RE: Do Hydrant Butts have a K Factor?

2017-02-24 Thread Travis Allen- Allen Engineering
22, 2017 5:45 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Do Hydrant Butts have a K Factor? Or just use the formula in NFPA 291- Standard for Hydrant Marking and flow tests or something like that... Q = 29.83*d^2*Cd*P^0.5 d = hydrant outlet diameter in inches C = the outlet

Do Hydrant Butts have a K Factor?

2017-02-24 Thread Roland Huggins
I think we’ve again hit the saturation point on a topic. I’m all for extensive discussions but when something is such an obscure nuance that I suspect holds little interest to the majority of the whole group, I’m include to limit the run (or as they say in Texas - shoot it in the head).

RE: Do Hydrant Butts have a K Factor?

2017-02-24 Thread Brad Casterline
nklerforum [mailto:sprinklerforum-bounces@lists.firesprinkler. > org] *On Behalf Of *Brad Casterline > *Sent:* Friday, February 24, 2017 4:19 AM > *To:* sprinklerforum@lists.firesprinkler.org > *Subject:* Re: Do Hydrant Butts have a K Factor? > > > > Just one more thing if the Forum wil

RE: Do Hydrant Butts have a K Factor?

2017-02-24 Thread Steve Leyton
Uhh … maybe it’s a 4” port? From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Friday, February 24, 2017 4:19 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Do Hydrant Butts have a K Factor? Just one more thing

Re: Do Hydrant Butts have a K Factor?

2017-02-24 Thread Brad Casterline
nts. Here are the values: >> 2 3/8" 134 >> 2 1/2" 149 >> 2 5/8" 164 >> >> On Wed, Feb 22, 2017 at 6:48 PM, John Denhardt < >> jdenha...@stricklandfire.com> wrote: >> >>> Travis - well said >>> >>>

Re: Do Hydrant Butts have a K Factor?

2017-02-23 Thread Brad Casterline
is info from this very forum but I have noted that FM > global used to have k-factors for hydrants. Here are the values: > 2 3/8" 134 > 2 1/2" 149 > 2 5/8" 164 > > On Wed, Feb 22, 2017 at 6:48 PM, John Denhardt < > jdenha...@stricklandfire.com> wrote: >

Re: Do Hydrant Butts have a K Factor?

2017-02-22 Thread IPA
well said > > Brad - who really cares if hydrants have a K factor? I know I don't. > > John August Denhardt, P.E. > Strickland Fire Protection > > On Feb 22, 2017, at 8:45 PM, Travis Mack, SET <tm...@mfpdesign.com> wrote: > > Or just use the formula in NFPA 291- Standa

Re: Do Hydrant Butts have a K Factor?

2017-02-22 Thread John Denhardt
Travis - well said Brad - who really cares if hydrants have a K factor? I know I don't. John August Denhardt, P.E. Strickland Fire Protection On Feb 22, 2017, at 8:45 PM, Travis Mack, SET <tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>> wrote: Or just use the formula in NFPA 2

Re: Do Hydrant Butts have a K Factor?

2017-02-22 Thread Travis Mack, SET
Or just use the formula in NFPA 291- Standard for Hydrant Marking and flow tests or something like that... Q = 29.83*d^2*Cd*P^0.5 d = hydrant outlet diameter in inches C = the outlet coefficient (0.7, 0.8 or 0.9) P = Pitot pressure that is measured Not everything has to be extremely

Do Hydrant Butts have a K Factor?

2017-02-22 Thread Brad Casterline
Say it's a 2.5" C=.9. I've tried to work this out a couple different ways: 1) a kind of long drawn out way, call it 'brad's way', and I get ~168. 2) a way i call the 'Bill Brooks back of napkin' way based on a few words he posted here a few years ago-- lightening fast, and i'll be damned if i

Re: Different K factor in each floor practical?

