RE: Fire Pump Test Header Valve Location

2017-05-09 Thread Hinson, Ryan
not be enforceable. Section 4.20.1.4 indicates that the test header is to be installed “…on an exterior wall or in another location outside the pump room…” Since this valve must be a listed indicating valve per Section 4.20.3.3.1, I believe the intent is similar to that of the pump controller

Fire Pump Test Header Valve Location

2017-05-09 Thread Reed A. Roisum, SET
I have a pump room where an esteemed colleague suggested I locate the fire pump test header control valve near the test header on the vertical pipe to limit the amount of “dry” pipe. Since the valve would be located near the top of vertical pipe the dry portion of the pipe would drain well

RE: Test header on riser

2016-07-14 Thread David Williams
“backwards” or a test header arrangement. David Toshio Williams, FPE, LEED-AP O+M (218) 279-2436 direct | (218) 310-2446 cell LHB, Inc. | PERFORMANCE DRIVEN DESIGN From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Forest Wilson Sent: Thursday, July 14, 2016

RE: Test header on riser

2016-07-14 Thread Forest Wilson
ust issued a design with such a test header (COE > project where they “suggested” we look at this provision in the design). My > view is that the FDC is fine for project with less than 500 gpm flow > requirements. If over that (and in my case the flow was 1100 gpm), then we > need a

Re: Test header on riser

2016-07-14 Thread rongreenman .
So define test header and for what test. We just went through a huge thread about BOR and testing this that and everything else with the original questioner never defining what the test was for (or at least not before I got bored). First picture in my head when someone says test header is one

RE: Test header on riser

2016-07-14 Thread Scott Futrell
) 759-5556 On Jul 14, 2016, at 7:41 AM, Todd Williams <fpdcdes...@gmail.com<mailto:fpdcdes...@gmail.com>> wrote: Is there any requirement to install a test header on a riser without a pump (In addition to arrangement for full flow FDC test)? I have an engineer insisting that it is.

Re: Test header on riser

2016-07-14 Thread Justin Stewart
Had a project at a military base and they insisted that we installed a test header for the forward flow test on the back-flow preventer. Sent from my iPhone > On Jul 14, 2016, at 7:41 AM, Todd Williams <fpdcdes...@gmail.com> wrote: > > Is there any requirement to instal

RE: Test header on riser

2016-07-14 Thread David Williams
As an engineer who just issued a design with such a test header (COE project where they "suggested" we look at this provision in the design). My view is that the FDC is fine for project with less than 500 gpm flow requirements. If over that (and in my case the flow was 1100 gpm), th

RE: Test header on riser

2016-07-14 Thread Todd Williams
We installed a by-pass on the FDC line for the forward flow test, but he wants a test header as well. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-608-4559 (cell) Sent using CloudMagic [https://cloudmagic.com/k/d/mailapp?ct=ti=6.0.64=8.2] On Thu

RE: Test header on riser

2016-07-14 Thread Ryan Labrie
I have installed a test header on a riser to do a flow test of a backflow, take a look at NFPA #13 2010 10.10.2.5 Ryan Labrie Fire Protection Designer Critical System Solutions, LLC 2830 Scherer Drive, Suite 300 St. Petersburg, FL 33716 Office: 727.209.5122 Fax: 727.209.5126 Cell

RE: Test header on riser

2016-07-14 Thread Michael Hill
Subject: Test header on riser Is there any requirement to install a test header on a riser without a pump (In addition to arrangement for full flow FDC test)? I have an engineer insisting that it is. When I asked for referenced, I get the "you look it up" response. Just want to be sur

Test header on riser

2016-07-14 Thread Todd Williams
Is there any requirement to install a test header on a riser without a pump (In addition to arrangement for full flow FDC test)? I have an engineer insisting that it is. When I asked for referenced, I get the "you look it up" response. Just want to be sure before I scream back Todd

Test Header Calc

2014-05-15 Thread Brian Harris
I'm running a theoretical calc on a pump test header to try and determine if the existing pump is running at or near its rating, there are (4) 2-1/2 hose valves flowing 375 gallons each. The question I have is what pressure would be plugged into the calc's for each valve? I have a test chart

RE: Test Header Calc

2014-05-15 Thread RFletcher
Why not just read the gauges on the pump? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Brian Harris Sent: Thursday, May 15, 2014 8:22 AM To: sprinklerforum@lists.firesprinkler.org Subject: Test Header Calc I'm running

