On the news right now there's a story about the shell of a burnt-out
Dairy Queen. Damages estimated at $500,000.00. The reason for my
writing is that the firefighter being interviewed just a moment ago
said that if there had been sprinklers he'd probably not still be
there to talk to the reporter.
Our FD is more then glad to hook up an engine, handline and flow them.
(Except in the dead of winter)
Its a win-win-win, contractor gets it tested without having the greater
expense of renting his own equipment, AHJ gets his flow test and the FD gets
to work with the system and gain confidence in
Kurt,
I'd do a couple of things to attempt to get some clarity (sanity?) from
your AHJ.
First, I'd direct his to the applicable definitions of feed main, cross
main, and branch
lines in chapter 3 of NFPA-13. They are 3.5.3, 3.5.2 and 3.5.1,
respectively. After
he's had a chance to look tha
I didn't find anything about an air test in Chapter 9 of the Oregon Fire Code.
Only reference to testing in accordance with NFPA 25.
Ed
Roland Huggins <[EMAIL PROTECTED]> wrote:
The issue here is verifying both piping integrity and ability to flow
system demand. How do you do that with
The issue here is verifying both piping integrity and ability to flow
system demand. How do you do that with air (you go for 500 cfm
instead of gpm on the most remote standpipe -lol)?
Roland
On Jan 17, 2008, at 7:30 PM, [EMAIL PROTECTED] wrote:
The Oregon Fire Code allowed testing with a
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
Website says they do:
http://www.huguenotlabs.com/metalAnalysis.html
Terri Simmons Leyton
PROTECTION DESIGN & CONSULTING
Ph: 858-751-2930 - ext. 101
Fax: 858-751-2933
Cell: 619-871-8450
Go CHARGERS! We take care of our KIDS!
-Original Message-
From: [EMAIL PROTECTED] [mailto
Try this link.
www.corrconsult.com
Ray Schmid, P.E.
President
Schmid & Associates, PC
Fire Protection Engineers
443-465-4206
[EMAIL PROTECTED]
This communication is confidential. This information may be privileged and
is intended for the exclusive use of the above named addressee(s). If you
a
Did the Cal-Val work OK with the flow from the inspector's test?
At 03:19 PM 1/18/2008, you wrote:
Off Standpipe (in direction of flow):
BV - Cla-Val - Tee (to FDV) - BV - CHV - WFS - T&D (to Spkrs.)
Worked well.
Tom
Tom,
Is the BF before the Cla-Val required or was it installed in case there
Off Standpipe (in direction of flow):
BV - Cla-Val - Tee (to FDV) - BV - CHV - WFS - T&D (to Spkrs.)
Worked well.
Tom
Tom,
Is the BF before the Cla-Val required or was it installed in case there
is maintenance required on the Cla-Val and not to shut down the feed?
_
That's all true, but I believe a joint committee was the reason for the
changes in the NFPA 13, 2007. And if you look at 2007 there are very
different requirements for bracing / spacing, and loads. All I'm saying is
that 2007 will provide seismic protection that has been judged to meet the
inte
In my situation I have an AHJ that is saying that a gridded system
doesn't use branch lines but rather all piping components in a grid
system are either feed or cross mains and so even 2" and smaller piping
needs to be braced.
I sent him a copy of the Appendix brace location examples for gridded
sy
Tom,
I feel that this should be clarified further.
My understanding, at least as affected by the ICC Codes, is as follows:
The 2003 edition of IBC removes the reference to the use of NFPA 13 from
ASCE 7 2002 edition. (The version of NFPA 13 referenced is NFPA 13, 1999,
NOT NFPA 13 2002). NFP
Remember that if your spec. requires you to meet ASCE 7 requirements that
NFPA 13, 2002 was found not to meet these, however 2007 was accepted as
substantially meeting these requirements. Also there was a TIA to 2002 to
move toward meeting ASCE 7, but 2007 is much better.
Most AHJ's will accept
I'm re-posting this and any opinions or comments as to whether the
seismic bracing locations shown figures in the 2002 NFPA 13 Appendix are
OK to use would be appreciated.
