So each floor will have a separate riser instead of using a combined standpipe 
riser?

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, April 12, 2012 10:59 AM
To: [email protected]
Subject: Floor control valve

The floor control valve for all intents and purposes is going the way  
of the dodo bird. Starting with the next edition, each floor for  
building 3 stories and above must be set-up as an individual system.   
It's also amusing if you follow the current criteria trail, there is  
nothing that dictates the floor assembly displayed in A.8.17.4.2(b) is  
currently required (even on a high-rise)!!!

Roland


On Apr 12, 2012, at 5:08 AM, Morey, Mike wrote:

> From NFPA 25 2011:
> 3.3.7.2 Sectional Drain. A drain lo cated beyond a sectional control  
> valve that drains only a portion of the system (e.g., a drain  
> located beyond a floor control valve on a multistory building).
>
> Interestingly there is a conflicting entry in NFPA 13 2010 that  
> probably should be addressed if this is the way we're going (not  
> requiring full flow main drain tests @ floor controls):
> 8.17.3.1 A pressure gauge with a connection not smaller than 1/4 in.  
> (6 mm) shall be installed at the system main drain, at each main  
> drain associated with a floor control valve, and on the inlet and  
> outlet side of each pressure-reducing valve.
>
>
> Mike Morey, SET, CFPS
> Sprinkler Designer

-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20120412/c14b2722/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to