RE: Test Header Calc

2014-05-15 Thread Tim Stone
Brian, I just performed this on a warehouse project with a diesel fire pump taking suction from a municipal water supply. The EOR wanted to know the pressures on the Suction Flange of the pump. I started off with 375 GPM on each test header valve and assigned a pressure of 47 PSI to one

RE: Test Header Calc

2014-05-15 Thread RFletcher
@lists.firesprinkler.org Subject: RE: Test Header Calc Brian, I just performed this on a warehouse project with a diesel fire pump taking suction from a municipal water supply. The EOR wanted to know the pressures on the Suction Flange of the pump. I started off with 375 GPM on each test header valve

RE: Test Header Calc

2014-05-15 Thread Tim Stone
Sent: Thursday, May 15, 2014 11:43 AM To: Sprinklerforum@lists.firesprinkler.org Subject: RE: Test Header Calc Okay, what am I missing? There are gauges on the suction and discharge sides of the pump, right? Ron F -Original Message- From: Sprinklerforum [mailto:sprinklerforum-boun

RE: Test Header Calc

2014-05-15 Thread Craig.Prahl
Are you trying to determine a pressure so you can assign a k-factor to the test header outlets? Why not just put a fixed flow from each test connection outlet and then see what the pressure is and how that compares to the pump rating? Do you have a flow test showing what's going into the pump

RE: Test Header Calc

2014-05-15 Thread RFletcher
...@comcast.net] Sent: Thursday, May 15, 2014 8:51 AM To: Ronl.Fletcher; Sprinklerforum@lists.firesprinkler.org Subject: RE: Test Header Calc Ron, In my case the EOR was worried about negative pressures on the suction flange before the sprinkler contractor ordered the pump. Regards, G. Tim Stone G

Re: Test Header Calc

2014-05-15 Thread Brad Casterline
...@comcast.net] Sent: Thursday, May 15, 2014 8:51 AM To: Ronl.Fletcher; Sprinklerforum@lists.firesprinkler.org Subject: RE: Test Header Calc Ron, In my case the EOR was worried about negative pressures on the suction flange before the sprinkler contractor ordered the pump. Regards, G

Re: Test Header Calc

2014-05-15 Thread Brad Casterline
glad tomorrow is Friday. Ron F -Original Message- From: Tim Stone [mailto:tston...@comcast.net] Sent: Thursday, May 15, 2014 8:51 AM To: Ronl.Fletcher; Sprinklerforum@lists.firesprinkler.org Subject: RE: Test Header Calc Ron, In my case the EOR was worried about negative

RE: pump test header valves

2014-04-10 Thread John Denhardt
. A.4.20.1.4 The hose valves of the fire pump test header should be located on the building exterior. This is because the test discharge needs to be directed to a safe outdoor location, and to protect the fire pumps, controllers, and so forth, from accidental water spray. In instances where damage from theft

pump test header valves

2014-04-09 Thread Ben Young
Last week I was at an ASCET meeting where a pump presentation was given. Someone asked the presenter if it was allowed to remove the test header valves and keep them in the pump room to stop them from being stolen. The presenter and few other attendees chimed in that this was ok, and nothing

RE: pump test header valves

2014-04-09 Thread Morey, Mike
They make test header outlets with male threaded outlets (basically the opposite of an FDC) with hose caps that you remove and then screw on hose valves that have a female swivel on the inlet side. Of course there's still the risk of someone stealing the hose caps and/or brass adapteer

RE: pump test header valves

2014-04-09 Thread Bobby McCullough
-boun...@lists.firesprinkler.org] On Behalf Of Morey, Mike Sent: Wednesday, April 09, 2014 8:49 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: pump test header valves They make test header outlets with male threaded outlets (basically the opposite of an FDC) with hose caps that you

Re: pump test header valves

2014-04-09 Thread rongreenman .
-Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Morey, Mike Sent: Wednesday, April 09, 2014 8:49 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: pump test header valves They make test

Re: pump test header valves

2014-04-09 Thread MPhelps
Subject: RE: pump test header valves They make test header outlets with male threaded outlets (basically the opposite of an FDC) with hose caps that you remove and then screw on hose valves that have a female swivel on the inlet side. Of course there's still the risk of someone stealing

RE: pump test header valves

2014-04-09 Thread Bobby McCullough
: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ben Young Sent: Wednesday, April 09, 2014 12:05 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: pump test header valves Bobby, Do you mean screw-on PVC caps, or the plastic

