How about a lawn sprinkler that pops up through the gaps in the deck planking 
when it goes off? (knew I'd find a use for one of those....)


At 11:01 AM 8/5/2011, you wrote:
>While I'm tempted to say old-style sprinklers as still used in fur vaults and 
>roundhouses 
>(doesn't everyone do three or four of these a year?) 
>Half the water up, half down-
>But by controlling the fire below the deck above, you're protecting it by 
>controlling the fire below that threatens it.
>
>
>George L.  Church, Jr., CET  
>Rowe Sprinkler Systems, Inc.
>PO Box 407, Middleburg, PA 17842
>877-324-ROWE       570-837-6335 fax
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Joel Chaim
>Sent: Friday, August 05, 2011 10:06 AM
>To: [email protected]
>Subject: RE: sprinkler heads in exterior decks or balconies
>
> 
>
>Where I'm missing clarification is, how do I provide deck protection when I 
>place the sprinkler head under the it?
>
> 
>
>It says in the first sentence of the code (903.3.1.2.1 Balconies and decks.
>"Sprinkler protection shall be provided for exterior balconies, decks and 
>ground floor patios of dwelling units where the building is of Type V
>construction.) and then it explains how (Sidewall sprinklers that are used to 
>protect such areas shall be permitted to be located such that their deflectors 
>are within 1 inch (25 mm) to 6 inches (152 mm) below the structural members 
>and a maximum distance of 14 inches (356 mm) below the deck of the exterior 
>balconies and decks that are constructed of open wood joist construction." [F])
>
> 
>
>
> 
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to