Isn't it the building code that requires sprinklers? If nothing in 409
is applicable to the type of hangar then it would be EH-I IAW #13,
wouldn't it?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Since the building and the sprinkler system are subject to the same
ambient conditions wouldn't the expansion rates kind of offset each
other?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
And hopefully your proposal had an exclusion something like Span hangers to
distribute load to more than one structural member. It is assumed that the
structure can adequately support the fire sprinkler system without such
hangers.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original
The 250# is so a sprinkler fitter can swing on the pipe.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd
Williams
Sent: Monday, November 08, 2010 10:04 AM
To:
How about dielectric flanges?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Travis
Mack, SET
Sent: Thursday, November 04, 2010 9:07 AM
To:
NICET is going to attach electronic exhibits to the questions that require
reference materials not allowed in the test room. It is my understanding that
the only books allowed will be 13, 13R and 13D, no handbooks and no calculator.
An electronic calculator will be available on the computer
Science :)
WHAT? What about the math questions, etc that are not found anywhere
close to any NFPA documents?
On 11/3/2010 9:25 AM, Fletcher, Ron wrote:
NICET is going to attach electronic exhibits to the questions that
require reference materials not allowed in the test room. It is my
understanding
International Drive
Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension 74102
craig.pr...@ch2m.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday
Some issues other than those already mentioned are higher horsepower,
electrical conductor size, higher locked rotor amps.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On
I hope there isn't there is a standard that requires an enclosure. We
recently installed some systems at a copper mine with the AFFF tanks,
risers and other stuff outside. It is pretty easy to build a rack from
Unistrut and plywood to mount panels etc... One drawback might be the
shelf life of the
-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Tuesday, October 19, 2010 9:47 AM
To: sprinklerforum
Have used swaged nipples in the past but not so many in the 1/2 size. Back in
the day when doing deluge systems and being limited to extra heavy screwed
galvanized fittings we had to take what we could get. There weren't a lot tee's
available that reduced on the run so we used swaged nipples
at a greater rate and thereby run
the risk of freezing the wet section. I think you'd be better off with
a foam donut at the point where the dry barrel enters the freezer
box to mitigate against moisture running down the barrel but I'd check
with Viking first.
On Tue, Oct 5, 2010 at 2:07 PM, Fletcher, Ron
We call them feel good sprinklers. Some jurisdictions make us put them in while
others do not. The heads at the deck will almost certainly active first
preventing the water shielded heads from operating. If it is light or ordinary
hazard and the obstructions are not structural the heads aren't
I looked through my old engineers reference book that I got at Grinnell
in the early 70's and found nothing with an A126 number on it.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
worst case scenario, they would have to change the old nozzles
with
new.
My drawing date is 8-5-1963 so it may be too old.
Thanks for your reply
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Fire flow is from IFC Appendix B not NFPA. As far as I know 1500 gpm is the
minimum fire flow for any property. The inside/outside hose flow added to
sprinkler flow has nothing to do with fire flow from hydrants, they are two
completely separate issues. A reduction in fire flow is allowed for
For a retrofit you wouldn't do a pump test and then use the results of the test
for the calculations?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
the ERO was building in.
Thom
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Wednesday, September 01, 2010 7:58 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Diesel Pump Engine RPM
NFPA #20, 2003, 11.2.4.1.1. Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump.
Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?
If a 1760 rpm rated pump
First thing I would do is send a change order for the cost impact if the
requirements were not in the original specifications.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On
Main drain.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
craig.pr...@ch2m.com
Sent: Monday, July 26, 2010 5:32 AM
To: sprinklerforum@firesprinkler.org;
Anyone have experience with an ammonia quenching systems?
Ron Fletcher
Aero Automatic
Phoenix, AZ
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical
3.4.5 in the handbook says dry systems should only be installed where
pipe is subject to freezing. I have had AHJ's use this to require a wet
system in the heated areas and dry in the unheated.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From:
If the room (hall) is less than 300 sqft it could be classified as panel
(obstructed) construction and a 22 inch deflector would be okay. Would
that take care of the problem?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Thanks for the idea. I'll save this one.
