable in that regard. > > > > Bill Dorsett > > > > *From:* RE-wrenches [mailto:re-wrenches-boun...@lists.re-wrenches.org] *On > Behalf Of *Bradley Bassett > *Sent:* Thursday, September 15, 2016

Re: [RE-wrenches] SB2500U vac-bfr error

2017-01-13 Thread Bradley Bassett
Try Solar Cowboyz in Grass Valley. They may be able to repair it, they say. http://www.solarcowboyz.com/ Brad On Fri, Jan 13, 2017 at 10:26 AM, William Miller wrote: > Dear Wrenches: > > > > I have a customer with a SMA SB2500U exhibiting the vac-bfr error code. I >

Re: [RE-wrenches] SMA SB240 - Multigate Required

2017-01-13 Thread Bradley Bassett
It would be difficult to know what the inverters are doing without a Multigate in the circuit. There is no monitoring, LED indicators, or other means to see the status of the inverters. It would require a third party meter to see if there was current flow or not. My hunch is that the inverters

Re: [RE-wrenches] Solar World Wind Damage

2017-01-13 Thread Bradley Bassett
SnapNrack makes a snap on channel for the REC module as part of their rail-less system. I expect it would be a little pricey to buy full lengths of it, assuming they'd sell it that way. One can ask. Brad AEE Solar On Thu, Jan 12, 2017 at 7:10 PM, William Miller wrote:

Re: [RE-wrenches] SMA US 40 & AC coupling

2017-03-10 Thread Bradley Bassett
I just checked with SMA and they do not have an RS485 card for the -40 inverters. What this means is that you can set them up to be permanently in off grid mode where the SB will follow the frequency shift of the SI, ok for an off grid system. But for grid tie with backup, the SB will not

Re: [RE-wrenches] Sta-Rite Submersible Well Pump

2017-04-27 Thread Bradley Bassett
Dana, For off grid you may not want to use the constant pressure pumps. They will run a little bit, a lot of the time to keep the pressure constant. I think it might be more efficient to use a pressure switch and regular pressure tank. Anyone with experience in this? Brad On Wed, Apr 26, 2017

Re: [RE-wrenches] for all you Aquion installers

2018-01-31 Thread Bradley Bassett
To clarify what Darryl is saying, that is to separate them electrically only. To loosen the main nut holding the stack together is to destroy them permanently. I inherited five stacks that had been in service with good results. I had actually been working the system hard remotely using OpticsRE,

Re: [RE-wrenches] Aqueon disposal

2018-07-26 Thread Bradley Bassett
I was lucky that my local county Hazo-house took a look at the MSDS and said drop them off. The person there saw my big MSDS printout and said uh oh, but then she knew just where to look and said fine no problem drop them off. Too bad not everyone is that knowledgeable about what they are looking

Re: [RE-wrenches] Aqueon disposal

2018-07-27 Thread Bradley Bassett
Mine had been mishandled when taken out of service, the uninstaller loosened the main nuts on the top of the stacks. They were then trucked up the west coast that way. Loosening the main nut is known to damage them, and I expect the vibration from being trucked probably finished the job. Brad On

Re: [RE-wrenches] Outback Rapid Shutdown RTB rewiring

2018-07-27 Thread Bradley Bassett
The OutBack GFP breaker is generally on the battery side of the charge control, the RTB breaker for the ICS+ is installed on the array side of the charge control. I have not seen, nor been told by OutBack engineers, that there is a GFP in the ICS+ combiner, but that is where the AFCI is. Brad AEE

Re: [RE-wrenches] Rapid Shutdown Off Grid

2018-08-16 Thread Bradley Bassett
I set it up so the 12VDC transmitter was powered by the AUX on one of the charge controls. Except the receivers did not go on with the charge control I have. Brad On Tue, Aug 14, 2018 at 8:42 PM, Jeremy Rodriguez wrote: > We’ve installed many Midnite BHs with the disconnecting combiners (and >

Re: [RE-wrenches] Pika

2018-09-07 Thread Bradley Bassett
Kris, LG batteries are not approved for off grid use at this time, and the only inverter they work with so far is the StorEdge which is not an off grid inverter. This pertains to the high voltage units anyway. And, I'm not aware of anyone bringing the 48v units into the country yet. Either of

