RE: Residential systems in California

2009-02-19 Thread Mike Henke
. Flowswitches do not activate until over 6gpm. The sprinkler installer does not have to install the toilet. They can leave a connection for the plumber to connect the toilet to. Regards, mike Mike Henke CET Sprinkler Product Manager www.pottersignal.com 1-800-325-3936 -Original Message- From

RE: Pre-action abort

2009-04-06 Thread Mike Henke
It is prohibited by UL. UL 864 states: Abort switches shall not be used on systems intended to perform pre-action or deluge functions. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. LLC WWW.POTTERSIGNAL.COM 866-572-3005 -Original Message- From

RE: Pre-action abort

2009-04-07 Thread Mike Henke
something that cannot be accomplished, an abort switch on a listed pre-action panel. Regards mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. LLC WWW.POTTERSIGNAL.COM 866-572-3005 -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Normally closed butterfly valves

2012-05-30 Thread Mike Henke
cornered. Regards, mike Mike Henke CET Sprinkler Product Manager 314-595-6740 direct mi...@pottersignal.com www.pottersignal.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Bruce Verhei Sent: Wednesday

RE: Air Supply

2012-10-05 Thread Mike Henke
. Regards, mike Mike Henke CET Sprinkler Product Manager 314-595-6740 direct mi...@pottersignal.com www.pottersignal.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ron Greenman Sent: Friday, October

RE: Flow switch problem

2013-02-20 Thread Mike Henke
was reduced to less than 60 seconds. It is the same problem. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun

RE: Flow switch problem

2013-02-20 Thread Mike Henke
moving the inspector's test. Thank you all for the education. Amazing what a few air bubbles can do. Best Regards, Ken Holsopple Design Manager Rowe Sprinkler Systems, Inc. 570-837-7647 fax 570-837-6335 Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co

RE: Some Kind of Flow Switch

2013-04-05 Thread Mike Henke
, WFTR, this one had a retard. https://www.dropbox.com/s/z99l4lprqsc6wfe/WFTA.pdf?m Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Some Kind of Flow Switch

2013-04-05 Thread Mike Henke
or red dot on the gear to provide a visual indication of the status of the pressure switch. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Cleaning Sprinklers

2013-04-25 Thread Mike Henke
Committees. In addition, responses provided are not intended, nor should they be relied upon, to provide professional consultation or services. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message

RE: 13R local alarm

2013-05-29 Thread Mike Henke
Todd, Potter makes a small 120 VAC mini horn in white or red, model MH 120. It's the size of a single gang plate. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message- From: sprinklerforum-boun

RE: 13R local alarm

2013-05-29 Thread Mike Henke
but I don't know if they universally work with all makes and models of smoke alarms. There was also a carrier frequency device made by Cepco products for this. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct

RE: Fire Pump Test Header Valve Supervision

2007-10-19 Thread MIKE HENKE
Make sure about it monitoring the valve in the closed position. Chances are you will have to almost completely open the valve before the switches will activate. Typically the switches are set to activate within the first 2 revolutions of the handwheel or 1/5 of the valve travel from the fully

RE: Re[2]: Pre-action Solenoid valve

2008-06-26 Thread Mike Henke
on the continuously energized systems compared to the number of normal systems that didn't operate when required due to a total loss of power and if these normal systems were properly maintained. Regards, Mike Henke Potter Electric -Original Message- From: [EMAIL PROTECTED] [mailto:[EMAIL

RE: water flow timing

2009-07-15 Thread Mike Henke
If you are just ringing a bell for compliance with 13 it is 5 minutes If you are activating alarms in accordance with 72 it is 90 seconds local alarm = 5 minutes Fire alarm system = 90 seconds Retards on flowswitches are limited to 90 seconds by UL Regards, mike -Original Message-

RE: pump failure/flow alarm

2009-11-02 Thread Mike Henke
? Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal WWW.Pottersignal.com 1-800-325-3936 -Original Message- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Todd Williams Sent: Monday, November 02, 2009 10

RE: Nitrogen compressors

2009-11-23 Thread Mike Henke
problems when they used an air compressor. They couldn't comprehend the limited supply in a bottle vs the ability to generate more with a compressor. Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 1-800-325-3936 -Original Message

