Sorry to be a pessimist, but why would a AHJ buy off on this calculated time
delivery versus seeing the real thing? I can think of a number of instances
that the owner of this software has messed up before.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
similar.
My persistence to understand engineering principles is what I have to back
my last hand calc. All I am saying is I would have a lot more faith in a
water delivery time program if it came from a reputable engineering firm
rather than a manufacturer of sprinkler equipment.
Jim Johnston
with a control valve and a flow switch. This arrangement
creates a messed up alarm scenario.
Contact me off forum if you wish, I can e-mail you a pdf of the arrangement.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248
agree that you
can't replace the system as originally installed?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
is that? Lets stick a bullet in the cylinder and pull the
trigger, there's a 5 in 6 chance nothing is going to happen, boom!
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
Was this one those that are shown in NFPA 13 - Parallel Combined systems? I
could never figure why one would use these? Craig, I know you pretty on the
ball with things but just in case look at 13- 2002 edition fig. 7.4.2.2?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection
Say it aint so snowboarding ya knuckle dragger! lol
Jim Johnston, P.E.
-Original Message-
From: Chris Cahill [mailto:chr...@sentryfiremn.com]
Sent: Tuesday, February 02, 2010 7:39 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: Mansions in the Sky (No Place for NFPA Standards)
My
I don't provide a checklist for this, but I do spell out the commodity
(class # and specific items) their storage method, height and the NFPA
section # so the AHJ can follow along with my thinking.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima
measurement, then re-energize the panel and take the readings.
There is a whole lot more comfort using this versus the handheld multi-meter
/ clamp on, it was kinda expensive $2500.00, but lots cheaper than a lawsuit
and fine.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
of these homes are $1,000,000 the high end is $10,000,000+, problems like
these just add fuel to the fire for our home builder opponents.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
of
experts out there making political decisions for the fire service - just
makes you wonder how people sleep at night maybe one of them will fall into
the 3000 annual fire deaths statistic?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Tom,
Not sure what state you are in but if your state utilizes the International
Fire Code there is a procedure to follow 2006 IFC 901.7.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j
I have always made the owner take care of this procedure, I just give him or
her the information and let them run with it.
Jim Johnston
-Original Message-
From: Forest Wilson [mailto:cherokeefire...@aol.com]
Sent: Wednesday, January 13, 2010 8:31 AM
To: sprinklerforum@firesprinkler.org
Good for California!! I wish the home builder idiots, building association
idiots, and our State Building Code idiots, could open their eyes and see
that a life is worth more than whatever the going square foot price is!
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
Test e-mail
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
___
Sprinklerforum mailing list
Sprinklerforum
Jim,
I don't do specifications since I am in the contracting world, but we use
Fairbanks Morse pumps, when using a vertical turbine I install a Fairbanks
Morse submersible pump for the jockey pump. Don't know if this helps you or
not?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire
temps than the traditional Class A fuels, all for what to save
1-3% of the building cost? I can keep rambling, but we all know the same
story. I'm sure when the first residential fire related death takes place
after the new codes take effect the lawyers are going to a hay day?
Jim Johnston
.
We then pump the glycerin in and pull heads at the high points until the
glycerin comes out, once filled we pump the solution up to about 10 psi
above the static conditions of the water supply.
Does this sound appropriate?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire
Are you talking expansion tank? If so we have those installed.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Chris Cahill [mailto:chr
to
the false since of security and the likelihood that the owner won't be
proactive.
I agree with you, people need to be better educated with these systems.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
, etc). So we can calc until we are blue in the face and demand that
the calcs are correct, but it really just doesn't matter if the functional
test doesn't work.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509
is
the system was designed inadequate back in 1992 just don't have the
information to justify my statement. Can any of my fellow comrades help me
out?
Thanks in advance.
Also I hope all of you a very Merry Christmas.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
the
requirements prior to 1993 were? I just don't see it as Ordinary II?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: craig.pr
.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: craig.pr...@ch2m.com [mailto:craig.pr...@ch2m.com]
Sent: Thursday, December 17, 2009 12:25
It was existing at the time, so the hazard was present when originally
installed.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Todd
that this design was applicable at the time? Again I find that hard to
believe that Ord II was acceptable back then?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
(by today's standards) that what was originally installed. The
only leg one can stand on is hoping that the codes were a lot less lax when
originally installed, thus allowing their particular situations. I agree
these hazards are nowhere close to Ord II not to mention dry!
Jim Johnston, P.E.