Re: [RE-wrenches] Forced air Furnace

2018-09-07 Thread Bradley Bassett
I have multiple ElSid pumps in my heating system which have been running for just about 15 years without the slightest hitch. At 10W each they are hard to beat, but they do need DC so a power supply is needed. I ran them off 24VDC direct from the battery for the first 10 years and from a small

Re: [RE-wrenches] Neutral sizing

2018-09-24 Thread Bradley Bassett
I have a long triplex wire run with a smaller neutral to my place from the utility entrance, and I do end up with a large load on one leg often. When another large load is on the other leg to balance the legs, it reduces the voltage drop dramatically. The voltage on the one leg rises when I

Re: [RE-wrenches] Low voltage DC v. higher voltage DC

2018-09-25 Thread Bradley Bassett
A more recent spec sheet shows the MPPT window starting at 200v instead of 250v, which is a significant improvement. Brad On Tue, Sep 25, 2018 at 2:41 PM Dave Angelini Offgrid Solar < offgridso...@sti.net> wrote: > AEE had a training course webinar. The screenshot is from them and they > say

Re: [RE-wrenches] Aquion Testing

2018-12-24 Thread Bradley Bassett
Better yet, use Amphenol connectors. Brad On Mon, Dec 24, 2018 at 1:43 PM Tom Duffy wrote: > If you’re showing a lower voltage tray in the stack… You can’t overcharge > the whole set to get the 6 volt tray to come up but you can separate > (electrically) not physically (leave the center bolt

Re: [RE-wrenches] Off-grid Sunny Island to backup

2019-02-18 Thread Bradley Bassett
I think you can leave it DC coupled and enable grid tie in the Sunny Island inverters. It might not be quite as efficient but a lot more cost effective. If you don't already have it Midnite makes a comm box that makes the Classic look like an SMA device. That might be helpful to coordinate MPPT

Re: [RE-wrenches] Solar edge storeedge question

2019-02-13 Thread Bradley Bassett
Jay, The inverter will do 5kW to backup with 7.6kW surge. My understanding is that it will draw from the PV as a priority and then battery. The battery can do this power level also, though LG recommends keeping to 3.3kW most of the time for longer battery life. I'm not sure how much effect the

Re: [RE-wrenches] Need UL Listed direct DC pump

2019-02-06 Thread Bradley Bassett
Try Franklin solar pumps http://solar.franklin-electric.com/products/subdrive/subdrive-solarpak/ Brad On Wed, Feb 6, 2019 at 1:26 PM William Miller wrote: > Friends: > > > > I have been asked to consult on an agricultural water pumping project. > The project is funded in part by NRCS. There

Re: [RE-wrenches] No Communication to XW CC

2019-02-01 Thread Bradley Bassett
And make sure that both ends of the Xanbus network are properly terminated. Brad On Fri, Feb 1, 2019 at 8:44 AM Sandra Herrera < sandra.herr...@schneider-electric.com> wrote: > Hello Drake. > > In the Xanbus network, you have devices with power such as inverters, and > other devices without

Re: [RE-wrenches] rapid shutdown units for obscure inverter

2019-05-30 Thread Bradley Bassett
The IMO FireRaptor units are as far as I know immune to any interference from charge controls or inverters. It does not rely on wireless or power line communications. It is simply a hard wired module level disconnect that runs on 24VDC. It has two-wire daisy chain cables between them, with a nice

Re: [RE-wrenches] Schneider ac coupling time.

2019-06-05 Thread Bradley Bassett
I still recommend using a relay triggered from the Aux for AC coupling, it works reliably and quickly. Brad AEE Solar On Wed, Jun 5, 2019 at 10:11 AM Kienan Maxfield wrote: > Jay, > > It waits 50 seconds to even start to try to shift the frequency. I don’t > know how long it takes to get up to

Re: [RE-wrenches] Aquion - Mix and Matching Layers

2019-05-09 Thread Bradley Bassett
As Aquion said, loosening the main nut will destroy the battery. I can vouch for that as well, not my doing, but I could not recover the batteries where that had been done. I tightened the nuts and got just about one cycle before they were gone. I suspect that the temperature cycling of the