Regards,
Ron Fletcher
Pre Construction Services
rfletc...@aerofire.com
Aero Automatic Sprinkler Co.
21605 N. Central Avenue
Phoenix, AZ 85024
Phone 623-580-7836
Fax 623-434-3420
-Original Message-
From:
The last ones I used came from a company in Denver. I order them through
a local company that sells hydraulic hoses. You can contact me off forum
if you want more information on the vendors but you should be able to
find a local supplier that can make what you need. Of course there is no
UL
Sometime back there was a thread about flow tests and the accuracy of
using diffusers with built in pitot tubes. I had said that I had an
article written for the AWWA Journal on the subject. Some of you had
asked for a copy of the article which I couldn't find at the time. I
found it, it's been
Maybe there is something in the 2009 commentary about why it was
removed? The commentary wasn't available when I ordered the codes. If
anyone out there in forum land has the commentary maybe they would be
kind enough to check?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
Yes. Greater than 250 ft egress up to 400 ft with smoke and heat vents.
No exception for ESFR.
Not George
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike
Hairfield
Sent: Tuesday, June 22, 2010 9:49 AM
So is a single interlock electric release pre-action system without supervision
air allowed by NFPA #13?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
So is 3.4.9 (2010) wrong when it says piping system that
contains air that might or might not be under pressure. If 7 psi minimum is
required how could there be a P/A system without air pressure?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From:
Even more interesting will be when the electrician, HVAC or ceiling guy decide
they can put the head back close to where it was without a sprinkler contractor
on site.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
and life safety
system.
Norm
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Friday, May 28, 2010 11:02 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Flexible Heads
Is there a correlation between the IBC occupancy and NFPA #13 Hazard? I
have a set of plans where the building occupancy classification is H-1
and the EOR has specified OH-II for the sprinkler system. I have always
thought (maybe mistakenly) that any H occupancy would be EH-I minimum.
Ron
-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Wednesday, May 26, 2010 4:53 PM
To: sprinklerforum@firesprinkler.org
Subject: Occupancy vs Hazard
Is there a correlation between the IBC occupancy and NFPA #13 Hazard? I
have a set of plans
. Box 882136
Steamboat Springs, CO 80488
Tel: 970-879-7952
Fax: 970-879-7926
Fletcher, Ron
Sent: Wednesday, May 26, 2010 5:30 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Occupancy vs Hazard
It's a munitions maintenance facility for missiles. I suppose once the
mushroom cloud clears
I think it is 3 pumps 3 arresters. The main line of reasoning here is,
it's the government and they are buying something that is useless and
unnecessary so more must be better. It's like when the pump is in the
room with the riser manifold. It's a 100 gallon on the pump and a 10
gallon arrester on
I am trying to find out how a new rule is added into 13 without having a
bar next to it in the margin and without being in the ROP or the ROC?
Case in point. NFPA 13, 2007 Section 18.2.4. The protection specified
in 18.2.1 shall not be required where ESFR or large drop sprinkler
systems that are
, April 28, 2010 10:16 AM
To: sprinklerforum@firesprinkler.org
Subject: Re: NFPA #13 changes/additions
The criteria was indeed in the 2002 edition (just not in the first
printing). Get Errata 02-1 from www.NFPA.org
Roland
On Apr 28, 2010, at 9:34 AM, Fletcher, Ron wrote:
I am trying to find out
? For those of use who use
this Forum regularly and are not AFSA members: SHAME ON YOU.
On Wed, Apr 28, 2010 at 10:18 AM, Fletcher, Ron rfletc...@aerofire.com wrote:
It figures that I and the AHJ would have the first printing of 13 and
the handbook.
Ron Fletcher
Aero Automatic
Phoenix, AZ
We have an AHJ that is using the 2002 NFPA 13 and doesn't care what is
in the 07. We have 25 ft. high tire storage in portable racks in a 35 ft
bldg. They want column sprinklers installed with the ESFR's because
there is no specific exception (that I can find) for column sprinklers
as there is in
In the past I have seen what was called a canned pump used with wells.
