Re: Structural Load

2020-06-03 Thread Parsley Consulting via Sprinklerforum
Jerry, Although I'm slightly unclear over what you're being told I would make sure that whoever is providing that information to you has read 9.2.1.3.1 of the '16 edition of -13: 9.2.1.3.1 Sprinkler piping shall be substantially supported from the building structure, *which must

Re: NFPA 13D

2020-03-30 Thread Parsley Consulting via Sprinklerforum
Gary, I have to disagree with your position.  Reading from the '16 edition of NFPA 13D, §7.4.1 states that, /"Listed pipe shall be supported in accordance with any listing limitations./" What I've read from most of the manufacturer's of CPVC is that the support criteria they've developed are

Re: NFPA 13D

2020-03-28 Thread Parsley Consulting via Sprinklerforum
Tom, I did not see this post until today, so I apologize for the delayed response.  I'll share my thoughts on what you've observed. No, there is nothing in NFPA 13D regarding hangers for sprinkler system piping not being allowed to be used for non-system components, as there is in -13.  As

Re: Minimum Lead-in Sizing

2020-03-18 Thread Parsley Consulting via Sprinklerforum
I've been away from the office all day for a medical issue and missed all the exchanges. The mistaken position taken by many - AHJ's and Contractors alike - is that the two most commonly used materials for UG service of a fire sprinkler system are C900 PVC and Ductile Iron pipe.  Those two

Re: Compartment

2020-02-26 Thread Parsley Consulting via Sprinklerforum
Bob, I'm not sure if 2 ft² can be overlooked by your AHJ, however when I read your text the provisions of 8.15.8.1.1 came to mind that any bathroom > 55 ft² require a sprinkler, except that smaller bathrooms require them if they are in a limited care facility or open directly on to a public

Re: Misc. Storage

2020-01-29 Thread Parsley Consulting via Sprinklerforum
nse.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_=DwMFAw=wn3mZQLIuInh2ClcJ0_DIA=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A=_i-3gtRgUe3C3_NF6JEVrRsp03qeNc1whW5ctjjD9go=Eehr8EULwOEFVj7mx_BUUA9FU4i6_xpQB4y6xdkenyc=> *From:* Sprinklerforum <mailto:sprinklerforum-boun...@lists.firesprinkler.org>

Re: Misc. Storage

2020-01-29 Thread Parsley Consulting via Sprinklerforum
Brian, I'll be happy to share my perspective for you. * Review the definition of miscellaneous storage in the paragraph you quoted.  It sounds to me as though you've described a building where the storage of 42,000 ft² _*is not*_ "incidental" to other use of the building, _*is not*_

Re: Fire Pump NFPA 20

2020-01-23 Thread Parsley Consulting via Sprinklerforum
Per the 2019 edition of NFPA 20: /4.7.1* Fire pumps shall be dedicated to and listed for fire protection service. / The identical language was contained in the 2013 and 2016 editions. It would be a good idea to be familiar with the term "listed" as defined in NFPA 20 [also 2019

Re: Fire Pump NFPA 20, part 2

2020-01-23 Thread Parsley Consulting via Sprinklerforum
Apparently I missed the designation "UL" in your question, and thanks to Matt and Craig for providing clarity. So, the answer is "listed", yes, "UL", not necessarily. sincerely, *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *Phone

private reply

2020-01-09 Thread Parsley Consulting via Sprinklerforum
Bob, My thought is that it's asking for a way to evaluate the one variable which can't be changed - elevation gain or loss. Just my opinion, *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *Phone 760-745-6181* Visit the website

Re: Detached Garage

2019-12-06 Thread Parsley Consulting via Sprinklerforum
Tagging on to the point Travis raised regarding the potential cost of a meter upsize. There is a water purveyor in San Diego County which has established a _*minimum*_ meter size of 2" for a sprinkler system designed to NFPA 13, with the potential for even larger devices should the demand