Re: [RE-wrenches] 1 kW 120 Vac grid tied inverter

2019-04-29 Thread Bradley Bassett
You could also look for an SMA SB700. Not very efficient and the metering is pretty far off, but likely much better than an old AES. Brad On Sun, Apr 28, 2019 at 8:49 PM Peter Parrish wrote: > I replaced a number of AES (?) 120 Vac 1 kW grid tied inverter back when I > was just starting out

Re: [RE-wrenches] Load break DC breaker for combiner

2019-04-23 Thread Bradley Bassett
Gary, MidNite Solar sells their MNEPV16-600-RT breaker. It is 16A and is 2" wide and DIN rail mount. Brad AEE Solar On Tue, Apr 23, 2019 at 5:16 AM gary easton wrote: > I’m looking for a load break rated 15amp 600v DC breaker din rail mount. > Any suggestions? > -- > Sent from Gmail Mobile >

Re: [RE-wrenches] Grid tie w/o battery no sell back

2019-08-28 Thread Bradley Bassett
I think you do need either a battery or AC source to start up the inverter in the morning. It's also possible that if it is overloaded and shuts down it might not restart. It will not start from PV alone. Brad On Wed, Aug 28, 2019 at 6:28 PM Chris Sparadeo wrote: > Jay, > > My understanding is

Re: [RE-wrenches] Light Flicker Off grid

2019-09-21 Thread Bradley Bassett
I've noticed this is worse with multiple bulbs in one fixture, and it is even slightly noticeable on grid power, but worse on inverter power. I first saw this with CFL's also, but not as bad as with the LED's. And this is without any motor loads going. It's not consistent either, sometimes it does

Re: [RE-wrenches] connector mismatch

2019-09-19 Thread Bradley Bassett
Someone previously at AEE tried to get NEMA involved in setting a standard, but it turned out that they were not getting cooperation from the mfg, so could not proceed. Brad On Thu, Sep 19, 2019 at 1:28 PM Bryan Norkunas wrote: > Yes, I have seen and have copies of many of these 3rd party >

Re: [RE-wrenches] Parts List For AC Couple Disconnect

2019-11-04 Thread Bradley Bassett
Mark, The difference is that when AC coupled the power is coming backwards into the AC out. When it's charging from the grid or generator it is charging from the AC inputs. The inverter can control the charge from the inputs but not what is coming in reverse into the output. Brad On Sun, Nov 3,

Re: [RE-wrenches] Running a grid tied system when the grid is down

2019-09-20 Thread Bradley Bassett
If you're not using the SB -40 inverter's rapid shutdown system, it has the SPS Secure Power Supply which does just what your customer wants. My understanding from talking to inverter mfg, is that trying to do AC coupling with a smaller battery inverters does not work because the anti-islanding

Re: [RE-wrenches] outback 200 PLC questions

2019-09-23 Thread Bradley Bassett
The 200PLC was not an Enersys battery, and is no longer available, the upcoming 200HLC will be the Enersys replacement for the 200PLC. The manual for the 200-PLC is posted here: PLC_User_Manual.pdf

Re: [RE-wrenches] OK, so what would happen if I do this...

2020-03-04 Thread Bradley Bassett
My hunch is that the anti-islanding in the grid tie inverter is going to push the little battery inverter out of spec, even with a diversion load, and they will never connect. But I'd be very interested to see if that is so if someone tries it. Brad AEE Solar On Wed, Mar 4, 2020 at 4:08 PM

Re: [RE-wrenches] NEC 2020 not available as a portable PDF?

2020-01-08 Thread Bradley Bassett
The best price I've found for the handbook is at Barnes & Noble. If you go into the store you have to ask for the internet price. Also at least at my store they had it behind the counter in case you go looking for it. Brad On Wed, Jan 8, 2020 at 3:26 PM Jason Szumlanski <

Re: [RE-wrenches] Outback battery box shelve height dimensions.