Put a vertical turbine pump in a 5 ft diameter sleeve 20 ft. deep and
use the wells to keep it full of water while the pump runs. It saves the
cost of a large tank but obviously is not as fail safe.
Ron Fletcher
Aero Automatic
Some years ago we did an upgrade/replacement and abandoned the existing
system in place. We even used some of the old mains as trapeze hangers
for the new mains. I wasn't there but I heard that we had the inspector
scratching his head trying to figure it out. I sent a picture into FPC
Magazine for
?
Chris Payne
FPS
Owensboro, KY
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Fletcher, Ron
Sent: Thursday, April 08, 2010 8:24 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: abandoned pipe
Some years
Is there a maximum pile volume for rubber tires stored on side in
portable racks 25 ft. high? Roof height is 35 ft.
Ron Fletcher
Aero Automatic
Phoenix, AZ
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
Forest,
I think the RTI on a 165F link and 155F bulb are about the same, anyway they
are both considered ordinary temperature. Intermediate starts at 175F.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Doesn't it say minimum 80 sqft per head?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Dewayne
Martinez
Sent: Friday, March 26, 2010 11:48 AM
To:
Have you checked out the Viking C-1 release? I think it can be spaced more than
8 ft apart. Probably pricey but maybe worth a look.
Ron Fletcher
Aero Automatic
Phoenix, AZ
.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
There was a thread a while back (I think) that discussed a way of
finding leaks in dry systems using a colored gas or something like that.
I didn't save the thread because we live in Phoenix and don't have dry
systems except in freezers. My mistake. We are working on a freezer
system repair, have
...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Thursday, March 18, 2010 3:27 PM
To: sprinklerforum@firesprinkler.org
Subject: dry system air leak
There was a thread a while back (I think) that discussed a way of
finding leaks in dry systems using a colored gas or something like that.
I didn't save
We usually go every 8 ft. I don't think it's addressed in a code. It won't take
the installers long to figure out where they need them.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Logic? Try this.
Shell retail space with 4-12 pitch wood roof. Rough in core and shell
system for OH2 at 10 ft. x 12 ft. spacing. Tenant installs a suspended
ceiling. The attic is now light hazard combustible concealed space that
must comply with 8.6.4.1.4. A lesser hazard yet the OH2 design is
The only program I'm aware of is used for a Quell system by Tyco
designed for cold storage.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Vince
Sabolik
Sent:
32233
904-652-4200 Phone
904-212-0868 Fax
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher, Ron
Sent: Monday, February 08, 2010 4:56 PM
To: sprinklerforum@firesprinkler.org
Subject: Bio Diesel
Anyone
Anyone have experience with diesel/methanol bio diesel plant. They have
outdoor methanol and diesel storage. The building is 20k sqft with
mixing, purification etc... inside. Looking for advice.
Ron Fletcher
Aero Automatic
Phoenix, AZ
___
I thought it was closer to 4AM but I might have lost track of the time.
Orival www.orval.com makes what you need. We installed the filter (model
OR-03-PS) in cooling line. The thing cost about $8k but is much cheaper than
replacing the engine. We had the water examined at a test laboratory to
We have 65,000 sqft of rack storage that requires in-rack sprinklers.
The racks span an area that is protected by 4 roof systems. Can we use a
single system to supply the in-rack and have all 65,000 sqft on a single
valve?
I thought that I read somewhere once upon a time that in-rack systems
had
-piled, palletized, *rack storage*,
bin
box, and shelf storage in excess of 12 ft (3.7 m) in height.
-Jim
On Thu, Jan 14, 2010 at 11:48 AM, Fletcher, Ron
rfletc...@aerofire.comwrote:
We have 65,000 sqft of rack storage that requires in-rack sprinklers.
The racks span an area that is protected
reading the same thing and it did include the rack aisles. I
will try to find it.
