-----Original Message-----
From: John Drucker 
Sent: Thursday, May 29, 2008 2:39 PM
To: '[email protected]'
Subject: RE: partial system

Is this a means of egress question ?

If so then take a look at the following 2006 IBC Chapter 10 provisions;

1) Exit Access 1014.3 - Exception 1 - "building is equipped THROUGHOUT
with an automatic sprinkler system installed in accordance with Section
903.3.1.1" (NFPA-13-2002)

2) Travel Distance Table 1016.1 Note c. -"buildings equipped THROUGHOUT
with an automatic sprinkler system installed in accordance with Section
903.3.1.1" (NFPA-13-2002)

3) Corridor Fire Resistance Rating Table 1017.1 Note c. -"buildings
equipped THROUGHOUT with an automatic sprinkler system installed in
accordance with Section 903.3.1.1(NFPA-13-2002) or 903.3.1.2
(NFPA-13R-2002) [13R provision not applicable in non residential
buildings]

Does that help ?

John Drucker
Fire Protection Subcode Official (AHJ)
New Jersey

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, May 29, 2008 12:25 PM
To: [email protected]
Subject: partial system

OK, got a architect and engineer that claim that they can protect the
corridors only on a mini-storage warehouse. 
:

The IBC states that if the building has sprinklers but does not say
sprinklered throughout - has anyone else seen/done this?




Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or entity to 
which it is addressed and may contain information that is privileged and 
confidential, nor is it, unless specifically stated, intended to be relied upon 
by any person or persons other than the individual or entity named above and no 
warranties or representations are made or intended to persons or entities not 
named above.  If the reader is not the intended recipient, you are hereby 
notified that any dissemination, distribution or copying of this communication 
is strictly prohibited.  If you have received this communication in error, 
please notify us immediately by telephone, return this message to the address 
above and delete all copies.  Thank you.


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to