2020-05-11 Thread Bradley Bassett
Jay, I don't have one to measure, but according to OB the NSB190FT BLUE+ battery fits at 12.6" tall and the NSB210FT BLUE+ battery at 12.9" tall does not. Brad On Mon, May 11, 2020 at 3:42 PM jay wrote: > HI All, > > I’m wondering if anyone has a outback battery box that they can measure >

Re: [RE-wrenches] Name that Racking

2020-05-05 Thread Bradley Bassett
I can confirm that the SnapNrack series 200 ground mount is alive and well. The series 100 roof mount has been replaced by the UltraRail product. Brad Bassett AEE Solar (which is part of the same company as SnapNrack) On Mon, May 4, 2020 at 7:12 PM Glenn Burt wrote: > We use it on almost all

Re: [RE-wrenches] Lithium Ion Batteries

2020-03-23 Thread Bradley Bassett
Discover Battery has been around since just after WWII. I think that since each Li battery is native to the system voltage, the way to get some redundancy is to simply have more than one battery, most systems will anyway. Then if one fails you can use the other ones until the failed one is

Re: [RE-wrenches] Mixing Outback 100 series C with old FX system

2020-10-17 Thread Bradley Bassett
I think there is a jumper in the FM100 that will allow the Mate3s to communicate with it. I don't remember off hand where it is and am not at a computer with that info, but maybe this will prompt a look at the manual to see if they mention it. Brad On Fri, Oct 16, 2020 at 11:11 PM William Miller

Re: [RE-wrenches] Mixing Outback 100 series C with old FX system

2020-10-19 Thread Bradley Bassett
> > Dan Fink > Owner, Buckville Energy Consulting > NABCEP Certified PV System Inspector > IREC Certified Instructor™ for: > ~ PV Installation Professional > ~ Small Wind Installer > NABCEP Registered Continuing Education Providers > d anbo...@gmail.com > 970-6

Re: [RE-wrenches] GFDI requirements

2020-10-27 Thread Bradley Bassett
At least when we sold these they were not listed. We got caught on this a couple of times in WA state and were not allowed to install them. Also Grundfos said not to use a Gfi with them. Maybe a dc gfi might be ok on the PV side of the CU200. Brad Sent from my iPhone > On Oct 27, 2020, at

Re: [RE-wrenches] Magnum Frequency Shift

2020-06-12 Thread Bradley Bassett
Wow! Someone else with SMA SB240's, I have 12 of them that I've AC coupled to an XW+5548. They are very solid performers. Brad AEE Solar On Fri, Jun 12, 2020 at 3:39 PM Mark Frye wrote: > Hello, > > I have a small array of 8 - SMA SB240 microinverters on the roof. Peak > power out of the array

Re: [RE-wrenches] Magnum Frequency Shift

2020-06-12 Thread Bradley Bassett
B240 does not have frequency shift /wattage control. How are you > implementing charge control in stand alone mode? > On 6/12/2020 4:28 PM, Bradley Bassett wrote: > > Wow! Someone else with SMA SB240's, I have 12 of them that I've AC coupled > to an XW+5548. They are very solid performe

Re: [RE-wrenches] Magnum Frequency Shift

2020-06-12 Thread Bradley Bassett
e > controller has a high limit switch which I could use to cut the AC feed to > the GT inverters. But then both functions are in the same device. On the > other hand, it is a very reliable device soperhaps sufficient. > On 6/12/2020 6:37 PM, Bradley Bassett wrote: > > I have a rel

Re: [RE-wrenches] 120v batteryless gT inverter

2021-01-14 Thread Bradley Bassett
The only 120VAC grid tie inverters that I know of are the OutBack FXR series. Brad On Thu, Jan 14, 2021 at 6:19 AM Glenn Burt wrote: > I dont think micros do only 120 volts though... > > Maybe a Schneider SW inverter? I recently was called to work on a DIY > special that used a 4024 that was

[RE-wrenches] Autoformer and long AC run

2021-08-02 Thread Bradley Bassett
The system currently has a 600 foot run of 2-2-4 aluminum from the service to the house loads. The load is often only 120VAC which gives a large voltage drop using only the #2 and #4 conductors. My thought was to install an autotransformer at the load end so that the current runs through the #2

Re: [RE-wrenches] 2v agm batteries

2021-11-22 Thread Bradley Bassett
I'd recommend the best battery that is close to those is the Deka UnigyII. Top notch quality, similar rack. Made in USA. I've been curious about the FireFly batteries, but not much in the way of reviews for solar use. RV use gets mixed reviews, but are mostly for the smaller units. Brad On Thu,

Re: [RE-wrenches] DC Rating of Square D QO?