2013-08-24 Thread Reza Esmaeili
I was trying to use a smaller K factor for the sprinklers which are near to the pump in order to adjust the flow rate and to choose a smaller water tank! but now I understand that calculating the amount of required water is depended on fire-flow and the system model. I am not that much familiar

Re: Different K factor in each floor practical?

2013-08-23 Thread Dwight Havens
can't do it.. Dwight From: rfletc...@aerofire.com rfletc...@aerofire.com To: sprinklerforum@lists.firesprinkler.org Sent: Thursday, August 22, 2013 9:31 AM Subject: RE: Different K factor in each floor practical? Ron, Agreed that if you add the fire flow

Re: Different K factor in each floor practical?

2013-08-23 Thread Ron Greenman
: Thursday, August 22, 2013 9:31 AM Subject: RE: Different K factor in each floor practical? Ron, Agreed that if you add the fire flow to the sprinkler demand you will have plenty of water. Isn't the sprinkler demand separate and not additive? Similar to standpipe and sprinkler demands. I do a lot

RE: Different K factor in each floor practical?

2013-08-23 Thread RFletcher
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron Greenman Sent: Friday, August 23, 2013 10:32 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Different K factor in each floor practical? And the required fire flow is always the AHJs call. On Fri, Aug 23, 2013

Re: Different K factor in each floor practical?

2013-08-23 Thread Dwight Havens
: RE: Different K factor in each floor practical? Yeah we have one AHJ out here that says we have to add the sprinkler to the fire flow because that is the way it always was. He also allows only a 25% reduction for the same reason. Must be good to be king. Ron F -Original Message- From

Re: Different K factor in each floor practical?

2013-08-22 Thread John Drucker
2013 Subject: Re: Different K factor in each floor practical? Reza, first you have to provide for fire flow per IFC. That is a whole lot of water. Typically you can reduce basic fire flow by 75% if you have sprinklers. That gives you an idea of how much fire flow can be. The AHJ is who determines what

RE: Different K factor in each floor practical?

2013-08-22 Thread RFletcher
-Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron Greenman Sent: Wednesday, August 21, 2013 7:35 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: Different K factor in each floor practical

RE: Different K factor in each floor practical?

2013-08-22 Thread Craig.Prahl
@lists.firesprinkler.org Subject: RE: Different K factor in each floor practical? Ron, Agreed that if you add the fire flow to the sprinkler demand you will have plenty of water. Isn't the sprinkler demand separate and not additive? Similar to standpipe and sprinkler demands. I do a lot fire flow

Re: Different K factor in each floor practical?

2013-08-21 Thread Reza Esmaeili
...@gmail.com To: sprinklerforum@lists.firesprinkler.org Sent: Tuesday, August 20, 2013 5:51 PM Subject: Re: Different K factor in each floor practical? Reza, If you have a demand of 0.1 over 1500 sqft the least number of heads you could possibly have, if you are able to maximize the layout

Re: Different K factor in each floor practical?

2013-08-21 Thread Ron Greenman
@lists.firesprinkler.org Sent: Tuesday, August 20, 2013 5:51 PM Subject: Re: Different K factor in each floor practical? Reza, If you have a demand of 0.1 over 1500 sqft the least number of heads you could possibly have, if you are able to maximize the layout (we're talking standard spray

Re: Different K factor in each floor practical?

2013-08-20 Thread Reza Esmaeili
of water tank and pump. I was thinking about adjusting the flow rate of the sprinklers that are near to fire pump which have high flow rate around 40Gpm that I don't really need, I need only 20GPM. So I was thinking about below options: 1- Using smaller K factor sprinklers at 1st, 2nd and 3rd floors

RE: Different K factor in each floor practical?

2013-08-20 Thread Brad Casterline
Reza, if your minimum density/area is .1/1500 and you end up with a demand less than 150 GPM you have done something wrong, no matter what K-Factor you use! -Original Message- From: Reza Esmaeili [mailto:rezaesmaeili...@yahoo.com] Sent: Tuesday, August 20, 2013 7:39 AM To: sprinklerforum

Re: Different K factor in each floor practical?

