Correct. Emphasis in CAPS.

2009 IBC

[F] 903.3.1.2.1 Balconies and decks. Sprinkler protection
shall be provided for exterior balconies, decks
and ground floor patios of dwelling units where the
building is of Type V construction, PROVIDED THERE IS A
ROOF OR DECK ABOVE. Sidewall sprinklers that are used
to protect such areas shall be permitted to be located
such that their deflectors are within 1 inch (25 mm) to
6 inches (152 mm) below the structural members and
a maximum distance of 14 inches (356 mm) below the
deck of the exterior balconies and decks that are constructed
of open wood joist construction.

Hope that helps


John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Williams
Sent: Thursday, August 04, 2011 12:07 PM
To: [email protected]
Subject: RE: sprinkler heads in exterior decks or balconies

I believe the point is to protect the structure above from a fire below. No
balcony or roof, no exterior sprinkler required.

David Toshio Williams, PE, LEED-AP O+M
High Performance Projects Principal

LHB, Inc. | PERFORMANCE DRIVEN DESIGN


-----Original Message-----
From: Joel Chaim [mailto:[email protected]] 
Sent: Thursday, August 04, 2011 10:30 AM
To: [email protected]
Subject: sprinkler heads in exterior decks or balconies

I'm trying to get clarification already for a while regarding sprinklers on
exterior decks, balconies & ground floor patios my questions are as follows:


 

.         Ground floor patios without a roof on top of it, where do I place
the sprinkler head?

.         Are terraces required to have a sprinkler head?

.         What is the purpose of installing a sprinkler head below the decks
if I want to protect the deck area?

 

I tried contacting New York state DOB and I never got a straight answer, I
looked up the IBC in different states and they added the words "provided
there is a roof above the deck"  looks to me that there is some
typographical error error in this section

 

 

 

 

SECTION OF FIRE CODE OF NYS CODE:

 

FCNYS  903.3.1.2.1 Balconies and decks. Sprinkler protection shall be
provided for exterior balconies, decks and ground floor patios of dwelling
units where the building is of Type V construction. Sidewall sprinklers that
are used to protect such areas shall be permitted to be located such that
their deflectors are within 1 inch (25 mm) to 6 inches (152 mm) below the
structural members and a maximum distance of 14 inches (356 mm) below the
deck of the exterior balconies and decks that are constructed of open wood
joist construction.

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to