2021-10-26 Thread Bradley Bassett
As I remember Ananda got a UL listing with a rating up to 60VDC on their APT power centers using the QOU breakers. I think the SqD rating on those is the same as for the QO breakers at 48VDC. I would not go any higher than that though. Also be aware that the QO does not work well when used at

Re: [RE-wrenches] outback skybox remote power off

2021-11-07 Thread Bradley Bassett
If you open terminals 4 and 12 it will turn off the Skybox, both PV input and AC as far as I know. Terminals 5 and 13 then will open on RSD to send a signal to whatever other devices need RSD. Brad On Sun, Nov 7, 2021 at 9:34 AM Kirk Herander wrote: > I just installed one of these in a

Re: [RE-wrenches] grundfos cu200 failure?

2022-02-25 Thread Bradley Bassett
Jay, As I remember, that is the classic failure mode. We used to see it now and then, more often than we liked. It's why I used to recommend always getting the extended warranty. And, it can be either the CU200 or the pump itself. It might also be a corroded connection between the two. Brad On

Re: [RE-wrenches] grundfos cu200 failure?

2022-02-25 Thread Bradley Bassett
I have about 1200 ft from float switches, two in parallel, to the CU200 and another 200 ft to the pump without any issues. If there is bad connection it could be a problem though. Brad Sent from my iPhone > On Feb 25, 2022, at 12:17 PM, Nick Soleil wrote: > > Hi Jay, > > Is it a long wire

Re: [RE-wrenches] alternatives to Outback GSLC xxxx box?

2022-03-01 Thread Bradley Bassett
I have not had any feedback about different shunts not working. I can’t see how the FNDC would even be able to tell the difference if they are the same ratio. Brad B Sent from my iPhone > On Mar 1, 2022, at 8:00 AM, Kirk Herander wrote: > > Thanks all. I just found it is included as

Re: [RE-wrenches] alternatives to Outback GSLC xxxx box?

2022-03-01 Thread Bradley Bassett
I think the blank GSLC comes with the main breaker bracket and the bus bars for connecting them. What I have not had a chance to try is connecting the breaker bus that usually connects the bottom of the two main breakers directly to the upper bus bars, and not installing the two breakers at all.

Re: [RE-wrenches] Rapid Shutdown for Off-grid systems

2022-02-01 Thread Bradley Bassett
"A switch, outside of the building, opening the PV circuit to the power electronics, and functioning as the pv system disco and the rapid shutdown initiation device, should be all that is required." That is what I have found most inspectors will accept, but not all. A strict reading of the code

Re: [RE-wrenches] Flickering lights on off grid AC coupled radian system

2022-02-04 Thread Bradley Bassett
I’ve had LED lights, with multiples in one fixture, flicker on grid power. Brad Sent from my iPhone > On Feb 4, 2022, at 7:18 AM, Dana Orzel wrote: > > Ditto on misc flickering w LEDs on my Off grid Radian system > I have some LEDs that are absolutely stable all the time and some of the >

Re: [RE-wrenches] Well siphon?

2022-01-27 Thread Bradley Bassett
Years ago, and maybe still there, a siphon was used to go over the existing dam on the Pocono reservoir to run a hydro generator. There was a vacuum pump pulling a vacuum at the top of the arch to keep it full of water in case air bubbles got in. They did have to prime it to get it going. I think

Re: [RE-wrenches] 24v to 48v upgrade help

2022-01-27 Thread Bradley Bassett
Over the years I have *never *seen loads, no matter how small, taken off of a mid point of a battery not cause serious issues with cell balancing. Even with the use of the Vanner equalizer there were always still problems with the battery bank. So I would never do it. When I converted to a 48

Re: [RE-wrenches] Off Grid, Cloudy Days, Solar Tilt Question

2023-10-25 Thread Bradley Bassett via RE-wrenches
I used to have both an array at a 60° tilt and one at 14° tilt. In the winter the high tilt array did better on sunny days, and on cloudy days the shallow array did better. They were different modules and different sized arrays, so without more analysis than I did, it would be hard to tell which

[RE-wrenches] APsmart and charge controllers

2023-10-26 Thread Bradley Bassett via RE-wrenches
I had a talk with tech support at APS about using the APSmart RSD devices in my DC coupled system. I found it hard to understand him so I'm not completely clear on what he said. One thing was clear and that is they do not test these for use with charge controllers, so can't support that use. Other