2013-08-20 Thread Ron Greenman
Casterline bcasterl...@fsc-inc.comwrote: Reza, if your minimum density/area is .1/1500 and you end up with a demand less than 150 GPM you have done something wrong, no matter what K-Factor you use! -Original Message- From: Reza Esmaeili [mailto:rezaesmaeili...@yahoo.com] Sent: Tuesday

Re: Different K factor in each floor practical?

2013-08-19 Thread AKS-Gmail-IMAP
Sent: Tuesday, August 13, 2013 11:14 PM Subject: Re: Different K factor in each floor practical? remember that pressure is your friend. Not having enough pressure is usually the problem. On Tue, Aug 13, 2013 at 1:09 PM, Eric Tysinger er...@waynefire.com wrote: Also to add, given a 6

Re: Different K factor in each floor practical?

2013-08-14 Thread Reza Esmaeili
To: sprinklerforum@lists.firesprinkler.org Sent: Tuesday, August 13, 2013 11:14 PM Subject: Re: Different K factor in each floor practical? remember that pressure is your friend. Not having enough pressure is usually the problem. On Tue, Aug 13, 2013 at 1:09 PM, Eric Tysinger er...@waynefire.com wrote

Re: Different K factor in each floor practical?

2013-08-14 Thread Ron Greenman
From: Ron Greenman rongreen...@gmail.com To: sprinklerforum@lists.firesprinkler.org Sent: Tuesday, August 13, 2013 11:14 PM Subject: Re: Different K factor in each floor practical? remember that pressure is your friend. Not having enough pressure is usually the problem. On Tue, Aug 13, 2013

RE: Different K factor in each floor practical?

2013-08-14 Thread Brad Casterline
Ron, isn't the duration 30 minutes? -Original Message- From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Sent: Wednesday, August 14, 2013 10:05 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Different K factor in each floor practical? AND... I was thinking about

Re: Different K factor in each floor practical?

2013-08-14 Thread Ron Greenman
] Sent: Wednesday, August 14, 2013 10:05 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Different K factor in each floor practical? AND... I was thinking about this last night and was struck by something that felt like the late, great George Church was trying post-- think about

Different K factor in each floor practical?

2013-08-13 Thread Reza Esmaeili
considered? Is it common to use different K factor sprinklers in each floor? like the below: Lets say the pump is 30Gpm at 70Psi and consider the below: - Pressure at 1st floor= 60 psi I choose a sprinkler with K=2.8 to have Q=21.7Gpm - Pressure at 2nd floor= 50 psi I choose a sprinkler with K

RE: Different K factor in each floor practical?

2013-08-13 Thread Eric Tysinger
Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Reza Esmaeili Sent: Tuesday, August 13, 2013 3:34 PM To: sprinklerforum@lists.firesprinkler.org Subject: Different K factor in each floor practical? Hi! For a 6 floor

RE: Different K factor in each floor practical?

2013-08-13 Thread Eric Tysinger
...@lists.firesprinkler.org] On Behalf Of Eric Tysinger Sent: Tuesday, August 13, 2013 4:06 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Different K factor in each floor practical? Assuming that you do not exceed the psi rating of the components (typically 175psi) on any given floor, why worry

Re: Different K factor in each floor practical?

2013-08-13 Thread Ron Greenman
@lists.firesprinkler.org Subject: RE: Different K factor in each floor practical? Assuming that you do not exceed the psi rating of the components (typically 175psi) on any given floor, why worry about the pressure at each floor? If you do exceed 175psi, the use of a pressure reducing valve at the ground

Re: adjusting the K-Factor with our bare hands

2013-06-12 Thread Roland Huggins
To restate John's comment a little more bluntly, the requirement to adjust the K-factor for antifreeze solutions was deleted the following edition because it created an insignificant difference considering the approximate nature of our overall methodology and especially the assigned average