T
On 1/14/2010 1:10 PM, Fletcher, Ron wrote:
Would the 40,000 sqft limit apply to the area including the aisles? Of
the 65,000 sqft of area the racks cover only about half is actually
rack. So if there is only 32,500
...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Thursday, January 14, 2010 12:49 PM
To: sprinklerforum@firesprinkler.org
Subject: In-rack system zoning
We have 65,000 sqft of rack storage that requires in-rack sprinklers.
The racks span an area
We have installed window sprinklers on a lot of the glass at Phoenix Sky
Harbor Airport but they are all on wet systems.
Deluge with standard nozzles should work as a performance based design
provided you can get the AHJ to buy it.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original
the other restrictions on small orifice
heads.
On Tue, Dec 1, 2009 at 8:41 AM, Fletcher, Ron
rfletc...@aerofire.comwrote:
8.3.4 doesn't say for light hazard only and it doesn't prohibit the
use of small orifice sprinklers in OH. The Tyco TY-FRB is UL Listed in
2.8k,4.2k, 5.6k and 8k for light
as are
sprinklers with a nominal K-factor and also do not pass the same fire
tests that K-5.6 and larger sprinklers do. Small orifice sprinklers are
restricted to wet systems because
And it goes on to talk about the other restrictions on small orifice
heads.
On Tue, Dec 1, 2009 at 8:41 AM, Fletcher
Drive
PO Box 491, Spartanburg, SC 29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
craig.pr...@ch2m.com
http://www.ch2m.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Tuesday
We are doing a project with a FM design. The tipping area is a dual
density .80/1500 .30/5000 and the processing area design is 12 K16.8 @
63 psi. FM references Data Sheet 2-2.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
When is a framing member not a framing member? When it's a 2x4. I'm pretty sure
2x4's would be considered smooth ceiling so there wouldn't be any framing
members to speak of and the 225 sqft should be okay.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From:
Are you sure it isn't the FDC with the Storz connection?
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Splawn,
Shannon
Sent: Monday, November 02, 2009 10:48 AM
Interesting video. Have you seen FM Data Sheet 7-20 Oil Cookers? It says to put
a deluge system discharging at 0.5 gpm per sqft over the hot oil surface.
Ron Fletcher
Aero Automatic
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
AM
To: sprinklerforum@firesprinkler.org
Subject: Re: Report: Antifreeze sprinkler system may have
contributedtofatalexplosion
that's for a flat surface (thin layer of oil) verses a pan of oil (or
deep aft fryer)
Roland
On Oct 23, 2009, at 5:51 AM, Fletcher, Ron wrote:
Interesting video. Have
-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Fletcher,
Ron
Sent: Friday, October 23, 2009 11:45 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Report: Antifreeze sprinkler system may have
contributedtofatalexplosion
It isn't a very thin layer of oil
] On Behalf Of Fletcher,
Ron
Sent: Friday, October 23, 2009 11:57 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Report: Antifreeze sprinkler system may
havecontributedtofatalexplosion
It's vegetable oil.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
think).
Roland
On Oct 23, 2009, at 8:45 AM, Fletcher, Ron wrote:
It isn't a very thin layer of oil. We are doing 4 fryers that are 6 ft
wide by 18 ft long and hold about 250 gallons of oil at 325F. They run
potato chips through on a conveyor. I'm not sure but I think the oil
is
at least 4-6
Where does it say not exit electrical rooms? I know about the
restricted space limitations and the required clearances.
Ron Fletcher
Aero Automatic
Phoenix
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
12.1.3.4 sort of. But not a problem.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Greg
Lindholm
Sent: Tuesday, October 13, 2009 11:32 AM
To:
IFC Chapter 34.
Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Hinson,
Ryan
Sent:
Here where it doesn't freeze we rise up outside and elbow through the
outside wall about 1.5 ft. above the floor. Build a 2'x2'x2' insulated
dog house to enclose the pipe and it's freeze protected.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix
-Original Message-
From:
There are lots of construction types that cannot be sprinklered in accordance
with NFPA #13, at least not at a reasonable cost. Ever seen a building
containing more than 12 ft high storage that has a roof pitch greater than
2/12? A couple of scenarios I have seen that don't fit into a
Is there such a thing as an ordinary hazard extended coverage concealed
sprinkler? Thanks in advance for the help.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org]
A preposition is a word you should never end a sentence with.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Thursday, September
If the heads aren't changed the ESFR obstruction rules still apply.