Re: [RE-wrenches] Off Grid, Cloudy Days, Solar Tilt Question

2023-10-26 Thread Bradley Bassett via RE-wrenches
curiosity, what is the actual difference between the two on those > cloudy days. > > Thx > Jay > > > > On Oct 25, 2023, at 5:04 PM, Bradley Bassett via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >  > I used to have both an array at a 60° tilt and

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Bradley Bassett via RE-wrenches
AFAIK Or any of the variants of that like the dual input unit Brad Sent from my iPhone > On Apr 19, 2022, at 9:18 AM, jay via RE-wrenches > wrote: > > HI All > > I’ve got a project coming up that has specified a Schneider XW 80/600 > controller. > > Its going to need RS. > > Is the only

Re: [RE-wrenches] Schneider XW MPPT 80/600 rapid shut down

2022-04-19 Thread Bradley Bassett via RE-wrenches
The Schneider RSD switch has a Tigo transmitter, which is no longer SunSpec compliant. SunSpec devices do NOT work. I know for certain that the APsmart devices do not work. Fire Raptors are very robust and might be a good choice for off grid where reliability is paramount. But they come with 6ft

Re: [RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?

2023-11-08 Thread Bradley Bassett via RE-wrenches
Hi George, It's good to see you're still with REC. I'd assume this would fall under the purview of UL rather than NEC. Anything that meets UL will pass NEC. With temperature derates I think you'd have had to go to larger wire long ago to meet NEC standards. It might be good to go to a larger

Re: [RE-wrenches] Magnum Inverters

2022-07-20 Thread Bradley Bassett via RE-wrenches
The Samlex EVO4248SP is a potential substitute. The only system panel is the MidNite E-panel. This is a 4.2 kW split phase inverter. Brad AEE Solar Sent from my iPhone > On Jul 20, 2022, at 1:25 PM, Ron Young via RE-wrenches > wrote: > > I have been waiting literally months for delivery of

Re: [RE-wrenches] EG4

2022-07-28 Thread Bradley Bassett via RE-wrenches
Check out YouTube videos by Will Prowse. He’s used them and taken them apart. It would be better if any wrenches have used them though Brad Sent from my iPhone > On Jul 28, 2022, at 12:49 PM, Dave Tedeyan via RE-wrenches > wrote: > > Hi all, > > Does anyone have any experience with EG4

Re: [RE-wrenches] Samlex EVO series and AGS

2022-09-03 Thread Bradley Bassett via RE-wrenches
The EVO has an AUX contact closure, either NO or NC that can be programmed for a two wire generator. If you need 3 or 4 wire start logic you can use the Atkinson GSCM. Brad On Fri, Sep 2, 2022 at 9:30 PM frenergy via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Doesn't the EVO have

Re: [RE-wrenches] HomeGrid batteries

2022-10-11 Thread Bradley Bassett via RE-wrenches
I'm curious what you consider mediocre about the HomeGrid? Brad On Mon, Oct 10, 2022 at 7:07 PM Lou Russo via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Aloha All, > > I am considering doing a job with one of these (14kWH) with a Sol-Ark 12kW > for a client who is demanding them.

Re: [RE-wrenches] AC coupled grid tie only inverter

2022-10-08 Thread Bradley Bassett via RE-wrenches
The ACLD was long ago discontinued. The Morningstar relay driver would work fine. I think Magnum limited the size of the grid tie inverter to 90% of the Magnum inverter max power. So 3960W for a MS4448PAE. Brad On Sat, Oct 8, 2022 at 8:47 AM Jay via RE-wrenches <

Re: [RE-wrenches] solar panel recycling

2022-08-17 Thread Bradley Bassett via RE-wrenches
Matt Ferrell gives a good summary of the issues: https://www.youtube.com/watch?v=3JqzSsStwF4 Brad On Wed, Aug 17, 2022 at 5:55 AM jay via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi All, > > Some asked me a question about recycling of panels and I can’t exactly > find out the

Re: [RE-wrenches] Discover LiFe battery question

2023-01-10 Thread Bradley Bassett via RE-wrenches
It’s not required but it has the only reliable means of generator start stop. There are three relays that can be programmed. You can’t get accurate battery state of charge by using voltage except near empty or full. The LynkII also has a little bar graph showing state of charge to the nearest