RE: adjusting the K-Factor with our bare hands

2013-06-12 Thread John Denhardt
@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands To restate John's comment a little more bluntly, the requirement to adjust the K-factor for antifreeze solutions was deleted the following edition because it created an insignificant difference considering the approximate nature of our

Re: adjusting the K-Factor with our bare hands

2013-06-12 Thread Ron Greenman
: sprinklerforum-boun...@lists.firesprinkler.org [mailto: sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Wednesday, June 12, 2013 11:03 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands To restate John's comment

RE: adjusting the K-Factor with our bare hands

2013-06-12 Thread Brad Casterline
Thanks Roland, John again, and Ron again. This post is for adjusting the K-Factor for fluid properties other than water at ~40F, 62.4 lb/ft3, not for 'pure' water flowing through an area that varies a couple hundredths of a square foot. See 13-2007, A.22.4.4.5.1, which, if deleted in later

Re: adjusting the K-Factor with our bare hands

2013-06-12 Thread IPA
Casterline bcasterl...@fsc-inc.comwrote: Thanks Roland, John again, and Ron again. This post is for adjusting the K-Factor for fluid properties other than water at ~40F, 62.4 lb/ft3, not for 'pure' water flowing through an area that varies a couple hundredths of a square foot. See 13-2007

RE: adjusting the K-Factor with our bare hands

2013-06-12 Thread Brad Casterline
a more direct link to it? -Original Message- From: IPA [mailto:nsfdc...@gmail.com] Sent: Wednesday, June 12, 2013 1:32 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands Aren't Darcy calcs a bit counterintuitive? We want to make sure

RE: adjusting the K-Factor with our bare hands

2013-06-12 Thread Brad Casterline
-Original Message- From: Brad Casterline [mailto:bcasterl...@fsc-inc.com] Never mind Roland, dumb question, of course you did. The main reason I wanted to check it out was to see how you adjusted the K-Factor. Then I saw in 13-2010 the formula for doing this. In my original post I got

adjusting the K-Factor with our bare hands

2013-06-11 Thread Brad Casterline
From NFPA 13-2007, 22.4.4.5.1, we are required to, among other things, adjust the K-Factor. Using the Hazen-Williams friction formula, 62.4 lb/ft3 / 144 in2 = .433 lb/in2/ft(h). If we have an AF solution at 65.5 lb/ft3, / 144 = .455 lb/in2/ft(h). If K=5.6, and we assume P=7 PSI.: 7/.433

Re: adjusting the K-Factor with our bare hands

2013-06-11 Thread George Church
bcasterl...@fsc-inc.com wrote: From NFPA 13-2007, 22.4.4.5.1, we are required to, among other things, adjust the K-Factor. Using the Hazen-Williams friction formula, 62.4 lb/ft3 / 144 in2 = .433 lb/in2/ft(h). If we have an AF solution at 65.5 lb/ft3, / 144 = .455 lb/in2/ft(h). If K=5.6

RE: adjusting the K-Factor with our bare hands

2013-06-11 Thread Brad Casterline
...@rowesprinkler.com] Sent: Tuesday, June 11, 2013 12:05 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands I'd be concerned that you have completely muddled up kfactors for someone who no longer looks at it as the standard and industry practices

RE: adjusting the K-Factor with our bare hands

2013-06-11 Thread Matt Grise
and the K-factor concept are two VERY specialized cases that are intended only to describe warm water in pipes coming out of a smooth hole. The k-factor only relates the ease with which water can escape a sprinkler. If you plug in a modified k-factor, you are still using H-W to describe how the fluid

Re: adjusting the K-Factor with our bare hands

2013-06-11 Thread Ron Greenman
using this method for estimate calculations. (Without doing extensive testing to verify that it is accurate) The D-W and H-W calculation methods are simply approximations of how fluids interact with themselves and the pipe they are in. The H-W equation and the K-factor concept are two VERY

RE: adjusting the K-Factor with our bare hands

2013-06-11 Thread Brad Casterline
[mailto:rongreen...@gmail.com] Sent: Tuesday, June 11, 2013 2:03 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands can I say strongly enough how much I agree with what Matt said? can I say it again? And third time being the charm, I agree with what Matt