RE: Impaired preaction

2010-02-12 Thread Mike Henke
How is he keeping the preaction valve tripped? Is the panel in alarm with the solenoid energized? The solenoid and/or panel may not be able to handle continuous energization/alarm. Also what if someone resets the panel? Regards, Mike Henke Potter Electric -Original Message- From

RE: 13D Question

2010-03-29 Thread Mike Henke
Tom, His name was Mark Phillips he was in AZ. Have not heard from him in several years. I have info on those tanks including the manufacturer that I will send you off line. Regards, Mike Ps; Why no beer served, what's baseball without beer, for that matter what's life without beer. Mike

RE: St. Louis Sprinkler Article

2010-06-11 Thread Mike Henke
especially since there are HBA members on all committees and the County Council. I'm going to try to write a reply to the paper before I leave on vacation tomorrow morning. This is really bad timing for me. Regards, mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740

RE: Automatic air release

2010-06-24 Thread Mike Henke
going to take a long time and a lot of sales to recoup our expenses on this and I am reminded of that frequently by the people above me. This is not an advertisement; I'm just answering a question. Regards, mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740 Direct

RE: Check valves on floor control stations

2010-07-12 Thread Mike Henke
Flowswitches will not operate if the water flows backward and they will not be damaged either. Regards, mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740 Direct www.pottersignal.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Anti-Microbial System Poses Chemical Hazard

2010-07-20 Thread Mike Henke
,   Doug Chartier Corrosion Solutions Product Manager Potter Electric Signal Company 1609 Park 370 Place Hazelwood, MO 63042 Direct: 314-595-6739 Cell: 314-853-6983 Toll Free: 1-800-325-3936 Regards, mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740 Direct

RE: Tamper/Supervision of Alarm Line Valve

2010-12-06 Thread Mike Henke
require the installation of the tamper switch. The requirement for a tamper or flowswitch falls under a building code, then 72 details the operation and connection of the previously required device. 72-2010 23.8.5.10.4 is for Releasing Systems. Regards, mike Mike Henke CET Sprinkler Product

RE: Code reference for replacing remote end inspectors test withalisted Test N' Drain Valve....

2011-01-14 Thread Mike Henke
that there should also be a vent, either manual or automatic to vent off the air as the system is being filled to aid in the reduction of oxygen corrosion and cycling or delayed flowswitch operation. Sorry to be so wordy but we receive calls about this on a regular basis. Regards, mike Mike

RE: $7b/yr rebuild market

2011-03-11 Thread Mike Henke
they would insure them. We also need to keep pointing out the hypocrisy and greed of the HBA. Regards, mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740 Direct www.pottersignal.com -Original Message- From: sprinklerforum-boun...@firesprinkler.org

RE: Pressure Vessel Question

2011-10-20 Thread Mike Henke
Ron, We used compressed gas cylinders such as a 2,000 psi cylinder from Airgas. It discharged through a regulator set for the pressure needed to deliver the water to the calc'd sprinkler at the pressure required. Regards, mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740

RE: Pressure Vessel Question

2011-10-20 Thread Mike Henke
Ron, It was stored as a gas. Airgas cylinder part # NI200, approximately 238 cubic ft of gas at 2,000 psi per cylinder. mike Mike Henke CET Sprinkler Product Manager 1-800-325-3936 314-595-6740 Direct www.pottersignal.com -Original Message- From: sprinklerforum-boun

RE: Flow switch for 6 sch80

2013-09-19 Thread Mike Henke
is it that is using sched 80? Regards, mike Mike Henke CET Sprinkler Product Manager Potter Electric Signal Co. www.pottersignal.com 314-595-6740 Direct -Original Message- From: sprinklerforum-boun...@lists.firesprinkler.org [mailto:sprinklerforum-boun...@lists.firesprinkler.org

RE: single interlock pre-action less than 20 heads

2014-12-18 Thread Mike Henke
out Joe got hit by a bus... Kind regards, mike Mike Henke CET Sprinkler Product Manager ___ Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325-3936 | direct: 314-595-6740 mi...@pottersignal.com

RE: MIC and corrosion

2015-02-13 Thread Mike Henke
Manager Andy Kaempfer, both are copied on this message Kind regards, mike Mike Henke CET Sprinkler Product Manager ___ Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325-3936 | direct: 314-595-6740 mi