Re: pump test header valves

2014-04-09 Thread rongreenman .
Too bad, I was liking the 2 1/2 plastic pipe caps idea a lot. The removing the entire test header is Ok but that has to be at least two and probably three guys on anything bigger that a couple of three valves. On Wed, Apr 9, 2014 at 10:20 AM, Bobby McCullough bo...@atlantasprinkler.com wrote

RE: pump test header valves

2014-04-09 Thread Ed Kramer
09, 2014 11:54 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: pump test header valves We usually install the header exposed on the outside of the pump house/room with a grooved connection. When not in use, we remove the entire header with valves and store it inside for the next test

Re: pump test header valves

2014-04-09 Thread MPhelps
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of mphe...@aerofire.com Sent: Wednesday, April 09, 2014 11:54 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: pump test header valves We usually install the header exposed on the outside of the pump house/room

RE: pump test header valves

2014-04-09 Thread David Autry
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rongreenman . Sent: Wednesday, April 09, 2014 12:43 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: pump test header valves Too bad, I was liking the 2 1/2 plastic pipe caps idea a lot. The removing the entire test header

RE: pump test header valves

2014-04-09 Thread Ed Kramer
: pump test header valves Grooved cap! Sent from my iPhone On Apr 9, 2014, at 10:51 AM, Ed Kramer kd...@knology.net wrote: Mark, how does the owner typically 'plug' the hole in the side of the building? Ed Kramer Lawrence, KS -Original Message- From: sprinklerforum-boun

Re: pump test header valves

2014-04-09 Thread RFletcher
, John Denhardt jdenha...@stricklandfire.com wrote: Funny but true story: I had a client who was worried about security with the test header penetrating the exterior of the building. They had us remove the test header after each test and store in the fire pump/mechanical room. We were

RE: pump test header valves

2014-04-09 Thread John Denhardt
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of rfletc...@aerofire.com Sent: Wednesday, April 09, 2014 5:58 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: pump test header valves Or, if possible keep headed in the pump room without valves, run hoses out to a truck mounted test rack

RE: pump test header valves

2014-04-09 Thread Steve Leyton
We have jurisdictions out here with very specific requirements and one city mandates a proprietary test header design for high-rise buildings that is only to be located in the pump room. Because we typically cast high-rise tanks in place with concrete, it's a simple exercise to block out

Re: pump test header valves

2014-04-09 Thread rongreenman .
This strikes me as somewhat counter-productive. Even in this mild climate (PacNW coastal) we do experience freezing event os long enough duration to freeze things. Even a slight leak in the control valve to the test header can fill the header and valves sufficiently between tests that damage could

RE: Fire Pump Test Header Calculation

2013-09-19 Thread Brad Casterline
[mailto:jdwa...@flsamerica.com] Sent: Wednesday, September 18, 2013 6:10 PM To: sprinklerforum@lists.firesprinkler.org Subject: Fire Pump Test Header Calculation Can I get some assistance with a fire pump test header calculation? I got the calculation form from 20:4.20.3.4, and I have it filled

RE: Fire Pump Test Header Calculation

2013-09-19 Thread James D. Waite
-boun...@lists.firesprinkler.org] On Behalf Of Brad Casterline Sent: Thursday, September 19, 2013 6:17 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Fire Pump Test Header Calculation Jimmy, I would guess that if your pump discharge PSI at the 150% rated GPM test flow (from the pump

RE: Fire Pump Test Header Calculation

2013-09-19 Thread James D. Waite
I like the analogy. To make sure we're on the same page, if I require a pitot pressure of 10 psi at my hose monster, and I lose 60 psi back to the pump discharge. If the pump discharge gauge shows 100 psi, my test header line would be adequately sized (under the curve). Correct? Jimmy Waite

RE: Fire Pump Test Header Calculation

2013-09-19 Thread Brad Casterline
I would look at it like this: The discharge gage is like the flow test hydrant that you are calcing to. The test header is like the remote area with a PSI and GPM demand, and the test header pipe, fittings, and hose is between the two points. The pitot gage reading at the test header is measuring

RE: Fire Pump Test Header Calculation

2013-09-19 Thread Smith, David L.(FAC)
19, 2013 10:47 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: Fire Pump Test Header Calculation Right. So the worksheet from NFPA 20 basically calculates a total amount of friction loss from the pump to the pitot. So, my discharge gauge shows the total of the pump pressure

