Re: Water supply test data

2019-08-28 Thread Skyler Bilbo via Sprinklerforum
A fire pump flow test would typically have this information. You could just look at the inlet pressure and the flow. The backflow preventer might complicate things slightly. It would be helpful to know why you need this information. Thanks, Skyler Bilbo On Wed, Aug 28, 2019 at 8:52 AM

Re: Water supply test data

2019-08-28 Thread Skyler Bilbo via Sprinklerforum
Engineering* > > *CNS PTX / Y-12* | 865-576-5258 > > > > *From:* Sprinklerforum [mailto: > sprinklerforum-boun...@lists.firesprinkler.org] *On Behalf Of *Skyler > Bilbo via Sprinklerforum > *Sent:* Wednesday, August 28, 2019 10:03 AM > *To:* sprinklerforum@lists.firesp

Re: Private reply

2019-09-10 Thread Skyler Bilbo via Sprinklerforum
g.com/> * > On 09/10/2019 12:51 PM, Skyler Bilbo via Sprinklerforum wrote: > > I think it is worth pointing out that the way our table reads in 13R, and > the way that the plumbing code sizes piping, uses fixture units to convert > to flow, which do not convert linearly. For example,

Re: Auto Parts Storage

2019-12-11 Thread Skyler Bilbo via Sprinklerforum
I just ran into a somewhat similar situation last week. It seems like you are forgetting something major. It is very likely that you have to install sprinklers below the mezzanine floor. Unless I'm wrong, this counts as an obstruction over 4 ft in width for standard spray sprinklers, and I

Re: Combustible dust collector

2020-02-24 Thread Skyler Bilbo via Sprinklerforum
I have a little experience with this. I have seen a system brand called "Flamex" on the dust collection ducts. This system uses flame sensors and solenoids to extinguish a fire in the duct, which is a better system than just installing sprinklers in there. I can say that installing sprinklers

Re: Misc. Storage

2020-01-29 Thread Skyler Bilbo via Sprinklerforum
Take a look at section 16.2.1.2. I believe in your case, the Misc. Storage criteria does apply. However, for Class IV commodities on racks 10-12 ft tall, the criteria is EH1, per the Misc. Storage Table 13.2.1. I believe where the biggest confusion, and the importance of the definition comes

Re: Minimum Lead-in Sizing

2020-03-18 Thread Skyler Bilbo via Sprinklerforum
Could it be based on minimum supply for standpipe? I believe it is 4" minimum for combined standpipe/sprinkler system. Could be a case of the AHJ applying that requirement, incorrectly? -Skyler On Wed, Mar 18, 2020, 1:00 PM Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum wrote: >

Re: Help Finding Code Section

2020-05-20 Thread Skyler Bilbo via Sprinklerforum
Brian, I believe you are looking for section 8.15.23.3 (2013 edition). The handbook has a nice picture, and does a much better job of explaining this. Extend coverage into the space above the ceiling a distance of at least 0.6 times the square root of the remote area. Note that it also says:

Seed Hopper/Bulk Container

2020-09-22 Thread Skyler Bilbo via Sprinklerforum
All, I'm in need of some wisdom. I am seeing these polyethylene bulk containers for seed (corn/soy) more and more, and I'm wondering if anyone has done full scale testing with them to classify the commodity. The best information that I have been able to find is in FMDS 8-1,Table 1, which would

Re: ESFR spacing

2020-05-29 Thread Skyler Bilbo via Sprinklerforum
Matt, My main concern with your application would be that the section you are referring to doesn't apply to the situation you are describing. You can't apply a rule to spacing off a wall that is meant for offsetting a line due to an obstruction. Two different sections/situations. You say you

Re: ESFR spacing

2020-05-29 Thread Skyler Bilbo via Sprinklerforum
bstruction? > > > > Matt > > > > > > *From:* Sprinklerforum *On > Behalf Of *Skyler Bilbo via Sprinklerforum > *Sent:* Friday, May 29, 2020 4:58 PM > *To:* sprinklerforum@lists.firesprinkler.org > *Cc:* Skyler Bilbo > *Subject:* Re: ESFR spacing > > > &

