The combined standpipe/sprinkler riser complies with the definition
for a system so no change. No change on zoning. Things wil still be
done as you see today for high-rises but it will actually be stated
(and of course applied to mid-rises as well).
Bullseye Mike. You aptly did not identify a water flow switch per
floor as part of the high-rise requirements. Fortunately that as
never been challenged (and everyone provided one) but other than a
reference in the 907 section of the IBC on fire alarms, nada.
Roland
On Apr 12, 2012, at 8:01 AM, <[email protected]> wrote:
So each floor will have a separate riser instead of using a combined
standpipe riser?
Craig L. Prahl, CET