RE: Fire Pump Test Header Calculation

2013-09-19 Thread Jeff Mc Nall
Exactly - you are basically calculating a demand flow pressure back to the fire pump discharge. If for instance that demand is 50 PSI at 750 GPM, as long as that demand is under your combined city/fire pump curve then you can use the minimize test header pipe size as indicated in NFPA 20

Fire Pump Test Header Calculation

2013-09-18 Thread James D. Waite
Can I get some assistance with a fire pump test header calculation? I got the calculation form from 20:4.20.3.4, and I have it filled out. But what to I do next? How do I use it to confirm the pipe size? Jimmy Waite, CET – Design Manager Fire Life Safety America- Raleigh District 7711

RE: test header

2013-06-04 Thread Tom Duross
...@lists.firesprinkler.org] On Behalf Of Roland Huggins Sent: Monday, June 03, 2013 1:18 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: test header NFPA 13 has stated for a couple of cycles that a means shall be provided to forward flow test the BFP. Look at 8.17.4.6.1. Because Mr Greenman requested

Re: test header

2013-06-04 Thread Charles Thurston
and were unable to hook to the male valves on the FDC. I met with the Battalion Chief that sent the letter and pointed out they had climbed over a wall into a service area (access was from the other side around the building) to try to connect to the Backflow test header, Yes it had a red engraved sign

RE: test header

2013-06-03 Thread Mark A. Sornsin, P.E.
://www.kfiengineers.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Ron Greenman Sent: Friday, May 31, 2013 2:41 PM To: sprinklerforum@lists.firesprinkler.org Subject: Re: test header By the time toy've

RE: test header

2013-06-03 Thread John Denhardt
To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Moreover, the engineer could specify Ron's solution up front. Doesn't help the design-build jobs - but you as the contractor could offer it up front...in such a way that makes you look like you're helping the customer, not just

RE: test header

2013-06-03 Thread RFletcher
...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A. Sornsin, P.E. Sent: Monday, June 03, 2013 6:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Moreover, the engineer could specify Ron's solution up front. Doesn't help

Re: test header

2013-06-03 Thread Ron Greenman
: sprinklerforum-boun...@lists.firesprinkler.org [mailto: sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A. Sornsin, P.E. Sent: Monday, June 03, 2013 6:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Moreover, the engineer could specify Ron's solution up

Re: test header

2013-06-03 Thread Todd - Work
Subject: RE: test header Moreover, the engineer could specify Ron's solution up front. Doesn't help the design-build jobs - but you as the contractor could offer it up front...in such a way that makes you look like you're helping the customer, not just seeking a means to get more money out

Re: test header

2013-06-03 Thread Ron Greenman
A. Sornsin, P.E. Sent: Monday, June 03, 2013 6:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Moreover, the engineer could specify Ron's solution up front. Doesn't help the design-build jobs - but you as the contractor could offer it up front...in such a way

Re: test header

2013-06-03 Thread George Church
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A. Sornsin, P.E. Sent: Monday, June 03, 2013 6:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Moreover, the engineer could specify Ron's solution up front. Doesn't help the design-build jobs - but you

RE: test header

2013-06-03 Thread Cahill, Christopher
, June 03, 2013 9:23 AM To: sprinklerforum@lists.firesprinkler.org Subject: Re: test header I think we're talking about the 25 test here and this is an ongoing deal. When you find a system without means it is in the owner's interest to pay for installing a header, which can be as little as dropping

Re: test header

2013-06-03 Thread Roland Huggins
[mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mark A. Sornsin, P.E. Sent: Monday, June 03, 2013 6:13 AM To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Moreover, the engineer could specify Ron's solution up front. Doesn't help the design-build

RE: test header

2013-06-03 Thread Mark A. Sornsin, P.E.
: RE: test header This discussion is about the minority of systems right? Doesn't the 2 main drain take care of most LH and OH? Chris Cahill, PE* Senior Fire Protection Engineer, Aviation Facilities Group Burns McDonnell 8201 Norman Center Drive Bloomington, MN 55437 Phone: 952.656.3652 Fax

Re: test header

2013-06-03 Thread Roland Huggins
you calculate it just like flow from any other orifice open to the exterior. The judgement part comes in for assigning a discharge coefficient and the exact size for a threaded orifice. This issue was the exact topic of an article in the May issue of Sprinkler Age. It can be accessed from

test header

2013-05-31 Thread Easter, Timothy
Designer is required to do a forward flow test for BFP. However, the riser is existing to remain, and does not have a test header. How can a forward backflow test be done? Regards, Timothy Easter E.I.T. Graduate Fire Protection Engineer This e-mail and any attachments contain URS