Re: Covered Parking in 13R

2020-05-29 Thread Skyler Bilbo via Sprinklerforum
I don't think this has been said yet on this thread, but I think it is worth mentioning. It is not a fire sprinkler contractor's job to decide where sprinklers are required, and/or which standard is applicable (NFPA 13/13R). I know we all probably do this, but we really shouldn't. I would bet

Re: Schedule 10 vs. Schedule 40 pipe

2020-07-15 Thread Skyler Bilbo via Sprinklerforum
The following is a good read. Should be educational for you and the engineer. Google Corrosion Resistance Ratio for more information. The CRR for each size pipe should be listed on your submittal from the pipe manufacturer that you use.

Re: Antifreeze Rp issue

2020-07-21 Thread Skyler Bilbo via Sprinklerforum
I have not had this issue, but from what you have said, my best guess would be that the pressure is dropping on the city side, and causing the backflow to dump. I would ask if any big water users have been built nearby, and/or if someone has been flow testing/flushing hydrants nearby. You may

Re: stairways & elevators when only the basement is sprinklered

2020-06-10 Thread Skyler Bilbo via Sprinklerforum
I agree with John, but I will add some more information. I have seen this situation. In my case, it came from IBC 2015, section 903.2.11. "...the basement shall be equipped throughout with an approved automatic sprinkler system." I would still have the same question you asked originally about

Re: Structural Load

2020-06-03 Thread Skyler Bilbo via Sprinklerforum
The structure needs to support a larger point load (with a very complex explanation, it probably does). Otherwise, if a guy working on the roof were to stand on one foot, the structure could potentially collapse. Structural engineering calculations are extremely complex (I would say more so than

Re: Hersey BFP

2020-12-01 Thread Skyler Bilbo via Sprinklerforum
https://www.bavco.com/ref-manual/model/beeco-hersey/BEECO-HERSEY-HERSEY-2.pdf Skyler Bilbo 1700 S. Raney Street Effingham, IL 62401 217-819-6404 Direct 217-347-7315 Fax sbi...@wenteplumbing.com www.wenteplumbing.com On Tue, Dec 1, 2020 at 11:47 AM BILL MENSTER via Sprinklerforum <

Re: Domestic Demands 13R

2020-11-12 Thread Skyler Bilbo via Sprinklerforum
I don't think I disagree with anything here, but I might add to the conversation. It is amazing how us sprinkler guys always end up telling the engineers what size pipe they need. Background: Generally, the plumbing code calculations for domestic water usage looks like a curve. This means that

Re: Obstruction Clarification

2020-11-11 Thread Skyler Bilbo via Sprinklerforum
Yes, this has been true for a long time. It can be very important to mention that this is only for standard spray sprinklers that we are talking about. I have seen this misapplied to ESFR's often. - Skyler On Wed, Nov 11, 2020 at 7:00 PM Bob Knight via Sprinklerforum <

Re: Hollow Core Concrete Seismic Braces

2021-06-17 Thread Skyler Bilbo via Sprinklerforum
The details I have seen involve the regular long concrete wedge anchors installed between the hollow cores, in the solid part. I would start by asking the structural engineer and/or hollow core manufacturer how they recommend installing seismic bracing attachments for the sprinkler piping. Welding

Re: Dry head boot retrofit

2021-06-30 Thread Skyler Bilbo via Sprinklerforum
I believe the Viking boot matches your description. https://www.vikinggroupinc.com/dry-sprinkler-insulating-boot-assembly -Skyler On Wed, Jun 30, 2021, 6:47 PM Mark Phillips via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Hello everyone > Need some help identifying a

Re: Exposed unexpanded Group A plastic storage

2021-04-29 Thread Skyler Bilbo via Sprinklerforum
Micah, I agree with your conclusion. The only thing I would add, is that you may look at the definition of miscellaneous storage (3.9.1.18). If you can meet this, you could use the criteria from Chapter 13, which I think is essentially what you are trying to accomplish. Plastic storage is

