What's to defend?  The building doesn't require any sprinklers at all.
I've yet to see a protected mini-warehouse facility, even those built to
be occupied for business purposes adjacent to storage units.  

If there's still a level of discomfort either pass on the job or put
disclaimers on the drawings and bid stating that the sprinkler system
does not comply with the intent of XYZ Code and Standards for a fully
sprinkled facility and that you as the designer/installer will not
guarantee it's function for the protection of the building, it's
contents or occupants, blah, blah blah.....




Craig L. Prahl, CET   
Fire Protection Group
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[EMAIL PROTECTED]
http://www.ch2m.com 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Greg
McGahan
Sent: Thursday, May 29, 2008 4:37 PM
To: [email protected]
Subject: RE: partial system

I understand that, but do I really want to try to defend us in the event
of a fire that starts in a non-sprinklered storage unit and overruns the
sprinklers in the corridor?

Maybe in another type of occupancy; but I have helped people move before
and I have seen the partially filled plastic gas cans and lawnmowers,
weedeaters and gas grill LP bottles, etc in these units.

Scary to me.

Thank you,
Greg McGahan

Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
Fax: 850-937-1852


-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Ed Kramer
Sent: Thursday, May 29, 2008 3:22 PM
To: [email protected]
Subject: RE: partial system

Greg, NFPA 13 recognizes that under certain conditions, partial
sprinkler systems may be installed as allowed or required by other
standards or codes.
Section 8.1 and 8.1.1 (07) along with A.8.1 and A.8.1.1 and the
commentary in the handbook will give you the details.

Ed Kramer
Littleton, CO

> -----Original Message-----
> From: [EMAIL PROTECTED] [mailto:sprinklerforum-

> [EMAIL PROTECTED] On Behalf Of Greg McGahan
> Sent: Thursday, May 29, 2008 1:52 PM
> To: [email protected]
> Subject: RE: partial system
> 
> I am not sure exactly what their purpose is.
> 
> The chief building inspector says that they do not have to protect the

> building at all because the arch. Has compartmentalized the building 
> into 4
> - 3,000 sq ft compartments which kicks them out of the greater than 30

> people chart.
> 
> The building is classified as "S" btw.
> 
> Therefore since sprinklers are not required he is happy with corridor 
> only.
> I of course informed him of the "if you go you have to go all the way"
> requirement and he blew me off and there we are.
> 
> We will not do this project as is, I was just trying to get answers 
> before I stuck my foot in my mouth again.
> 
> Thank you,
> Greg McGahan
> 
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> Fax: 850-937-1852

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email
to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/mailman/listinfo/sprinklerforum

To Unsubscribe, send an email to:[EMAIL PROTECTED]
(Put the word unsubscribe in the subject field)

Reply via email to