RE: adjusting the K-Factor with our bare hands

2013-06-11 Thread John Denhardt
Keep in mind that you started with a nominal K factor of 5.6. Per Table 6.2.3.1 (NFPA 13 - 2007), the range for the K factor under laboratory testing conditions was 5.3 to 5.8. Just talking out loud, but I wonder if that correction is really that important when the reality is the base number

RE: adjusting the K-Factor with our bare hands

2013-06-11 Thread Brad Casterline
: Tuesday, June 11, 2013 4:42 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: adjusting the K-Factor with our bare hands Keep in mind that you started with a nominal K factor of 5.6. Per Table 6.2.3.1 (NFPA 13 - 2007), the range for the K factor under laboratory testing conditions was 5.3

Re: adjusting the K-Factor with our bare hands

2013-06-11 Thread George Church
, June 11, 2013 2:03 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands can I say strongly enough how much I agree with what Matt said? can I say it again? And third time being the charm, I agree with what Matt said--a lot--and with George's

Re: adjusting the K-Factor with our bare hands

2013-06-11 Thread Ron Greenman
- adjusting K-Factors I mean, from NFPA 13 referenced earlier? -Original Message- From: Ron Greenman [mailto:rongreen...@gmail.com] Sent: Tuesday, June 11, 2013 2:03 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands can I say

RE: adjusting the K-Factor with our bare hands

2013-06-11 Thread Steve Leyton
...@lists.firesprinkler.org on behalf of Ron Greenman Sent: Tue 6/11/2013 5:53 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands I love the 1. Typo. or 2. Auto Correct. or 3. Freudian ? or 4. Slotism. ...and I'm licking myself You just keep

Re: adjusting the K-Factor with our bare hands

2013-06-11 Thread George Church
@lists.firesprinkler.org Subject: Re: adjusting the K-Factor with our bare hands I love the 1. Typo. or 2. Auto Correct. or 3. Freudian ? or 4. Slotism. ...and I'm licking myself You just keep hanging out with the woman and licking yourself. It's not a pretty picture, but it will be now

Re: K-Factor

2013-05-11 Thread George Church
: In support of the teacher of the hole, even the listing labs assign the k-factor empirically verses calculating it. (and leave his balloon alone too…) Roland On May 6, 2013, at 1:07 PM, Sprinkler Academy - C Bilbo prodesigngr...@msn.com wrote: and none of the math can be applied because

Re: K-Factor

2013-05-07 Thread Roland Huggins
In support of the teacher of the hole, even the listing labs assign the k-factor empirically verses calculating it. (and leave his balloon alone too…) Roland On May 6, 2013, at 1:07 PM, Sprinkler Academy - C Bilbo prodesigngr...@msn.com wrote: and none of the math can be applied because

RE: K-Factor

2013-05-07 Thread Brad Casterline
% ideal. for example (actual measured / ideal) equals .98 and .8, respectively. -Original Message- From: Roland Huggins [mailto:rhugg...@firesprinkler.org] Sent: Tuesday, May 07, 2013 10:30 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: K-Factor In support of the teacher

Re: K-Factor

2013-05-07 Thread bverhei
. bv - Original Message - From: djj8...@aol.com To: sprinklerforum@lists.firesprinkler.org Sent: Sunday, May 5, 2013 5:19:28 PM Subject: Re: K-Factor Wow. You are a genius. In a message dated 5/5/2013 12:46:06 P.M. Eastern Daylight Time, bcasterl...@fsc-inc.com writes: cubic feet

RE: K-Factor

2013-05-07 Thread Brad Casterline
perhaps you are right Bruce, thanks. (i wouldn't want anybody having nightmares about feet and seconds) -Original Message- From: bver...@comcast.net [mailto:bver...@comcast.net] Sent: Tuesday, May 07, 2013 11:06 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: K-Factor I

