Jamey,
Not sure about the specific instructions below for their RiserManifold
used as a sectional floor control assembly? If so then the instructions
would pertain to the semi annual NFPA 25 requirements not related to the
Main Drain test on the inbound system line.
Jim

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jamey
Prentice
Sent: Wednesday, April 11, 2012 4:21 PM
To: [email protected]
Subject: RE: main drain test

This one has always confused me, If you are not required to perform a
residual drain test on each sectional valve assembly why does the
manufacturers literature state to do so? Have included Tyco's
requirements for reference:
The following inspection procedure must be performed as indicated, in
addition to any specific requirements of the NFPA, and any impairment
must be immediately corrected.
Alarm/Flow Test Procedure
Step 1. Place the test & drain Valve in the "test" position.
Step 2. Fully open the drain valve. Make certain that drainage water
will not cause any damage or injury.
Step 3. Verify operation of associated alarms.
Step 4. Close the drain valve.
Step 5. Place the test & drain Valve in the "drain" position.
Step 6. Verify that the residual (flowing) pressure indicated by the
pressure gauge is no less that originally recorded for the system when
it was first installed.
Step 7. Close the drain valve.
Step 8. Verify that the static (not flowing) pressure indicated by the
pressure gauge is no less that originally recorded for the system when
it was first installed.

Jamey

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron
Greenman
Sent: Wednesday, April 11, 2012 3:06 PM
To: [email protected]
Subject: Re: main drain test

Drains at floor control valves are auxiliary drains regardless of the
sign you put on it. It's purpose is to drain the water beyond the
sectional control valve. If you have a flow switch on each section then
you need an inspectors test port and it needs a sight glass (if
discharge cannot be
seen) with an appropriate orifice (k factor) for tresting the flow
switch.
A test and drain fitting will properly have two different flow points on
the
valve: the first flows water through the orifice and the second fully
opens the valve.

On Wed, Apr 11, 2012 at 11:03 AM, Greg McGahan
<[email protected]>wrote:

> Well, that changes my perspective a but doesn't it.
>
> On Wed, Apr 11, 2012 at 1:02 PM, Greg McGahan <[email protected]>
> wrote:
>
> > The main drain test doesn't necessarily verify the operation of the 
> > flow switch. If it does, then usually it is a test and drain. And in

> > many
> cases,
> > there is not a huge difference in flow between the 1/2" orifice on 
> > test
> and
> > the full 1" orifice when on drain if it is being fed from a stand 
> > pipe
> with
> > a pump.
> >
> > We flow them all, but we get asked why we are flowing so much water 
> > when the previous inspectors did not. Of course we give them the 
> > proper answer about doing things right, but I wanted to check
ourselves.
> >
> >
> > Greg
> >
> > On Wed, Apr 11, 2012 at 12:54 PM, <[email protected]> wrote:
> >
> >> If the individual floor control valves have their own flow switches

> >> flowing only one system wouldn't provided verification of operation

> >> of
> the
> >> individual flow switches.
> >>
> >>
> >>
> >> Craig L. Prahl, CET
> >> Fire Protection
> >> CH2MHILL
> >> Lockwood Greene
> >> 1500 International Drive
> >> Spartanburg, SC  29304-0491
> >> Direct - 864.599.4102
> >> Fax - 864.599.8439
> >> CH2MHILL Extension  74102
> >> [email protected]
> >>
> >>
> >>
> >> -----Original Message-----
> >> From: [email protected] [mailto:
> >> [email protected]] On Behalf Of Greg McGahan
> >> Sent: Wednesday, April 11, 2012 1:47 PM
> >> To: [email protected]
> >> Subject: main drain test
> >>
> >> When you have a building with multiple floor control valves I have 
> >> the following question:
> >>
> >> If the intent of the main drain test is to test the supply, can you

> >> accomplish that by flowing the largest or the furtherest from the 
> >> riser instead of flowing each one individually?
> >>
> >> Thanks,
> >>
> >> --
> >> Greg McGahan
> >> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> >> 1160 McKenzie Road
> >> Cantonment, FL 32533
> >> 850-937-1850
> >> fax 850-937-1852
> >> -------------- next part -------------- An HTML attachment was 
> >> scrubbed...
> >> URL: <
> >>
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hments/20120411/6df53a7f/attachment.html
> >> >
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >
> >
> >
> > --
> > Greg McGahan
> > Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> > 1160 McKenzie Road
> > Cantonment, FL 32533
> > 850-937-1850
> > fax 850-937-1852
> >
> >
>
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC <http://www.livingwaterfp.com>
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> -------------- next part -------------- An HTML attachment was 
> scrubbed...
> URL: <
> http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attac
> hments/20120411/b42490ac/attachment.html
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach
ment
s/20120411/e1e10bd2/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to