Fire
Should be State, but when community is agricultural based and Billy Bob is
the local elected official anything is possible.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j
watch?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Doug Hicks [mailto:fire...@eoni.com]
Sent: Thursday, December 10, 2009 11:50 AM
Jose the jalapino
Jim
-Original Message-
From: Thom McMahon [mailto:tmcma...@firetechinc.com]
Sent: Wednesday, December 09, 2009 1:42 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: fire pump - 10 diameters
Reed:
I think the idea was to minimize the amount of supply pipe inside
Sorry all, replied to the wrong thing, left handed blonde day I quess.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Jim Johnston
Thanks Bob,
For some reason I can't open the link, not sure why? I figured it was
something out of ASCE 7, just don't have a copy of it.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j
looked in the IBC Chapter 16, is it in
ASCE7? What do the Californians know about this?
Thanks in advance, and all have a great weekend.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j
Craig,
Without spending time to dig thru 13, I believe that is correct.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: craig.pr
How does an apartment become a 13D design? 13D is for single family and
duplexes. Am I missing something?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original
Off the top of my head I'm not sure about the spacing criteria but from what
I recall this exception allows for the use of pipe other than steel - namely
cpvc to be run in this room.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone
the FM Global
criteria since they (FM) aren't involved, any thoughts on this?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
provided that the AHJ buys off on it?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: craig.pr...@ch2m.com [mailto:craig.pr...@ch2m.com
was
involved in live fire comparison of wood bins versus plastic - very
impressive.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Dewayne Martinez
I wouldn't interpolate it, either jump up to the 6' span or you can calc it.
If you want I can fax you an example.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
). As far
as reference material goes if I remember correctly it had to be bound or
3-ring binder nothing loose, used a dolly to carry all the books as did lots
of other fellow engineers.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248
Got a stupid question: Have you compared values from an actual factory pump
curve to this software rendition? What variables do you provide the
software with? This sounds like a good tool for the pumps without factory
curves.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection
Sorry for the stupid question but is this for food or industrial process?
Without looking at the codes and shooting from the hip I would think it
would be required even if it's a food oven - again it's from the hip? I
have protected industrial ovens (driers) with closed head and deluge.
Jim
George,
I could be off-base on this but if my memory is correct ASME is the accepted
pressure vessel listing authority, much like USC is for double check
assemblies.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax
I have done a couple of these both were under 30 off the floor, both had
access panels, and both had lots of wiring under them. I didn't consider
using 8.15.6, due to the wiring and access panels.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima
provided
that the AHJ accepts it. I have utilized this numerous times in Eastern
Washington and Oregon, you still need to provide enough hydrants though but
you don't have to provide the IFC required fire flow for the particular
building.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire
Ron,
Gut reaction would say the 90,000 gallon would take care of your needs, I
don't believe the intent is to provide fire flow in addition to sprinkler
demand w/ hoses. I think if it were the intent it would be stated in IFC
508 or Appendix B?
Jim Johnston, P.E.
Fire Protection Engineer
Inland
Foam is what the insurance guy would like, I realize that it is not needed.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: craig.pr
can help me out it would be much appreciated, please contact me
off forum.
Thanks,
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471 or 800-742-6156
Fax 509-248-1180
j...@inlandfireprotection.com
is 1%
soluble in water according to the MSDS sheets. This totally blows the
original system out of wack, the building was originally designed to protect
this very commodity might have been in metal IBC's though?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum
This might be overkill but sounds to me like a pre-action release panel
being used for other purposes?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original
if bailed green.
Just thought I would share a little
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Joe Burtell [mailto:j
NFPA 72 5.11.2 says within 90 seconds.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Geoff Dyce [mailto:ghd...@delta-fire.com]
Sent
nursing
homes. For present and future projects since AHJ's are looking at this I
would think they would require the access panels when hard lid ceilings
exist throughout a facility? Any of the AHJ's on the forum have any ideas?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection
an
engineers standpoint I think it's great if you can calc the delivery time,
also from an engineers point I want to actually see the time it takes and
not trust a program. I don't know how any AHJ would accept the time from a
program and not actually see it for his or her sake.
Jim Johnston
Todd,
Can you use a Victaulic #51 6 x 2 1/2 groove eccentric and connect to
flanges using vic flanges?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original
% in wood barrels is a class
II.
Any input?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
___
Sprinklerforum mailing
my density more than doubles to a .32 in accordance with Table
16.2.1.3.2.
The more I look at this I think the best option would be to treat it as
racked storage, that way there shouldn't be any second guessing. Thanks for
your input.