RE: K-Factor

2013-05-06 Thread Brad Casterline
to be unique in that it is the only 'timeless' quantity of the bunch! -Original Message- From: djj8...@aol.com [mailto:djj8...@aol.com] Sent: Sunday, May 05, 2013 7:19 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: K-Factor Wow. You are a genius. In a message dated 5/5/2013

RE: K-Factor

2013-05-06 Thread Fairchild, Jack
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Monday, May 06, 2013 7:41 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: K-Factor Uhhh... thanks DJJ8389? Me? If someone whom has spent years trying to wring the magic out of NFPA 13 Hydraulic Calculations

RE: K-Factor

2013-05-06 Thread Sprinkler Academy - C Bilbo
K-factor I'll also refer you to section 3.6.1 where it states that a sprinkler is defined by many things including its K-factor. And it tells us to see chapter 6. Wherein, we are told that sprinkler identification shall include the K-factor (orifice size). We are also refered by other

RE: K-Factor

2013-05-06 Thread Fairchild, Jack
: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Sprinkler Academy - C Bilbo Sent: Monday, May 06, 2013 4:08 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: K-Factor Jack, As I said in my earlier post, Dude, I teach my

RE: K-Factor

2013-05-05 Thread Brad Casterline
before Bernoulli. Newton used the experimental results of this, later called 'The Law of Falling Bodies', as one of the verifications of his Gravitational Constant. So if someone asked me What is K-Factor?, I would say It is the constant area acted upon by constant gravity around which Flow

Re: K-Factor

2013-05-05 Thread DJJ8389
. So if someone asked me What is K-Factor?, I would say It is the constant area acted upon by constant gravity around which Flow and Pressure vary. -Original Message- From: Ron Greenman [mailto:rongreen...@gmail.com] Sent: Friday, May 03, 2013 6:13 PM To: sprinklerforum

Re: K-Factor

2013-05-04 Thread drbryan123
2007 NFPA 13 22.4.2.4.3 refers to use of k factor for balancing branch lines. Sent from my Verizon Wireless Phone - Reply message - From: Fairchild, Jack jfairch...@ballinger-ae.com To: sprinklerforum@lists.firesprinkler.org sprinklerforum@lists.firesprinkler.org Subject: K-Factor Date

K-Factor

2013-05-03 Thread Fairchild, Jack
Here's a Friday question that was asked of me: What's a K-Factor? The Brock Hydraulics book states it is the discharge coefficient, but I can't find it in NFPA 13. Am I missing it? Jack Fairchild ___ Sprinklerforum mailing list Sprinklerforum

Re: K-Factor

2013-05-03 Thread Vince Sabolik
Jack - A K factor (in sprinkler world) is an expression of the relationship between pressure and discharge, as K is equal to the DISCHARGE / SQUARE ROOT of PRESSURE Note that the formula is not based on actual square root, but on a log of 1.54 Square root is accepted in place of 1.54

RE: K-Factor

2013-05-03 Thread Sprinkler Academy - C Bilbo
Jack, A K-factor is a WAAYYY over simplified description of the relationship between waterflow and two different pressures. I am certain that Bernoulli would roll in his grave if he knew how we use his work in this regard. Or perhaps, he would think we were practical wonders

Re: K-Factor

2013-05-03 Thread Ron Greenman
, 2013 at 1:36 PM, Fairchild, Jack jfairch...@ballinger-ae.com wrote: Here's a Friday question that was asked of me: What's a K-Factor? The Brock Hydraulics book states it is the discharge coefficient, but I can't find it in NFPA 13. Am I missing it? Jack Fairchild

Seeking a K-factor estimate for an exposure sprinkler

2011-04-13 Thread å . . . . . . .
We are evaluating a sprinkler exposure protection system. If anyone cares to offer up an estimate for a K-factor on an exposure sprinkler, they are most welcome. I estimate the K-factor between 1.8 - 4 gpm/psig^0.5 (26 - 60 Lpm/bar^0.5). I realize these don't sound like much of a difference