RE: test header

2013-05-31 Thread G. Tim Stone
:39 PM To: sprinklerforum@lists.firesprinkler.org Subject: test header Designer is required to do a forward flow test for BFP. However, the riser is existing to remain, and does not have a test header. How can a forward backflow test be done? Regards, Timothy Easter E.I.T. Graduate

RE: test header

2013-05-31 Thread Brad Casterline
There is a good article in the latest Sprinkler Age (by Roland) that might give you some ideas. -Original Message- From: Easter, Timothy [mailto:timothy.eas...@urs.com] Sent: Friday, May 31, 2013 1:39 PM To: sprinklerforum@lists.firesprinkler.org Subject: test header Designer

RE: test header

2013-05-31 Thread Mark A. Sornsin, P.E.
://www.kfiengineers.com -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of G. Tim Stone Sent: Friday, May 31, 2013 1:52 PM To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Why is the designer

RE: test header

2013-05-31 Thread G. Tim Stone
To: sprinklerforum@lists.firesprinkler.org Subject: RE: test header Of course, if your design flow is high enough, you may not get enough flow out of the FDC inlet - especially one equipped with flappers. Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | Fargo, ND

determining number of outlets for test header

2013-03-29 Thread Easter, Timothy
I am use to providing one 2 ½ connection for every 250 gpm of system demand. I do not know where this requirement came from nor do I know of any requirement. Does anyone know of such a requirement? Regards, Timothy Easter E.I.T. Graduate Fire Protection Engineer URS Corporation 11832 Rock

RE: determining number of outlets for test header

2013-03-29 Thread Dale Wingard
-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Easter, Timothy Sent: Friday, March 29, 2013 10:58 AM To: sprinklerforum@firesprinkler.org Subject: determining number of outlets for test header I am use to providing one 2 ½ connection for every 250 gpm

Re: determining number of outlets for test header

2013-03-29 Thread Travis Mack
. -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Easter, Timothy Sent: Friday, March 29, 2013 10:58 AM To: sprinklerforum@firesprinkler.org Subject: determining number of outlets for test header I am

RE: determining number of outlets for test header

2013-03-29 Thread Hinson, Ryan
: determining number of outlets for test header My guess is that usage comes from standpipe calculations that require the 250gpm per valve up to the required flow. I do not recall a requirement on how may valves to provide for a specified system demand for testing the backflow preventer

RE: determining number of outlets for test header

2013-03-29 Thread Johnson, Duane (NIH/OD/ORS) [C]
See NFPA 20:Table 4.26 for test header requirements. Duane Johnson, PE Program Manager Division of the Fire Marshal (Contractor) Office of Research Services National Institutes of Health 301-496-0487 Protecting Science - One Sprinkler at a Time -Original Message- From: Easter

RE: determining number of outlets for test header

2013-03-29 Thread Bobby Gillett
That’s where I was going to send him - the question was for test header, I didn't see where the backflow testing came in... if its for number of hose valves on a test header, then what Duane said. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285

RE: determining number of outlets for test header

2013-03-29 Thread Tom Duross
him - the question was for test header, I didn't see where the backflow testing came in... if its for number of hose valves on a test header, then what Duane said. Bobby Gillett See NFPA 20:Table 4.26 for test header requirements. Duane Johnson, PE I am use to providing one 2 ½ connection

Test header at pump house

2009-11-02 Thread Splawn, Shannon
Is there any thing wrong with using 5 Storz-type connections for a fire pump test header in lieu of the standard 2-1/2 hose valves? Shannon Splawn, CFPS Jacobs Fire Protection | Mechanical Engineering Dept. 513.674.3822 shannon.spl...@jacobs.com NOTICE - This communication may contain

Re: Test header at pump house

2009-11-02 Thread rahe . loftin
Subject er.orgTest header at pump house 11/02/2009 11:32

RE: Test header at pump house

2009-11-02 Thread Chris Cahill
Of Splawn, Shannon Sent: Monday, November 02, 2009 11:33 AM To: sprinklerforum@firesprinkler.org Subject: Test header at pump house Is there any thing wrong with using 5 Storz-type connections for a fire pump test header in lieu of the standard 2-1/2 hose valves? Shannon Splawn, CFPS Jacobs Fire