Re: [EXTERNAL] RE: Trouble getting Architects to give Revit files

2019-12-04 Thread Parsley Consulting via Sprinklerforum
Permit me to endorse and support Steve's comment I've highlighted below. In the course of doing 3rd party plan review for various AHJ's in San Diego county I've seen numerous sets of plans as prepared by the staff at Protection Design.  As a result I've become familiar with the style and

Re: [EXTERNAL] Not required, requirement

2019-11-19 Thread Parsley Consulting via Sprinklerforum
Owen, Let me offer a couple of thoughts here. First, please be aware that that figure of 26 gpm for two sprinklers flowing makes a couple of dubious assumptions.  If the layout used horizontal sidewall sprinklers and covered an area 14' wide with a throw of 26', the required flow is 42 gpm

Re: 13D CAD and Calc Program

2019-11-08 Thread Parsley Consulting via Sprinklerforum
I have to agree with the others Owen.  Those programs which are integrated provide so much more flexibility and functionality than due two separate stand-alone programs. There are two caveats here however. The first is noting your criteria that the solution be "simple and inexpensive if

Re: Through Bolt in Timber

2019-11-05 Thread Parsley Consulting via Sprinklerforum
Bob, You're certainly welcome, and that is pretty much what most contractors do when they submit plans. Regarding concrete. In the cycle for the 2016 edition the application of the prying factor for anchors in concrete moved from annex material, and thus advisory, to the body of the

Re: Through Bolt in Timber

2019-11-04 Thread Parsley Consulting via Sprinklerforum
Bob, I can only give you my thoughts. From what I understood in some of the committee meetings the maximum load weights shown in table 9.3.5.12.2(h) were based on the diameter of the bolt, and the length of that bolt in the timber, which had been tested. Several times I've run across

Re: 13D GPM to use?

2019-11-01 Thread Parsley Consulting via Sprinklerforum
Ask the correct question, Owen. Is the "compartment" one with a beamed ceiling with sprinklers at the bottom of the beams, or beamed and sloped with sprinklers at the bottom of the beams, or in the pockets?  And, if any of the above are true is the compartment of greater than 600 ft²? It

Re: Fire Alarm plan checklist

2019-10-23 Thread Parsley Consulting via Sprinklerforum
The most I've seen is from A.3.3.251: /Shop Drawings. Shop drawings typically include the property location, scaled//floor plans, equipment wiring details, typical equipment installation details, riser details, conduit///conductor size, and routing information needed to install a

Re: Pump? Or Pump & Tank?

2019-09-12 Thread Parsley Consulting via Sprinklerforum
And to add on to what Steve noted - there are always four considerations - at least - when protecting storage.  The ones I use: 1. What is being stored? * If it's plastic, is it in cartons or exposed? 2. How is it being stored? Racks? (single, double, multiple?) Pallets?  Shelf? *

Private reply

2019-09-10 Thread Parsley Consulting via Sprinklerforum
Maybe we could hire a bunch of homeless people to run through a building and flush all the toilets at the same time.  Sort of a man made undertow? Just thinking... *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *Phone 760-745-6181*

Re: N 1.85 graph

2019-08-30 Thread Parsley Consulting via Sprinklerforum
David, I'm delighted I waited to answer him.  You're entirely correct, and that is exactly what I was going to say. Have a great weekend my friend, *Ken Wagoner, SET *Parsley Consulting*** *350 West 9th Avenue, Suite 206 *Escondido, California 92025 *Phone 760-745-6181* Visit the website

Re: Can a Branchline cross the main when Bracing

2019-08-08 Thread Parsley Consulting via Sprinklerforum
Jerry, I have to admit I'm a bit confused. Why are you longitudinally bracing branch lines?  That certainly isn't required by NFPA 13.  Per §9.3.5.6.1 of the '16 edition, longitudinal bracing is only required for feed and cross mains. As I am a member of the hanging and bracing committee,