2009 IBC

201.4 Terms not defined. Where terms are not defined
through the methods authorized by this section, such terms
shall have ordinarily accepted meanings such as the context implies.

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, August 04, 2011 12:09 PM
To: [email protected]
Subject: Re: sprinkler heads in exterior decks or balconies

Drucker will probably have better answers but:

When you say roof above do you mean deck above? If the latter (and this
would apply to roof also) I've successfully argued against in that there's
no way to collect heat and so no purpose and unsuccessfully argued being
countered with burning siding and the head being eventually opened by direct
impingement.

What distinguishes a terrace from a deck? Is this real estate speak?

You're protecting the siding and the deck structure above by minimizing the
intensity of fire below. I believe the purpose is to minimize the threat
from barbecues and deck furniture and a fire becoming intense enough to
breach the exterior and enter the structure, particularly the floor cavity.

On Thu, Aug 4, 2011 at 8:30 AM, Joel Chaim
<[email protected]>wrote:

> I'm trying to get clarification already for a while regarding sprinklers
on
> exterior decks, balconies & ground floor patios my questions are as
> follows:
>
>
>
>
> .         Ground floor patios without a roof on top of it, where do I
place
> the sprinkler head?
>
> .         Are terraces required to have a sprinkler head?
>
> .         What is the purpose of installing a sprinkler head below the
> decks
> if I want to protect the deck area?
>
>
>
> I tried contacting New York state DOB and I never got a straight answer, I
> looked up the IBC in different states and they added the words "provided
> there is a roof above the deck"  looks to me that there is some
> typographical error error in this section
>
>
>
>
>
>
>
>
>
> SECTION OF FIRE CODE OF NYS CODE:
>
>
>
> FCNYS  903.3.1.2.1 Balconies and decks. Sprinkler protection shall be
> provided for exterior balconies, decks and ground floor patios of dwelling
> units where the building is of Type V construction. Sidewall sprinklers
> that
> are used to protect such areas shall be permitted to be located such that
> their deflectors are within 1 inch (25 mm) to 6 inches (152 mm) below the
> structural members and a maximum distance of 14 inches (356 mm) below the
> deck of the exterior balconies and decks that are constructed of open wood
> joist construction.
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to