. Flowswitches do not activate until over 6gpm.
The sprinkler installer does not have to install the toilet. They can
leave a connection for the plumber to connect the toilet to.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
www.pottersignal.com
1-800-325-3936
-Original Message-
From
It is prohibited by UL.
UL 864 states: Abort switches shall not be used on systems intended to
perform pre-action or deluge functions.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005
-Original Message-
From
something that cannot be accomplished, an abort switch on a listed
pre-action panel.
Regards
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co. LLC
WWW.POTTERSIGNAL.COM
866-572-3005
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
cornered.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
314-595-6740 direct
mi...@pottersignal.com
www.pottersignal.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bruce Verhei
Sent: Wednesday
.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
314-595-6740 direct
mi...@pottersignal.com
www.pottersignal.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman
Sent: Friday, October
was reduced
to less than 60 seconds. It is the same problem.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun
moving the
inspector's test. Thank you all for the education. Amazing what a few air
bubbles can do.
Best Regards,
Ken Holsopple
Design Manager
Rowe Sprinkler Systems, Inc.
570-837-7647
fax 570-837-6335
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co
, WFTR, this one had a retard.
https://www.dropbox.com/s/z99l4lprqsc6wfe/WFTA.pdf?m
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
or red dot on the gear to provide a visual indication
of the status of the pressure switch.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Committees. In addition, responses
provided are not intended, nor should they be relied upon, to provide
professional consultation or services.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
-Original Message
Todd,
Potter makes a small 120 VAC mini horn in white or red, model MH 120. It's the
size of a single gang plate.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
-Original Message-
From: sprinklerforum-boun
but I don't know
if they universally work with all makes and models of smoke alarms.
There was also a carrier frequency device made by Cepco products for this.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
Make sure about it monitoring the valve in the closed position. Chances are you
will have to almost completely open the valve before the switches will activate.
Typically the switches are set to activate within the first 2 revolutions of
the handwheel or 1/5 of the valve travel from the fully
on the
continuously energized systems compared to the number of normal systems
that didn't operate when required due to a total loss of power and if
these normal systems were properly maintained.
Regards,
Mike Henke
Potter Electric
-Original Message-
From: [EMAIL PROTECTED]
[mailto:[EMAIL
If you are just ringing a bell for compliance with 13 it is 5 minutes
If you are activating alarms in accordance with 72 it is 90 seconds
local alarm = 5 minutes
Fire alarm system = 90 seconds
Retards on flowswitches are limited to 90 seconds by UL
Regards,
mike
-Original Message-
?
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal
WWW.Pottersignal.com
1-800-325-3936
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd
Williams
Sent: Monday, November 02, 2009 10
problems when they used an air compressor. They couldn't
comprehend the limited supply in a bottle vs the ability to generate
more with a compressor.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
1-800-325-3936
-Original Message
How is he keeping the preaction valve tripped?
Is the panel in alarm with the solenoid energized?
The solenoid and/or panel may not be able to handle continuous
energization/alarm.
Also what if someone resets the panel?
Regards,
Mike Henke
Potter Electric
-Original Message-
From
Tom,
His name was Mark Phillips he was in AZ. Have not heard from him in
several years.
I have info on those tanks including the manufacturer that I will send
you off line.
Regards,
Mike
Ps; Why no beer served, what's baseball without beer, for that matter
what's life without beer.
Mike
especially since there are HBA members on all committees and
the County Council.
I'm going to try to write a reply to the paper before I leave on
vacation tomorrow morning. This is really bad timing for me.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740
going to take a long time and a lot of sales to recoup our expenses
on this and I am reminded of that frequently by the people above me.
This is not an advertisement; I'm just answering a question.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
Flowswitches will not operate if the water flows backward and they will
not be damaged either.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
www.pottersignal.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
,
Doug Chartier
Corrosion Solutions Product Manager
Potter Electric Signal Company
1609 Park 370 Place
Hazelwood, MO 63042
Direct: 314-595-6739
Cell: 314-853-6983
Toll Free: 1-800-325-3936
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
require the installation of the tamper
switch. The requirement for a tamper or flowswitch falls under a building code,
then 72 details the operation and connection of the previously required device.
72-2010 23.8.5.10.4 is for Releasing Systems.