RE: Test header at pump house

2009-11-02 Thread Splawn, Shannon
Cahill Sent: Monday, November 02, 2009 12:40 PM To: sprinklerforum@firesprinkler.org Subject: RE: Test header at pump house Just whoever does ITM (or for that matter the initial acceptance) do they have 5 storz hose adapters and way to split the flow to hose monsters or playpipes or I guess do

RE: Test header at pump house

2009-11-02 Thread Fletcher, Ron
To: sprinklerforum@firesprinkler.org Subject: RE: Test header at pump house Not sure about it who will do the ITM. It's a case where I am duplicating an existing fire pump house to a brand new site in another state and the existing one is set-up like I described. I just am not 100% comfortable

RE: Test header at pump house

2009-11-02 Thread Splawn, Shannon
Yep. I had to add the FDC to my plans because it did have one on the original The test header has (3) 5 storz connections on a 12 manifold and 12 pipe from two fire pumps. Shannon Splawn, CFPS Jacobs Fire Protection | Mechanical Engineering Dept. 513.674.3822 shannon.spl...@jacobs.com

RE: Test header at pump house

2009-11-02 Thread Thom McMahon
Sent: Monday, November 02, 2009 10:59 AM To: sprinklerforum@firesprinkler.org Subject: RE: Test header at pump house Yep. I had to add the FDC to my plans because it did have one on the original The test header has (3) 5 storz connections on a 12 manifold and 12 pipe from two fire pumps. Shannon

RE: Test header at pump house

2009-11-02 Thread Splawn, Shannon
@firesprinkler.org Subject: RE: Test header at pump house I'd say that this is ok if you supply the owner with 3 - 5 storz hose monsters, to be kept on site in the pump house for ITM use . Is there a valve you could use to control the flow from each connection? (How to balance the flows

RE: Test header at pump house

2009-11-02 Thread George Church
Sent: Monday, November 02, 2009 1:20 PM To: sprinklerforum@firesprinkler.org Subject: RE: Test header at pump house Each storz has a 6 butterfly control valve. The plan also includes a flow meter that is returned to the storage tank. As I said, this is just me copying the design done by another

RE: Test header at pump house

2009-11-02 Thread Mark Sornsin
It sounds to me that you need to confirm with the owners that that is in fact what they really want for the pump test header. It's a unique enough configuration that one would think the owner has a plan for the use of these connections as test outlets. Then again, the original design may have

RE: Test header at pump house

2009-11-02 Thread George Church
Actually, there is no need for the test header on a fire pump- IF you have standpipe FHVs, hydrants or other means for testing the flow. And with a flow meter installed, you only have to flow water and measure it every -3 yrs? Sorry, I didn't commit #25 to memory, but its less than annually

RE: Test header at pump house

2009-11-02 Thread Splawn, Shannon
...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of George Church Sent: Monday, November 02, 2009 3:53 PM To: sprinklerforum@firesprinkler.org Subject: RE: Test header at pump house Actually, there is no need for the test header on a fire pump- IF you have standpipe FHVs

RE: Test header at pump house

2009-11-02 Thread George Church
-boun...@firesprinkler.org] On Behalf Of Splawn, Shannon Sent: Monday, November 02, 2009 3:54 PM To: sprinklerforum@firesprinkler.org Subject: RE: Test header at pump house They will have private yard hydrants; in fact, lots and lots of them. ... Especially if, in the background, something

RE: Test Header

2009-08-09 Thread Tom Duross
Not exactly, you modulate your flow with the test header valve. Those individual valves in the header should be just to open another stream, full open or full closed. You never want to expose the downstream side of the test header valve to full system pressure when it's normally empty

Test Header

2009-08-08 Thread Jay Jay Blocker
I have a two thousand GPM diesel riven pump that supplies 3 large warehouses.  The test header has 4 hose connections.  Inspection team tells customer that the test header needed 4 more valves in order to do the test.  Customer calls and ask where thats written that each connection is rated

RE: Test Header

2009-08-08 Thread Michael Fitz
What about putting a large connection (4 stortz) on the end of the header so that the testing company can use a large hose monster? That's what I did on the test header at our office.. Works GREAT. One 4 X 10' hose, one big hose monster, throttle the valve and get a great test curve