Re: [RE-wrenches] 24V Multi Mode Inverter Options

2023-01-03 Thread Bradley Bassett via RE-wrenches
Samlex EVO4024 is supposed to be a very robust simple inverter. 120VAC output, AC charging, good value. Brad On Tue, Jan 3, 2023 at 6:44 AM Chris Sparadeo via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hey there, > > I have a client with a dead 24V Xantrex SW…It had a good 20+

Re: [RE-wrenches] BACKUP system revival

2022-12-17 Thread Bradley Bassett via RE-wrenches
The Radian grid AC in is connected to the utility side of the transfer switch. You may need a service rated fused disconnect on that line, probably 60A. Then you can feed the AC out to the generator input on the transfer switch to power the main house panel. It's best and usually required by code

Re: [RE-wrenches] Sola-ark cold morning

2022-12-04 Thread Bradley Bassett via RE-wrenches
If they are the AES 48-6650 batteries I think they do *not* have low temperature mode, and will be damaged if they are charged while they are below freezing. The AES 48-3000 I think *do* have a low temperature mode and would prevent charging if they are below freezing. Wind will tend to make any

Re: [RE-wrenches] SolArk and Tigo compatibility

2022-11-16 Thread Bradley Bassett via RE-wrenches
The issue as I see it is that the Tigo RSS Transmitter and the APsmart transmitter are both rated to draw up to 800ma. The 12VDC output of the Sol-Ark inverters is limited to 100ma. Since some have used this successfully I suppose that means that either these transmitters don't really use more

Re: [RE-wrenches] Low voltage lithiums

2022-11-19 Thread Bradley Bassett via RE-wrenches
On some LFP batteries the cell balancing only happens at full charge, so you do need to get to full every so often. Discover AES is one that needs this. Brad On Sat, Nov 19, 2022 at 10:10 AM Dana Orzel via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Another issue is what charge

Re: [RE-wrenches] Remote battery disconnects

2023-01-28 Thread Bradley Bassett via RE-wrenches
My design for one customer was to have one initiator for the PV and inverter, and a separate one for the battery initiator. And, to put up a plaque giving instructions to turn off the PV and inverter first, then the battery. Brad On Sat, Jan 28, 2023 at 4:22 PM William Miller via RE-wrenches <

Re: [RE-wrenches] Off Grid Battery Charging

2023-03-16 Thread Bradley Bassett via RE-wrenches
I tried this back in the 1970's with an exercise bike and a high efficiency generator (still have this if anyone wants it). If I pushed hard I could get it up to 200W, but only sustain about 100W. The only time I used it is when my battery was depleted and I wanted to watch TV. I had a 12VDC 5" B

Re: [RE-wrenches] absolyte GP battery question/ sideways mounting.

2023-02-21 Thread Bradley Bassett via RE-wrenches
; > Solar Energy International > http://www.solarenergy.org > > > > On Mon, Feb 20, 2023 at 3:13 PM Bradley Bassett via RE-wrenches < > re-wrenches@lists.re-wrenches.org> wrote: > >> Flat is the preferred orientation and they say that if installed with the >> cel

Re: [RE-wrenches] absolyte GP battery question/ sideways mounting.

2023-02-20 Thread Bradley Bassett via RE-wrenches
Flat is the preferred orientation and they say that if installed with the cells vertical it would lose some small percentage of capacity. They never said anything about reduced life that I remember. It is very easy to have short life on these if not fully charged very often. The will sulphate

Re: [RE-wrenches] Backwards compatibility Schneider

2023-03-29 Thread Bradley Bassett via RE-wrenches
I have an XW5548+ with Gateway and Discover AES battery and can vouch that it works slick. Brad AEE Solar Sent from my iPhone > On Mar 29, 2023, at 9:26 AM, Dave Angelini Offgrid Solar via RE-wrenches > wrote: > > It will be some work to make this work right for you! The XWP is based on

Re: [RE-wrenches] [EXTERNAL] Solark-Fortress Com? (was Fortress Battery Heater)

2023-02-10 Thread Bradley Bassett via RE-wrenches
That is with Discover batteries. Sent from my iPhone > On Feb 10, 2023, at 8:34 AM, Dave Angelini Offgrid Solar via RE-wrenches > wrote: > > Agree Will and adding that for generator users closed loop will save 25% or > more on fuel. > > I know alot of you folks do not use Schneider but it

