Ok, but you still haven't explained the intention of this proposed change.  So 
what are they expecting to be provided?


"The floor control valve for all intents and purposes is going the way of the 
dodo bird. Starting with the next edition, each floor for  
building 3 stories and above must be set-up as an individual system.   
It's also amusing if you follow the current criteria trail, there is nothing 
that dictates the floor assembly displayed in A.8.17.4.2(b) is currently 
required (even on a high-rise)!!!

Roland"

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, April 12, 2012 11:29 AM
To: [email protected]
Subject: Re: Floor control valve

The combined standpipe/sprinkler riser complies with the definition  
for a system so no change.  No change on zoning.  Things wil still be  
done as you see today for high-rises but it will actually be stated  
(and of course applied to mid-rises as well).

Bullseye Mike.  You aptly did not identify a water flow switch per  
floor as part of the high-rise requirements.  Fortunately that as  
never been challenged (and everyone provided one) but other than a  
reference in the 907 section of the IBC on fire alarms, nada.

Roland



On Apr 12, 2012, at 8:01 AM, <[email protected]> wrote:

> So each floor will have a separate riser instead of using a combined  
> standpipe riser?
>
> Craig L. Prahl, CET