Re: Test Header

2009-08-08 Thread Jay Jay Blocker
.  Or does it? J From: Michael Fitz mf...@mde.com To: sprinklerforum@firesprinkler.org Sent: Saturday, August 8, 2009 3:51:51 PM Subject: RE: Test Header What about putting a large connection (4 stortz) on the end of the header so that the testing company can use

Re: Test Header

2009-08-08 Thread cherokeefirepro
No it does not change it. Your concern is with testing the pump at churn, 50, 100, and 150 rated. You use the test header control valve to control the flow, the control valve serves the same purpose as the individual hose valves. -Original Message- From: Jay Jay Blocker

RE: Fire Pump Test Header Sign

2008-02-05 Thread John Drucker
05, 2008 3:41 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Pump Test Header Sign We might have some left over from when Phoenix required a sign labeled TEST HEADER - DO NOT PUMP. I guess they were getting requests for F X F swivel adapters because some FDC's had the wrong type inlet

RE: Fire Pump Test Header Valve Supervision

2007-10-24 Thread David de Vries
(763) 425-1001 Office (612) 759-5556 Cell -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Monday, October 22, 2007 9:16 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Pump Test Header Valve Supervision Gregg, Aside from

RE: Fire Pump Test Header Valve Supervision

2007-10-22 Thread Gregg
If I may ask the obvious, where does the code state that the test header valve requires supervision? Operation of it would not impede the fire protection system. While I'm sticking my neck out, is the jockey pump control valve supposed to be supervised? Gregg -Original Message- From

RE: Fire Pump Test Header Valve Supervision

2007-10-22 Thread John Drucker
Gregg, Aside from from preventing the test header line and outlets from freezing (that's the obvious part up north) there is a code reference; 1999 NFPA-20 2-11 Exception: The test outlet control valves shall be supervised closed. One could always cite 2002 NFPA-13 8.15.3.1.1 in colder climates

RE: Fire Pump Test Header Valve Supervision

2007-10-22 Thread Scott A. Futrell
To: sprinklerforum@firesprinkler.org Subject: RE: Fire Pump Test Header Valve Supervision Gregg, Aside from from preventing the test header line and outlets from freezing (that's the obvious part up north) there is a code reference; 1999 NFPA-20 2-11 Exception: The test outlet control valves shall

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread MIKE HENKE
, October 19, 2007 11:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Pump Test Header Valve Supervision John, I went through the same exercise last month. The only luck I had was with Ferguson Fire Fab out of Tucker, GA. They have a company that will alter a butterfly tamper to work

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread John Drucker
Mike, Please; [EMAIL PROTECTED] John -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of MIKE HENKE Sent: Friday, October 19, 2007 5:10 PM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Pump Test Header Valve Supervision Make sure about

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread John Drucker
Hi Ron, Yikes, not the hose valves just the valve in the test header LINE. Opps left that key word out. John -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Fletcher, Ron Sent: Friday, October 19, 2007 12:43 PM To: sprinklerforum@firesprinkler.org

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread Joe Burtell
] On Behalf Of Mike Wisneski Sent: Friday, October 19, 2007 11:01 AM To: sprinklerforum@firesprinkler.org Subject: RE: Fire Pump Test Header Valve Supervision John, I went through the same exercise last month. The only luck I had was with Ferguson Fire Fab out of Tucker, GA. They have a company

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread Mike Wisneski
John, I went through the same exercise last month. The only luck I had was with Ferguson Fire Fab out of Tucker, GA. They have a company that will alter a butterfly tamper to work correctly with a fire pump test header. Contact Jim Sutton. Mike Wisneski -Original Message- From: [EMAIL

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread Fletcher, Ron
Why monitor the hose gates? Monitor the big valve inside unless it is a wet test header without a main control valve. Ron Fletcher Aero Automatic Phoenix, AZ -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of John Drucker Sent: Friday, October 19, 2007 8:13

Fire Pump Test Header Valve Supervision

2007-10-19 Thread John Drucker
Does anyone have product reference for a tamper switch and or tamper switch/valve assembly configured for use on a fire pump test header aside from pull type (PTS) cable devices ?. Thanks John Drucker ___ Sprinklerforum mailing list Sprinklerforum

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread Joe Burtell
, 2007 9:13 AM To: sprinklerforum@firesprinkler.org Subject: Fire Pump Test Header Valve Supervision Does anyone have product reference for a tamper switch and or tamper switch/valve assembly configured for use on a fire pump test header aside from pull type (PTS) cable devices ?. Thanks John

  1   2   >