The floor control valve for all intents and purposes is going the way of the dodo bird. Starting with the next edition, each floor for building 3 stories and above must be set-up as an individual system. It's also amusing if you follow the current criteria trail, there is nothing that dictates the floor assembly displayed in A.8.17.4.2(b) is currently required (even on a high-rise)!!!

Roland


On Apr 12, 2012, at 5:08 AM, Morey, Mike wrote:

From NFPA 25 2011:
3.3.7.2 Sectional Drain. A drain lo cated beyond a sectional control valve that drains only a portion of the system (e.g., a drain located beyond a floor control valve on a multistory building).

Interestingly there is a conflicting entry in NFPA 13 2010 that probably should be addressed if this is the way we're going (not requiring full flow main drain tests @ floor controls): 8.17.3.1 A pressure gauge with a connection not smaller than 1/4 in. (6 mm) shall be installed at the system main drain, at each main drain associated with a floor control valve, and on the inlet and outlet side of each pressure-reducing valve.