Re: [RE-wrenches] Tech Support Issues with Sensata

2023-05-31 Thread Bradley Bassett via RE-wrenches
Just so you know, AEE Solar still has a bunch of Magnum panels and controls, no inverters, no support though. At least until they find someone to take it all. Keep an eye out for other close out stuff too. But, yes they are still going and working on getting better. Brad Bassett Retired--- 1985

Re: [RE-wrenches] Hawaiian Tie in

2023-08-08 Thread Bradley Bassett via RE-wrenches
I have no experience with the Hawaii connection, but another choice for a tap connector is the Ilso GTA type with cover. You don't have to cut the tapped line and don't rely on piercing it. Brad Bassett Application Engineer (ret.) 1985 Solar Eng Svcs -> Applied Power -> Applied Power (Idaho

Re: [RE-wrenches] Parallel Homegrid Stack'd Busbar

2023-06-29 Thread Bradley Bassett via RE-wrenches
Note that MidNite now also makes 2000A and 500A versions of their BCB. With two Sol-Ark 15k you do need to use the 1000A version with 275A each inverter. I can also confirm that you do need to use both of the battery terminals in the Sol-Ark 15k for full power, or the Homegrid bus bars that Jason

Re: [RE-wrenches] Magnum Energy ME-AGS-S

2023-06-15 Thread Bradley Bassett via RE-wrenches
AEE might still have some of those if I remember Brad. Retired On Thu, Jun 15, 2023, 7:41 AM Chris Daum via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Hi folks: > > > > Any chance one of you has this auto gen start module they can part with? I > do NOT need the one with the

Re: [RE-wrenches] Outback Board Repair

2024-02-21 Thread Bradley Bassett via RE-wrenches
Regarding AEE and off grid support, I'm not really in touch with them much any more so I can't say. You could ask Glenn Hall, he'd be able to say if he's heard anything about hiring a new tech. Of course finding someone with much off grid experience would be hard. Glenn and Alex do have some

Re: [RE-wrenches] Tigo RSS Off Grid

2024-02-17 Thread Bradley Bassett via RE-wrenches
I powered a MidNite LSOB transmitter from a Classic AUX, though the receivers didn't work with the Classic. The Classic is limited to 200ma output and the Tigo and APS transmitters are rated at up to 800ma input, so it might overload the Classic AUX output if they really do draw that much. I

Re: [RE-wrenches] Deka Duration

2024-02-07 Thread Bradley Bassett via RE-wrenches
Read the warranty. Very limited uses to maintain coverage. Mfg by an Italian Co that is somewhat condescending toward customers. But of course East Penn is good to work with. My understanding is that they do work with the three phase Sol-Ark inverters. Brad On Wed, Feb 7, 2024 at 4:52 AM William

Re: [RE-wrenches] Schneider Rapid shutdown with 2023 compliance

2024-01-01 Thread Bradley Bassett via RE-wrenches
Note that the MPPT disco RS works only with Schneider charge controllers. With any other charge controllers you'll need to use Fire Raptors. Specifically the power line type rsd do not work with classic cc. I see no reason why the Schneider units would not meet 2020 or 2023 codes. On Mon, Jan 1,

Re: [RE-wrenches] Non-battery string inverter options?

2024-02-23 Thread Bradley Bassett via RE-wrenches
Growatt MIN. They're capable of battery connection but work fine as a string inverter at a decent price. Brad On Fri, Feb 23, 2024 at 4:09 AM Glenn Burt via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Fronius. > Solis > > -Glenn > Sent from my 'smart'phone, so please excuse typos

Re: [RE-wrenches] Ballasted ground mounts

2024-03-21 Thread Bradley Bassett via RE-wrenches
Is Aerocompact still around ? They had a nice simple ballasted ground mount Brad Bassett On Thu, Mar 21, 2024, 10:45 AM Kristopher Schmid via RE-wrenches < re-wrenches@lists.re-wrenches.org> wrote: > Thanks for the info, Sam. > > I guess that I should have mentioned that I am looking at an 8kw

Re: [RE-wrenches] 120 Vac and 12Vdc mixed distribution system

2024-04-25 Thread Bradley Bassett via RE-wrenches
I had a lot of trouble keeping QO breakers functional on a 12VDC distribution system. I'd have to move them around every week or so to keep a good contact on the plug in contacts. They seem to work fine on a 24VDC system. I went to using MNPV or MNDC breakers instead in PV combiner or other