Manufacturing areas will typically have numerous obstructions greater
than 24 wide that will require additional sprinklers. Then the system
will have to be re-calculated for 13 or 14 flowing heads instead of the
original 12 and
Numerous times locally we have had problems with water supply not being
what it should. For instance the flow test was now half of what it was
six months ago. We would call the water company tell them a valve was
closed somewhere. They would check into it and always call back saying
everything was
Ron.
With a city supply we calc the fire flow separate from the sprinkler demand. I
don't see why it would be any different with a tank. The onsite underground
would not be sized to flow both simultaneously so I don't see why the tank
would be sized for both.
Ron Fletcher
Aero Automatic
What C Factor should be used for stainless steel pipe?
Ron Fletcher
Aero Automatic
Phoenix
___
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
Thanks! I looked right at it but all I saw was copper.
Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
From: Jim Zimmerman [mailto:zimm...@gmail.com]
Sent: Tuesday, August 25, 2009 7:57 AM
To: Fletcher, Ron
http://www.dicksondata.com/info/home.php
Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On
I wouldn't calc a RA straddling the wall. The wall makes a great draft
stop.
Depending on how the system is spaced the minimum 960 sqft RA may become
a consideration.
Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
.
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Fletcher, Ron
Sent: Thursday, July 30, 2009 12:21 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: Renegade HVAC Contractor
At least you are not spending money
At least you are not spending money and time on BIM while all the other
trades are doing installation. Remember the sprinkler creed install
high install first.
Ron Fletcher
Aero Automatic
Phoenix
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
ESFR's are very limited, averaging the height is not allowed. There is
also a 20 ft maximum limit for distance from the top of storage to the
roof sprinklers but I don't know if applies when there are in-rack
sprinklers.
Ron Fletcher
Aero Automatic Phoenix
-Original Message-
From:
It is found in the 2006 Uniform Plumbing Code 603.4.16.2 says that if
you have an FDC you need an RPZ. It isn't in the IPC.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
What information are you looking for? We installed monitors in a tent in
Scottsdale where they have the Barrett Jackson auto auction every year.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
IMHO no heads under the conveyor.
Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C: 602.763.4160
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
Is there still a generic log in and password? It's been a while since I
tried logging in.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
___
Sprinklerforum mailing list
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
For
If it's a municipal water supply the two graphs will probably not be the
same. The graph isn't from a zero flow to the 2.5 flow and then the
4.5 flow. If there was 2,000 gpm domestic flow at the time of the test
the graph is actually from 2,000 to 2,000 plus the 2.5 flow or 2,000
plus the 4.5flow.
We have used insulation covering the CPVC as a separation many times. We have
even used copper pipe through the insulation to sprig SSU's into the attic for
NFPA #13 systems.
Ron Fletcher
Aero Automatic Sprinkler
21605 N. Central Ave
Phoenix, AZ 85024
P: 623.580.7836
F: 623.434.3420
C:
Assuming the pumps are installed parallel to each other I don't see any
reason to spend the extra dollars for the PLD's.
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Bill,
An excellent idea, please count me in. There are many things could be
better defined. We currently involved in a number of 13R projects at DOD
facilities. Most have common areas like dayrooms, laundry rooms
mechanical rooms and so on but the entire building is classified as R2
occupancy,
Has anyone read the RFQ? Was the intent for a remodel (tenant improvement) or a
re-build to meet current codes? The UFGS is a guide specification and is
suppose to be edited for each project. If the spec. wasn't edited to suit the
project it would include bunch of stuff that probably isn't
Why would the sprinklers under the plywood have to be included in the
remote area? Isn't it like putting a head under a duct or some other
obstruction?
Ron Fletcher
Aero Automatic Sprinkler
Phoenix, AZ 85024
___
Sprinklerforum mailing list