Re: [EXTERNAL] Fire Pump Sprk & Fire Flow Demand

2021-04-23 Thread Skyler Bilbo via Sprinklerforum
Out of curiosity, what happens if a fire department pumps 2000 GPM through a small (say 750 GPM) fire pump with a city bypass? I want to say that one of the pump reps told me that fire pumps can pump well past 150% of their flow rating without any issue, but I'm curious if anyone can confirm this

Re: Existing Dry System

2021-02-04 Thread Skyler Bilbo via Sprinklerforum
I think horizontal separations are very often misunderstood. Many people think these are the same as firewalls. I may have missed it, but I don't think section 510 of the building code was mentioned. This is a great place to start, and if you haven't read it recently, it is worth a refresh.

Re: NFPA 13R & NFPA 14

2021-02-04 Thread Skyler Bilbo via Sprinklerforum
I could dream up a scenario where a 13R system had a higher pressure requirement (with a lower flow) than a standpipe calculation. Being limited to 4 stories definitely makes this a lot less likely to occur in the real world. It could happen, but I have never seen it here in the real world.

Re: [EXTERNAL] Re: Question regarding protection of sprinkler heads in Sugar Refinery

2021-03-30 Thread Skyler Bilbo via Sprinklerforum
It took me a while to find the right ones, but here is where I buy cellophane bags: https://www.clearcellobags.com/catalog/item/6438551/6271045.htm Thanks, Skyler Bilbo 1700 S. Raney Street Effingham, IL 62401 217-819-6404 Direct 217-347-7315 Fax sbi...@wenteplumbing.com www.wenteplumbing.com

Re: 4 1/2" FDC

2021-03-18 Thread Skyler Bilbo via Sprinklerforum
Same site offers a 4" NPT to 4-1/2" NST female-female adapter. Probably need to get AHJ approval, since it is not listed/approved. https://www.firehosedirect.com/aluminum-4-1-2-nh-to-4-nh-double-female https://www.firehosedirect.com/aluminum-4-1-2-nh-rocker-lug-plug - Skyler Bilbo On Thu,

Re: 4 1/2" FDC

2021-03-18 Thread Skyler Bilbo via Sprinklerforum
Sorry, the one I sent was NST on the 4" side. This should be the correct one. https://www.firehosedirect.com/aluminum-4-1-2-nh-to-4-npt-double-female - Skyler Bilbo On Thu, Mar 18, 2021 at 1:52 PM Skyler Bilbo wrote: > Same site offers a 4" NPT to 4-1/2" NST female-female adapter.

Re: Does a remote free standing FDC require a valve pit?

2021-03-10 Thread Skyler Bilbo via Sprinklerforum
Consider installing the check valve vertically. Should help with your concerns, since gravity would help keep the clapper shut. I would think the longer the vertical pipe drop is on top of the check, the more likely it is to hold, so you may consider that when laying out your riser room. To

Standard HSW at 12 to 18 inches down

2021-02-24 Thread Skyler Bilbo via Sprinklerforum
I see in NFPA 13 where standard coverage HSW sprinklers are allowed to be used 12 to 18 inches below the ceiling, where listed for such use. Does such a sprinkler exist? All of the Tyco, Reliable, and Viking sprinklers that I looked up say they are listed for 4 to 12 inches. Thanks, Skyler

Re: Metal Mesh Ceiling tile replacement

2021-03-04 Thread Skyler Bilbo via Sprinklerforum
Open-Grid Ceilings are addressed in NFPA 13, 2013 edition, section 8.15.14. Thanks, Skyler Bilbo 1700 S. Raney Street Effingham, IL 62401 217-819-6404 Direct 217-347-7315 Fax sbi...@wenteplumbing.com www.wenteplumbing.com On Thu, Mar 4, 2021 at 8:54 AM David Williams via Sprinklerforum <