Kurt Kingston
Commercial Fire Protection Inc.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On
Q
Peter Thomas --
Sent from my BlackBerry Wireless Handheld
This message contains information which may be confidential and privileged.
Unless you are the addressee (or authorized to receive this message for the
addressee), you may not use, copy or disclose to anyone the
MDE can analyze the pipe (metallurgically) as well as provide sampling kits.
http://www.mde.com/mde/home.shtml
Michael
At 06:52 PM 1/17/2008, you wrote:
Where do you send pipe for MIC testing?
Forest Wilson
Cherokee Fire
**Start the year off right. Easy ways to stay in shape.
I would not fill the space with those of Cowboys fans, as this is an actual
vacuum. As we all know, if this space is placed under a vacuum, the flash
point is lowered dramatically, and can result in a much faster developing
fire.
Matt
Matthew J. Willis
Living Water Fire Protection, LLC.
1160 McKe
Peter Thomas --
Sent from my BlackBerry Wireless Handheld
This message contains information which may be confidential and privileged.
Unless you are the addressee (or authorized to receive this message for the
addressee), you may not use, copy or disclose to anyone the
That sound you hear, my friend, is the wind of change.
Or, the sound of several lightning bolts!
Terri Simmons Leyton
PROTECTION DESIGN & CONSULTING
Ph: 858-751-2930 - ext. 101
Fax: 858-751-2933
Cell: 619-871-8450
Go CHARGERS! We take care of our KIDS!
-Original Message-
Will they test the pipe too? I only know of them testing the water and the
scale, not the quality of the pipe.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Terri Leyton
Sent: Friday, January 18, 2008 1
So long as the manufacturer will warrant/underwrite the listing of a
valve within a given range of minimum to maximum flow, it should be
okay.
Steve Leyton
Protection Design & Consulting
The foregoing is my opinion only and is not intended to represent the
Technical Committee on Standpipe Systems
http://www.fpscmi.com/about_us.htm
This is a spinoff of the Code Consultant's (CCI) corrosion guys; they have
then worked with Potter Electric to develop the Potter line of Corrosion
Monitoring products.
Another source
Glc
Go PSU (neener neener to Michigan- next year's the charm, game is bro
You're right. There's a huge stockpile of broken and shattered dreams
in Big D.
Memo to the Munce: I know, I know, stick to sprinklers. But it's just
so darned EXCITING. We're pro sports Siberia out here ...
Steve Leyton
Protection Design & Consulting
-Original Message-
From: [EMAI
http://www.huguenotlabs.com/
These guys are pretty good.
Terri Simmons Leyton
PROTECTION DESIGN & CONSULTING
Ph: 858-751-2930 - ext. 101
Fax: 858-751-2933
Cell: 619-871-8450
Go CHARGERS! We take care of our KIDS!
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTEC
I'LL throw my hat in for the Bill's as well! (next year)
Brian Harris
FDFP INC.
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Dyce Geoffrey
H.
Sent: Friday, January 18, 2008 9:35 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: NFPA 13, 2002 A.3.7
Go Bills!! (next year)
-Original Message-
From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Todd Williams -
FPDC
Sent: Thursday, January 17, 2008 7:43 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: NFPA 13, 2002 A.3.7.1 (4)
Was that a Santa Ana wind or just hot air?
No, use instead the broken dreams of Cowboys fans.
Bill Minkel, Designer
Western States Fire Protection, Dallas
NFPA Member #2578666
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Steve Leyton
Sent: Thursday, January 17, 2008 5:10 PM
To: sprinklerforum
There is a forensic metallurgist in Northern Virginia that I have used a
few times. I am looking for his card, but no luck yet.
Paul J. Pinigis, P.E.
Chief Life Safety Engineer
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of
[EMAIL PROTECTED]
Sent: Thur
Tom,
Is the BF before the Cla-Val required or was it installed in case there
is maintenance required on the Cla-Val and not to shut down the feed?
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Tom
Duross
Sent: Thursday, January 17, 2008 3:56 PM