Is this a means of egress question ? If so then take a look at the following 2006 IBC Chapter 10 provisions;
1) Exit Access 1014.3 - Exception 1 - "building is equipped THROUGHOUT with an automatic sprinkler system installed in accordance with Section 903.3.1.1" (NFPA-13-2002) 2) Travel Distance Table 1016.1 Note c. -"buildings equipped THROUGHOUT with an automatic sprinkler system installed in accordance with Section 903.3.1.1" (NFPA-13-2002) 3) Corridor Fire Resistance Rating Table 1017.1 Note c. -"buildings equipped THROUGHOUT with an automatic sprinkler system installed in accordance with Section 903.3.1.1(NFPA-13-2002) or 903.3.1.2 (NFPA-13R-2002) [13R provision not applicable in non residential buildings] Does that help ? John Drucker Fire Protection Subcode Official (AHJ) New Jersey -----Original Message----- From: [EMAIL PROTECTED] [mailto:[EMAIL PROTECTED] On Behalf Of Greg McGahan Sent: Thursday, May 29, 2008 12:25 PM To: [email protected] Subject: partial system OK, got a architect and engineer that claim that they can protect the corridors only on a mini-storage warehouse. : The IBC states that if the building has sprinklers but does not say sprinklered throughout - has anyone else seen/done this? Thank you, Greg McGahan Living Water Fire Protection, LLC 1160 McKenzie Road Cantonment, FL 32533 850-937-1850 Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field) CONFIDENTIAL AND PROPRIETARY: This email message is intended only for the use of the individual or entity to which it is addressed and may contain information that is privileged and confidential, nor is it, unless specifically stated, intended to be relied upon by any person or persons other than the individual or entity named above and no warranties or representations are made or intended to persons or entities not named above. If the reader is not the intended recipient, you are hereby notified that any dissemination, distribution or copying of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately by telephone, return this message to the address above and delete all copies. Thank you. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)