Re: Standpipe Testing

2021-04-19 Thread Skyler Bilbo via Sprinklerforum
Hey Tom, Without explaining all of the math, if your system is 10,000 gallons and you already had it full of water (I think you said you could fill to 70 PSI from the city supply), with no air in the system, you would have it pumped up to 200 psi with your little 4 GPM pump in less than 12

Re: Standpipe Testing

2021-04-16 Thread Skyler Bilbo via Sprinklerforum
Scot - I don't think your base equation is quite right. You may be trying to use the ideal gas law here, on a liquid, which doesn't work. Also, I think technically you would be changing "n" in the equation, not V (the volume of the system is constant at P1 and P2), but I don't think this really

Re: FPC

2021-04-11 Thread Skyler Bilbo via Sprinklerforum
Tom, My company doesn't do alarms, but we always suggest pump run being a full alarm, regardless if it dials out or not. In theory, this is supposed to indicate a water flow condition, implying a sprinkler activation. Of course, more often than not it is a clogged jockey sensing line, or a

Re: Old sprinklers

2021-04-08 Thread Skyler Bilbo via Sprinklerforum
Tom, Seeing that you are in Illinois, it may be helpful to mention that the Illinois Plumbing Code allows up to 20 heads to be directly connected to the domestic water system. There are other requirements in the Plumbing Code, which can be found in Section 890.1130. Unfortunately, I don't know

Re: Bathroom Chase

2021-02-12 Thread Skyler Bilbo via Sprinklerforum
There is a section that talks about only going back 1.2 times the square root of the remote area beyond the ceiling. NFPA 13, 2013 edition, Section 8.15.23. Skyler Bilbo On Fri, Feb 12, 2021 at 7:25 AM Brian Harris via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > There's

Re: [EXTERNAL] Noncontinuous obstructions More than 18" down

2021-02-12 Thread Skyler Bilbo via Sprinklerforum
It sounds like the architect is working hard to inspire kids with his beautiful ceiling design... From the little information you gave, it may be more like a cloud ceiling than a traditional obstruction. See section 3.3.5.1 for the definition, and then 8.15.1.2.1.3 for criteria. You may also

Re: Fire Pump Backflow

2021-08-25 Thread Skyler Bilbo via Sprinklerforum
I never had this problem before, but it looks like a Deringer 20 backflow has lower opening pressures. You may also consider something like several smaller Watts 2000B-FP in parallel, depending on the flows you need. I don't think piping the jockey differently would help, but let me know if you

Re: Open Slat Ceilings

2021-09-01 Thread Skyler Bilbo via Sprinklerforum
IMHO, the 3x rule does not apply. Only because I can't say with certainty that you can meet this requirement from A.10.2.7.2.1.3: "This works for small noncontinuous obstructions and for continuous obstructions where the sprinkler can throw water over and under the obstruction." It seems to me

Re: Definitions

2021-09-09 Thread Skyler Bilbo via Sprinklerforum
You may also want to double check A.11.1.2, depending on the square footages of your areas. Thanks, Skyler Bilbo 217-819-6404 Cell On Thu, Sep 9, 2021 at 3:10 PM tstone52--- via Sprinklerforum < sprinklerforum@lists.firesprinkler.org> wrote: > Chapter 12 adjacent hazards or design methods,

Re: Flexible hose head connectors on a pipe schedule system

2021-08-02 Thread Skyler Bilbo via Sprinklerforum
I agree with JH's logic, but I am struggling with this pressure gain from a 20 ft drop idea. Isn't the net effect due to elevation 0 since the pressure gets changed by the same amount at the riser, or wherever it goes up in elevation, before it comes back down? All that matters is the source

Re: Material Prices !!

