Greg, NFPA 13 recognizes that under certain conditions, partial sprinkler systems may be installed as allowed or required by other standards or codes. Section 8.1 and 8.1.1 (07) along with A.8.1 and A.8.1.1 and the commentary in the handbook will give you the details.
Ed Kramer Littleton, CO > -----Original Message----- > From: [EMAIL PROTECTED] [mailto:sprinklerforum- > [EMAIL PROTECTED] On Behalf Of Greg McGahan > Sent: Thursday, May 29, 2008 1:52 PM > To: [email protected] > Subject: RE: partial system > > I am not sure exactly what their purpose is. > > The chief building inspector says that they do not have to protect the > building at all because the arch. Has compartmentalized the building > into 4 > - 3,000 sq ft compartments which kicks them out of the greater than 30 > people chart. > > The building is classified as "S" btw. > > Therefore since sprinklers are not required he is happy with corridor > only. > I of course informed him of the "if you go you have to go all the way" > requirement and he blew me off and there we are. > > We will not do this project as is, I was just trying to get answers > before I > stuck my foot in my mouth again. > > Thank you, > Greg McGahan > > Living Water Fire Protection, LLC > 1160 McKenzie Road > Cantonment, FL 32533 > 850-937-1850 > Fax: 850-937-1852 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum To Unsubscribe, send an email to:[EMAIL PROTECTED] (Put the word unsubscribe in the subject field)