RE: Seeking a K-factor estimate for an exposure sprinkler

2011-04-13 Thread Matt Grise
f 913.927.0222 cell www. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of å... Sent: Wednesday, April 13, 2011 2:56 AM To: SprinklerFORUM@firesprinkler.org Subject: Seeking a K-factor

Seeking a K-factor estimate for an exposure sprinkler

2011-04-13 Thread å . . . . . . .
correct. it is a spray nozzle after NFPA 15. No plug or cap. scot deal excelsior fire ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an

RE: Seeking a K-factor estimate for an exposure sprinkler

2011-04-13 Thread Brad Casterline
with relish- (it was usually lunch time). You can get the K-Factor by using the natural beauty at the very root of sprinkler calcs: Torricelli's Theorem-- v = sqrt (2gh) For example, if the id of the opening is 3/8, square feet= .000767. If the pressure was 7 psi, feet of head, h = 16.17 ft. 2 * 32.2

RE: Seeking a K-factor estimate for an exposure sprinkler

2011-04-13 Thread Matt Grise
. AFPsprink.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Brad Casterline Sent: Wednesday, April 13, 2011 8:08 AM To: sprinklerforum@firesprinkler.org Subject: RE: Seeking a K-factor estimate

Seeking a K-factor estimate for an exposure sprinkler

2011-04-13 Thread å . . . . . . .
Thanks for helping, it IS appreciated. The shape of the opening is a slit, as if someone took a hacksaw and cut perpendicular to the long axis of a tube -- taking away 30% of the tube circumference. The slit is roughly 2 mm tall and width is ... 30% of the approximately 13mm (1/2-inch diameter)

Re: 5.62 K Factor

2009-11-05 Thread George Medina
Subject: 5.62 K Factor Anybody know the make and model of a sprinkler head with a 5.62 k? of hand? Thanks Guys, George Medina ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo

Re: 5.62 K Factor

2009-11-05 Thread Ron Greenman
, November 04, 2009 10:17 PM Subject: 5.62 K Factor Anybody know the make and model of a sprinkler head with a 5.62 k? of hand? Thanks Guys, George Medina ___ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http

RE: 5.62 K Factor

2009-11-05 Thread Thom McMahon
-Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Thursday, November 05, 2009 12:49 PM To: sprinklerforum@firesprinkler.org Subject: Re: 5.62 K Factor If you're proving this pipe schedule system

Re: 5.62 K Factor

2009-11-05 Thread George Medina
? - Original Message - From: fireg...@aol.com To: sprinklerforum-requ...@firesprinkler.org Cc: SprinklerFORUM@firesprinkler.org Sent: Wednesday, November 04, 2009 10:17 PM Subject: 5.62 K Factor Anybody know the make and model of a sprinkler head with a 5.62 k? of hand? Thanks Guys

RE: 5.62 K Factor

2009-11-05 Thread Thom McMahon
...@firesprinkler.org] On Behalf Of Thom McMahon Sent: Thursday, November 05, 2009 3:22 PM To: sprinklerforum@firesprinkler.org Subject: RE: 5.62 K Factor The difference between a 5.6K orifice and a 5.62K is only .20 GPM @ 100 PSI, so unless your calculating discharge at very high pressures who

Re: 5.62 K Factor

2009-11-04 Thread Thomas Watt
All makes, many models. Are you trying to identify a sprinkler? - Original Message - From: fireg...@aol.com To: sprinklerforum-requ...@firesprinkler.org Cc: SprinklerFORUM@firesprinkler.org Sent: Wednesday, November 04, 2009 10:17 PM Subject: 5.62 K Factor Anybody know the make

RE: k-factor in DW calcs

2008-10-17 Thread Travis Mack, SET
To: sprinklerforum@firesprinkler.org Subject: RE: k-factor in DW calcs Travis, When you finish I would really like to see the results of your DW calc compared to a regular old HW calc just to see the order of magnitude. Since we deal in GPM have you found a way to account for the gradual dilution