Jim Johnston
-Original Message-
From: Arthur Tiroly
with
tji's) fire with no protection the 3000 sq. ft most likely won't touch the
fire. TJI's are great for an engineered joist - structurally, however they
fail under fire conditions very early in the event. Just my thoughts.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
books and look at Column
Analysis no problem, however what about Joe Contractor that has never been
exposed to this analysis? For those on this forum that are on 13's Hanging
Committee - is this really the intent of 9.2.6?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
for CPVC systems, I'm
not willing to make this same statement back to the AHJ without seeing the
code reference myself. I can't find any verbage in 2006 IFC or NFPA 25 that
excludes CPVC from this inspection - is it in here and I'm just not seeing
it?
Jim Johnston, P.E.
Fire Protection
, 2009, at 10:00 AM, Jim Johnston wrote:
Happy Friday All:
Got a question regarding 5-year internal inspection on 13R CPVC
systems. I
have a system we installed back in 2003 as an exposed retro fitted
system
using CPVC, the local AHJ wants a 5-year inspection on this.
Somewhere
I personally wouldn't touch it, if something bad happens in any area of the
system I'm sure the legal system would try to tie you to it since you were
aware of the problems even though you didn't originally cause it.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100
No, I don't believe this is a requirement per 2007 13 6.2.9.4. People have
asked in the past, but where would you put them?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j
I agree with you, AHJ's can fix this by rejecting plans that don't meet the
requirements of 13 or whatever guideline is being used. Till this happens
it will continue cause owners of sprinkler companies don't want the
designers to devote enough time to cpvc in comparison to steel.
Jim Johnston
thoughts.
Jim Johnston, P.E.
Fire Protection Engineer
-Original Message-
From: George Church [mailto:for...@ptd.net]
Sent: Wednesday, March 18, 2009 8:31 AM
To: sprinklerforum@firesprinkler.org
Subject: RE: 13R egress
Single exit path for 5 not 4 units will be addressed:
Hopefully
type, so
backflow shouldn't cause a problem as there isn't anything to damage. Are
you using a turbine type meter?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
ring, 3 days later a 6 Vic coupling blew apart on top of the riser
caused lots of water damage. We got blamed since we installed the system 10
years earlier. What a great legal system we have here, nobody seems to fess
up to their own actions or lack of.
Jim Johnston, P.E.
Fire Protection
to the
municipal supply, I am pretty certain plumbers can't touch our backflows?
Give me a call if you get a chance.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original
Scott,
My company has done a lot of high end homes, I asked our residential
superintendent to get me some pictures. I will gladly forward them to you.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j
I would say as long as it wasn't specified in bid documents for the higher
RA, I would tell him to pound sand.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
Jimmy,
Look at 2007 Section 8.1.1 (f).
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Jimmy Waite [mailto:jim...@burtellfire.com]
Sent
smelling pond water!
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Ron Greenman [mailto:rongreen...@gmail.com]
Sent: Monday, February
to
supply the truck.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Ryan Peterson [mailto:ry...@waynefire.com]
Sent: Friday, February 06
and sometimes successfully drives over 5 hose. With that said in my region
the AHJ typically goes back the the verbage of 903.3.7.
Jim Johnston
-Original Message-
From: Maag, Barry [mailto:bm...@siouxfalls.org]
Sent: Friday, February 06, 2009 2:10 PM
To: sprinklerforum
style
hangers with lags into the structure (fire treated 2x's) for the shielding,
ferrous ring hangers are not allowed as well as escutcheons - we use
stainless steel from Viking. If you have any questions feel free to call
me.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
diagrams for
you to use.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Todd Williams [mailto:t...@fpdc.com]
Sent: Friday, January 23, 2009 7
demanding?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Jimmy Waite [mailto:jim...@burtellfire.com]
Sent: Tuesday, January 20, 2009 3:33
Bobby,
I would start NFPA 495 (Explosive Materials Code) and go from there.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
-Original Message-
From: Bobby
George,
If you are operating out of the IFC, Section 903.3.7 tells you the location
shall be approved by the fire code official. In most jurisdictions that we
work in the fdc is to be within 75 feet of a hydrant.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100
the IBC IFC (or their state
adopted code) say's in order accomplish the originally intended scope of
work, being that these codes are law and NFPA is a guide on how to fulfill
the law.
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone
per its listing. Does anybody have any ideas?
Jim Johnston, P.E.
Fire Protection Engineer
Inland Fire Protection, Inc
1100 Ahtanum Road
Yakima, WA 98903
Phone 509-248-4471
Fax 509-248-1180
j...@inlandfireprotection.com
___
Sprinklerforum
We used cpvc strap hangers, no rod was used. We spoke to AFCON (hanger
manufacturer) their engineer say's strap hangers don't provide the exemption
- my guess would be the #18 screws are the primary problem, the punched
holes will not allow any attachment larger than 1/4.
Jim Johnston, P.E