2021-08-05 Thread Skyler Bilbo via Sprinklerforum
Domestic steel prices are through the roof. Domestic HRB went from around $600 per ton around October 2020 to around $1,966 per ton recently, in pretty much a straight line up. Make sure you are communicating this to your customers. Wood has pretty much come back to earth from the recent high,

Foreign Piping

2021-07-29 Thread Skyler Bilbo via Sprinklerforum
Does anyone have a source for foreign pipe that you can send me off forum? I'm having difficulty finding a supplier that can quote it. Specifically schedule 10. Thanks, Skyler Bilbo Wente Plumbing and Fire Protection 1700 S. Raney Street Effingham, IL 62401 217-819-6404 Direct

Re: Tire Storage

2021-07-30 Thread Skyler Bilbo via Sprinklerforum
It says 0.6 over 5000 square feet or 0.90 over 3000 square feet. Either could be more demanding depending on pipe layout/size and maybe sprinkler k-factor. 0.6 over 5000 is actually 300 GPM more demanding than the other criteria, so in certain situations the .6 criteria could be controlling

Re: Concealed Space Between Floors

2021-10-15 Thread Skyler Bilbo via Sprinklerforum
>From the picture you sent, it looks like you have to install sprinklers. I think section 8.15.1 is what you are looking for (at least in the 2013 or 2016 editions). The most common way I have seen to avoid installing sprinklers in this area is to fill it with noncombustible insulation. If this

Re: Concealed Space Between Floors

2021-10-15 Thread Skyler Bilbo via Sprinklerforum
inal Message- > From: Sprinklerforum On > Behalf Of Skyler Bilbo via Sprinklerforum > Sent: Friday, October 15, 2021 8:37 AM > To: sprinklerforum@lists.firesprinkler.org > Cc: Skyler Bilbo ; Brian Harris < > bhar...@bvssystemsinc.com> > Subject: Re: Concealed Space B

Re: Foam Insulation Spraying

2021-10-12 Thread Skyler Bilbo via Sprinklerforum
See the video below. Fast forward to the spray foam test at about 3 minutes in. Spoiler: flashover takes 44 seconds. Since you are probably acting as the only fire professional on this project, I would suggest you share the video with your customer so they understand the gravity of the

Re: NFPA #13 (2013) Exterior Projections 8.15.7

2021-10-05 Thread Skyler Bilbo via Sprinklerforum
I think you are correct for your described situation: you have a noncombustible overhang, under 4 ft, with no storage underneath, then no sprinklers is OK. It sure seems to me like we don't have to install sprinklers under *combustible* overhangs 4 ft or less as long as there is no storage

Re: Gridded dry system

2021-10-27 Thread Skyler Bilbo via Sprinklerforum
IMHO, defining a grid as any system that can supply a sprinkler from more than one direction is a poor threshold. Just because you install sprinklers on a looped main or line, does not magically turn it into a gridded system. The location of the sprinklers should have nothing to do with it. May I

Re: Gridded dry system

2021-10-26 Thread Skyler Bilbo via Sprinklerforum
Consider the following picture (I'm an Engineer, not an artist). It shows the same connections as the one you presented, in 2D and exaggerated to emphasize that the main routing doesn't matter. I would argue this is a grid, whether it is laid out the way I show, or the way it is on your drawing.

Re: [EXTERNAL] Joining black carbon steel with stainless steel piping

2022-03-04 Thread Skyler Bilbo via Sprinklerforum
I'll bring it up, because I think it is pertinent. It is popular in my area to throw in chlorine tablets every so often when installing an underground water main into a building. Once the main is completely installed, they typically fill it, shut the control valve off and see if pressure drops

Re: 8 inch sprinkler pipe fall from factory ceiling

2022-02-24 Thread Skyler Bilbo via Sprinklerforum
What was the exact make/model of the grooved couplings? While flexible grooved couplings will definitely allow the pipe to move under a pressure surge, I have seen some rigid couplings "grow" as well. If they were replaced with quality rigid couplings, then tested with the pump, you probably

Re: infrared heaters

2022-02-14 Thread Skyler Bilbo via Sprinklerforum
Jamie, In my experience, they are extremely directional. Ask for the cut sheets, or get the model number and find the cut sheets. Many times there is a diagram showing the directional heat, since they usually want to make sure these are actually mounted high enough that they aren't