RE: Resi Riser - Character set not allowed

2016-07-21 Thread Mike Henke
PAAR-B or PAV, that can be used to automatically vent air from the system or remote valves can be installed for venting the system as it is being filled. Regards, Mike Henke CET Sprinkler Product Manager Kind Regards, mike Mike Henke CET Sprinkler Product Manager

RE: VSRD

2017-01-20 Thread Mike Henke
Tom, The hole sizes are the same for all revisions of our flowswitches. I’ll dig up an older VSR-D data sheet and send it to you off line. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___ [http://www.pottersignal.com/signatures

RE: Pre-action detection

2016-09-20 Thread Mike Henke
s shut down. Furthermore, when the ventilating system is operating, the detector(s) can be less responsive to a fire condition in the room of fire origin due to dilution by clean air. They both point out smoke dilution and delayed activation. Kind Regards, mike Mike Henke

RE: Seeking false water flow alarm suggestions

2016-10-14 Thread Mike Henke
shing for the VSR-ST, our part # 5180205. They should be willing to send it at no charge. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___ [cid:image001.jpg@01D225FF.429C8D90] Potter Electric Signal Company, LLC 1609 Park 370 Plac

RE: Seeking false water flow alarm suggestions

2016-10-12 Thread Mike Henke
to just get a VSR-S but was told I couldn't take it apart to screw it on, and as you can see there is no room to rotate it on the fitting without a union. Is the VSR-ST the most cost effective solution? On 10/12/2016 6:59 AM, Mike Henke wrote: > Barry, > > The unwanted waterflow alarms a

RE: Seeking false water flow alarm suggestions

2016-10-12 Thread Mike Henke
flow through the test valve will not eliminate ALL the air pockets, even if the test valve is at the most remote location. Change the flowswitch to the correct one. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___     Potter Elec

Excessive air leak rate

2016-12-01 Thread Mike Henke
leak? When someone complains about the compressor running all the time? When the compressor burns out? When/if you conduct a 3 year leak rate test? When you go to investigate low air supervisory signals? Kind Regards, mike Mike Henke CET Sprinkler Product Manager

RE: Excessive air leak rate

2016-12-02 Thread Mike Henke
? Feel free to email me off line. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___ [http://www.pottersignal.com/signatures/graphics/logo.jpg] Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325

RE: Tank Temperature Switch

2017-06-21 Thread Mike Henke
tanks. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___ [http://www.pottersignal.com/signatures/graphics/logo.jpg] Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325-3936 | direct: 314-595

RE: Potter WLS

2017-06-15 Thread Mike Henke
can satisfy some of the orders we have. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___ [http://www.pottersignal.com/signatures/graphics/logo.jpg] Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone

RE: Potter WLS

2017-06-15 Thread Mike Henke
With all due respect to your diligence in polishing the brand, I think you mean to say that a WLS “or equivalent” is required? SL From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of Mike Henke Sent: Thursday, June 15, 2017 8:37 AM To: sprinklerforum

RE: Flow Switch Maximum Surge

2018-07-31 Thread Mike Henke
rater of 4-10 gpm. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___ [http://www.pottersignal.com/signatures/graphics/logo.jpg] Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325-3936 | direct

RE: New coil actuators - New standard

2021-03-26 Thread Mike Henke via Sprinklerforum
with products for this. One solenoid manufacturer has a built in switch. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___     Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325-3936   |   direct

RE: New coil actuators - New standard

2021-03-26 Thread Mike Henke via Sprinklerforum
to those who helped. Kind Regards, mike Mike Henke CET Sprinkler Product Manager ___     Potter Electric Signal Company, LLC 1609 Park 370 Place, St. Louis, MO 63042 phone: 800-325-3936   |   direct: 314-595-6740   mi...@pottersignal.com

RE: Check Valve After Flow switch?

2021-03-15 Thread Mike Henke via Sprinklerforum
to prevent people from installing the flowswitch too close to a valve or change in direction that could cause enough turbulence to prevent the flowswitch from operating when a calibrated flow test is conducted. The installer would then have to relocate the flowswitch. Kind Regards, mike Mike Henke CET