Tom,

NFPA 14, 2007

5.2.5* Manual Wet. A manual wet standpipe system shall be a wet
standpipe system connected  to a small water supply for the purpose of
maintaining water within the system or sharing a water supply with an
automatic sprinkler system, but not having a water supply capable of
delivering the system demand attached to the system.

On 3/1/08, Tom Duross <[EMAIL PROTECTED]> wrote:
>
>  Tom,
>
>  The Mass Code is confusing on this issue. Section 914.1 states that
>  when standpipes are required to be installed, they shall be automatic
>  wet type. This would mean that they would need to meet the flow and
>  pressure demands with the on site supply. However, section 914.3
>  Exception states that the residual pressures are not required to met
>  if the building is under 70 feet high, effectively making it a manual
>  wet standpipe. I think an interpretation may be in order.
>
>  Todd
>
>  Todd, I'm very familiar with that section BUT these are not manual
>  standpipes if they're connected to an automatic water supply.  If they were
>  separate, OK I can see the justification but they're not.  They're connected
>  to the same supply as the sprinklers and the fire (sprinkler) pump.  My
>  understanding of that section says if I have enough street pressure to
>  satisfy the sprinklers, I don't have to install a pump just for the hose
>  demand (only class 3 in MA).  But, these guys designed and installed a fire
>  pump connected to two combination class 3 standpipes and only sized it for
>  the sprinklers.  I don't think that's right.
>
>  Tom
>
>
>  _______________________________________________
>  Sprinklerforum mailing list
>  [email protected]
>  http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>  To Unsubscribe, send an email to:[EMAIL PROTECTED]
>  (Put the word unsubscribe in the subject field)
>


-- 
Ron Greenman
at home....
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to