Regards,
mike
Mike Henke CET
Sprinkler Product
that there
should also be a vent, either manual or automatic to vent off the air as the
system is being filled to aid in the reduction of oxygen corrosion and cycling
or delayed flowswitch operation.
Sorry to be so wordy but we receive calls about this on a regular basis.
Regards,
mike
Mike
they
would insure them.
We also need to keep pointing out the hypocrisy and greed of the HBA.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
www.pottersignal.com
-Original Message-
From: sprinklerforum-boun...@firesprinkler.org
Ron,
We used compressed gas cylinders such as a 2,000 psi cylinder from
Airgas.
It discharged through a regulator set for the pressure needed to deliver
the water to the calc'd sprinkler at the pressure required.
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740
Ron,
It was stored as a gas.
Airgas cylinder part # NI200, approximately 238 cubic ft of gas at 2,000
psi per cylinder.
mike
Mike Henke CET
Sprinkler Product Manager
1-800-325-3936
314-595-6740 Direct
www.pottersignal.com
-Original Message-
From: sprinklerforum-boun
is it that is using sched 80?
Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Potter Electric Signal Co.
www.pottersignal.com
314-595-6740 Direct
-Original Message-
From: sprinklerforum-boun...@lists.firesprinkler.org
[mailto:sprinklerforum-boun...@lists.firesprinkler.org
out Joe got hit by a bus...
Kind regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct: 314-595-6740
mi...@pottersignal.com
Manager Andy Kaempfer, both are copied on
this message
Kind regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct: 314-595-6740
mi
PAAR-B or PAV, that can be used to
automatically vent air from the system or remote valves can be installed for
venting
the system as it is being filled.
Regards,
Mike Henke CET
Sprinkler Product Manager
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
Tom,
The hole sizes are the same for all revisions of our flowswitches.
I’ll dig up an older VSR-D data sheet and send it to you off line.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
[http://www.pottersignal.com/signatures
s shut down. Furthermore, when the ventilating system is
operating, the detector(s) can be less responsive to a fire condition in the
room of fire origin due to dilution by clean air.
They both point out smoke dilution and delayed activation.
Kind Regards,
mike
Mike Henke
shing for the
VSR-ST, our part # 5180205. They should be willing to send it at no charge.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
[cid:image001.jpg@01D225FF.429C8D90]
Potter Electric Signal Company, LLC
1609 Park 370 Plac
to just get a VSR-S but was told I couldn't
take it apart to screw it on, and as you can see there is no room to rotate it
on the fitting without a union. Is the VSR-ST the most cost effective solution?
On 10/12/2016 6:59 AM, Mike Henke wrote:
> Barry,
>
> The unwanted waterflow alarms a
flow through the test valve will not
eliminate ALL the air pockets, even if the test valve is at the most remote
location.
Change the flowswitch to the correct one.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
Potter Elec
leak?
When someone complains about the compressor running all the time?
When the compressor burns out?
When/if you conduct a 3 year leak rate test?
When you go to investigate low air supervisory signals?
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
?
Feel free to email me off line.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
[http://www.pottersignal.com/signatures/graphics/logo.jpg]
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325
tanks.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
[http://www.pottersignal.com/signatures/graphics/logo.jpg]
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct: 314-595
can satisfy some of the
orders we have.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
[http://www.pottersignal.com/signatures/graphics/logo.jpg]
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone
With all due respect to your diligence in polishing the brand, I think you mean
to say that a WLS “or equivalent” is required?
SL
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On
Behalf Of Mike Henke
Sent: Thursday, June 15, 2017 8:37 AM
To: sprinklerforum
rater of 4-10 gpm.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
[http://www.pottersignal.com/signatures/graphics/logo.jpg]
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct
with products for this.
One solenoid manufacturer has a built in switch.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct
to those who helped.
Kind Regards,
mike
Mike Henke CET
Sprinkler Product Manager
___
Potter Electric Signal Company, LLC
1609 Park 370 Place, St. Louis, MO 63042
phone: 800-325-3936 | direct: 314-595-6740
mi...@pottersignal.com
to prevent people
from installing the flowswitch too close to a valve or change in direction that
could cause enough turbulence to prevent the flowswitch from operating when a
calibrated flow test is conducted. The installer would then have to relocate
the flowswitch.
Kind Regards,
mike
Mike Henke CET