Mark,

The water supply requirements specified in Fire Code 507 and Appendix B are 
provided by any means "approved" by the fire code official. Generally speaking, 
fire departments seek a "reliable" water supply. In most instances the public 
water utility is the only means of a reliable water supply.

The fire flow requirements specified in Appendix B refer to the amount of water 
available, at fire hydrants, for fire fighting purposes. If a single fire 
hydrant cannot achieve the required fire flow fire code officials will 
typically permit simultaneous flows of multiple fire hydrants. The caveat here 
is a limitation on how many fire hydrants the fire code official will allow to 
be flowed. Generally, one hydrant for fire flows less than 2000 gpm, two 
hydrants for greater than 2000 gpm, and three hydrants for greater than 3000 
gpm. I'm not aware of any AHJ that allows more than three fire hydrants to be 
flowed. If private on-site fire hydrants are required to supplement available 
public fire hydrants a fire pump may be necessary to provide the correct gpm.

I hope this clarifies the issue for you.

Galen Taylor
Fire Prevention Engineering
County of Los Angeles Fire Department
323-890-4339
[email protected]
________________________________________
From: Sprinklerforum [[email protected]] on behalf 
of [email protected] [[email protected]]
Sent: Friday, December 05, 2014 6:12 PM
To: [email protected]
Subject: A Poll of the Experienced

Over this weekend I'd like to ask the opinion of those forumites experienced in 
the reading and understanding of the "International Fire  Code" on the topic of 
"Fire Flow" described in Chapter 5, and further prescribed in Appendix B. Is 
the available flow rate and residual pressure referenced, intended to describe 
these values of the municipal or private water supply available to the building 
site? Or, the minimum output of any fire pump associated specifically with the 
automatic sprinkler system in the building?
Any takers? Questions? Clarifications?
Thanks for any answers.

Mark at Aero
602 820-7894

Sent from my iPhone

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to