If it makes you feel any better, couple years ago I sat in on a "seminar
improvement review" of the AFSA section on Standpipes.

Since there was a bit of confusion amongst Roland, Bobby C, Scan and Russ L,
it was decided if we weren't clear, others probably weren't either and a
segment was added to run thru definitions and examples of each.

So you're in good company, don't feel bad.

glc

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ron Greenman
Sent: Saturday, March 01, 2008 2:38 PM
To: [email protected]
Subject: Re: Dumb Question maybe

Tom,

NFPA 14, 2007

5.2.5* Manual Wet. A manual wet standpipe system shall be a wet
standpipe system connected  to a small water supply for the purpose of
maintaining water within the system or sharing a water supply with an
automatic sprinkler system, but not having a water supply capable of
delivering the system demand attached to the system.